I'm using NUT 2.8.2_6 package in pfsense 25.11.1 and it successfully shut down's devices and after that finally the sockets on UPS. The problem comes when the system gets it's power back and the firewall start's to boot up... after some time (~3 min) it for some reason shut down's sockets on the ups without warning... This is really undesirable because it defeats the whole point of having power backup.
I've been able to verify it's pfsense who is doing that by leaving the firewall unplugged after UPS reconnect's power... Everything works until pfsense boot's up again... I've also been able to reproduce it without any modifications in advanced section of NUT package.
My UPS is Back-UPS BGM2200-MSX and it's connected using USB cable with usbhid-ups driver.
PS: I was doing the test in quick succession after shutdown... the UPS seems to ignore my ondelay=130 parametr...
-
@DomV said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
it successfully shut down's devices and after that finally the sockets on UPS
Can you clarify what this means please? Specifically "successfully shut down's devices" and "the sockets on UPS"? A quick look at that UPS does not show any switched sockets...
The phrase "I've been able to verify it's pfsense who is doing that by leaving the firewall unplugged" is a strong of statement. I don't think enough is known yet to make that blanket statement, particularly since pfSense itself doesn't actually do anything with the UPS. It could be the NUT driver running on pfSense, or the UPS itself.
-
@dennypage After it send's shutdown commands to servers and they turn off it than proceeds with the shutdown process for pfsense itself. After that it sends killpower command to the UPS and it's cut's power after predefined 120 seconds.
Broadcast Message from root@pfsense.REDACTED.arpa (no tty) at 1:43 CET... UPS apc on battery Broadcast Message from root@pfsense.REDACTED.arpa (no tty) at 1:43 CET... Executing automatic power-fail shutdown Broadcast Message from root@pfsense.REDACTED.arpa (no tty) at 1:43 CET... Auto logout and shutdown proceeding *** FINAL System shutdown message from root@pfsense.REDACTED.arpa *** System going down IMMEDIATELY Broadcast Message from root@pfsense.REDACTED.arpa (/dev/console) at 1:45 CET... NUT killing power... Connection to 192.168.1.1 closed by remote host. Connection to 192.168.1.1 closed. -
@DomV said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
After it send's shutdown commands to servers and they turn off it than proceeds with the shutdown process for pfsense itself. After that it sends killpower command to the UPS and its cut's power after predefined 120 seconds.
FWIW, NUT doesn't actually send a shutdown command to remote clients -- Remote clients actually make their own shutdown decisions based on reported status (such as low battery indication), run time remaining, and battery percentage remaining.
We can remove the remote clients from consideration. You can confirm by disconnecting the remote clients from the NUT upsd running on the pfSense system. In fact, I recommend that you do this to simplify your testing environment.
Also, the command to kill the power is send by nut before instructing the host OS (pfSense in this case) to shut down. The shutdown delay implemented by the UPS is to allow the OS to complete its shutdown. The shutdown delay is usually 20 seconds. Have you changed this value in the UPS? A shutdown delay of 120 seconds is quite large...
If you have changed the shutdown delay, have you also configured the startup delay? Most UPSs do not do this automatically, so if you change one you have to change both. And sometimes other related parameters.
My recommendation for how to proceed is to remove any advanced configuration you may have for NUT, restore the UPS's default values, and begin testing from there.
-
@DomV said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
UPS apc on battery
You see this message on the console access while this very same UPS is connected to the main electricity, 120 or 230 V ?
Before cycling the batterie, or even the entire UPS, you two should have a talk.
Get the name of your UPS - get the name you've used here :[25.11.1-RELEASE][root@pfSense.bhf.tld]/root: cat /usr/local/etc/nut/upsmon.conf MONITOR UPS 1 local-monitor 9b661f17bf95d56f892e master .....This makes sense as :


You need more :
[25.11.1-RELEASE][root@pfSense.bhf.tld]/root: cat /usr/local/etc/nut/upsd.users [admin] password=e8f2009d2a5ea51adf82 actions=set instcmds=all [local-monitor] password=9b661f17bf95d56f892e upsmon master .....Here you see who is the 'admin user : it's admin, and also the password of this admin user.
To know what command your UPS accepts, easy : no authentifcaition is needed : just ask :
[25.11.1-RELEASE][root@pfSense.bhf.tld]/root: upscmd -l UPS Instant commands supported on UPS [UPS]: beeper.disable - Disable the UPS beeper beeper.enable - Enable the UPS beeper beeper.mute - Temporarily mute the UPS beeper beeper.off - Obsolete (use beeper.disable or beeper.mute) beeper.on - Obsolete (use beeper.enable) driver.killpower - Tell the driver daemon to initiate UPS shutdown; should be unlocked with driver.flag.allow_killpower option or variable setting driver.reload - Reload running driver configuration from the file system (only works for changes in some options) driver.reload-or-error - Reload running driver configuration from the file system (only works for changes in some options); return an error if something changed and could not be applied live (so the caller can restart it with new options) driver.reload-or-exit - Reload running driver configuration from the file system (only works for changes in some options); exit the running driver if something changed and could not be applied live (so service management framework can restart it with new options) load.off - Turn off the load immediately load.off.delay - Turn off the load with a delay (seconds) shutdown.reboot - Shut down the load briefly while rebooting the UPS shutdown.stop - Stop a shutdown in progress test.battery.start.deep - Start a deep battery test test.battery.start.quick - Start a quick battery test test.battery.stop - Stop the battery testTo actually execute a command, you need the user and password.
Here I execute a quick battery test :[25.11.1-RELEASE][root@pfSense.brit-hotel-fumel.net]/root: upscmd -u admin -p e8f2009d2a5ea51adf82 UPS test.battery.start.quick OKand I detected relay activity in my UPS (an APC also, with just one big green status led).
But there is more :
[25.11.1-RELEASE][root@pfSense.bhf.tld]/root: upsrw -l -u admin -p e8f2009d2a5ea51adf82 ups [battery.charge.low] Remaining battery level when UPS switches to LB (percent) Type: STRING Maximum length: 10 Value: 10 [battery.mfr.date] Battery manufacturing date Type: STRING Maximum length: 10 Value: 2025/06/06 [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: STRING Maximum length: 10 Value: 120 [driver.debug] Current debug verbosity level of the driver program Type: NUMBER Value: 0 [driver.flag.allow_killpower] Safety flip-switch to allow the driver daemon to send UPS shutdown command (accessible via driver.killpower) Type: NUMBER Value: 0 [input.sensitivity] Input power sensitivity Type: STRING Maximum length: 10 Value: low [input.transfer.high] High voltage transfer point (V) Type: STRING Maximum length: 10 Value: 295 [input.transfer.low] Low voltage transfer point (V) Type: STRING Maximum length: 10 Value: 145 [ups.delay.shutdown] Interval to wait after shutdown with delay command (seconds) Type: STRING Maximum length: 10 Value: 20I'm just showing the UPS variables here.
You can also 'set' them, like the "[battery.mfr.date]" which is set to "2025/06/06" and that's the date I changed the batterie in the UPS.This is the command to show the 'status' of your UPS :
[25.11.1-RELEASE][root@pfSense.bhf.tld]/root: upsc UPS battery.charge: 98 battery.charge.low: 10 battery.mfr.date: 2025/06/06 battery.runtime: 1124 battery.runtime.low: 120 battery.type: PbAc battery.voltage: 13.6 battery.voltage.nominal: 12.0 device.mfr: American Power Conversion device.model: Back-UPS BX950MI device.serial: 9B2506A09546 device.type: ups driver.debug: 0 driver.flag.allow_killpower: 0 driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.synchronous: auto driver.state: quiet driver.version: 2.8.2 driver.version.data: APC HID 0.100 driver.version.internal: 0.53 driver.version.usb: libusb-1.0.0 (API: 0x1000102) input.sensitivity: low input.transfer.high: 295 input.transfer.low: 145 input.voltage: 232.0 input.voltage.nominal: 230 ups.beeper.status: disabled ups.delay.shutdown: 20 ups.firmware: 295202G -302202G ups.load: 27 ups.mfr: American Power Conversion ups.mfr.date: 2025/02/21 ups.model: Back-UPS BX950MI ups.productid: 0002 ups.realpower.nominal: 520 ups.serial: 9B2506A09546 ups.status: OL CHRG ups.test.result: Done and passed ups.timer.reboot: 0 ups.timer.shutdown: -1 ups.vendorid: 051dWhere "ups.status: OL CHRG" means : UPS is OnLine (so powered) and CHaRGing.
"input.voltage.nominal: 230" means my UPS is powered.
The battery state is at 98 %, as I just executed a test, a % or two are missing.Why all this info ?
Now you know how to question your UPS, and check in what state it is.
An UPS that signals 'UPS apc on battery' means that "NUT", the software that runs on pfSense actually communicated with the UPS, and it detected that it wasn't powered.
If it was powered, it's time to check the battery fuse, if there is one - my APC has one.
Check the battery tension. Etc.
And always : even if the UPS doesn't have a big load hooked up to it, change the battery after 36 months max. Normally, when I buy my APC's, I replace the batterie ones. After 6 years I recycle them to places where UPS has less priority. After 9 years => Land fill. -
@dennypage UPS shows these values as usable:
beeper.disable - Disable the UPS beeper beeper.enable - Enable the UPS beeper beeper.mute - Temporarily mute the UPS beeper beeper.off - Obsolete (use beeper.disable or beeper.mute) beeper.on - Obsolete (use beeper.enable) driver.killpower - Tell the driver daemon to initiate UPS shutdown; should be unlocked with driver.flag.allow_killpower option or variable setting driver.reload - Reload running driver configuration from the file system (only works for changes in some options) driver.reload-or-error - Reload running driver configuration from the file system (only works for changes in some options); return an error if something changed and could not be applied live (so the caller can restart it with new options) driver.reload-or-exit - Reload running driver configuration from the file system (only works for changes in some options); exit the running driver if something changed and could not be applied live (so service management framework can restart it with new options) load.off - Turn off the load immediately load.off.delay - Turn off the load with a delay (seconds) shutdown.reboot - Shut down the load briefly while rebooting the UPS shutdown.stop - Stop a shutdown in progress test.battery.start.deep - Start a deep battery test test.battery.start.quick - Start a quick battery test test.battery.stop - Stop the battery testOutput of upsrw -l:
[battery.charge.low] Remaining battery level when UPS switches to LB (percent) Type: STRING Maximum length: 10 Value: 97 [battery.mfr.date] Battery manufacturing date Type: STRING Maximum length: 10 Value: 1980/01/01 [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: STRING Maximum length: 10 Value: 120 [driver.debug] Current debug verbosity level of the driver program Type: NUMBER Value: 0 [driver.flag.allow_killpower] Safety flip-switch to allow the driver daemon to send UPS shutdown command (accessible via driver.killpower) Type: NUMBER Value: 0 [input.sensitivity] Input power sensitivity Type: STRING Maximum length: 10 Value: medium [input.transfer.high] High voltage transfer point (V) Type: STRING Maximum length: 10 Value: 298 [input.transfer.low] Low voltage transfer point (V) Type: STRING Maximum length: 10 Value: 176 [ups.delay.shutdown] Interval to wait after shutdown with delay command (seconds) Type: STRING Maximum length: 10 Value: 20I tried for example changing the battery mfr date:
upsrw -s "battery.date=2025November17" -u admin "apc@192.168.1.1" Password: Unexpected response from upsd: ERR ACCESS-DENIEDadmin should have all the rights but somehow getting this...
-
@dennypage I removed all my settings an re-ran my test and it was behaving the same... shutdown was alright (default settings tho) but when it than boot up it cut the power after 4 minutes from boot for no reason. Have to mention that at that point it was in this mode: OL CHRG LB
-
@DomV battery.charge.low is set to 97%. Try changing it to something like 15% via upsrw or the APC PowerChute utility.
NUT triggers a shutdown when the runtime or charge drop below battery.runtime.low or battery.charge.low, respectively. With the current settings, if NUT is started with anything less than 97% charge, NUT may be shutting down the host.
For the UPS outlets turning off, there's also configuration on the UPS (websearch for "apc backups minimum battery level for restart"). You may be able to check/set those with upsrw or via the APC PowerChute utility.
-
I've been able to install nut on raspberry pi and with default config it works like it should... I doesn't turn the sockets off after boot... that's wierd...
-
@DomV said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
I've been able to install nut on raspberry pi and with default config it works like it should... I doesn't turn the sockets off after boot... that's wierd...
What are the outputs of
upscandupsrw -lon the Pi? -
This is upsc on the pi:
battery.charge: 91 battery.charge.low: 97 battery.mfr.date: 1980/01/01 battery.runtime: 9836 battery.runtime.low: 120 battery.type: PbAc battery.voltage: 27.7 battery.voltage.nominal: 24.0 device.mfr: American Power Conversion device.model: Back-UPS BGM2200-MSX device.serial: REDACTED device.type: ups driver.debug: 0 driver.flag.allow_killpower: 0 driver.name: usbhid-ups driver.parameter.bus: 001 driver.parameter.busport: 002 driver.parameter.device: 003 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.product: Back-UPS BGM2200-MSX FW:481600G5-481700G2 driver.parameter.productid: 0002 driver.parameter.serial: REDACTED driver.parameter.synchronous: auto driver.parameter.vendor: American Power Conversion driver.parameter.vendorid: 051D driver.state: quiet driver.version: 2.8.1 driver.version.data: APC HID 0.100 driver.version.internal: 0.52 driver.version.usb: libusb-1.0.28 (API: 0x100010a) input.sensitivity: medium input.transfer.high: 298 input.transfer.low: 176 input.transfer.reason: input voltage out of range input.voltage: 241.0 input.voltage.nominal: 230 ups.beeper.status: disabled ups.delay.shutdown: 20 ups.firmware: 481600G5-481700G2 ups.load: 0 ups.mfr: American Power Conversion ups.mfr.date: 2025/11/17 ups.model: Back-UPS BGM2200-MSX ups.productid: 0002 ups.realpower.nominal: 1320 ups.serial: REDACTED ups.status: OL CHRG LB ups.test.result: Done and passed ups.timer.reboot: 0 ups.timer.shutdown: -1 ups.vendorid: 051dThis is upsrw -l on the pi:
[battery.charge.low] Remaining battery level when UPS switches to LB (percent) Type: STRING Maximum length: 10 Value: 97 [battery.mfr.date] Battery manufacturing date Type: STRING Maximum length: 10 Value: 1980/01/01 [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: STRING Maximum length: 10 Value: 120 [driver.debug] Current debug verbosity level of the driver program Type: NUMBER Value: 0 [driver.flag.allow_killpower] Safety flip-switch to allow the driver daemon to send UPS shutdown command (accessible via driver.killpower) Type: NUMBER Value: 0 [input.sensitivity] Input power sensitivity Type: STRING Maximum length: 10 Value: medium [input.transfer.high] High voltage transfer point (V) Type: STRING Maximum length: 10 Value: 298 [input.transfer.low] Low voltage transfer point (V) Type: STRING Maximum length: 10 Value: 176 [ups.delay.shutdown] Interval to wait after shutdown with delay command (seconds) Type: STRING Maximum length: 10 Value: 20 -
@marcg said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
battery.charge.low is set to 97%. Try changing it to something like 15% via upsrw or the APC PowerChute utility.
Good eye!
This would certainly cause the behavior mentioned.
@DomV, you should reset your UPS variables to default values. Generally, you should leave the variables at default values unless you have a very good reason to change them.
You can try restoring the default values via upsrw, but if that doesn't work then check with the manual or manufacturer on how to reset your UPS.
@DomV said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
I tried for example changing the battery mfr date:
upsrw -s "battery.date=2025November17" -u admin "apc@192.168.1.1"
Password:
Unexpected response from upsd: ERR ACCESS-DENIEDYou should not expect this to work as
battery.dateis not an available variable listed by upsrw. Trybattery.mfr.date. -
@DomV battery.charge.low is showing as 97% on the Pi, too. You may want to lower that to prevent future issues.
-
@marcg Because I think that this is the default value for this UPS. And I still really don't understand why with the pi it works correctly even with this setting.
@dennypage Also, this worked
upsrw -s "battery.mfr.date=2025/11/17" -u admin "apc@192.168.1.100"of course it did... ahh -
@DomV said in NUT server - After power is turned back on, pfsense shut's down sockets without warning for no reason:
Because I think that this is the default value for this UPS. And I still really don't understand why with the pi it works correctly even with this setting.
The default for low battery on APC UPSs is 10%. 97% would not make sense to use as a default setting on any UPS.
As to the Pi, there are any number of configuration reasons that would result in a change of behavior. If you want to explore that further, I recommend the NUT Users mailing list.
-