    Netgate 8300 Appliance and pure sine wave UPS

    Scheduled Pinned Locked Moved Official Netgate® Hardware
    22 Posts 8 Posters 5.4k Views 9 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • P Offline
      philippe richard
      last edited by

      Re: Newly purchased Netgate 8300 Appliance.

      Hello. I am having the same or a similar issue with my 8300s. The Netgate power supplies are plugged into two different UPS units, both of the same model, which provide a pure sine wave output. However, whenever there is a power outage, both firewalls go into a fault state.

      chpalmerC P 2 Replies Last reply Reply Quote 0
      • chpalmerC Offline
        chpalmer @philippe richard
        last edited by

        @philippe-richard What model UPS's?

        It is common that devices that claim to be pure sine-wave are not.

        Triggering snowflakes one by one..
        Primary- Intel(R) Pentium(R) CPU G4400 @ 3.30GHz on an M470 WG box. pfSense CE 2.8.1
        Lab Unit- Intel(R) Core(TM) i5-4590T CPU @ 2.00GHz on an M400 WG box. pfSense+

        P 1 Reply Last reply Reply Quote 1
        • P Offline
          philippe richard @chpalmer
          last edited by

          @chpalmer "Hello, this is a Tripp Lite SMART3000RMXL2U UPS unit.

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD Offline
            dennypage
            last edited by

            There is a difference between the output type (simulated sine wave, pure sine wave, etc.) and the amount of time that it takes to transfer to battery power.

            Different manufacturers use slightly different terms, but in general there are three types:

            • Offline / Standby
            • Interactive / Line Interactive
            • Online / Double Conversion

            Each of these types may offer a "pure sine wave" output, but they can have significantly different transfer times in the event of mains failure. It is the transfer time that is likely triggering the fault.

            Here are a couple of links for that offer further explanation:

            Wikipedia - Uninterruptible power supply
            Eaton - Choosing the optimal UPS topology
            FS - Comparison of UPS Topologies

            1 Reply Last reply Reply Quote 0
            • dennypageD Offline
              dennypage @philippe richard
              last edited by

              @philippe-richard said in Netgate 8300 Appliance and pure sine wave UPS:

              Tripp Lite SMART3000RMXL2U

              That's a Line Interactive model. The spec sheets says that the unit is pure sine wave, with a transfer time of "1-4ms for normal mode, >5ms for sensitive mode."

              Is it in normal mode?

              N P 2 Replies Last reply Reply Quote 0
              • N Offline
                netblues @dennypage
                last edited by

                For a typical router appliance as this, anything below 20 ms wouldn't be a problem.

                Can you elaborate on fault state?
                It hangs? It reboots?.

                Are these two on the same place ?
                Interconnected?
                Looks like a grounding issue.

                dennypageD P 2 Replies Last reply Reply Quote 0
                • dennypageD Offline
                  dennypage @netblues
                  last edited by

                  @netblues said in Netgate 8300 Appliance and pure sine wave UPS:

                  Looks like a grounding issue.

                  Could be. Or a floating neutral, swapped hot/neutral, etc. But you would expect the UPS itself to report a fault on these types of issues if it's the mains wiring.

                  Although, one interesting way that various issues materialize is people testing the UPS by pulling the plug out of the wall --which of course breaks the ground connection. 😊

                  luckman212L 1 Reply Last reply Reply Quote 1
                  • P Offline
                    Patch @philippe richard
                    last edited by

                    @philippe-richard said in Netgate 8300 Appliance and pure sine wave UPS:

                    whenever there is a power outage, both firewalls go into a fault state.

                    Does the power supply have a data connection as well as a power connection to the Netgate 8300?

                    If so to separate a Data processing fault from a power connection fault you could

                    • connect the 8300 to the mains power then simulate a loss of power to the UPS with ongoing data connection

                    • leave the 8300 connected to the UPS but disconnect the data connection and again simulate power loss to the UPS

                    N P P 3 Replies Last reply Reply Quote 0
                    • N Offline
                      netblues @Patch
                      last edited by

                      It really doesn't matter what kind of ups it is.
                      A netgate router appliance (and almost all such devices) nowdays operate on a universal switching psu that usually can work from 90volts up to 250 without issues.
                      Sine, simulated sine or even square, it doesn't matter.
                      As for transfer time, since this isnt a high power device, there is enough capacitance inside the psu to tackle even 100ms of outage/brown out.
                      In any case tripp lite is a known maker and unless it is faulty (which is strange for TWO units) it should be fine.

                      If the two routers are connected to different ups (for redundancy) at the same location, and end up interconnected via ethernet cables, (expected) then the possibility of ground loops creation, leading into residual current flowing through ethernet ports, becomes a reality.
                      When this happens, lockups occur (or even burned lan ports).
                      Best practices recommend to run a thick (yellow) cable bound to the screws on the chassis of all devices in the rack, which ends up to a dedicated ground. In bigger installations there is a separate "telecoms" ground wiring harness.
                      The rack must also be grounded as per regulations.

                      However its often too common to see networking equipment without ANY grounding
                      When different power sources are used, this becomes critical.

                      P 1 Reply Last reply Reply Quote 0
                      • P Offline
                        philippe richard @dennypage
                        last edited by

                        @dennypage
                        Thank you very much for taking the time to reply. I don't know much about UPS units, but in the web interface configuration, here is what I found: it is set to 'normal' mode.2026-05-25_14-56.png

                        1 Reply Last reply Reply Quote 0
                        • P Offline
                          philippe richard @netblues
                          last edited by

                          @netblues hello,
                          During a power outage, the firewall stops performing its function, as if the entire system were locked up. Access to the 8300s is unresponsive—whether via the web interface or SSH—and the entire network is blocked. The two Netgate units in HA are in the same network rack, and each power supply is fed by two Tripp Lite PDUs (PDUMV20NETLX). Each power supply is connected to a separate PDU, both of which are protected by two Tripp Lite SMART3000RMXL2U UPS units. No other equipment connected to these PDUs has experienced any issues. Both 8300s are properly grounded. The IPMI logs on both Netgate units report no hardware alerts or power supply errors. I had also connected both console ports via screen to log all activity should another failure occur. However, at the time of the latest failure, the console output showed absolutely nothing unusual before the units locked up. The status outputs reveal no anomalies."

                          1 Reply Last reply Reply Quote 0
                          • P Offline
                            philippe richard @Patch
                            last edited by

                            @Patch Hello, no, it does not have those connections.

                            1 Reply Last reply Reply Quote 0
                            • P Offline
                              philippe richard @netblues
                              last edited by

                              @netblues
                              Hello, regarding the HA link, the two Netgate units are not interconnected directly via an Ethernet cable but are connected through a switch. Both 8300s are properly grounded.

                              johnpozJ 1 Reply Last reply Reply Quote 0
                              • P Offline
                                philippe richard
                                last edited by

                                Here is a photo of the two Netgate units during their failure.Image (4).jpeg

                                1 Reply Last reply Reply Quote 0
                                • johnpozJ Offline
                                  johnpoz LAYER 8 Global Moderator @philippe richard
                                  last edited by

                                  @philippe-richard said in Netgate 8300 Appliance and pure sine wave UPS:

                                  not interconnected directly via an Ethernet cable but are connected through a switch

                                  Is this switch on a UPS? Your network is not going to be up if the switches that make up your network are not up.

                                  An intelligent man is sometimes forced to be drunk to spend time with his fools
                                  If you get confused: Listen to the Music Play
                                  Please don't Chat/PM me for help, unless mod related
                                  SG-4860 26.03.1 | Lab VMs 2.8.1, 26.07

                                  P 1 Reply Last reply Reply Quote 0
                                  • P Offline
                                    philippe richard @johnpoz
                                    last edited by

                                    @johnpoz
                                    Hello, yes, the switch is connected to a UPS. The entire architecture is on UPS power (firewall, switch, routers, and servers), and in the event of a power outage, only the 8300s end up frozen in a state where nothing works anymore.

                                    1 Reply Last reply Reply Quote 0
                                    • stephenw10S Offline
                                      stephenw10 Netgate Administrator
                                      last edited by

                                      Anything shown at the console when this happens? Does the IPMI still respond?

                                      P 1 Reply Last reply Reply Quote 0
                                      • P Offline
                                        Patch @Patch
                                        last edited by Patch

                                        said in Netgate 8300 Appliance and pure sine wave UPS:

                                        Does the power supply have a data connection as well as a power connection to the Netgate 8300?

                                        @philippe-richard said in Netgate 8300 Appliance and pure sine wave UPS:

                                        no, it does not have those connections.

                                        So during a prolonged power outage how is the 8300 powered down prior to the battery going flat?

                                        P 1 Reply Last reply Reply Quote 0
                                        • P Offline
                                          philippe richard @stephenw10
                                          last edited by

                                          @stephenw10 Hello, there is nothing displayed on the console. Furthermore, the consoles of both 8300s are physically connected to a PC using the command screen -L -Logfile logfile.txt /dev/ttyUSB0 115200, and there is nothing unusual in the log file, even though both firewalls are running in kernel debug mode. As for IPMI access, I was not on-site during the incident, and since I lost VPN access because of it, I wasn't able to check from that side.

                                          1 Reply Last reply Reply Quote 0
                                          • P Offline
                                            philippe richard @Patch
                                            last edited by

                                            @Patch
                                            Hello, that is also one of the many tasks I need to work on, so that the 8300s shut down gracefully instead of experiencing a hard crash when the battery runs out.

                                            1 Reply Last reply Reply Quote 1