    NUT server and UPS general question

    Scheduled Pinned Locked Moved General pfSense Questions
    71 Posts 6 Posters 14.9k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage @netboy
      last edited by

      @netboy said in NUT server and UPS general question:

      In my case 3 servers....Pick one server as PRIMARY say server 1 and install standard NUT on server 1. Install NUT secondary on server 2 and server 3. Run Remote NUT to the primary. I am going NUTS. In other words this UPS 3 is stand alone "farm" no connection to NUT installed in raspberry PI.

      Server 1 would be the NUT Primary (NUT's new term--previously called master), and would perform the actual control of the UPS. Server 2 & 3 would be Secondaries (previously called slaves), and take their instruction from the Primary. When the Primary says "time to shut down" the Secondaries shut down and disconnect from the Primary, after which the Primary shuts down which kills UPS power.

      Note that you can still "monitor" the the Server 1 UPS using NUT on another host (Pi). You would configure it as a Secondary, but use a power value of 0 to indicated that you are not actually connected to the UPS on Server 1. You can use this approach to monitor all the other UPSs from the Pi as well.

      N 2 Replies Last reply Reply Quote 0
      • dennypageD
        dennypage @netboy
        last edited by

        @netboy said in NUT server and UPS general question:

        It so happens, OMV has a NUT package and I installed it after making sure my UPS is connected to OMV using USB (checked lsusb to make sure the UPS shows up).

        Just about everyone has a NUT package. It's pretty universal.

        Have I got it right so far?

        I believe so.

        N 1 Reply Last reply Reply Quote 0
        • N
          netboy @dennypage
          last edited by

          @dennypage Thank you.... shall read more and figure it out

          1 Reply Last reply Reply Quote 0
          • N
            netboy @dennypage
            last edited by

            This post is deleted!
            1 Reply Last reply Reply Quote 0
            • N
              netboy @dennypage
              last edited by

              @dennypage said in NUT server and UPS general question:

              Server 1 would be the NUT Primary (NUT's new term--previously called master), and would perform the actual control of the UPS. Server 2 & 3 would be Secondaries (previously called slaves), and take their instruction from the Primary. When the Primary says "time to shut down" the Secondaries shut down and disconnect from the Primary, after which the Primary shuts down which kills UPS power.
              Note that you can still "monitor" the the Server 1 UPS using NUT on another host (Pi). You would configure it as a Secondary, but use a power value of 0 to indicated that you are not actually connected to the UPS on Server 1. You can use this approach to monitor all the other UPSs from the Pi as well.

              Very useful info....thanks

              N 1 Reply Last reply Reply Quote 0
              • N
                netboy @netboy
                last edited by netboy

                @netboy dennypage I got everything working....

                Now based on my success I would like to monitor the UPS attached to the Netgate router.

                I earlier installed apc package and it worked fine. I uninstalled the same and installed NUT.

                SSH into netgate and it reported the UPS.
                [22.05-RELEASE][admin@router2100.xxx.local]/root: usbconfig
                ugen0.1: <Marvell XHCI root HUB> at usbus0, cfg=0 md=HOST spd=SUPER (5.0Gbps) pwr=SAVE (0mA)
                ugen1.1: <Marvell EHCI root HUB> at usbus1, cfg=0 md=HOST spd=HIGH (480Mbps) pwr=SAVE (0mA)
                ugen1.2: <American Power Conversion Back-UPS ES 750G FW:841.I4 .D USB FW:I4> at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (2mA)

                My config on the NUT in netgate is as follows:

                5a7e9fdf-ed91-4dea-853c-fa1522b53a98-image.png

                However I am not having any success!!

                9f0d885f-b5d0-453d-ae30-9a47edd0d60a-image.png

                Any tips for troubleshooting?

                After some time in SSH I get this message:

                d40b2c50-d338-438b-a9ea-d0d4c9cb6332-image.png Broadcast Message from root@router2100.480.local
                (no tty) at 12:41 EST...

                UPS netgateUPS is unavailable

                dennypageD 1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage @netboy
                  last edited by

                  @netboy said in NUT server and UPS general question:

                  Any tips for troubleshooting?

                  Yes:

                  1. Remove everything from the Advanced settings section and leave it empty. [FYI: The lines you have are in the wrong section; The USB driver doesn't take a port. Some UPSs don't like to be polled too frequently.] Later, you can add lines to the "Additional configuration lines for upsd.users" section to allow remote access, but even then leave all the other sections empty.

                  2. If you haven't rebooted since you installed NUT, you need to do so. Alternatively, you can do an unplug and replug (see elsewhere in this thread), but the easiest thing to do is to reboot.

                  N 1 Reply Last reply Reply Quote 0
                  • N
                    netboy @dennypage
                    last edited by netboy

                    @dennypage Thanks
                    Followed your advice and it works now ....
                    e5aab3cc-5887-4a08-b410-e72de5115744-image.png
                    I added users to the upsd.users and "pointed" the hosts.conf and upsmon.conf on the raspberry pi.
                    The raspberry pi shows the drop down but when I select the one nothing shows up! Other drop down works like a charm.
                    Any other config I must change in netgate?

                    e0f5129c-0d32-4589-a5f4-42d477607868-image.png

                    The selection of "netgate UPS" does nothing and shows connection failure

                    dennypageD 1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage @netboy
                      last edited by

                      @netboy said in NUT server and UPS general question:

                      The selection of "netgate UPS" does nothing and shows connection failure

                      I note that in one location you have "netgateUPS" and in another you have "netgate UPS". FWIW, I recommend that you stay away from spaces in names.

                      N 1 Reply Last reply Reply Quote 0
                      • N
                        netboy @dennypage
                        last edited by netboy

                        @dennypage Hey dennypage the drop down shows the description as listed in Raspberry Pi hosts.conf

                        MONITOR netgateUPS@192.168.0.1 "Netgate UPS"

                        IMHO, I do not think this is the issue.

                        FYI, i have added the following user in netgate config:
                        [monslave]
                        password = {somepassword}
                        upsmon slave

                        Added the following in upsmon.conf in raspberry pi;

                        MONITOR netgateUPS@192.168.0.1 0 monslave {pswd for monslave} slave

                        dennypageD 1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage @netboy
                          last edited by

                          @netboy Please post your upsd.users and upsmon.conf from both systems.

                          N 1 Reply Last reply Reply Quote 0
                          • N
                            netboy @dennypage
                            last edited by netboy

                            @dennypage
                            Sure here we go...

                            Masked password as xxxx, yyyy and zzzz - BTW there are no spaces in my password:

                            netgate - upsd.users

                            [admin]
                            password = xxxxx
                            actions = set
                            actions = fsd
                            instcmds = ALL

                            [monmaster]
                            password = yyyyy
                            upsmon master

                            [monslave]
                            password = zzzzz
                            upsmon slave

                            pi- upsd.users

                            [admin]
                            password = nnnnnn
                            actions = set
                            actions = fsd
                            instcmds = ALL

                            [monmaster]
                            password = uuuuuuu
                            upsmon master

                            [monslave]
                            password = xxxxx
                            upsmon slave

                            netgate - upsmon.conf
                            blanks no entries

                            pi - upsmon.conf
                            MONITOR netgateUPS@192.168.0.1 0 monslave zzzzz slave

                            Am I missing MONITOR entries in upsmon.conf in netgate?

                            dennypageD 1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage @netboy
                              last edited by

                              @netboy said in NUT server and UPS general question:

                              netgate - upsmon.conf
                              blanks no entries

                              Based upon your prior screenshots, upsmon.conf on the pfSense system cannot be empty.

                              Also, please post ups.conf from both systems.

                              N 1 Reply Last reply Reply Quote 0
                              • N
                                netboy @dennypage
                                last edited by

                                @dennypage
                                I added the following to

                                netgate - upsmon.conf
                                MONITOR netgateUPS@localhost 1 monmaster yyyyy master

                                negate - ups.conf
                                blanks no entries

                                pi- ups.conf
                                [powerStrip]
                                driver = usbhid-ups
                                port = auto
                                vendorid = "051d"
                                productid = "0002"
                                desc = "APC BE600M1 600VA UPS"

                                dennypageD 1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage @netboy
                                  last edited by

                                  @netboy said in NUT server and UPS general question:

                                  I added the following to
                                  netgate - upsmon.conf
                                  MONITOR netgateUPS@localhost 1 monmaster yyyyy master
                                  negate - ups.conf
                                  blanks no entries

                                  Something is wrong. ups.conf cannot be empty, and you should not need to edit upsmon.conf.

                                  Let's restart from the ground up and make sure we have a known, stable base.

                                  Go to Services -> UPS -> Settings.

                                  • Set "UPS Type" to "Local USB"
                                  • Set "UPS Name" to "ups"
                                  • Uncheck the "Enable notifications" box
                                  • Set "Driver" to "usbhid".
                                  • Clear any content in "Extra Arguments to driver"
                                  • Clear any content in all sections of "Advanced sections"

                                  After doing this, press save.

                                  Then, log in via terminal and execute the following:

                                  cat /usr/local/etc/nut/ups.conf
                                  cat /usr/local/etc/nut/upsd.conf
                                  cat /usr/local/etc/nut/upsd.users
                                  cat /usr/local/etc/nut/upsmon.conf
                                  

                                  And post the complete output of each.

                                  N 1 Reply Last reply Reply Quote 1
                                  • N
                                    netboy @dennypage
                                    last edited by netboy

                                    @dennypage
                                    masked passwords

                                    [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/ups.conf
                                    [ups]
                                    driver=usbhid-ups
                                    port=auto
                                    [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/upsd.conf
                                    LISTEN 127.0.0.1
                                    LISTEN ::1
                                    [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/upsd.users
                                    [admin]
                                    password=xxxxx
                                    actions=set
                                    instcmds=all
                                    [local-monitor]
                                    password=xxxxx
                                    upsmon master
                                    [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/upsmon.conf
                                    MONITOR ups 1 local-monitor xxxxx master
                                    SHUTDOWNCMD "/sbin/shutdown -p +0"
                                    POWERDOWNFLAG /etc/killpower
                                    [22.05-RELEASE][admin@router2100.tttt.local]/root:

                                    dennypageD 1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage @netboy
                                      last edited by dennypage

                                      @netboy Okay, that looks much better.

                                      Now add this

                                      [monuser]
                                      password = secret
                                      upsmon slave
                                      

                                      to "Additional configuration lines for upsd.users" in the Advanced settings section.

                                      Now go to this post and follow the instructions to allow access to the NUT port from the LAN interface. I recommend that you choose option 1.

                                      Following that, you can confirm operation by going to the pi and executing the following command:

                                      upsc ups@192.168.0.1
                                      [Based on prior posts, I am assuming that 192.168.0.1 is the LAN IP address of your pfSense firewall]

                                      When you run the upsc command, you should see all the variables of your UPS displayed.

                                      Lastly, for the pi end, put this in upsmon.conf:

                                      MONITOR ups@192.168.0.1 0 monuser secret slave
                                      
                                      N 1 Reply Last reply Reply Quote 0
                                      • N
                                        netboy @dennypage
                                        last edited by

                                        @dennypage I guess the MONITOR must be like below (see bold) - correct - Probably you have a typo?

                                        MONITOR ups@192.168.0.1 0 monuser secret slave

                                        dennypageD N 2 Replies Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage @netboy
                                          last edited by

                                          @netboy said in NUT server and UPS general question:

                                          I guess the MONITOR must be like below (see bold) - correct - Probably you have a typo?
                                          MONITOR ups@192.168.0.1 0 monuser secret slave

                                          You are correct. I copied and pasted from another example. Sorry about that.

                                          1 Reply Last reply Reply Quote 1
                                          • N
                                            netboy @netboy
                                            last edited by netboy

                                            @netboy SUCCESS!!!
                                            I had to make an entry in hosts.conf for pi

                                            MONITOR ups@192.168.0.1 "Netgate UPS"

                                            Worked. I sincerely thank you very much for all your help.