      SG3100 keeps locking up after latest update. Only way i've been able to resume network is with hard power cycle. User interface was unresponsive.

      Currently running 23.01-RELEASE (arm) It's happened (confirmed) 2 times since the upgrade. Once today and again a 4 days ago.

      The last errors i see from sent from pfSense to remote syslog during the crash are the following (ignore log at 16:02:51 as it did not cause outage):
      2b8a878f-6c04-4a24-86eb-e0589f77ec79-image.png
      file:///home/travis/Pictures/screenshots/Screenshot_20230420_183027.png

      Maybe the following is issue: Error 22, Unretryable error?
      Any idea what could be wrong? Any additional ways to troubleshoot besides swapping hardware? Is this the result of hardware failure or firmware?

      S 1 Reply Last reply Reply Quote 0
      • S
        SteveITS Galactic Empire @tuser11
        last edited by

        @tuser11 doesn’t sound great. check
        https://docs.netgate.com/pfsense/en/latest/troubleshooting/disk-lifetime.html

        Pre-2.7.2/23.09: Only install packages for your version, or risk breaking it. Select your branch in System/Update/Update Settings.
        When upgrading, allow 10-15 minutes to restart, or more depending on packages and device speed.
        Upvote 👍 helpful posts!

        T 1 Reply Last reply Reply Quote 0
        • T
          tuser11 @SteveITS
          last edited by

          @steveits thanks.

          Test results aren't clear. Unless there are other ideas, it looks like I may have to swap hardware. mmc test appeared normal. S.M.A.R.T. test reported overall self-assessment test "passed" but summary reported "warning":

          smartctl 7.3 2022-02-28 r5338 [FreeBSD 14.0-CURRENT arm] (local build)
          Copyright (C) 2002-22, Bruce Allen, Christian Franke, www.smartmontools.org
          
          === START OF READ SMART DATA SECTION ===
          SMART Error Log Version: 1
          Warning: ATA error count 0 inconsistent with error log pointer 3
          
          ATA Error Count: 0
          	CR = Command Register [HEX]
          	FR = Features Register [HEX]
          	SC = Sector Count Register [HEX]
          	SN = Sector Number Register [HEX]
          	CL = Cylinder Low Register [HEX]
          	CH = Cylinder High Register [HEX]
          	DH = Device/Head Register [HEX]
          	DC = Device Command Register [HEX]
          	ER = Error register [HEX]
          	ST = Status register [HEX]
          Powered_Up_Time is measured from power on, and printed as
          DDd+hh:mm:SS.sss where DD=days, hh=hours, mm=minutes,
          SS=sec, and sss=millisec. It "wraps" after 49.710 days.
          
          Error -1 occurred at disk power-on lifetime: 0 hours (0 days + 0 hours)
            When the command that caused the error occurred, the device was in an unknown state.
          
            After command completion occurred, registers were:
            ER ST SC SN CL CH DH
            -- -- -- -- -- -- --
            00 00 00 00 00 00 00
          
            Commands leading to the command that caused the error were:
            CR FR SC SN CL CH DH DC   Powered_Up_Time  Command/Feature_Name
            -- -- -- -- -- -- -- --  ----------------  --------------------
            00 00 44 00 05 00 00 00   6d+15:43:32.864  NOP [Abort queued commands]
            55 00 05 00 00 00 aa 04      00:06:33.221  [RESERVED]
            00 00 11 00 78 01 00 00  16d+15:13:24.797  NOP [Abort queued commands]
            55 00 0f a0 00 00 aa 00      00:03:16.611  [RESERVED]
            00 00 aa 55 02 00 01 00      08:31:10.848  NOP [Abort queued commands]
          
          Error -2 occurred at disk power-on lifetime: 402 hours (16 days + 18 hours)
            When the command that caused the error occurred, the device was in an unknown state.
          
            After command completion occurred, registers were:
            ER ST SC SN CL CH DH
            -- -- -- -- -- -- --
            01 ff 00 00 37 01 00  Device Fault; Error: 
          
            Commands leading to the command that caused the error were:
            CR FR SC SN CL CH DH DC   Powered_Up_Time  Command/Feature_Name
            -- -- -- -- -- -- -- --  ----------------  --------------------
            00 00 00 00 01 00 00 00      00:18:34.112  NOP [Abort queued commands]
            00 00 00 00 00 00 00 00      00:01:05.536  NOP [Abort queued commands]
            00 01 58 03 00 00 8f 92      00:08:47.214  NOP [Don't abort queued commands] [OBS-ACS-2]
            00 00 01 00 00 00 00 10      15:34:59.218  NOP [Abort queued commands]
            01 00 06 00 00 00 cf 00   2d+02:13:34.312  [RESERVED]
          
          Error -4 occurred at disk power-on lifetime: 0 hours (0 days + 0 hours)
            When the command that caused the error occurred, the device was active or idle.
          
            After command completion occurred, registers were:
            ER ST SC SN CL CH DH
            -- -- -- -- -- -- --
            00 00 00 00 00 00 00
          
            Commands leading to the command that caused the error were:
            CR FR SC SN CL CH DH DC   Powered_Up_Time  Command/Feature_Name
            -- -- -- -- -- -- -- --  ----------------  --------------------
            b0 d5 01 01 4f c2 40 08      00:00:00.000  SMART READ LOG
            b0 d5 01 01 4f c2 40 08      00:00:00.000  SMART READ LOG
            b0 d5 01 00 4f c2 40 08      00:00:00.000  SMART READ LOG
            b0 d0 01 00 4f c2 40 08      00:00:00.000  SMART READ DATA
            ec 00 01 00 00 00 40 08      00:00:00.000  IDENTIFY DEVICE
          

          Extended

          smartctl 7.3 2022-02-28 r5338 [FreeBSD 14.0-CURRENT arm] (local build)
          Copyright (C) 2002-22, Bruce Allen, Christian Franke, www.smartmontools.org
          
          === START OF READ SMART DATA SECTION ===
          SMART Extended Comprehensive Error Log Version: 1 (1 sectors)
          Device Error Count: 13 (device log contains only the most recent 4 errors)
          	CR     = Command Register
          	FEATR  = Features Register
          	COUNT  = Count (was: Sector Count) Register
          	LBA_48 = Upper bytes of LBA High/Mid/Low Registers ]  ATA-8
          	LH     = LBA High (was: Cylinder High) Register    ]   LBA
          	LM     = LBA Mid (was: Cylinder Low) Register      ] Register
          	LL     = LBA Low (was: Sector Number) Register     ]
          	DV     = Device (was: Device/Head) Register
          	DC     = Device Control Register
          	ER     = Error register
          	ST     = Status register
          Powered_Up_Time is measured from power on, and printed as
          DDd+hh:mm:SS.sss where DD=days, hh=hours, mm=minutes,
          SS=sec, and sss=millisec. It "wraps" after 49.710 days.
          
          Error 13 [0] log entry is empty
          Error 12 [3] log entry is empty
          Error 11 [2] log entry is empty
          Error 10 [1] occurred at disk power-on lifetime: 0 hours (0 days + 0 hours)
            When the command that caused the error occurred, the device was active or idle.
          
            After command completion occurred, registers were:
            ER -- ST COUNT  LBA_48  LH LM LL DV DC
            -- -- -- == -- == == == -- -- -- -- --
            00 -- 00 00 00 00 00 00 00 00 00 00 00
          
            Commands leading to the command that caused the error were:
            CR FEATR COUNT  LBA_48  LH LM LL DV DC  Powered_Up_Time  Command/Feature_Name
            -- == -- == -- == == == -- -- -- -- --  ---------------  --------------------
            b0 00 d5 01 01 00 00 4f 00 c2 01 40 08     00:00:00.000  SMART READ LOG
            2f 00 00 01 01 00 00 00 00 00 03 40 08     00:00:00.000  READ LOG EXT
            2f 00 00 01 01 00 00 00 00 00 00 40 08     00:00:00.000  READ LOG EXT
            b0 00 d0 01 01 00 00 4f 00 c2 00 40 08     00:00:00.000  SMART READ DATA
            ec 00 00 01 01 00 00 00 00 00 00 40 08     00:00:00.000  IDENTIFY DEVICE
          

          Device stats logs

          Device Statistics (GP Log 0x04)
          Page  Offset Size        Value Flags Description
          0x01  =====  =               =  ===  == General Statistics (rev 1) ==
          0x01  0x008  4              41  ---  Lifetime Power-On Resets
          0x01  0x010  4            1565  ---  Power-on Hours
          0x01  0x018  6        88793676  ---  Logical Sectors Written
          0x01  0x020  6      2179588462  ---  Number of Write Commands
          0x01  0x028  6      2631079764  ---  Logical Sectors Read
          0x01  0x030  6       239503858  ---  Number of Read Commands
          0x04  =====  =               =  ===  == General Errors Statistics (rev 1) ==
          0x04  0x008  4               0  ---  Number of Reported Uncorrectable Errors
          0x04  0x010  4               7  ---  Resets Between Cmd Acceptance and Completion
          0x05  =====  =               =  ===  == Temperature Statistics (rev 1) ==
          0x05  0x008  1              45  ---  Current Temperature
          0x05  0x010  1              14  ---  Average Short Term Temperature
          0x05  0x018  1              74  ---  Average Long Term Temperature
          0x05  0x020  1              45  ---  Highest Temperature
          0x05  0x028  1              45  ---  Lowest Temperature
          0x05  0x030  1              -1  ---  Highest Average Short Term Temperature
          0x05  0x038  1               0  ---  Lowest Average Short Term Temperature
          0x05  0x040  1              -1  ---  Highest Average Long Term Temperature
          0x05  0x048  1               0  ---  Lowest Average Long Term Temperature
          0x05  0x050  4               0  ---  Time in Over-Temperature
          0x05  0x058  1             100  ---  Specified Maximum Operating Temperature
          0x05  0x060  4               0  ---  Time in Under-Temperature
          0x05  0x068  1               0  ---  Specified Minimum Operating Temperature
          0x06  =====  =               =  ===  == Transport Statistics (rev 1) ==
          0x06  0x008  4             366  ---  Number of Hardware Resets
          0x06  0x018  4               0  ---  Number of Interface CRC Errors
          0x07  =====  =               =  ===  == Solid State Device Statistics (rev 1) ==
          0x07  0x008  1              86  ---  Percentage Used Endurance Indicator
                                          |||_ C monitored condition met
                                          ||__ D supports DSN
                                          |___ N normalized value
          
          GertjanG 1 Reply Last reply Reply Quote 0
          • GertjanG
            Gertjan @tuser11
            last edited by

            @tuser11 said in SG3100 keeps locking up after latest update:

            0x01 0x010 4 1565 --- Power-on Hours
            0x01 0x018 6 88793676 --- Logical Sectors Written
            0x01 0x020 6 2179588462 --- Number of Write Commands

            That's how may write command per hour ?
            ....
            Or 386 write commands per second ?

            No "help me" PM's please. Use the forum, the community will thank you.
            Edit : and where are the logs ??

            T 1 Reply Last reply Reply Quote 0
            • T
              tuser11 @Gertjan
              last edited by

              @gertjan said in SG3100 keeps locking up after latest update:

              @tuser11 said in SG3100 keeps locking up after latest update:

              0x01 0x010 4 1565 --- Power-on Hours
              0x01 0x018 6 88793676 --- Logical Sectors Written
              0x01 0x020 6 2179588462 --- Number of Write Commands

              That's how may write command per hour ?
              ....
              Or 386 write commands per second ?

              I'm not 100% sure and could not find a reference to confirm what "Value" is in relation to "Offset" and "Size". "Value" by itself is not correct for "Power-on Hours" because the device has been in production for roughly 4 years and 6 months.

              1 Reply Last reply Reply Quote 0
              • stephenw10S
                stephenw10 Netgate Administrator
                last edited by

                Mmm, that does look like a disk issue with the SSD. If you see it again I would just replace it.

                T 1 Reply Last reply Reply Quote 1
                • T
                  tuser11 @stephenw10
                  last edited by

                  @stephenw10 just an FYI, our lockups have continued. We even swapped SG-3100 boxes (we had a cold spare). So it looks like the issue either isn't related to v23.01 (we are on 23.05.1 now) or we're just seeing a higher number of lockups. https://forum.netgate.com/topic/182065/troubleshooting-repeated-sg-3100-lockups

                  1 Reply Last reply Reply Quote 0
                  • stephenw10S
                    stephenw10 Netgate Administrator
                    last edited by

                    Are you still seeing the same disk errors?

                    T 1 Reply Last reply Reply Quote 0
                    • T
                      tuser11 @stephenw10
                      last edited by

                      @stephenw10 Nope, no disk errors

                      1 Reply Last reply Reply Quote 0
                      • stephenw10S
                        stephenw10 Netgate Administrator
                        last edited by

                        Hmm so just stops responding entirely? Nothing on the console? Can you log the console output across an outage to see if anything is shown when it happens?

                        T 1 Reply Last reply Reply Quote 0
                        • M
                          michmoor LAYER 8 Rebel Alliance
                          last edited by

                          Just curious but can you downgrade to a 22.X code. See if the problem follows

                          Firewall: NetGate,Palo Alto-VM,Juniper SRX
                          Routing: Juniper, Arista, Cisco
                          Switching: Juniper, Arista, Cisco
                          Wireless: Unifi, Aruba IAP
                          JNCIP,CCNP Enterprise

                          T 1 Reply Last reply Reply Quote 0
                          • T
                            tuser11 @stephenw10
                            last edited by

                            @stephenw10 Nope, USB console unresponsive when connected until after reboot. I'm not sure how to log console output across an outage. I don't have a computer I can leave connected to the unit. I was hoping remote syslog would give me all data I needed in this situation but was wrong.

                            1 Reply Last reply Reply Quote 0
                            • T
                              tuser11 @michmoor
                              last edited by

                              @michmoor while I agree it's a fair step of elimination (owner discussed this as soon as we realized the issues are across 2 different SG-3100 units), I'm against downgrading and not having latest security patches on a device we depend on for network security.

                              S 1 Reply Last reply Reply Quote 0
                              • S
                                SteveITS Galactic Empire @tuser11
                                last edited by

                                @tuser11 Two devices does make it seem unlikely to be hardware. But yet specific to your setup since others haven't had the issue. Our 3100 has 32 days' uptime because that's when I installed 23.05.1.

                                OK new random thought: is there a chance of a ground loop? Do you have two buildings connected with a wire? Or two power feeds/grounds in a building?

                                Pre-2.7.2/23.09: Only install packages for your version, or risk breaking it. Select your branch in System/Update/Update Settings.
                                When upgrading, allow 10-15 minutes to restart, or more depending on packages and device speed.
                                Upvote 👍 helpful posts!

                                T 1 Reply Last reply Reply Quote 0
                                • T
                                  tuser11 @SteveITS
                                  last edited by tuser11

                                  @SteveITS funny you should mention a ground loop issue. I do not know if we have a ground loop issue. Basic equipment and APCs equipment show no ground or wiring faults. All test we've done ourselves and by a third party electrician revealed stable power, correct wiring and solid ground. We even had the main outside disconnect panel replaced beginning of this year to resolve some corrosion related problems found. Sometimes we have random issues with voltage that cause different UPSs in the building to randomly go on backup or cycle between AC/DC as if stuck in a power loop.

                                  Yes, we do have 2 buildings physically connected and connected with a wire. Our electrical problems are....well lets just say I'm grateful for so many UPS's and APC being so kind about honoring their warranty considering the failure rate here is abnormal.

                                  Could a power problem sneak past our UPS and damage our equipment? We haven't had any abnormal hardware failures downstream of the UPSs beyond the SG-3100. Dell PowerEdge Servers, Switches, NAS, all good.

                                  Or better yet, are you thinking there may be a ground issue with some other equipment that the SG-3100 is sensitive to?

                                  S 1 Reply Last reply Reply Quote 0
                                  • stephenw10S
                                    stephenw10 Netgate Administrator
                                    last edited by

                                    It's possible. Does the 2nd 3100 still stop responding if you run it somewhere else?

                                    To log the console output would require something there connected to it. That could be something else that happens to be there, a server etc. Or a laptop perhaps or a RasPi maybe.
                                    How practical that might be would depend on how often this happens I guess.

                                    T 1 Reply Last reply Reply Quote 0
                                    • S
                                      SteveITS Galactic Empire @tuser11
                                      last edited by

                                      @tuser11 said in SG3100 keeps locking up after latest update:

                                      Yes, we do have 2 buildings physically connected and connected with a wire

                                      If they have separate grounds, then what happens is, that wire carries the voltage difference between the grounds. We actually measured voltage on one once but it was long ago. IIRC it was burning out switch ports. Fiber is ideal to connect buildings.

                                      That said, the first two sites I found say it's only an issue with shielded twisted pair and UTP is not a probem, which isn't my recollection at all, but it's been a long time since I've run into a situation not using fiber.

                                      https://www.truecable.com/blogs/cable-academy/how-to-fix-a-ground-loop
                                      https://networkencyclopedia.com/ground-loop/

                                      Often an actual Ethernet cable isn't fed through a UPS and even if it is it's likely looking for a 1000v surge not 10 volts.

                                      Pre-2.7.2/23.09: Only install packages for your version, or risk breaking it. Select your branch in System/Update/Update Settings.
                                      When upgrading, allow 10-15 minutes to restart, or more depending on packages and device speed.
                                      Upvote 👍 helpful posts!

                                      T 1 Reply Last reply Reply Quote 1
                                      • T
                                        tuser11 @stephenw10
                                        last edited by tuser11

                                        @stephenw10 the other SG-3100 is offline in a box. I'm going to see if i can connect a USB from the SG-3100 to one of the Dell Servers and pass it through to a virtual machine that i can leave a putty session running on. As long as i have a static IP i can plug my laptop into the same switch and get access to that virtual machine even if SG-3100 goes offline. If that doesn't work I'll setup a pi or similar.

                                        1 Reply Last reply Reply Quote 1
                                        • T
                                          tuser11 @SteveITS
                                          last edited by

                                          @SteveITS said in SG3100 keeps locking up after latest update:

                                          https://www.truecable.com/blogs/cable-academy/how-to-fix-a-ground-loop

                                          Good tip, i will look into this more as i just setup a Ethernet to an outdoor building near the house at home. Would hate to see these issues start creeping up at home.

                                          1 Reply Last reply Reply Quote 0
                                          • R rcoleman-netgate referenced this topic on
                                          • N
                                            netplumbers
                                            last edited by

                                            I had some locking up issues a while back on my sg-3100 that turned out to be a bad power supply. When you swapped for your spare, did you also change PSUs?

                                            T 2 Replies Last reply Reply Quote 2