  • G
    Gertjan @robertofelix
    last edited by Dec 22, 2023, 8:05 AM

    @robertofelix said in NUT Package (2.8.1 and above):

    Edited the file /usr/local/etc/nut/upsmon.conf removing the following lines

    ... and the next time nut (re) starts, that file, as the other 'nut' config files, will get re generated.
    It's the core functionality of pfSense : one GUI to create one or more config file(s). From is one source, for every process, the needed config files are created and set up with the GUI settings.
    If you want to have control yourself over the config files, go for a native FreeBSD, and install the needed packages manually, and now you've control, by editing all these files yourself 😊

    You probably want to know that this file exists : /usr/local/pkg/nut/nut.inc
    Look what you find at 255 😊

    No "help me" PM's please. Use the forum, the community will thank you.
    Edit : and where are the logs ??

    R 1 Reply Last reply Dec 22, 2023, 4:03 PM Reply Quote 0
    • W
      whoami TM
      last edited by Dec 22, 2023, 3:22 PM

      After migrating from a SG-4860 to a XG-7100 I think I'm starting to narrow down my disconnect issue.

      I've even gone as far as replacing the battery in the UPS.

      Sometime over the last few updates my APC UPS stopped reporting ONLINE/CHARGED and now reports ONLINE/DISCHARGING

      I've tried setting
      onlinedischarge_log_throttle_sec=num

      Set the minimum frequency (in seconds) at which warnings would be emitted for an otherwise not handled OL+DISCHRG device status combination. Negative values disable sequentially repeated messages (when this state appears and persists).

      in Extra Arguments to driver field for usbhid but it prevents NUT from connecting to the UPS.

      D 1 Reply Last reply Dec 22, 2023, 10:58 PM Reply Quote 0
      • R
        robertofelix @Gertjan
        last edited by robertofelix Dec 22, 2023, 4:04 PM Dec 22, 2023, 4:03 PM

        @Gertjan said in NUT Package (2.8.1 and above):

        You probably want to know that this file exists : /usr/local/pkg/nut/nut.inc

        Yup, you're right, I rebooted and the config is back. I don't know if people using Opnsense are also facing this issue, maybe?
        Anyways, good tip about that line 255. That helps.

        1 Reply Last reply Reply Quote 0
        • D
          dennypage @whoami TM
          last edited by Dec 22, 2023, 10:58 PM

          @whoami-TM said in NUT Package (2.8.1 and above):

          I've tried setting
          onlinedischarge_log_throttle_sec=num

          I don't believe that is implemented yet. To my knowledge, that's planned for the next release of NUT.

          D 1 Reply Last reply Dec 25, 2023, 3:14 PM Reply Quote 0
          • D
            dem @dennypage
            last edited by Dec 25, 2023, 3:14 PM

            Speaking of onlinedischarge, we had several power flickers yesterday and with the latest NUT package I get a message like this for every flicker:

            Dec 24 16:25:22 router usbhid-ups[31461]: ups_status_set: seems that UPS [CP1500PFCLCD] is in OL+DISCHRG state now. Is it calibrating or do you perhaps want to set 'onlinedischarge' option? Some UPS models (e.g. CyberPower UT series) emit OL+DISCHRG when offline.
            

            There was also a brief outage which was detected correctly:

            Dec 24 12:52:22 router upsmon[30759]: UPS CP1500PFCLCD on battery
            Dec 24 12:52:27 router upsmon[30759]: UPS CP1500PFCLCD on line power
            

            The onlinedischarge messages seem harmless so I guess I'll just ignore them.

            1 Reply Last reply Reply Quote 0
            • D dennypage referenced this topic on Dec 27, 2023, 4:35 PM
            • H
              ha11oga11o
              last edited by Dec 27, 2023, 5:42 PM

              With pfSense 2.7.0 and nut 2.8.2 i still have huge problems with Riello 2200.

              Dec 27 18:33:38 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:35 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:34 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
              Dec 27 18:33:33 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:31 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:29 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:29 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
              Dec 27 18:33:27 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:25 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:24 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
              Dec 27 18:33:23 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:21 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:19 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:19 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
              Dec 27 18:33:17 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:15 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:14 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
              Dec 27 18:33:13 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:11 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:09 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
              Dec 27 18:33:09 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
              Dec 27 18:33:07 	riello_usb 	43008 	Communication with UPS is lost: status read failed! 
              

              Only stopping and starting nut service brings it back for some time. Restart not helping. I check hardware, it works fine on windows machine.

              Thnx

              D 1 Reply Last reply Dec 27, 2023, 8:06 PM Reply Quote 0
              • D
                dennypage @ha11oga11o
                last edited by dennypage Dec 27, 2023, 8:17 PM Dec 27, 2023, 8:06 PM

                @ha11oga11o said in NUT Package (2.8.1 and above):

                With pfSense 2.7.0 and nut 2.8.2 i still have huge problems with Riello 2200.

                Something is off with the version numbers here. pfSense-pkg-nut version 2.8.2 requires pfSense version 23.09/2.7.1 or above. Are you sure you are not running pfSense-pkg-nut version 2.8.0?

                Edit: In the other thread you started, it appears that you haven't updated anything since Nov 10th. The pattern you are describing is characteristic of version 2.8.0. Did you go through any of the later posts in that thread? @Unoptanio indicates success with the Riello using version 2.8.2 of the pfSense-pkg-nut on pfsense version 2.7.1.

                H N 2 Replies Last reply Dec 28, 2023, 11:15 AM Reply Quote 0
                • D
                  dennypage
                  last edited by Dec 28, 2023, 12:01 AM

                  For those of you that are on amd64 based systems (Intel or AMD), and are severely affected by the shutdown on calibration/self-test issue, attached are replacement versions of upsmon and usbhid-ups that you can use until the update is published.

                  Note that these files are for amd64 systems only. I do not have a build/test system for arm. Sorry!

                  upsmon.gz

                  usbhid-ups.gz

                  P M H 3 Replies Last reply Dec 28, 2023, 7:02 PM Reply Quote 1
                  • H
                    ha11oga11o @dennypage
                    last edited by ha11oga11o Dec 28, 2023, 11:25 AM Dec 28, 2023, 11:15 AM

                    @dennypage

                    I am really sorry! i Made typo mistake. Actually system is

                    2.7.2-RELEASE (amd64)
                    built on Fri Dec 8 21:55:00 CET 2023
                    FreeBSD 14.0-CURRENT

                    nut package 2.8.2

                    and error is still persists on this setup. This is latest log, and i found it online this morning.

                    Dec 27 18:42:48 	upsmon 	57881 	UPS RielloSEP2200 on line power
                    Dec 27 18:42:43 	upsmon 	57881 	UPS RielloSEP2200: on bypass (powered, not protecting)
                    Dec 27 18:42:43 	upsmon 	57881 	Communications with UPS RielloSEP2200 established
                    Dec 27 18:42:43 	upsd 	61706 	User local-monitor@127.0.0.1 logged into UPS [RielloSEP2200]
                    Dec 27 18:42:41 	upsd 	61706 	Connected to UPS [RielloSEP2200]: riello_usb-RielloSEP2200
                    Dec 27 18:42:41 	riello_usb 	67935 	Startup successful
                    Dec 27 18:42:39 	upsd 	61706 	Startup successful
                    Dec 27 18:42:39 	upsd 	61406 	Found 1 UPS defined in ups.conf
                    Dec 27 18:42:39 	upsd 	61406 	Can't connect to UPS [RielloSEP2200] (riello_usb-RielloSEP2200): No such file or directory
                    Dec 27 18:42:39 	upsd 	61406 	listening on ::1 port 3493
                    Dec 27 18:42:39 	upsd 	61406 	listening on 127.0.0.1 port 3493
                    Dec 27 18:42:38 	upsmon 	57881 	Communications with UPS RielloSEP2200 lost
                    Dec 27 18:42:38 	upsmon 	57881 	UPS [RielloSEP2200]: connect failed: Connection failure: Connection refused
                    Dec 27 18:42:38 	upsmon 	57329 	Startup successful
                    Dec 27 18:42:38 	riello_usb 	43008 	Signal 15: exiting
                    Dec 27 18:42:38 	upsd 	34960 	Signal 15: exiting
                    Dec 27 18:42:38 	upsd 	34960 	mainloop: Interrupted system call
                    Dec 27 18:42:38 	upsd 	34960 	User local-monitor@127.0.0.1 logged out from UPS [RielloSEP2200]
                    Dec 27 18:42:38 	upsmon 	33505 	Signal 15: exiting
                    Dec 27 18:42:37 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 27 18:42:37 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:35 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:33 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:32 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 27 18:42:31 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:29 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:27 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 27 18:42:27 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:24 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:22 	riello_usb 	43008 	Communication with UPS is lost: status read failed!
                    Dec 27 18:42:22 	upsmon 	33505 	Poll UPS [RielloSEP2200] failed - Data stale 
                    

                    Thanks and sorry again.

                    Speaking of the devil, just while i was writing this it lost connection.

                    Dec 28 12:24:12 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:24:12 	upsmon 	8652 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 28 12:24:10 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:24:08 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:24:07 	upsmon 	8652 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 28 12:24:06 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:24:04 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:24:02 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:24:02 	upsmon 	8652 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 28 12:24:00 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:23:58 	riello_usb 	24097 	Communication with UPS is lost: status read failed!
                    Dec 28 12:23:57 	upsmon 	8652 	Poll UPS [RielloSEP2200] failed - Data stale
                    Dec 28 12:23:56 	riello_usb 	24097 	Communication with UPS is lost: status read failed! 
                    
                    D 1 Reply Last reply Dec 28, 2023, 5:10 PM Reply Quote 0
                    • M
                      msurg
                      last edited by Dec 28, 2023, 3:34 PM

                      Hello,

                      With Pfsense 2.7.0 CE I could get UPS status with the following config.

                      UPS Type: Local USB

                      Driver: nutdrv_qx

                      Extra Arguments to drive:
                      port=auto
                      vendorid="0001"
                      productid="0000"
                      langid_fix=0x409
                      protocol="megatec"
                      subdriver="hunnox"
                      novendor
                      noscanlangid

                      UPS is Makelsan. Link below

                      https://www.makelsan.com.tr/en/ups/urundetay/lion-serisi-650---2200-va/index-500.html

                      After upgrading Pfsense to 2.7.2 I don't get UPS status. It says "Failed to retrieve status".

                      Nothing changed. Only upgraded from 2.7.0 CE to 2.7.2 CE.

                      Any help will be appreciated.

                      D 1 Reply Last reply Dec 28, 2023, 5:24 PM Reply Quote 0
                      • D
                        dennypage @ha11oga11o
                        last edited by dennypage Jan 13, 2024, 5:23 PM Dec 28, 2023, 5:10 PM

                        @ha11oga11o Your first example appears to be an interface state change. You can see that NUT is explicitly being terminated (signal 15).

                        There is not enough information in your second example to say anything about.

                        There is a patch you may try to help with the interface state change:

                        --- nut.inc.org	2023-11-17 05:42:10.000000000 -0800
                        +++ nut.inc	2023-12-05 15:20:38.575637000 -0800
                        @@ -82,14 +82,19 @@
                         		$start .= "\n	/usr/bin/killall -q -9 $driver";
                         	}
                         
                        -	/* Service status keys off upsmon, so start it first. */
                        -	$start .= "\n	/usr/local/sbin/upsmon";
                         	if (isset($driver)) {
                         		$start .= "\n	/usr/local/sbin/upsdrvctl start &";
                        -		/* Since we are starting the driver in backgroud, give it a moment to start. */
                        -		$start .= "\n	sleep 1";
                         		$start .= "\n	/usr/local/sbin/upsd -u root";
                        +
                        +		/*
                        +		 * Since we are starting the driver in backgroud, give
                        +		 * the driver and upsd a moment to start.
                        +		 */
                        +		$start .= "\n	sleep 1";
                         	}
                        +
                        +	/* NB: Service status keys off of upsmon. */
                        +	$start .= "\n	/usr/local/sbin/upsmon";
                         	$start .= "\n	return 0";
                         
                         	$stop = "echo stopping NUT";
                        

                        Note that after applying the patch, you will need to go into UPS -> settings and press Save in order to activate the change..

                        H 1 Reply Last reply Dec 28, 2023, 5:23 PM Reply Quote 0
                        • H
                          ha11oga11o @dennypage
                          last edited by ha11oga11o Dec 28, 2023, 5:27 PM Dec 28, 2023, 5:23 PM

                          @dennypage

                          signal 15 means that i stopped and restarted service. Only then i got it working for some time. Basically, updating box and nut did nothing for me regarding random disconnect.

                          Im not saying nut is bad, im just trying to figure it out whats going on with my USB link.

                          Tried 4-5 cables, and have 3 same UPSs... all doing same problem. I could link it via rs232 but, maybe someone cant, so im just reporting what kind of error i have.

                          Nut service is stable, not crashing and such, so patch is not needed? I think i troubles properly explaining my case. Sorry.

                          Can you, please tell me, what data you need from my box to have big picture here, and i will provide.

                          EDIT:

                          my log is actually flooded with this. I cant see where is beginning and where it is end. Log rotation is too often too.

                          Dec 28 17:42:21 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:18 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:17 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:42:16 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:14 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:12 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:12 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:42:10 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:08 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:07 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:42:06 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:04 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:02 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:02 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:42:00 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:42:00 	sshguard 	18696 	Now monitoring attacks.
                          Dec 28 17:42:00 	sshguard 	54116 	Exiting on signal.
                          Dec 28 17:42:00 	newsyslog 	18014 	logfile turned over due to size>500K
                          Dec 28 17:42:00 	newsyslog 	18014 	logfile turned over due to size>500K
                          Dec 28 17:41:58 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:57 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:41:56 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:54 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:52 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:52 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:41:50 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:48 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:47 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale
                          Dec 28 17:41:46 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:44 	riello_usb 	99096 	Communication with UPS is lost: status read failed!
                          Dec 28 17:41:42 	upsmon 	92937 	Poll UPS [RielloSEP2200] failed - Data stale 
                          

                          Thanks

                          1 Reply Last reply Reply Quote 0
                          • D
                            dennypage @msurg
                            last edited by Dec 28, 2023, 5:24 PM

                            @msurg said in NUT Package (2.8.1 and above):

                            Driver: nutdrv_qx

                            Extra Arguments to drive:
                            port=auto
                            vendorid="0001"
                            productid="0000"
                            langid_fix=0x409
                            protocol="megatec"
                            subdriver="hunnox"
                            novendor
                            noscanlangid

                            The version of NUT has changed quite a bit. From 2.7.4 to 2.8.1+. It's a major revision of NUT itself.

                            Things to do:

                            • Run usbconfig -v to confirm that the UPS is properly attached and recognized.
                            • Look for error messages associated with your driver in the system log. Not error messages from upsd or upsmon, but the actual driver.
                            • Remove everything from the Extra Arguments to driver and use auto detection.
                            • Try the blazer_usb driver.

                            Beyond that, I would recommend soliciting advice on the networkupstools user mailing list.

                            1 Reply Last reply Reply Quote 0
                            • P
                              pfpv @dennypage
                              last edited by Dec 28, 2023, 7:02 PM

                              @dennypage said in NUT Package (2.8.1 and above):

                              For those of you that are on amd64 based systems (Intel or AMD), and are severely affected by the shutdown on calibration/self-test issue, attached are replacement versions of upsmon and usbhid-ups that you can use until the update is published.

                              When will the package be updated in the pfSense repository so it becomes updatable from the GUI? Do you have an approximate timeline?

                              D 1 Reply Last reply Dec 28, 2023, 7:32 PM Reply Quote 1
                              • P
                                pfpv @dennypage
                                last edited by Dec 28, 2023, 7:23 PM

                                @dennypage said in NUT Package (2.8.1 and above):

                                I will point out one thing that you said that you may wish to reconsider. You indicate that the NAS is the most important thing to have a proper shutdown. I agree with this general sentiment. However, by running the NAS as the NUT primary, you are actually incurring higher risk for the NAS rather than less.

                                The NUT primary does not initiate a shutdown until all the associated secondaries have logged out of the primary. Assuming a default polling interval of 5 seconds, a pfSense or Linux system will take something on the order of 10-15 seconds before they log out, and another 30-90 seconds to complete a shutdown. This means that the NAS will not begin its shutdown until 10-15 seconds after the UPS declares a low battery. Depending upon configuration and current activity, a Synology usually takes over 2 minutes to complete a shutdown. If the UPS is off in calculating remaining runtime, you run the risk of exhausting the battery before the NAS has completed its shutdown.

                                If you reverse this situation and use pfSense or a Linux system as the primary, then the NAS will begin its shutdown within 5 seconds. Not only does this give a wider margin of safety for the NAS, it can give an increased margin of safety for the other systems as well. When the NAS shuts down, there is suddenly a lot less load on the UPS, which gives more time for the other systems to complete their shutdown even if the estimated remaining runtime was incorrect.

                                Thank you for your wise advice. I will follow it. I did not know that the primary waits for secondaries' logout.

                                Can you please advise me on how to setup pfSense primary with Synology secondary? If I chose UPS Type "Local USB" on pfSense will it serve as a NUT server? I suppose I need to define a user for Synology in upsd.users?

                                On Synology, do I select UPS type "Synology UPS server"? There are only 3 options: "USB UPS", "SNMP UPS" and "Synology UPS server". While not obvious, only the last option has some sense.

                                When does one use an "apcupsd" package in pfSense? The description indicates I should be using it since I have an APC UPS.

                                D 1 Reply Last reply Dec 28, 2023, 7:42 PM Reply Quote 0
                                • D
                                  dennypage @pfpv
                                  last edited by Dec 28, 2023, 7:32 PM

                                  @pfpv said in NUT Package (2.8.1 and above):

                                  @dennypage said in NUT Package (2.8.1 and above):

                                  For those of you that are on amd64 based systems (Intel or AMD), and are severely affected by the shutdown on calibration/self-test issue, attached are replacement versions of upsmon and usbhid-ups that you can use until the update is published.

                                  When will the package be updated in the pfSense repository so it becomes updatable from the GUI? Do you have an approximate timeline?

                                  PRs for the next version are in place, but I expect that the core devs are off this week so the PR will not be looked at until next week. Best guess, one to two weeks.

                                  P 1 Reply Last reply Jan 22, 2024, 3:27 PM Reply Quote 1
                                  • D
                                    dennypage @pfpv
                                    last edited by Dec 28, 2023, 7:42 PM

                                    @pfpv said in NUT Package (2.8.1 and above):

                                    Can you please advise me on how to setup pfSense primary with Synology secondary? If I chose UPS Type "Local USB" on pfSense will it serve as a NUT server? I suppose I need to define a user for Synology in upsd.users?

                                    See post #2 in this thread, Notes on remote access to NUT, in this thread for information on how to enable remote access to NUT. At the end of the post, there is a section Notes on Synology which has the name and password requirements for interoperation with NUT on Synology.

                                    @pfpv said in NUT Package (2.8.1 and above):

                                    On Synology, do I select UPS type "Synology UPS server"? There are only 3 options: "USB UPS", "SNMP UPS" and "Synology UPS server".

                                    NUT is the UPS management system on Synology, though they disguise the fact that they are using it. You would select "Synology UPS server" as the type UPS type.

                                    APCUPSD is an alternative to NUT for managing APC UPSs. It does not interoperate with other UPS types, and does not work with NUT on Synology.

                                    1 Reply Last reply Reply Quote 1
                                    • H
                                      ha11oga11o
                                      last edited by Dec 29, 2023, 1:06 PM

                                      Hello,

                                      USB connection is totally unstable so i connected it on rs232 port. It works fine so far, but still it says "Status Alert: The UPS requires attention". In logs i cannot find what kind of attention it needs this time. For me all data looks fine. Batteries are ok. temperature is 26C. Is there any way to see on what error is nut referring its statement about attention?

                                      heres latest log:

                                      Dec 29 13:52:00 	sshguard 	2303 	Now monitoring attacks.
                                      Dec 29 13:52:00 	sshguard 	35323 	Exiting on signal.
                                      Dec 29 13:50:22 	upsmon 	59353 	UPS RielloSEP2200 on line power
                                      Dec 29 13:50:17 	upsmon 	59353 	UPS RielloSEP2200: on bypass (powered, not protecting)
                                      Dec 29 13:50:17 	upsmon 	59353 	Communications with UPS RielloSEP2200 established
                                      Dec 29 13:50:16 	upsd 	60905 	Connected to UPS [RielloSEP2200]: riello_ser-RielloSEP2200
                                      Dec 29 13:50:15 	riello_ser 	87467 	Startup successful
                                      Dec 29 13:50:12 	upsmon 	59353 	Poll UPS [RielloSEP2200] failed - Driver not connected
                                      Dec 29 13:50:07 	upsmon 	59353 	Poll UPS [RielloSEP2200] failed - Driver not connected
                                      Dec 29 13:50:02 	upsmon 	59353 	UPS RielloSEP2200 is unavailable
                                      Dec 29 13:50:02 	upsmon 	59353 	Poll UPS [RielloSEP2200] failed - Driver not connected
                                      Dec 29 13:50:02 	upsd 	60905 	User local-monitor@127.0.0.1 logged into UPS [RielloSEP2200]
                                      Dec 29 13:49:58 	upsd 	60905 	Startup successful
                                      Dec 29 13:49:58 	upsd 	60830 	Found 1 UPS defined in ups.conf
                                      Dec 29 13:49:58 	upsd 	60830 	Can't connect to UPS [RielloSEP2200] (riello_ser-RielloSEP2200): No such file or directory
                                      Dec 29 13:49:58 	upsd 	60830 	listening on ::1 port 3493
                                      Dec 29 13:49:58 	upsd 	60830 	listening on 127.0.0.1 port 3493
                                      Dec 29 13:49:57 	upsmon 	59353 	Communications with UPS RielloSEP2200 lost
                                      Dec 29 13:49:57 	upsmon 	59353 	UPS [RielloSEP2200]: connect failed: Connection failure: Connection refused
                                      Dec 29 13:49:57 	upsmon 	59032 	Startup successful
                                      Dec 29 13:49:57 	php-fpm 	37711 	/nut_settings.php: Starting service nut
                                      Dec 29 13:49:57 	check_reload_status 	4706 	Syncing firewall
                                      Dec 29 13:49:57 	php-fpm 	37711 	/nut_settings.php: Configuration Change: admin@192.168.1.210 (Local Database): Updated UPS settings
                                      Dec 29 13:49:00 	php-cgi 	86948 	servicewatchdog_cron.php: Service Watchdog detected service nut stopped. Restarting nut (UPS monitoring daemon)
                                      Dec 29 13:48:30 	riello_usb 	5395 	Signal 15: exiting
                                      Dec 29 13:48:30 	upsd 	97144 	Signal 15: exiting
                                      Dec 29 13:48:30 	upsd 	97144 	mainloop: Interrupted system call
                                      Dec 29 13:48:30 	upsd 	97144 	User local-monitor@127.0.0.1 logged out from UPS [RielloSEP2200]
                                      Dec 29 13:48:30 	upsmon 	95612 	Signal 15: exiting
                                      Dec 29 13:48:30 	php-fpm 	2827 	/nut_settings.php: Stopping service nut 
                                      

                                      If that highlight is because of

                                      Dec 29 13:50:22 	upsmon 	59353 	UPS RielloSEP2200 on line power
                                      Dec 29 13:50:17 	upsmon 	59353 	UPS RielloSEP2200: on bypass (powered, not protecting) 
                                      

                                      That statement "not protecting" is not true. Its in ECO mode, so its not act like turbine. And works on demand relaying on its switching speed which works rather flawless.

                                      login-to-view

                                      Thank you in advance.

                                      D 1 Reply Last reply Dec 29, 2023, 5:16 PM Reply Quote 0
                                      • D
                                        dennypage @ha11oga11o
                                        last edited by Dec 29, 2023, 5:16 PM

                                        @ha11oga11o said in NUT Package (2.8.1 and above):

                                        It works fine so far, but still it says "Status Alert: The UPS requires attention".

                                        Dec 29 13:50:17 upsmon 59353 UPS RielloSEP2200: on bypass (powered, not protecting)
                                        That statement "not protecting" is not true. It's in ECO mode, so it's not act like turbine. And works on demand relaying on its switching speed which works rather flawless.

                                        The UPS requires attention because NUT indicates that the UPS is on bypass, which would mean that power has bypassed the UPS protection circuits. This could be either a manual operation, or something automatic in response to an input power issue. Many UPSs have ECO modes, but this should not be reported as being in bypass mode.

                                        Glancing at the manual for your unit, it appears to have a rich automatic bypass capability. Look carefully to see if your UPS is actually indicating that it is in bypass.

                                        In the end, here are the possibilities as I see them:

                                        1. The UPS is in bypass mode, and it is reporting correctly.
                                        2. The UPS is incorrectly reporting that it is in bypass mode when it is not.
                                        3. The UPS is not reporting that it is in bypass mode, but the driver is incorrectly declaring it to be.

                                        If the issue is #2, then you will need to go to the UPS vendor.

                                        If the issue is #3, then you will need to go to the networkupstools folk, or ask the vendor to go to them on your behalf.

                                        H 1 Reply Last reply Dec 29, 2023, 9:45 PM Reply Quote 0
                                        • H
                                          ha11oga11o @dennypage
                                          last edited by Dec 29, 2023, 9:45 PM

                                          @dennypage

                                          I see what is problem here. As stated in manual:
                                          "In order to optimize performance, in ECO mode, the load is normally powered by the bypass. If the mains goes out of the permitted tolerance range, the UPS switches to ON LINE operation. If the mains returns within the permitted tolerance range for at least five minutes, the UPS goes back to powering the load from the bypass."

                                          And its exactly behaving like that. And thats fine i want it that way. It states "Summary status: On line, Bypass, Charging", its not sending in eg. "ECO mode", which should be unique status. It seems its mix of problem 1 and 2. Sadly i doubt manufacturer care to do anything about it. I just hope networkupstools folks will have time and way to fix this for this line of product. I think all SEPxxx have same function and could be affected with same issue. Also i can be that UPS itself not sending trigger about ECO mode and what it is actually means.

                                          Many thnx for helping me understanding problem. That was really kind of you.

                                          Cheers!

                                          M 1 Reply Last reply Jan 12, 2024, 6:06 PM Reply Quote 1