      @dennypage said in NUT Package (2.8.1 and above):

      Secondly, I note that it is taking quite a long time for your UPS driver to start. As an experiment, you might remove the ampersand from the start of upsdrvctl in /usr/local/etc/rc.d/nut.sh and see if that helps the startup.

      Removed the &

       	/usr/local/sbin/upsdrvctl start &
      
       	/usr/local/sbin/upsdrvctl start
      

      And restarted the service.
      Seems like it helped - no more poll ups failures and connections being refused. Not sure if this is related to edited file.

      Feb 19 03:07:45 	upsmon 	17987 	Signal 15: exiting
      Feb 19 03:07:45 	upsd 	17183 	User local-monitor@127.0.0.1 logged out from UPS [asustor]
      Feb 19 03:07:45 	upsd 	17183 	mainloop: Interrupted system call
      Feb 19 03:07:45 	upsd 	17183 	Signal 15: exiting
      Feb 19 03:07:45 	usbhid-ups 	19139 	Signal 15: exiting
      Feb 19 03:07:52 	usbhid-ups 	26744 	Startup successful
      Feb 19 03:07:52 	upsd 	26874 	listening on 127.0.0.1 port 3493
      Feb 19 03:07:52 	upsd 	26874 	listening on ::1 port 3493
      Feb 19 03:07:52 	upsd 	26874 	listening on 192.168.x.1 port 3493
      Feb 19 03:07:52 	upsd 	26874 	listening on 10.x.x.1 port 3493
      Feb 19 03:07:52 	upsd 	26874 	Connected to UPS [asustor]: usbhid-ups-asustor
      Feb 19 03:07:52 	upsd 	26874 	Found 1 UPS defined in ups.conf
      Feb 19 03:07:52 	upsd 	27039 	Startup successful
      Feb 19 03:07:53 	upsmon 	27550 	Startup successful
      Feb 19 03:07:53 	upsd 	27039 	User local-monitor@127.0.0.1 logged into UPS [asustor] 
      
      1 Reply Last reply Reply Quote 0
      • GertjanG
        Gertjan @rarlup
        last edited by

        @rarlup said in NUT Package (2.8.1 and above):

        faulty wiring on one of the pfSense interfaces can/will cause weird UPS status?

        A faulty network cable, WAN, LAN, whatever, will cause system network event. One of the effects will be that that interface is taken down (and/or up if the connections returns).
        Software that is bound (uses) to a (any !) interface will get restarted, even if that interface wasn't the one triggering the event.
        Instead of a weird behavior, look at the logs again : it gets stopped, and restarted again.
        The monitoring process will re open the USB port, if that's your UPS connection, re contact the UPS, signal the obtained stated to the local NUT process, etc.
        Even the localhost or 127.0.0.1 is no exception, it's probably not the interface that can be taken down by a bad cable, as it has no cable ^^ but processes using it will also get restarted.

        No "help me" PM's please. Use the forum, the community will thank you.
        Edit : and where are the logs ??

        dennypageD 1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @rarlup
          last edited by

          @rarlup said in NUT Package (2.8.1 and above):

          you have a lot of pogo
          what do you mean? bouncing back and forth / up and down?

          Yes.

          @rarlup said in NUT Package (2.8.1 and above):

          The thing is it didn't lose the connection with the UPS it just showed On Battery after WAN down event and stayed with that status.

          There was a persistent connection loss in the logs you posted. Feb 14 12:35:26.

          @rarlup said in NUT Package (2.8.1 and above):

          Previously, just breathing near the cable could cause a WAN down event so this may be the actual cause - faulty wiring on one of the pfSense interfaces can/will cause weird UPS status?

          Yes, this could be the cause of the pogo.

          R 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @Gertjan
            last edited by

            A common mistake people make is to directly connect a PC or Mac to a port on pfSense rather than through a switch. The frequent sleep/wake cycles of these systems, which bring link down/up on their ports, wreak havoc on the pfSense.

            GertjanG R 2 Replies Last reply Reply Quote 1
            • GertjanG
              Gertjan @dennypage
              last edited by

              @dennypage said in NUT Package (2.8.1 and above):

              A common mistake people make is to directly connect a PC or Mac to a port on pfSense rather than through a switch. The frequent sleep/wake cycles of these systems, which bring link down/up on their ports, wreak havoc on the pfSense.

              Yeah ... big +1 that one.
              No excuse if they have an UPS : the upstream ISP device (router, modem, powered ONT, whatever, pfSense itself, and all the LAN attached switch(es) should be powered by the same - or linked - UPS.
              This solves a load of potential pitfalls.
              (admin) Live is so easy ones you reached this conclusion / setup ^^

              No "help me" PM's please. Use the forum, the community will thank you.
              Edit : and where are the logs ??

              1 Reply Last reply Reply Quote 0
              • R
                rarlup @dennypage
                last edited by rarlup

                @dennypage
                Not the case - that pfsense box has 9 interfaces (5 rj45 and 4 sfp+)
                0 - wan pppoe
                1 - another pfsense box
                2 - not used yet
                3 - not used
                4 - switch A

                0 - lacp to switch B
                1 - lacp to switch B
                2 - not used
                3 - not used

                Checked the UPS logs and no new events. Guess that & fixed it.

                1 Reply Last reply Reply Quote 1
                • R
                  rarlup @dennypage
                  last edited by

                  @dennypage said in NUT Package (2.8.1 and above):

                  There was a persistent connection loss in the logs you posted. Feb 14 12:35:26.

                  So WAN glitched, triggered package restart and somehow it detected the UPS as on battery before losing connection to it?

                  GertjanG 1 Reply Last reply Reply Quote 0
                  • GertjanG
                    Gertjan @rarlup
                    last edited by

                    @rarlup said in NUT Package (2.8.1 and above):

                    detected the UPS as on battery

                    If that state was known at the moment, then it is because NUT got that state from the UPS.
                    An UPS on battery, yeah, something has glitched - and the WAN agrees ^^

                    No "help me" PM's please. Use the forum, the community will thank you.
                    Edit : and where are the logs ??

                    1 Reply Last reply Reply Quote 0
                    • R
                      rarlup
                      last edited by

                      I see and it makes sense. Thank you both!
                      Looking to purchase a few more UPSes - any particular model that is 100% compatible with NUT and you can truly recommend?
                      min 700VA, cheap (<$200) and rack mountable would be ideal

                      dennypageD 1 Reply Last reply Reply Quote 1
                      • dennypageD
                        dennypage @rarlup
                        last edited by

                        @rarlup said in NUT Package (2.8.1 and above):

                        Looking to purchase a few more UPSes - any particular model that is 100% compatible with NUT and you can truly recommend?

                        NUT is compatible with a wide variety of UPSs. That said, some UPSs have more quirks than others.

                        Specific recommendations are difficult, but I would generally stay with usb-hid capable units from one of the big manufacturers such as APC, Cyber Power or Tripp Lite.

                        My personal preference is for APC, but they tend to be a bit more expensive.

                        1 Reply Last reply Reply Quote 0
                        • J
                          j.koopmann
                          last edited by

                          Hi @dennypage

                          thanks so much for your tremendous effort on this package. For months now after upgrading pfSense my previously working (most likely pre nut 2.8.x) Eaton 9SX 3000i keeps loosing the USB connection. A restart of nut fixes it immediately. I tried to work my way through the thread but seem to be at a loss. Everything is running as root already. I have not applied quirks. I am on nut 2.8.2. I have not set things to interrupt. Using usbhid-ups with no additional parameters.

                          Any (!) hint on how to further debug this, where to look in the logs, make adjustments whatever would be greatly appreciated!

                          GertjanG 1 Reply Last reply Reply Quote 0
                          • GertjanG
                            Gertjan @j.koopmann
                            last edited by

                            @j-koopmann said in NUT Package (2.8.1 and above):

                            Any (!) hint on how to further debug this

                            Check also NUT suddenly stops working every app. 6 minutes.
                            It's also a "The UPS is a usb connected Eaton 9SX 3000i.".

                            No "help me" PM's please. Use the forum, the community will thank you.
                            Edit : and where are the logs ??

                            J 1 Reply Last reply Reply Quote 0
                            • J
                              j.koopmann @Gertjan
                              last edited by

                              @Gertjan turns out it is my thread and still an unresolved problem. I just had forgotten I was already working on it here in the forum. :-)

                              No quirks installed. Problem persisting.

                              GertjanG 1 Reply Last reply Reply Quote 0
                              • GertjanG
                                Gertjan @j.koopmann
                                last edited by

                                @j-koopmann

                                Do you see the disconnect in the system log ?

                                Normally, like a mouse, or a printer, ones the USB link is made, it stays up until 'something' happens'.
                                Btw : I said 'link', be ware a simple USB connection it a lot more more then an simple electrical link. USB connectors, the wire (the cable) etc can be in a bad shape. USB concentrator (the USB chip) used on both side can be 'military grade' or worse then 'alibaba' grade.
                                "APC", as mentioned above, delivers the close to set it and forget it (and their battery still dies at a worst moment ... )

                                To test your UPS : forget about the genric NUT = pfSense for now. Hook it up using a desktop top PC, with the software that came long with it.
                                Check for some time if you see 'disconnect issues'.

                                Have look at this page : https://networkupstools.org/docs/man/ and locate (couldn't find it myself right now) the schema that lays out how all this stuff is interconnected.
                                You'll find details about upsd - the ups deamon, the connection method, which is 'USB' in this case, the driver (usbhid) used, "upsmon".
                                There are command line tools that can give you a lot of details :

                                [25.03-BETA][root@pfSense.bhf.tld]/root: upsc UPS
                                battery.charge: 100
                                battery.charge.low: 10
                                battery.charge.warning: 50
                                battery.date: 2001/09/25
                                battery.mfr.date: 2024/06/19
                                battery.runtime: 500
                                battery.runtime.low: 120
                                battery.type: PbAc
                                battery.voltage: 13.3
                                battery.voltage.nominal: 12.0
                                device.mfr: American Power Conversion
                                ...
                                

                                but a USB that 'disconnects' is, imho, more a hardware issue, like a cable or connector, or a bad power issue.
                                UPSs have often internally bad power ( 😊 ) as they do ugly things with power - it's their job.

                                No "help me" PM's please. Use the forum, the community will thank you.
                                Edit : and where are the logs ??

                                J 1 Reply Last reply Reply Quote 0
                                • J
                                  j.koopmann @Gertjan
                                  last edited by

                                  @Gertjan is it fair to assume that I would be seeing and usb disconnects the kernel is aware of in dmesg?

                                  I just intentionally pulled the USB:

                                  ugen0.2: <EATON Eaton 9SX> at usbus0 (disconnected)
                                  ugen0.2: <EATON Eaton 9SX> at usbus0
                                  

                                  However when nut stops working there is NOTHING in dmsg indicating an issue. Moreover: Once it stops working a simple restart of the nut service makes it work again immediately. If the USB stops working due to a hardware issue I would suspect that the problem would persist. Vice versa: When I pulled the USB and reinserted it, NUT was immediately happy again and did NOT loose its connection. Indeed it did not even throw an error in syslog...

                                  So if this was a problem on the Eaton or a physical problem I would assume that I should be seeing usb related dmesg/syslog output. I do not.

                                  Moreover the problem started pretty much when I upgraded from 23.x to 24.x. What was the nut version with 23.x? I read somewhere that nut 2.8 has introduced some usb related regressions. Agreed it could be unrelated but the timing is very suspicious.

                                  GertjanG 1 Reply Last reply Reply Quote 0
                                  • GertjanG
                                    Gertjan @j.koopmann
                                    last edited by

                                    @j-koopmann said in NUT Package (2.8.1 and above):

                                    I upgraded from 23.x to 24.x.

                                    For what it's worth : I switched to 25.03 Beta 6, the one that came out last week, and its rock solid.
                                    I only use the beta on my work, at home I still use 24.x as I can only upgrade @home to the offciial version as per my boss's rules (the home wife).
                                    At work, Im' the boss (a hotel with many connected clients) so I can use the beta over there.
                                    It's, imho, perfect.

                                    No "help me" PM's please. Use the forum, the community will thank you.
                                    Edit : and where are the logs ??

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      One thread please...

                                      1 Reply Last reply Reply Quote 0
                                      • dennypageD
                                        dennypage
                                        last edited by

                                        There is now a UPS Tools section, so I ask everyone to use problem specific threads rather than continuing this thread. Thank you.

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD dennypage locked this topic
                                        • First post