Netgate Discussion Forum
    • Categories
    • Recent
    • Tags
    • Popular
    • Users
    • Search
    • Register
    • Login

    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.1m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage
      last edited by

      @bulldog5:

      @dennypage:

      Btw, unless you were previously running pfSense 2.2.X or below, I'm guessing that the "something changed with nut" may be coincidental. This stuff hasn't changed much in the last year. The underlying release of nut for pfSense, version 2.7.4, was introduced in pfSense 2.3.0. The current generation of the nut package, version 2.7.4, was introduced shortly thereafter. Note that the prior generation nut package, 2.3.X, didn't have the ability to send email notifications so you would have only noticed LOWBATT messages if you scanned the system log.

      Ok sorry, let me clear that up, I'm on the latest version now of 2.3.4.  Previously on 2.3.2, never had a single LOWBATT alert. Back checked email, July 9th I upgrade to 2.3.4, alerts start rolling in since, randomly.  Is something polling differently now?

      The only scenario I can think of would be having an earlier version of pfSense and the nut package installed, then installing 2.3.2 and not reinstalling the packages until the upgrade to 2.3.4.

      If this was the case, there would have been two changes. First would have been the underlying nut version going from 2.7.3 to 2.7.4. Second would have been the nut package going from 2.3.X to 2.7.4. If this happened, it should have been pretty obvious because the nut package would have put up a banner about settings migration and forced the migrated settings to be explicitly saved before it would start. Nut email notifications are also off by default, so at some point they had to be explicitly enabled as well.

      For nut, the release notes are here. Nothing in particular jumps out at me, but I'm not a nut developer. For the nut package, there hasn't been much since the introduction of 2.7.4, which is when the ability to configure email was introduced. Overall, my best guess is that the LOWBATT thing has been happening all along and it wasn't noticed in the system logs until email notifications were enabled because it didn't impair operation.

      So I guess the key questions to think about are: Was there a nut configuration migration performed? If so, when? And when were email notifications enabled?

      1 Reply Last reply Reply Quote 0
      • B
        bulldog5
        last edited by

        @dennypage:

        @bulldog5:

        @dennypage:

        Btw, unless you were previously running pfSense 2.2.X or below, I'm guessing that the "something changed with nut" may be coincidental. This stuff hasn't changed much in the last year. The underlying release of nut for pfSense, version 2.7.4, was introduced in pfSense 2.3.0. The current generation of the nut package, version 2.7.4, was introduced shortly thereafter. Note that the prior generation nut package, 2.3.X, didn't have the ability to send email notifications so you would have only noticed LOWBATT messages if you scanned the system log.

        Ok sorry, let me clear that up, I'm on the latest version now of 2.3.4.  Previously on 2.3.2, never had a single LOWBATT alert. Back checked email, July 9th I upgrade to 2.3.4, alerts start rolling in since, randomly.  Is something polling differently now?

        The only scenario I can think of would be having an earlier version of pfSense and the nut package installed, then installing 2.3.2 and not reinstalling the packages until the upgrade to 2.3.4.

        If this was the case, there would have been two changes. First would have been the underlying nut version going from 2.7.3 to 2.7.4. Second would have been the nut package going from 2.3.X to 2.7.4. If this happened, it should have been pretty obvious because the nut package would have put up a banner about settings migration and forced the migrated settings to be explicitly saved before it would start. Nut email notifications are also off by default, so at some point they had to be explicitly enabled as well.

        For nut, the release notes are here. Nothing in particular jumps out at me, but I'm not a nut developer. For the nut package, there hasn't been much since the introduction of 2.7.4, which is when the ability to configure email was introduced. Overall, my best guess is that the LOWBATT thing has been happening all along and it wasn't noticed in the system logs until email notifications were enabled because it didn't impair operation.

        So I guess the key questions to think about are: Was there a nut configuration migration performed? If so, when? And when were email notifications enabled?

        Email notifications have been on all along, I'd get OL and OB notifications during switches, but never random LOWBATTs until after the upgrade, nut package has been on 2.7.4.  I just don't see why its sending LOWBATT, when it never comes off 100%, LOWBATT shouldn't even come out until past 70% or so and if it was actually discharging, it sure wouldn't come back to 100% that quick.  I'm going to try moving NUT master servers and see if it continues, before trying a rollback as another experiment.

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          Do you have another UPS to test with by chance?

          1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage
            last edited by

            @bulldog5:

            Email notifications have been on all along, I'd get OL and OB notifications during switches, but never random LOWBATTs until after the upgrade, nut package has been on 2.7.4.  I just don't see why its sending LOWBATT, when it never comes off 100%, LOWBATT shouldn't even come out until past 70% or so and if it was actually discharging, it sure wouldn't come back to 100% that quick.

            Okay, so no changes in the nut version or the nut package. Presuming the same UPS the entire time.

            Just for completeness, can you post output from the following two commands?

            upsc <upsname>upsrw <upsname>Thanks</upsname></upsname>

            1 Reply Last reply Reply Quote 0
            • B
              bulldog5
              last edited by

              @dennypage:

              @bulldog5:

              Email notifications have been on all along, I'd get OL and OB notifications during switches, but never random LOWBATTs until after the upgrade, nut package has been on 2.7.4.  I just don't see why its sending LOWBATT, when it never comes off 100%, LOWBATT shouldn't even come out until past 70% or so and if it was actually discharging, it sure wouldn't come back to 100% that quick.

              Okay, so no changes in the nut version or the nut package. Presuming the same UPS the entire time.

              Just for completeness, can you post output from the following two commands?

              upsc <upsname>upsrw <upsname>Thanks</upsname></upsname>

              battery.charge: 100
              battery.charge.low: 50
              battery.charge.warning: 20
              battery.mfr.date: CPS
              battery.runtime: 960
              battery.runtime.low: 600
              battery.type: PbAcid
              battery.voltage: 24.0
              battery.voltage.nominal: 24
              device.mfr: CPS
              device.model: OR1500PFCRT2U
              device.type: ups
              driver.flag.ignorelb: enabled
              driver.name: usbhid-ups
              driver.parameter.pollfreq: 30
              driver.parameter.pollinterval: 2
              driver.parameter.port: /dev/ugen0.6
              driver.parameter.synchronous: no
              driver.version: 2.7.4
              driver.version.data: CyberPower HID 0.4
              driver.version.internal: 0.41
              input.transfer.high: 139
              input.transfer.low: 88
              input.voltage: 118.0
              input.voltage.nominal: 120
              output.voltage: 118.0
              ups.beeper.status: enabled
              ups.delay.shutdown: 20
              ups.delay.start: 30
              ups.load: 58
              ups.mfr: CPS
              ups.model: OR1500PFCRT2U
              ups.productid: 0601
              ups.realpower.nominal: 900
              ups.status: OL
              ups.test.result: Done and passed
              ups.timer.shutdown: -60
              ups.timer.start: -60
              ups.vendorid: 0764

              [input.transfer.high]
              High voltage transfer point (V)
              Type: STRING
              Maximum length: 10
              Value: 139

              [input.transfer.low]
              Low voltage transfer point (V)
              Type: STRING
              Maximum length: 10
              Value: 88

              [ups.delay.shutdown]
              Interval to wait after shutdown with delay command (seconds)
              Type: STRING
              Maximum length: 10
              Value: 20

              [ups.delay.start]
              Interval to wait before (re)starting the load (seconds)
              Type: STRING
              Maximum length: 10
              Value: 30

              1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage
                last edited by

                @bulldog5:

                battery.charge.low: 50
                battery.charge.warning: 20

                I didn't look at all the variables, but this one is an issue: battery.charge.warning should be higher than battery.charge.low.

                What is being set in the Extra Arguments to driver section? Anything in the Advanced section?

                1 Reply Last reply Reply Quote 0
                • B
                  bulldog5
                  last edited by

                  @dennypage:

                  @bulldog5:

                  battery.charge.low: 50
                  battery.charge.warning: 20

                  I didn't look at all the variables, but this one is an issue: battery.charge.warning should be higher than battery.charge.low.

                  What is being set in the Extra Arguments to driver section? Anything in the Advanced section?

                  Driver Extra Args:

                  port = /dev/ugen0.6
                  ignorelb
                  override.battery.charge.low = 50
                  override.battery.runtime.low = 600

                  upsmon.conf

                  RUN_AS_USER root

                  upsd.conf

                  LISTEN 10.10.0.1

                  upsd.users

                  [monitor]
                  password = *************
                  upsmon slave

                  1 Reply Last reply Reply Quote 0
                  • J
                    jg3
                    last edited by

                    Hello,

                    Is it possible to have the NUT daemon monitor and manage two UPSes?

                    I have a CyberPower1500 and a CyberPower1350 in my set-up and the pfSense firewall is the only bare-metal box (everything else is an ESXi server).  I want to have each of the other systems query the NUT daemon on the pfSense for the status of the UPS that host is connected to.  (the UPSes are on different circuits so there are scenarios where one goes down but not both)

                    What I don't know is how to set these configurations.  I see there are a number of advanced options in the UI, I'm a little lost as to where to start.  Has anyone done this before?  I'd like to do it via the pfSense UI so my configs will survive upgrades and reinstalls, rather than being hidden down in config files.

                    To make this work I figure I need to pass options for additional configurations here so that the port of each UPS is listed explicitly:

                    
                    [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: cat /usr/local/etc/nut/ups.conf
                    [CyberPower1500]
                    driver=usbhid-ups
                    port=auto
                    
                    

                    …and here so that each UPS has an explicit TCP port for communication with the remote servers.:

                    
                    [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: cat /usr/local/etc/nut/upsd.conf
                    LISTEN 127.0.0.1
                    LISTEN ::1
                    
                    

                    …  I'm really not sure what I need to do or what will happen automatically here:

                    
                    [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: cat /usr/local/etc/nut/upsmon.conf
                    MONITOR CyberPower1500 1 monuser f0e07165bec481f09a93 master
                    SHUTDOWNCMD "/sbin/shutdown -p +0"
                    POWERDOWNFLAG /etc/killpower
                    NOTIFYCMD /usr/local/pkg/nut/nut_email.php
                    NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
                    NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
                    NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
                    NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
                    NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
                    NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                    NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
                    NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
                    NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
                    NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
                    
                    

                    Here's the USB information .. the difference I can see is the "ugen1.[2|3]" but everything else is the same?  How do I identify/label the port?

                    [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: usbconfig dump_device_desc
                    ugen0.1: <uhci root="" hub="" intel="">at usbus0, cfg=0 md=HOST spd=FULL (12Mbps) pwr=SAVE (0mA)
                    
                     [ details from four root hubs elided ]
                    
                    ugen1.2: <cp 1500c="" cps="">at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (50mA)
                    
                      bLength = 0x0012
                      bDescriptorType = 0x0001
                      bcdUSB = 0x0110
                      bDeviceClass = 0x0000  <probed by="" interface="" class="">bDeviceSubClass = 0x0000
                      bDeviceProtocol = 0x0000
                      bMaxPacketSize0 = 0x0008
                      idVendor = 0x0764
                      idProduct = 0x0501
                      bcdDevice = 0x0001
                      iManufacturer = 0x0003  <cps>iProduct = 0x0001  < CP 1500C>
                      iSerialNumber = 0x0000  <no string="">bNumConfigurations = 0x0001
                    
                    ugen1.3: <cp 1350c="" cps="">at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (50mA)
                    
                      bLength = 0x0012
                      bDescriptorType = 0x0001
                      bcdUSB = 0x0110
                      bDeviceClass = 0x0000  <probed by="" interface="" class="">bDeviceSubClass = 0x0000
                      bDeviceProtocol = 0x0000
                      bMaxPacketSize0 = 0x0008
                      idVendor = 0x0764
                      idProduct = 0x0501
                      bcdDevice = 0x0001
                      iManufacturer = 0x0003  <cps>iProduct = 0x0001  < CP 1350C>
                      iSerialNumber = 0x0000  <no string="">bNumConfigurations = 0x0001</no></cps></probed></cp></no></cps></probed></cp></uhci> 
                    

                    I'm okay if only one shows up in the UPS widget, it's more important that the respective machines know how to validate their power source.

                    Thanks for any insights …

                    --jg3

                    1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage
                      last edited by

                      @bulldog5:

                      Driver Extra Args:

                      port = /dev/ugen0.6
                      ignorelb
                      override.battery.charge.low = 50
                      override.battery.runtime.low = 600

                      The ups is at 58% load, or approximately 610 watts. Expected runtime of 14-15 min according to Cyber. So the shutdown should be triggered approximately 5 min after mains go offline.

                      One of the notes in the nut documentation on ignorelb is that some UPSs generate a LB indication almost immediately after loss of mains. In the context of general Cyberpower flakiness, I can see this happening either from loss of mains, high/low transfer, or maybe even a UPS initiated self test. Even though it would not initiate a shutdown with your configuration, nut would still generate a notification if the UPS sent a LB alert. Is it possible this is happening?

                      In terms of timing, did the load level change around the time of the upgrade? Or Driver Extra arguments?

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage
                        last edited by

                        @jg3:

                        Is it possible to have the NUT daemon monitor and manage two UPSes?

                        There is no way to do this in the UI. Sorry.

                        1 Reply Last reply Reply Quote 0
                        • B
                          bulldog5
                          last edited by

                          @dennypage:

                          @bulldog5:

                          Driver Extra Args:

                          port = /dev/ugen0.6
                          ignorelb
                          override.battery.charge.low = 50
                          override.battery.runtime.low = 600

                          The ups is at 58% load, or approximately 610 watts. Expected runtime of 14-15 min according to Cyber. So the shutdown should be triggered approximately 5 min after mains go offline.

                          One of the notes in the nut documentation on ignorelb is that some UPSs generate a LB indication almost immediately after loss of mains. In the context of general Cyberpower flakiness, I can see this happening either from loss of mains, high/low transfer, or maybe even a UPS initiated self test. Even though it would not initiate a shutdown with your configuration, nut would still generate a notification if the UPS sent a LB alert. Is it possible this is happening?

                          In terms of timing, did the load level change around the time of the upgrade? Or Driver Extra arguments?

                          Not sure i'm following completely.  As far as I know, the main is never lost, i never get any switch alerts, and never see any power surge/ flicker etc if that's what you're asking?  The only thing that changed a while back was a 8port POE switch added to the load.  Don't see how going from 52% load to 58% should say LOWBATT?  Just had an alert come out now about 10minutes ago, checked the UPS immediately and its 100% charge.  Driver Args and all config stayed the same.  Is there something i can tweak / change  to try to eliminate this.

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage
                            last edited by

                            @bulldog5:

                            As far as I know, the main is never lost, i never get any switch alerts, and never see any power surge/ flicker etc if that's what you're asking?

                            Yep. Or load surges, mains frequency change, UPS initiated self tests, etc.

                            In general, I doubt that nut is "making up" the event, and believe that the Cyberpower is actually issuing a LB signal which nut is dutifully logging. You can get definitive verification by running usbdump to capture all the traffic involving the ups, but I'm not sure it's worth it to delve this deeply though. :)

                            The ups model doesn't have a modifiable battery.charge.low, so I don't know of anything you can tweak with nut. You might search/ask in the nut users mailing list, but I expect that they will view it as a UPS problem. About the only other diagnostic recommendation I can think of is to change the load characteristics and see if it affects the issue. Temporarily removing the PoE switch perhaps.

                            Sorry I don't have a better recommendation.

                            1 Reply Last reply Reply Quote 0
                            • B
                              bulldog5
                              last edited by

                              @dennypage:

                              @bulldog5:

                              As far as I know, the main is never lost, i never get any switch alerts, and never see any power surge/ flicker etc if that's what you're asking?

                              Yep. Or load surges, mains frequency change, UPS initiated self tests, etc.

                              In general, I doubt that nut is "making up" the event, and believe that the Cyberpower is actually issuing a LB signal which nut is dutifully logging. You can get definitive verification by running usbdump to capture all the traffic involving the ups, but I'm not sure it's worth it to delve this deeply though. :)

                              The ups model doesn't have a modifiable battery.charge.low, so I don't know of anything you can tweak with nut. You might search/ask in the nut users mailing list, but I expect that they will view it as a UPS problem. About the only other diagnostic recommendation I can think of is to change the load characteristics and see if it affects the issue. Temporarily removing the PoE switch perhaps.

                              Sorry I don't have a better recommendation.

                              Alright, appreciate the help.  the UPS still has warranty, I just dunno exactly how to pick that battle with CP, they will say its WOD because self test passes.  Fact of matter is, I've almost had this UPS for a year with flawless operation, and now this just started July 9th and coincidence or not with the upgrade.  It would be a shame if I can't run 58% load on a UPS, i would think 80% would be where you don't exceed.

                              I called CyberPower support, and of course, they just brush it off as a NUT issue since the battery never drops charge so its not really low.  He mentioned something about if your runtime goes below a certain value which can be specified if using "their power software" it would set an error.  Is there something equivalent in NUT?  Looking at the output again, i can change the battery.charge.low and .warning. I set charge.low = 40 and charge.warning = 50.  battery.runtime.low is set at 600, so load would need to increase to the point where runtime drops below 600?  It currently sits around 840.

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage
                                last edited by

                                @bulldog5:

                                Looking at the output again, i can change the battery.charge.low and .warning. I set charge.low = 40 and charge.warning = 50.  battery.runtime.low is set at 600, so load would need to increase to the point where runtime drops below 600?  It currently sits around 840.

                                Yes, you do want the warning to happen before the low. With your runtime number and low setting, you will actually initiate shutdown ~4 minutes after loosing mains.

                                I would tend to set all of them a little lower than what you have, but it depends upon your situation. I.E. how long it takes your systems to shut down. On my general purpose systems I use:

                                override.battery.charge.warning = 25
                                        override.battery.charge.low = 20
                                        override.battery.runtime.low = 300

                                The reason I set these variables is because I have several servers that can take 2-3 minutes to perform a clean shutdown. Certainly longer than the 60 seconds or so warning I get from the LB signal.

                                For the firewall I use more aggressive values because pfSense shuts down quickly:

                                override.battery.charge.warning = 25
                                        override.battery.charge.low = 10
                                        override.battery.runtime.low = 180

                                Truth be told, the LB signal on the UPS probably does a fine job here, and these settings are really not necessary. I just set them out of habit.

                                Your mileage may vary.

                                1 Reply Last reply Reply Quote 0
                                • B
                                  bulldog5
                                  last edited by

                                  I plugged the UPS into a 2K12 server and installed CPs PowerPanel software, let it run for few days and didn't get any LOWBATT messages, then plugged it into my FreeNAS server which is using driver 2.7.3, internal driver .39. and no LOWBATT messages.  Here is the output running on the FreeNAS box.  So, something is not the same after the upgrade on pfsense because i dont see the LOWBATT message on 2 other boxes.  Going to try mirroring the freenas NUT configs, (being doubtful that will matter) then going to have to find some time to reinstall pfsense to 2.3.2 and go from there).

                                  battery.charge: 100
                                  battery.charge.low: 10
                                  battery.charge.warning: 20
                                  battery.mfr.date: CPS
                                  battery.runtime: 960
                                  battery.runtime.low: 300
                                  battery.type: PbAcid
                                  battery.voltage: 24.0
                                  battery.voltage.nominal: 24
                                  device.mfr: CPS
                                  device.model: OR1500PFCRT2U
                                  device.type: ups
                                  driver.name: usbhid-ups
                                  driver.parameter.pollfreq: 30
                                  driver.parameter.pollinterval: 2
                                  driver.parameter.port: /dev/ugen0.6
                                  driver.parameter.synchronous: no
                                  driver.version: 2.7.3
                                  driver.version.data: CyberPower HID 0.4
                                  driver.version.internal: 0.39
                                  input.transfer.high: 139
                                  input.transfer.low: 88
                                  input.voltage: 120.0
                                  input.voltage.nominal: 120
                                  output.voltage: 120.0
                                  ups.beeper.status: enabled
                                  ups.delay.shutdown: 20
                                  ups.delay.start: 30
                                  ups.load: 57
                                  ups.mfr: CPS
                                  ups.model: OR1500PFCRT2U
                                  ups.productid: 0601
                                  ups.realpower.nominal: 900
                                  ups.status: OL
                                  ups.test.result: Done and passed
                                  ups.timer.shutdown: -60
                                  ups.timer.start: -60
                                  ups.vendorid: 0764

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    @bulldog5:

                                    I plugged the UPS into a 2K12 server and installed CPs PowerPanel software, let it run for few days and didn't get any LOWBATT messages, then plugged it into my FreeNAS server which is using driver 2.7.3, internal driver .39. and no LOWBATT messages.

                                    So, something is not the same after the upgrade on pfsense because i dont see the LOWBATT message on 2 other boxes.  Going to try mirroring the freenas NUT configs, (being doubtful that will matter) then going to have to find some time to reinstall pfsense to 2.3.2 and go from there).

                                    When you put it back on the pfSense box did the LOWBATT messages immediately return?

                                    1 Reply Last reply Reply Quote 0
                                    • B
                                      bulldog5
                                      last edited by

                                      @dennypage:

                                      @bulldog5:

                                      I plugged the UPS into a 2K12 server and installed CPs PowerPanel software, let it run for few days and didn't get any LOWBATT messages, then plugged it into my FreeNAS server which is using driver 2.7.3, internal driver .39. and no LOWBATT messages.

                                      So, something is not the same after the upgrade on pfsense because i dont see the LOWBATT message on 2 other boxes.  Going to try mirroring the freenas NUT configs, (being doubtful that will matter) then going to have to find some time to reinstall pfsense to 2.3.2 and go from there).

                                      When you put it back on the pfSense box did the LOWBATT messages immediately return?

                                      No

                                      1 Reply Last reply Reply Quote 0
                                      • C
                                        cuco
                                        last edited by

                                        Hi

                                        I tried to "add" my UPS to my pfSense installation with the nut-package as well. Configured it with "Remote NUT server" and it shows me the load, the remaining runtime, sends me emails and so on. But it doesn't shutdown pfsense.

                                        upsc on the remote nut server gives me:

                                        battery.charge: 100.0
                                        battery.charge.low: 20
                                        battery.date: 2011-05-06
                                        battery.runtime: 540.0
                                        battery.runtime.low: 240
                                        battery.voltage: 13.7
                                        battery.voltage.nominal: 12.0
                                        device.mfr: APC
                                        device.model: Back-UPS RS 550GI
                                        device.serial: 3B1119X20852
                                        device.type: ups
                                        driver.name: apcupsd-ups
                                        driver.parameter.pollinterval: 2
                                        driver.parameter.port: localhost
                                        driver.parameter.synchronous: no
                                        driver.version: 2.7.4
                                        driver.version.internal: 0.04
                                        input.sensitivity: H
                                        input.transfer.high: 276.0
                                        input.transfer.low: 176.0
                                        input.transfer.reason: Low line voltage
                                        input.voltage: 223.0
                                        input.voltage.nominal: 230
                                        ups.date: 2017-08-05
                                        ups.firmware: 857.L3 .I USB FW:L3
                                        ups.id: t-usv
                                        ups.load: 27.0
                                        ups.mfr: APC
                                        ups.model: Back-UPS RS 550GI
                                        ups.realpower.nominal: 330.0
                                        ups.serial: 3B1119X20852
                                        ups.status: OL
                                        ups.test.result: NO
                                        ups.time: 22:12:53
                                        
                                        

                                        pfSense shows the same.

                                        When the power fails (I plugged out the mains) I get this E-Mail:

                                        Sat, 05 Aug 2017 03:05:33 +0200

                                        UPS br550gi@t-usv.lan.xxxx.eu on battery

                                        When the battery runtime goes below 4 mins (240 secs) like configured in the UPS I get this:

                                        Sat, 05 Aug 2017 03:10:21 +0200

                                        UPS br550gi@t-usv.lan.xxxx.eu battery is low

                                        But nothing more happened. I waited about 2 more minutes, but pfSense didn't shut down and then I reconnected the mains.

                                        What may I have done wrong?

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          I don't think you are doing anything wrong per se. By default, the nut slave (pfSense) isn't going to initiate a shutdown until the master server declares a low battery condition. This is different than a low battery warning.

                                          When the master declares a low battery condition, it will send a notification to all the slaves indicating that there is a pending loss of power. The slaves will each disconnect from the master and then initiate their own shutdown. Once all the slaves have disconnected, the master will initiate its own shutdown.

                                          If you want to override how the master determines when to declare a low battery condition, see the section on "ignorelb" in the ups.conf man page.

                                          1 Reply Last reply Reply Quote 0
                                          • B
                                            bdf0506
                                            last edited by

                                            @bdf0506:

                                            @dennypage:

                                            I have. The power kill logic is gone from the base os level. Still searching to find out when and why.

                                            Ah, interesting. Sounds like it isn't an issue with my specific setup and it is a bug affecting anyone trying to use that functionality in the NUT package. Looking forward to seeing a fix for this whenever one can be found.

                                            Hi, I wanted to see if there has been any progress on fixing this issue? Thanks.

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post
                                            Copyright 2025 Rubicon Communications LLC (Netgate). All rights reserved.