      @dennypage:

      @endy66:

      But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

      
      ignorelb
      override.battery.charge.low = 50
      override.battery.runtime.low = 1200
      
      

      BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

      The section entitled "Additional configuration lines for ups.conf" in Advanced settings is for global directives. The values you are trying to set are UPS specific arguments. UPS specific arguments should be entered in the section above that says "Extra Arguments to driver"

      Sorry this isn't clear. I'll have a look at clarifying.

      Hello and thanks for the great work.
      I'm working with pfSense and NUT  2.7.4_5 package. The "bug" still remains, if I edit (via webpage) the "Extra Arguments to driver (optional)" with

      ignorelb
      override.battery.charge.low = 30

      all works correctly, it adds the 2 lines AFTER

      [myups]
      driver=usbhid-ups
      port=auto

      in "/usr/local/etc/nut/ups.conf" file.
      But if I edit the "Additional configuration lines for ups.conf", which it seems to be more correct (http://networkupstools.org/docs/man/ups.conf.html), it adds the lines at beginning of the file, and it doesn't work.
      All other configuration settings (upsmon.conf, upsd.conf, upsd.users) add lines at the end of the files (checked via ssh), as it should be I think…

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage
        last edited by

        @fox983:

        The "bug" still remains, if I edit (via webpage) the "Extra Arguments to driver (optional)" with

        ignorelb
        override.battery.charge.low = 30

        all works correctly, it adds the 2 lines AFTER

        [myups]
        driver=usbhid-ups
        port=auto

        in "/usr/local/etc/nut/ups.conf" file.
        But if I edit the "Additional configuration lines for ups.conf", which it seems to be more correct (http://networkupstools.org/docs/man/ups.conf.html), it adds the lines at beginning of the file, and it doesn't work.

        Not sure what "bug" you are referring to…

        The directives you are trying to use are not global directives, but are UPS specific directives.
        It's easy to overlook this at the beginning of the ups.conf manual page:

        "The file begins with global directives, and then each UPS has a section which contains a number of directives that set parameters for that UPS."

        In other words, the general format of ups.conf looks like this:

        global_directive1
        global_directive2
        global_directive3
        
        [ups1]
        ups_directive1
        ups_directive2
        ups_directive3
        
        [ups2]
        ups_directive1
        ups_directive2
        ups_directive3
        
        

        All global directives must appear before the first UPS section. So the "Additional configuration lines for ups.conf" in the Advanced section is only for global directives only, and anything put there will appear before the UPS section. The "Extra Arguments to driver" section is for things that apply to your UPS driver, and will be placed in the UPS section.

        Adding extra driver arguments is somewhat common, but the vast majority of users do not need anything under Advanced settings which is why they are hidden by default.

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          @dennypage:

          You should be able to check the PRs in the main pfSense and FreeBSD repos to see if they’re still outstanding. If not I’ll check it when I get home.

          The PR for the NUT package has been merged, but the PR for mainline pfSense is still pending review/testing.

          1 Reply Last reply Reply Quote 0
          • D
            dtallon13
            last edited by

            Probably a really stupid question, but I want to confirm that this package allow the firewall to shut off in the event of power loss? Even better, could I program it to keep the firewall on battery until it gets to a certain percentage or a certain amount of time passes?

            If the UPS model is important, I am looking at a CP850PFCLCD connected via USB but it's not set in stone.

            1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage
              last edited by

              @dtallon13:

              Probably a really stupid question, but I want to confirm that this package allow the firewall to shut off in the event of power loss? Even better, could I program it to keep the firewall on battery until it gets to a certain percentage or a certain amount of time passes?

              Yes to all. This is what NUT does for a living.

              By default, NUT will initiate a shutdown when the UPS issues a Low Battery signal. The default values for a Low Battery signal changes from UPS to UPS, but most UPSs are pre-programmed for a pretty low level–around 5% or so. You can override this with the battery.charge.low and battery.runtime.low variables discussed earlier in this thread. See the NUT driver documentation and the ups.conf man page and for more information.

              1 Reply Last reply Reply Quote 0
              • D
                dtallon13
                last edited by

                @dennypage:

                @dtallon13:

                Probably a really stupid question, but I want to confirm that this package allow the firewall to shut off in the event of power loss? Even better, could I program it to keep the firewall on battery until it gets to a certain percentage or a certain amount of time passes?

                Yes to all. This is what NUT does for a living.

                By default, NUT will initiate a shutdown when the UPS issues a Low Battery signal. The default values for a Low Battery signal changes from UPS to UPS, but most UPSs are pre-programmed for a pretty low level–around 5% or so. You can override this with the battery.charge.low and battery.runtime.low variables discussed earlier in this thread. See the NUT driver documentation and the ups.conf man page and for more information.

                Awesome sauce! Thanks for tolerating my stupidity :P

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  @dennypage:

                  The PR for the NUT package has been merged, but the PR for mainline pfSense is still pending review/testing.

                  Both PRs now merged. Note that both a new version of pfSense (presumably 2.4.3) and a new version of the NUT package (2.7.4_6) are required for power kill to function.

                  1 Reply Last reply Reply Quote 0
                  • D
                    dtallon13
                    last edited by

                    Ok, I think I broke it. I have two identical units (CP850PFCLCD), and both of them work with my Windows system but neither work with the firewall. So here's my settings:

                    And this is all it does:

                    Am I missing something obvious?

                    1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage
                      last edited by

                      Hey dtallon13,

                      Have you rebooted pfSense since you first installed NUT? If you have not, there is a USB permissions problem that may be tripping you up. Just leave the UPS connected via USB, and reboot the firewall.

                      If a reboot doesn't address the issue, then check the system log (Status / System Logs / System / General) for messages matching 'nut' or 'ups' and report back what you find please.

                      1 Reply Last reply Reply Quote 0
                      • w0wW
                        w0w
                        last edited by

                        Where can I find example for power kill function?

                        1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage
                          last edited by

                          @w0w:

                          Where can I find example for power kill function?

                          There isn't anything you will have to set up or code. It will be automatic with the new version of the NUT package and the new version of pfSense.

                          1 Reply Last reply Reply Quote 0
                          • D
                            digitalgimpus
                            last edited by

                            Anyone know how to get NUT to accept incoming connections?

                            I tried adding:

                            LISTEN 192.168.1.5
                            

                            in upsd.conf, however that seems to cause nut to freeze and any page in the webui with NUT goes nuts (pun intended). I had to restore from a backup config to get things working again.

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              @digitalgimpus:

                              Anyone know how to get NUT to accept incoming connections?

                              Covered earlier in this thread. See reply 1.

                              1 Reply Last reply Reply Quote 0
                              • D
                                digitalgimpus
                                last edited by

                                @dennypage:

                                Covered earlier in this thread. See reply 1.

                                Thanks! I missed that.

                                1 Reply Last reply Reply Quote 0
                                • D
                                  dtallon13
                                  last edited by

                                  @dennypage:

                                  Hey dtallon13,

                                  Have you rebooted pfSense since you first installed NUT? If you have not, there is a USB permissions problem that may be tripping you up. Just leave the UPS connected via USB, and reboot the firewall.

                                  If a reboot doesn't address the issue, then check the system log (Status / System Logs / System / General) for messages matching 'nut' or 'ups' and report back what you find please.

                                  Reboot worked like magic. Thanks!

                                  1 Reply Last reply Reply Quote 0
                                  • D
                                    DownloadDeviant
                                    last edited by

                                    Hello,

                                    My NUT package displays as 2.7.4_5.
                                    This page says there is a version 2.7.4_6 but I am offered no option to update.
                                    What am I doing wrong?

                                    Recent changes I've made -
                                    I was running pfSense 2.3.4x.  I upgraded to 2.4.2, saved a config after checking everything was running properly.
                                    I then did a fresh install of 2.4.2 (went with ZFS this time), then upgraded to p1 and restored from the backup config.xml.

                                    Everything went as smooth as possible. Not a single hiccup. UPS service is accurate and working.

                                    *IF it matters, my pfSense box is a slave to my Synology DS415+ for UPS.

                                    Thanks for any advice.

                                    System: pfSense 2.4.3p1 - ZFS CPU: AMD Athlon 5350 (Kabini) MOBO: ASRock AM1H-ITX HD: 60GB SSD Patriot Inferno RAM: G.SKILL 8GB DDR3 2133 NIC: Intel I350-T2 PS: Lite-On 75W AC PACKAGES: Cron, NUT

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      @DownloadDeviant:

                                      My NUT package displays as 2.7.4_5. This page says there is a version 2.7.4_6 but I am offered no option to update.

                                      NUT package version 2.7.4_6 isn't offered for pfSense 2.4.2 because the changes in 2.7.4_6 require pfSense 2.4.3 or later to function. Currently, you will only see 2.7.4_6 if you are running a pfSense development snapshot.

                                      1 Reply Last reply Reply Quote 0
                                      • D
                                        DownloadDeviant
                                        last edited by

                                        Ahhh, OK. Whew! I was thinking I borked my fresh install or something didn't translate from the backup config.
                                        Thanks for the reply. I'll sleep better tonight.  ;D

                                        System: pfSense 2.4.3p1 - ZFS CPU: AMD Athlon 5350 (Kabini) MOBO: ASRock AM1H-ITX HD: 60GB SSD Patriot Inferno RAM: G.SKILL 8GB DDR3 2133 NIC: Intel I350-T2 PS: Lite-On 75W AC PACKAGES: Cron, NUT

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          @DownloadDeviant:

                                          Thanks for the reply. I'll sleep better tonight.  ;D

                                          LOL. You're welcome.

                                          1 Reply Last reply Reply Quote 0
                                          • N
                                            newberger
                                            last edited by

                                            Hi New pfSense user.  I appreciate your work on NUT, it's the first package I have installed.

                                            I'm running pfSense on Netgate SG-3100, which I have as UPS Master.  I have a QNAP T-882 as slave.

                                            UPS is CyberPower OR700 and is connected to SG-3100 via USB.

                                            I have configured the psSense as described in post #2, in the pfSense: Services/UPS and the UPS shows up in properly in pfSense.

                                            Here's how I configured the NAT rule.  I am still working up the learning curve on Firewall in pfSense, so please let me know if you see any issues.

                                            I did not have to setup the remote access user as described in post 2.  In post #64, there are instructions to place directives in the advanced section for ups.conf if you want to override the shutdown levels:

                                            ignorelb
                                            override.battery.charge.low = 50
                                            override.battery.runtime.low = 600
                                            

                                            However, later posts (e.g. #85) say that UPS specific arguments should be entered in the section above that says "Extra Arguments to driver".

                                            So I added like this:

                                            After setting the Port Forward, the QNAP can now see the UPS:

                                            Any feedback is appreciated and, hopefully this will be helpful for other new users.

                                            1 Reply Last reply Reply Quote 0