    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.2m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • D
      DownloadDeviant
      last edited by

      Ahhh, OK. Whew! I was thinking I borked my fresh install or something didn't translate from the backup config.
      Thanks for the reply. I'll sleep better tonight.  ;D

      System: pfSense 2.4.3p1 - ZFS CPU: AMD Athlon 5350 (Kabini) MOBO: ASRock AM1H-ITX HD: 60GB SSD Patriot Inferno RAM: G.SKILL 8GB DDR3 2133 NIC: Intel I350-T2 PS: Lite-On 75W AC PACKAGES: Cron, NUT

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage
        last edited by

        @DownloadDeviant:

        Thanks for the reply. I'll sleep better tonight.  ;D

        LOL. You're welcome.

        1 Reply Last reply Reply Quote 0
        • N
          newberger
          last edited by

          Hi New pfSense user.  I appreciate your work on NUT, it's the first package I have installed.

          I'm running pfSense on Netgate SG-3100, which I have as UPS Master.  I have a QNAP T-882 as slave.

          UPS is CyberPower OR700 and is connected to SG-3100 via USB.

          I have configured the psSense as described in post #2, in the pfSense: Services/UPS and the UPS shows up in properly in pfSense.

          Here's how I configured the NAT rule.  I am still working up the learning curve on Firewall in pfSense, so please let me know if you see any issues.

          I did not have to setup the remote access user as described in post 2.  In post #64, there are instructions to place directives in the advanced section for ups.conf if you want to override the shutdown levels:

          ignorelb
          override.battery.charge.low = 50
          override.battery.runtime.low = 600
          

          However, later posts (e.g. #85) say that UPS specific arguments should be entered in the section above that says "Extra Arguments to driver".

          So I added like this:

          After setting the Port Forward, the QNAP can now see the UPS:

          Any feedback is appreciated and, hopefully this will be helpful for other new users.

          1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage
            last edited by

            @newberger:

            I did not have to setup the remote access user as described in post 2.

            You will want to set up a user for remote access as discussed in reply #2. The monuser in the config is intended for local use only. It is automatically generated based on a random number for security, and will change from time to time. If you set up your own user, the name and password will be under your control and will not change.

            @newberger:

            In post #64, there are instructions to place directives in the advanced section for ups.conf if you want to override the shutdown levels:

            ignorelb
            override.battery.charge.low = 50
            override.battery.runtime.low = 600
            

            However, later posts (e.g. #85) say that UPS specific arguments should be entered in the section above that says "Extra Arguments to driver".

            Reply #64 discusses pollinterval which does belong in the global section for ups.conf. The battery parameters are UPS specific, and belong in the driver section as noted in #85 and elsewhere. Your post above shows it in the correct section.

            1 Reply Last reply Reply Quote 0
            • N
              newberger
              last edited by

              Thanks for the reply!

              @dennypage:

              You will want to set up a user for remote access as discussed in reply #2. The monuser in the config is intended for local use only. It is automatically generated based on a random number for security, and will change from time to time.

              For 'remote access', it sounds like you mean any device other than the pfSense Master?  So the QNAP on the same LAN  is considered remote?  Sorry, it's not the context I'm used to for local/remote.

              @dennypage:

              If you set up your own user, the name and password will be under your control and will not change.

              So, I in adding the QNAP as a slave/user, I have read here (and elsewhere) that it only will accept admin/123456:

              1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage
                last edited by

                @newberger:

                For 'remote access', it sounds like you mean any device other than the pfSense Master?  So the QNAP on the same LAN  is considered remote?  Sorry, it's not the context I'm used to for local/remote.

                Remote access in this context refers to anything not running locally on the box that the UPS is attached to.

                @newberger:

                So, I in adding the QNAP as a slave/user, I have read here (and elsewhere) that it only will accept admin/123456:

                Very disappointing, but not horribly surprising. Synology does something equally stupid by hardcoding "monuser" and "secret".

                1 Reply Last reply Reply Quote 0
                • N
                  newberger
                  last edited by

                  Thanks for clarifying the remote/local definitions.

                  @dennypage:

                  Very disappointing, but not horribly surprising. Synology does something equally stupid by hardcoding "monuser" and "secret".

                  I found some additional information that states you can change the username/password by editing /etc/config/ups/upsmon.conf on the QNAP (it was on my system volume).

                  In that file I found:

                  
                  RUN_AS_USER admin
                  MONITOR qnapups@192.168.34.5 1 admin 123456 slave
                  ...
                  
                  

                  For now I haven't changed the configuration.  Would I need to change "admin" in both lines? Since the RUN_AS_USER parameter is <userid>and the MONITOR parameter is <username>, it's unclear.  Further, it appears that changing <userid>in RUN_AS_USER might cause some permission issues?</userid></username></userid>

                  1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage
                    last edited by

                    @newberger:

                    I found some additional information that states you can change the username/password by editing /etc/config/ups/upsmon.conf on the QNAP (it was on my system volume).

                    Yes, you can do the same thing with the Synology. The problem is that it the Synology (and presumably QNAP) will reset every time you touch the service or perform an OS update.

                    @newberger:

                    In that file I found:

                    
                    RUN_AS_USER admin
                    MONITOR qnapups@192.168.34.5 1 admin 123456 slave
                    ...
                    
                    

                    For now I haven't changed the configuration.  Would I need to change "admin" in both lines? Since the RUN_AS_USER parameter is <userid>and the MONITOR parameter is <username>, it's unclear.  Further, it appears that changing <userid>in RUN_AS_USER might cause some permission issues?</userid></username></userid>

                    It is only the MONITOR line that you would change. The RUN_AS_USER is a directive saying under what username the nut services should run on the local (QNAP) machine.

                    Given that changes will end up being sporadically reset by the NAS, I would leave the username/password alone and live with it. If you are feeling adventuresome, you could file a security bug report with QNAP.

                    1 Reply Last reply Reply Quote 0
                    • N
                      newberger
                      last edited by

                      @dennypage:

                      Given that changes will end up being sporadically reset by the NAS, I would leave the username/password alone and live with it.

                      Good to know and I'll leave as is.  Thanks for all of your help!

                      1 Reply Last reply Reply Quote 0
                      • M
                        Maxburn
                        last edited by

                        Is this the right package to monitor a UPS and shut down pfsense if I get a low battery?

                        I'm poking around and tried to add a remote snmp UPS but there doesn't seem to be a field to specify a community string. I don't run public for obvious reasons.

                        Edit; it's a Liebert GXT. My synology had no issue monitoring it and doing shutdown. Looked through the MAN pages linked under advanced config and didn't see anything mentioning community strings.

                        Edit2; added public in the UPS and it worked, where can I specify that in this package?

                        Also where do I specify shutdown settings?

                        1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage
                          last edited by

                          @Maxburn:

                          Is this the right package to monitor a UPS and shut down pfsense if I get a low battery?

                          I'm poking around and tried to add a remote snmp UPS but there doesn't seem to be a field to specify a community string. I don't run public for obvious reasons.

                          Yes, this is the right package.

                          As to the community string, if you are using the default ("public"), then you don't need to specify a community string. If you are using something other than the default, you would specify the community in the Extra Arguments to driver section. See the snmp-ups man page for more information on snmp driver arguments.

                          As an aside, a unique community name can be marginally effective at preventing accidents, but it offers nothing in the way of actual security because the name is sent across the network in clear text. While it used to be considered an important best practice to change the community name with v1/v2, many people don't bother any more. For actual security you need to use v3, at which point it doesn't matter if the community name is public. Even when using a unique community name for read/write with v1/v2/v3, it is common to leave public in place as an read only v1 community for monitoring things such as UPSs.

                          1 Reply Last reply Reply Quote 0
                          • P
                            pablo_deskObar
                            last edited by

                            Hello,

                            I have connected my apc ups to netgate pfsense and setup nut.

                            I have it as server, and connected my synology NAS to it.

                            These devices shutdown after the limit imposed.

                            Here,

                            i have battery low warning - 90
                            low battery - 80

                            (i like to preserve battery XD)

                            The ISSUE is my APC is not shutting down after pfsense and synology shuts off. It keeps running till battery  becomes 0.

                            Tried changing offdelay (ups.shutdown.delay from 20 to 30) no success.

                            Can i use shutdown timer to make the ups shut down after say like 5 mins? (all my devices shutdown before that), and when power returns will ups turn back on automatically?

                            Any help appreciated. :)

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              @pablo_deskObar:

                              The ISSUE is my APC is not shutting down after pfsense and synology shuts off. It keeps running till battery  becomes 0.

                              See post #1, version 2.7.4_6 which addresses this issue.

                              1 Reply Last reply Reply Quote 0
                              • P
                                pablo_deskObar
                                last edited by

                                @dennypage:

                                @pablo_deskObar:

                                The ISSUE is my APC is not shutting down after pfsense and synology shuts off. It keeps running till battery  becomes 0.

                                See post #1, version 2.7.4_6 which addresses this issue.

                                Didnt see that :) Also, will the ups power back on automatically after mains is restored after a power kill?

                                1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage
                                  last edited by

                                  @pablo_deskObar:

                                  Also, will the ups power back on automatically after mains is restored after a power kill?

                                  It should. Most all UPSs are designed to.

                                  1 Reply Last reply Reply Quote 0
                                  • Q
                                    q54e3w
                                    last edited by

                                    My pfsense server is running NUT package and I also have a separate ESXi host with NUT installed. I want to shut down the VMs and the ESXI host before pfsense shutdowns to ensure network services remain up to prevent problems closing down the VMs cleanly. How can I delay pfsense powering down until esxi has completed shutting down?
                                    I have a APC SMX UPS attached via AP9631 network card.

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      @q54e3w:

                                      How can I delay pfsense powering down until esxi has completed shutting down?

                                      The HOSTSYNC variable controls how long the master will wait for slaves to initiate their shutdown. You can find information on this in the ups.conf man page.

                                      1 Reply Last reply Reply Quote 0
                                      • Q
                                        q54e3w
                                        last edited by

                                        Thank you - I'll give it a try.

                                        I've noticed the following errors appearing in my logs, any idea why this would be?

                                        
                                        ...
                                        Feb 18 11:01:52	snmp-ups	44002	dstate_setflags: base variable (battery.runtime.low) is immutable
                                        Feb 18 11:01:20	snmp-ups	44002	dstate_setflags: base variable (battery.runtime.low) is immutable
                                        Feb 18 11:00:48	snmp-ups	44002	dstate_setflags: base variable (battery.runtime.low) is immutable
                                        ...
                                        
                                        

                                        I have the following code

                                        extra arguments

                                        
                                        ignorelb
                                        override.battery.charge.warning = 50
                                        override.battery.charge.low = 30
                                        override.battery.runtime.low = 1200
                                        
                                        

                                        upsmon.conf

                                        
                                        HOSTSYNC 600
                                        
                                        

                                        upsd.conf

                                        
                                        LISTEN 192.168.10.1
                                        
                                        

                                        upsd.users

                                        
                                        [remoteuser]
                                        password = mypassword
                                        upsmon slave
                                        
                                        

                                        the settings appear to be being applied correctly….

                                        
                                        upsc ups@localhost
                                        ambient.1.humidity.alarm.high: 60.00
                                        ambient.1.humidity.alarm.low: 30.00
                                        ambient.1.temperature.alarm.high: 40.00
                                        ambient.1.temperature.alarm.low: 10.00
                                        ambient.humidity: 39.00
                                        ambient.temperature: 15.0
                                        battery.charge: 100.00
                                        battery.charge.low: 30
                                        battery.charge.warning: 50
                                        battery.date: 11/15/2017
                                        battery.packs: 1.00
                                        battery.runtime: 4428.00
                                        battery.runtime.low: 1200
                                        battery.voltage: 54.20
                                        device.mfr: APC
                                        device.model: Smart-UPS X 1500
                                        device.type: ups
                                        driver.flag.ignorelb: enabled
                                        driver.name: snmp-ups
                                        driver.parameter.pollinterval: 2
                                        driver.parameter.port: 192.168.10.50
                                        driver.parameter.synchronous: no
                                        driver.version: 2.7.4
                                        driver.version.data: apcc MIB 1.2
                                        driver.version.internal: 0.97
                                        input.frequency: 60.00
                                        input.sensitivity: high
                                        input.transfer.high: 127
                                        input.transfer.low: 106
                                        input.transfer.reason: selfTest
                                        input.voltage: 122.20
                                        input.voltage.maximum: 123.20
                                        input.voltage.minimum: 121.30
                                        output.current: 4.80
                                        output.frequency: 60.00
                                        output.voltage: 122.20
                                        output.voltage.nominal: 120
                                        ups.delay.shutdown: 20
                                        ups.delay.start: 10
                                        ups.firmware: UPS 09.1 (ID20)
                                        ups.id: UPS
                                        ups.load: 48.30
                                        ups.mfr: APC
                                        ups.mfr.date: 06/30/2012
                                        ups.model: Smart-UPS X 1500
                                        ups.status: OL
                                        ups.temperature: 18.60
                                        ups.test.date: 02/14/2018
                                        ups.test.result: Ok
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          @q54e3w:

                                          Thank you - I'll give it a try.

                                          I've noticed the following errors appearing in my logs, any idea why this would be?

                                          
                                          ...
                                          Feb 18 11:01:52	snmp-ups	44002	dstate_setflags: base variable (battery.runtime.low) is immutable
                                          Feb 18 11:01:20	snmp-ups	44002	dstate_setflags: base variable (battery.runtime.low) is immutable
                                          Feb 18 11:00:48	snmp-ups	44002	dstate_setflags: base variable (battery.runtime.low) is immutable
                                          ...
                                          
                                          

                                          I believe it means that the variable is marked read-only in the SNMP MIB. For more information on this, I would suggest checking the nut users list.

                                          FWIW, if it were me I would just remove the setting of runtime and use charge %. You don’t need both.

                                          1 Reply Last reply Reply Quote 0
                                          • S
                                            spambait
                                            last edited by

                                            pfsense 2.4.2-RELEASE-p1 (amd64)
                                            nut 2.7.4_5

                                            Polling an APC AP9631 on the LAN via SNMP.

                                            When I reboot the appliance, UPS status shows as down. Log has a bunch of these:

                                            Feb 19 21:40:27 upsmon 66529 Poll UPS [office-UPS] failed - Driver not connected
                                            Feb 19 21:42:22 upsmon 67668 Startup successful
                                            Feb 19 21:42:23 upsd 68233 listening on ::1 port 3493
                                            Feb 19 21:42:23 upsd 68233 listening on 127.0.0.1 port 3493
                                            Feb 19 21:42:23 upsd 68233 Can't connect to UPS [office-UPS] (snmp-ups-office-UPS): No such file or directory
                                            Feb 19 21:42:23 upsd 68498 Startup successful
                                            Feb 19 21:42:24 snmp-ups 68710 Startup successful

                                            Now when I go to restart the service via the GUI In Services -> UPS, it starts up perfectly right away.

                                            apcupsd was installed but I removed it when switching to NUT.

                                            I tried using snmp v1 instead of v3 thinking I screwed up my v3 credentials but that doesn't seem to be the issue. Even with snmpv1 it wont come up after a reboot until I manually intervene.

                                            I tried some of the retry and delay parameters in the additional parameters for ups.conf but they also didn't help with this

                                            
                                            maxretry=3
                                            retrydelay=10
                                            pollinterval=5
                                            snmp_retries=10
                                            snmp_timeout=2
                                            pollfreq=10
                                            
                                            1 Reply Last reply Reply Quote 0