    kevindd992002 @dennypage
    last edited by Sep 3, 2018, 11:37 PM

    @dennypage

    I don't think the UPS is defective because when I directly connect the USB cable to a Windows machine with PowerChute installed, everything works just fine when I do the same test.

    Why would it need a startup delay?

    D 1 Reply Last reply Sep 4, 2018, 12:37 AM Reply Quote 0
    • Q
      q54e3w
      last edited by Sep 3, 2018, 11:49 PM

      Because it configures the amount to recharge the UPS to before turning back on. You can simulate by leave load off whilst the batteries charge back to 90% and when you power up you’ll see it operate correctly.
      Read up on the startup delay Denny mentioned. It’s probably your answer.

      K 1 Reply Last reply Sep 4, 2018, 8:04 AM Reply Quote 0
      • D
        dennypage @kevindd992002
        last edited by Sep 4, 2018, 12:37 AM

        @kevindd992002

        You said “... I plug the mains back into the UPS. As soon as I do this, the UPS turns on BUT stays at battery mode (so discharging). It supplies power back to all ports ...”

        If the UPS stays on battery even though mains have been restored, then that is a defect. It may be “by design” but it is still a defect. The UPS should return to main power before reenergizing the ports.

        Sometimes you can work around defect by design issues like this by setting delay parameters in the UPS, which is why I suggested that you read up on the various delay values. Ups.delay.start in particular.

        K 1 Reply Last reply Sep 4, 2018, 1:30 AM Reply Quote 0
        • K
          kevindd992002 @dennypage
          last edited by Sep 4, 2018, 1:30 AM

          @dennypage

          Exactly. But like I said, this only happens when the USB cable is plugged unto NUT. So there's somrthing going on with the UPS when NUT issues a killpower order. I would've noticed this issue long ago (when I wasn't still using NUT) if it also occured when using PowerChute, or if it happens when the USB serial cable is unplugged. Does that make sense?

          Yes, I will read up on that delay parameter later.

          1 Reply Last reply Reply Quote 0
          • K
            kevindd992002 @q54e3w
            last edited by Sep 4, 2018, 8:04 AM

            @q54e3w said in NUT package:

            Because it configures the amount to recharge the UPS to before turning back on. You can simulate by leave load off whilst the batteries charge back to 90% and when you power up you’ll see it operate correctly.
            Read up on the startup delay Denny mentioned. It’s probably your answer.

            In the NUT user manual (variables section), it says this:

            ups.delay.start - Interval to wait before restarting the load (seconds)

            This is in seconds. How does that description relate to what you said (it configures the amount to recharge the UPS to before turning back on)? Sorry, I'm confused and I can't find any start delay variable description that is close to what you're describing.

            1 Reply Last reply Reply Quote 0
            • D
              dennypage
              last edited by Sep 4, 2018, 3:38 PM

              Run your 10 count test again. After step 6, unplug the serial cable. How long does it take after step 7 does it take for the ups to come off battery and return to the mains? That is The startup delay you are trying to achieve.

              K 1 Reply Last reply Sep 4, 2018, 4:32 PM Reply Quote 0
              • Q
                q54e3w
                last edited by Sep 4, 2018, 3:47 PM

                If it only happens when the USB cable is connected then its possible your master is detecting the low battery condition still exists and instigating the shutdown again, this is potentially a poor driver or faulty hardware. Which brand & model is this?
                The UPS should be should report its on mains power which should prevent this. With my APC and Eaton units (both with network cards) I rcall shutdown only triggered when (on battery AND battery charge < X%).

                1 Reply Last reply Reply Quote 0
                • K
                  kevindd992002 @dennypage
                  last edited by Sep 4, 2018, 4:32 PM

                  @dennypage said in NUT package:

                  Run your 10 count test again. After step 6, unplug the serial cable. How long does it take after step 7 does it take for the ups to come off battery and return to the mains? That is The startup delay you are trying to achieve.

                  @q54e3w said in NUT package:

                  If it only happens when the USB cable is connected then its possible your master is detecting the low battery condition still exists and instigating the shutdown again, this is potentially a poor driver or faulty hardware. Which brand & model is this?
                  The UPS should be should report its on mains power which should prevent this. With my APC and Eaton units (both with network cards) I rcall shutdown only triggered when (on battery AND battery charge < X%).

                  I think I know what I did wrong. In step 7, I plugged the mains too early causing a power race condition as described by point #51 here . I thought that when APC BR1500GI's display went black (even with the fans still running) it is already in a shutdown state. This was not the case, it waited for a few more seconds until it totally went silent. At that time, I plugged the mains back and everything was working as expected :)

                  A question regarding the workaround implementation on point #51 of that FAQ article though. Where, in the pfsense NUT package, do I implement that if statement?

                  D 1 Reply Last reply Sep 4, 2018, 5:34 PM Reply Quote 0
                  • D
                    dennypage @kevindd992002
                    last edited by Sep 4, 2018, 5:34 PM

                    @kevindd992002

                    Unless you have a “stupid” ups, no. You may want to read up on offdelay and ondelay. But likely there is nothing else you need do. Just be happy.

                    K 1 Reply Last reply Sep 4, 2018, 5:51 PM Reply Quote 0
                    • K
                      kevindd992002 @dennypage
                      last edited by Sep 4, 2018, 5:51 PM

                      @dennypage

                      What do you mean no?

                      Well, there's still a chance (though slim) that a power race condition will happen. So might as well implement thst if statement as a workaround, no?

                      D 1 Reply Last reply Sep 4, 2018, 6:02 PM Reply Quote 0
                      • D
                        dennypage @kevindd992002
                        last edited by Sep 4, 2018, 6:02 PM

                        @kevindd992002 said in NUT package:

                        @dennypage

                        What do you mean no?

                        No as in no you don’t need to.

                        K 1 Reply Last reply Sep 4, 2018, 11:50 PM Reply Quote 0
                        • K
                          kevindd992002 @dennypage
                          last edited by kevindd992002 Sep 5, 2018, 12:26 PM Sep 4, 2018, 11:50 PM

                          @dennypage

                          I'm confused. I was able to recreate the power race problem. Are you saying that this happens with a very low probability that makes it not worth applying the workaround? Sorry, I know I'm persistent but I'm just into the nitty-gritty details.

                          EDIT:

                          Also, do you have any ideas about this? https://forum.netgate.com/topic/109510/upsmon-parent-process-died-shutdown-impossible/5 . I'm encountering the same issue every now and then.

                          K 1 Reply Last reply Sep 6, 2018, 2:39 PM Reply Quote 0
                          • K
                            kevindd992002 @kevindd992002
                            last edited by Sep 6, 2018, 2:39 PM

                            @dennypage

                            Would you be able to continue helping me? Thanks.

                            D 1 Reply Last reply Sep 6, 2018, 6:26 PM Reply Quote 0
                            • D
                              dennypage @kevindd992002
                              last edited by Sep 6, 2018, 6:26 PM

                              @kevindd992002

                              I’m traveling, so it’s a bit hard atm. Not sure what additional help you need. Not sure what you tested was the issue referred to in the link. Regardless, offdelay and ondelay are likely what you need to look at.

                              K 1 Reply Last reply Sep 7, 2018, 1:30 AM Reply Quote 0
                              • K
                                kevindd992002 @dennypage
                                last edited by Sep 7, 2018, 1:30 AM

                                @dennypage

                                Sorry.

                                So basically, I wanted to solve the power race problem wherein the UPS acts weird when the mains comes back exactly during its shutting down phase. There's already a script written in NUT's FAQ page but you mentioned that I don't need to do that and insteast just concentrate on ondelay and offdelay. I'm confused why I don't need to solve the power race problem according to what you said. What's the difference between implementing that script and implemnting off/ondelay?

                                As for the link I posted, that's regarding the upsmon parent process died error message that's being sent through email notification. I haven't gotten it in a few days now but was wondering what you thought about that since you replied to that old thread at one point.

                                D 1 Reply Last reply Sep 7, 2018, 10:46 PM Reply Quote 0
                                • D
                                  dennypage @kevindd992002
                                  last edited by Sep 7, 2018, 10:46 PM

                                  @kevindd992002

                                  The workaround you reference indicates that it is for dealing with contact closure (dumb) UPS units. But you don’t have one of those.

                                  It’s unclear to me what you have experienced. The nut users list is a better place to seek help with core nut behavior.

                                  1 Reply Last reply Reply Quote 0
                                  • P
                                    pfserik
                                    last edited by Sep 10, 2018, 2:03 PM

                                    I have a TrippLite ECO 850 LCD. The UPS is about 4-6 months old, has a 100% capacity still, and has been working flawlessly. It's ECO mode is tured off.

                                    I gracefully rebooted my pfSense three days ago. Since then, I've been receiving the following notices every 10 minutes. I get the first one and then about 5 seconds later I get the second one. Then 10 minutes later I get the same two messages again. When this started, I checked and there was an update for NUT that I installed. This didn't help. I've rebooted pfSense again and that didn't help.

                                    Is there additional information I can supply or steps I can try to resolve this issue?

                                    Subject: UPS Notification from pfsense.domain
                                    
                                    Mon, 10 Sep 2018 08:28:51
                                    
                                    Communications with UPS TrippLite_ECO850LCD lost
                                    
                                    Subject: UPS Notification from pfsense.domain
                                    
                                    Mon, 10 Sep 2018 08:28:56
                                    
                                    Communications with UPS TrippLite_ECO850LCD estabished
                                    
                                    D 1 Reply Last reply Sep 10, 2018, 5:11 PM Reply Quote 0
                                    • D
                                      dennypage @pfserik
                                      last edited by Sep 10, 2018, 5:11 PM

                                      @pfserik
                                      Most often this is cause by flakey USB connectivity. You kind of have to use the cable that came with the unit, so unless you have another unit to swap cables with it's kind hard to check that. If you have multiple USB hubs in the box, try one of the ports connected to a different hub. Lastly, if you you can try add/remove of an external hub.

                                      It could also be a bad UPS, but I think that unlikely. When these unit fail, it is usually complete. Worth running a self test however. Note of caution: although undocumented, when you run a self test the ECO sockets get turned off even if you have ECO disabled. I found that out the hard way. 😢

                                      Btw, I assume you are running 2.4.3-RELEASE-p1, yes?

                                      1 Reply Last reply Reply Quote 0
                                      • K
                                        kaeny123
                                        last edited by Sep 14, 2018, 9:38 PM

                                        Hi, I am currently having trouble accessing my SNMPv3 enabled APC SmartUPS 3000 using NUT 2.7.2 downloaded from package and NMC AP9631 on CentOS 7

                                        My ups.conf

                                        [ups6]
                                        driver = snmp-ups
                                        port = ups6.domain.name
                                        snmp_version = v3
                                        secLevel = authPriv
                                        secName = ups6
                                        authProtocol = MD5
                                        privProtocol = AES
                                        authPassword = <secret>
                                        privPassword = <secret>
                                        pollfreq = 15
                                        

                                        When I run /usr/sbin/upsdrvctl start I get

                                        # /usr/sbin/upsdrvctl start
                                        Network UPS Tools - UPS driver controller 2.7.2
                                        Network UPS Tools - Generic SNMP UPS driver 0.72 (2.7.2)
                                        No supported device detected
                                        Driver failed to start (exit status=1)
                                        

                                        But when I switch it to SNMPv1, it works
                                        ups.conf

                                        [ups6]
                                        driver = snmp-ups
                                        port = ups6.domain.name
                                        snmp_version = v1
                                        pollfreq = 15
                                        
                                        # /usr/sbin/upsdrvctl start
                                        Network UPS Tools - Generic SNMP UPS driver 0.72 (2.7.2)
                                        No matching MIB found for sysOID '.1.3.6.1.4.1.318.1.3.27'!
                                        Please report it to NUT developers, with an 'upsc' output for your device.
                                        Going back to classic MIB detection method.
                                        Detected Smart-UPS SRT 3000 on host <IP> (mib: apcc 1.2)
                                        [ups6] Warning: excessive poll failures, limiting error reporting
                                        [ups6] Warning: excessive poll failures, limiting error reporting
                                        

                                        Can someone help me out with this please

                                        D 1 Reply Last reply Sep 14, 2018, 10:07 PM Reply Quote 0
                                        • D
                                          dennypage @kaeny123
                                          last edited by Sep 14, 2018, 10:07 PM

                                          @kaeny123 said in NUT package:

                                          I am currently having trouble accessing my SNMPv3 enabled APC SmartUPS 3000 using NUT 2.7.2 downloaded from package and NMC AP9631 on CentOS 7

                                          This isn't the forum you are looking for. This forum relates to pfSense, which is a firewall distribution, and this thread is about the NUT package for pfSense. No relationship to NUT on CentOS. You should seek help in either the CentOS or NUT forums/mailing lists.

                                          Before you ask them for help however, you probably want to upgrade. The version of NUT you are using, 2.7.2, was obsolete more than 3 years ago. The current version is 2.7.4, which was released over 2 years ago. Just sayin'.

                                          K 1 Reply Last reply Sep 14, 2018, 10:11 PM Reply Quote 0