    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.1m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage @pfserik
      last edited by

      @pfserik
      Most often this is cause by flakey USB connectivity. You kind of have to use the cable that came with the unit, so unless you have another unit to swap cables with it's kind hard to check that. If you have multiple USB hubs in the box, try one of the ports connected to a different hub. Lastly, if you you can try add/remove of an external hub.

      It could also be a bad UPS, but I think that unlikely. When these unit fail, it is usually complete. Worth running a self test however. Note of caution: although undocumented, when you run a self test the ECO sockets get turned off even if you have ECO disabled. I found that out the hard way. 😢

      Btw, I assume you are running 2.4.3-RELEASE-p1, yes?

      1 Reply Last reply Reply Quote 0
      • K
        kaeny123
        last edited by

        Hi, I am currently having trouble accessing my SNMPv3 enabled APC SmartUPS 3000 using NUT 2.7.2 downloaded from package and NMC AP9631 on CentOS 7

        My ups.conf

        [ups6]
        driver = snmp-ups
        port = ups6.domain.name
        snmp_version = v3
        secLevel = authPriv
        secName = ups6
        authProtocol = MD5
        privProtocol = AES
        authPassword = <secret>
        privPassword = <secret>
        pollfreq = 15
        

        When I run /usr/sbin/upsdrvctl start I get

        # /usr/sbin/upsdrvctl start
        Network UPS Tools - UPS driver controller 2.7.2
        Network UPS Tools - Generic SNMP UPS driver 0.72 (2.7.2)
        No supported device detected
        Driver failed to start (exit status=1)
        

        But when I switch it to SNMPv1, it works
        ups.conf

        [ups6]
        driver = snmp-ups
        port = ups6.domain.name
        snmp_version = v1
        pollfreq = 15
        
        # /usr/sbin/upsdrvctl start
        Network UPS Tools - Generic SNMP UPS driver 0.72 (2.7.2)
        No matching MIB found for sysOID '.1.3.6.1.4.1.318.1.3.27'!
        Please report it to NUT developers, with an 'upsc' output for your device.
        Going back to classic MIB detection method.
        Detected Smart-UPS SRT 3000 on host <IP> (mib: apcc 1.2)
        [ups6] Warning: excessive poll failures, limiting error reporting
        [ups6] Warning: excessive poll failures, limiting error reporting
        

        Can someone help me out with this please

        dennypageD 1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @kaeny123
          last edited by

          @kaeny123 said in NUT package:

          I am currently having trouble accessing my SNMPv3 enabled APC SmartUPS 3000 using NUT 2.7.2 downloaded from package and NMC AP9631 on CentOS 7

          This isn't the forum you are looking for. This forum relates to pfSense, which is a firewall distribution, and this thread is about the NUT package for pfSense. No relationship to NUT on CentOS. You should seek help in either the CentOS or NUT forums/mailing lists.

          Before you ask them for help however, you probably want to upgrade. The version of NUT you are using, 2.7.2, was obsolete more than 3 years ago. The current version is 2.7.4, which was released over 2 years ago. Just sayin'.

          K 1 Reply Last reply Reply Quote 0
          • K
            kaeny123 @dennypage
            last edited by

            This isn't the forum you are looking for. This forum relates to pfSense, which is a firewall distribution, and this thread is about the NUT package for pfSense. No relationship to NUT on CentOS. You should seek help in either the CentOS or NUT forums/mailing lists.

            Oh oops I will do that then.

            Before you ask them for help however, you probably want to upgrade. The version of NUT you are using, 2.7.2, was obsolete more than 3 years ago. The current version is 2.7.4, which was released over 2 years ago. Just sayin'.

            The newest release for CentOS7 is 2.7.2-4. https://pkgs.org/download/nut
            Should I just download 2.7.4 from somewhere?

            1 Reply Last reply Reply Quote 0
            • DerelictD
              Derelict LAYER 8 Netgate
              last edited by

              Again, a question for the CentOS folks.

              Chattanooga, Tennessee, USA
              A comprehensive network diagram is worth 10,000 words and 15 conference calls.
              DO NOT set a source address/port in a port forward or firewall rule unless you KNOW you need it!
              Do Not Chat For Help! NO_WAN_EGRESS(TM)

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage @Derelict
                last edited by

                @derelict That I've noticed, OP posted here, on the NUT users list, and also on Reddit. I expect he found a CentOS board to post on as well. Spray and pray.

                K 1 Reply Last reply Reply Quote 0
                • K
                  kaeny123 @dennypage
                  last edited by

                  @dennypage said in NUT package:

                  @derelict That I've noticed, OP posted here, on the NUT users list, and also on Reddit. I expect he found a CentOS board to post on as well. Spray and pray.

                  Sheesh, you don't have to be so mean. I was researching this issue for over a day, so decided to go on forums to ask. Might as well post on many, since not all of these are super active. I saw one person having the same issue in this same thread and ended up using v1, and saying he will figure out v3, and not updating his post. @dennypage also replied to that comment saying it was a misonfiguration in the .config file, but it is just that NUT doesn't support SNMPv3 on the AP9631 APC UPS NMC.

                  I hope i didn't annoy you all with my question, and hopefully what I found out will help users in the future.

                  dennypageD 1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage @kaeny123
                    last edited by

                    @kaeny123 I wasn't being mean dude. You should understand that the approach you took is considered to be inappropriate and does not incline people to help you.

                    K 1 Reply Last reply Reply Quote 0
                    • K
                      kaeny123 @dennypage
                      last edited by

                      @dennypage said in NUT package:

                      @kaeny123 I wasn't being mean dude. You should understand that the approach you took is considered to be inappropriate and does not incline people to help you.

                      How so? I am fairly new to this, maybe I don't understand the etiquette. I apologize for any rude behavior on my part, I would like to know so I dont repeat the same mistake

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @kaeny123
                        last edited by

                        @kaeny123 Given that you are trying to hook up a UPS to a Linux system, and are trying to using SNMPv3 (!), I would have expected you to have some computer awareness. If not, there should be hundreds if not thousands of folk at Georgia Tech that would be able to help you.

                        That said, I'll try a simple analogy. Coming into a support forum for a firewall distribution based on FreeBSD and asking a question about the NUT package on CentOS is akin to going into a BMW forum and asking a question about tire recommendations for a Honda. It doesn't matter that both cars use tires, the question is completely out of scope for the audience.

                        Also, you had already asked your question upstream in the NUT users list. If the terms upstream and downstream don't make sense, ask some of the people around you.

                        K 1 Reply Last reply Reply Quote 1
                        • K
                          kaeny123 @dennypage
                          last edited by

                          @dennypage said in NUT package:

                          @kaeny123 Given that you are trying to hook up a UPS to a Linux system, and are trying to using SNMPv3 (!), I would have expected you to have some computer awareness. If not, there should be hundreds if not thousands of folk at Georgia Tech that would be able to help you.

                          That said, I'll try a simple analogy. Coming into a support forum for a firewall distribution based on FreeBSD and asking a question about the NUT package on CentOS is akin to going into a BMW forum and asking a question about tire recommendations for a Honda. It doesn't matter that both cars use tires, the question is completely out of scope for the audience.

                          Also, you had already asked your question upstream in the NUT users list. If the terms upstream and downstream don't make sense, ask some of the people around you.

                          Well, other than the blatant condescending tone, I understand what you mean. I was being modest when I said I was new to this. And it turns out my issue wasn't computer knowledge related. I should've checked the forum topic first, this just came as a result of googling.

                          Thank you for your replies, they were very helpful :)

                          dennypageD 1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @kaeny123
                            last edited by

                            @kaeny123 said in NUT package:

                            Well, other than the blatant condescending tone, I understand what you mean. I was being modest when I said I was new to this. And it turns out my issue wasn't computer knowledge related. I should've checked the forum topic first, this just came as a result of googling.

                            Thank you for your replies, they were very helpful :)

                            Dial it back son. You asked me to explain so you could avoide the same mistake in the future, and I did. Computer awareness meant understanding the difference between CentOS and a firewall distribution based on FreeBSD. This was not indented to be condescending.

                            1 Reply Last reply Reply Quote 0
                            • J
                              joesl
                              last edited by joesl

                              Hello all,

                              Trying to get NUT working with a local-usb apc back-ups pro (on pfsense ☺ ).

                              ugen0.2: <American Power Conversion Back-UPS RS 900G FW879.L4 .I USB FWL4> at usbus0
                              

                              I've configured the pfsense package gui with a random name, driver usbhid-ups and "Local USB" as type. Nothing else.

                              cat /usr/local/etc/nut/ups.conf
                              [APC_Back-UPS_PRO_900]
                              driver=usbhid-ups
                              port=auto
                              

                              Nothing works and I see:

                              Oct 19 16:33:25	upsd	15243	User local-monitor@::1 logged into UPS [APC_Back-UPS_PRO_900]
                              Oct 19 16:33:25	upsmon	14608	Poll UPS [APC_Back-UPS_PRO_900] failed - Driver not connected
                              Oct 19 16:33:25	upsmon	14608	Communications with UPS APC_Back-UPS_PRO_900 lost
                              Oct 19 16:33:30	upsmon	14608	Poll UPS [APC_Back-UPS_PRO_900] failed - Driver not connected
                              Oct 19 16:33:30	upsmon	14608	UPS APC_Back-UPS_PRO_900 is unavailable
                              Oct 19 16:33:35	upsmon	14608	Poll UPS [APC_Back-UPS_PRO_900] failed - Driver not connected
                              

                              Could someone please point me in the right direction?
                              (the same worked out of the box with apcupsd)

                              Thanks

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage
                                last edited by

                                The messages you are looking for are those from process "usbhid-ups". You can find them by going into the system logs (Status / System Logs / System / General), selecting the funnel icon, and then inputing "usbhid-ups" in the Process field.

                                Perhaps to short circuit the process, have you rebooted or unplugged / replugged the UPS since you installed it? If not, it's likely a permissions problem.

                                J 1 Reply Last reply Reply Quote 0
                                • J
                                  joesl @dennypage
                                  last edited by

                                  @dennypage you are right; rebooting the device did the trick. Thanks.

                                  1 Reply Last reply Reply Quote 0
                                  • Q
                                    q54e3w
                                    last edited by

                                    Is there anyway to silence the NUT error reporting I'm seeing? I've tested my setup and it appears to work correctly so appears to be info rather than a warning.

                                    <snip>
                                    Dec 31 15:15:10	snmp-ups	91308	dstate_setflags: base variable (battery.charge.low) is immutable
                                    Dec 31 15:14:38	snmp-ups	91308	dstate_setflags: base variable (battery.charge.low) is immutable
                                    Dec 31 15:14:06	snmp-ups	91308	dstate_setflags: base variable (battery.charge.low) is immutable
                                    Dec 31 15:13:34	snmp-ups	91308	dstate_setflags: base variable (battery.charge.low) is immutable
                                    and repeat.....
                                    

                                    my additional driver appear correct to me are

                                    ignorelb
                                    override.battery.charge.low = 50
                                    

                                    thanks for any info

                                    dennypageD 1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage @q54e3w
                                      last edited by

                                      @q54e3w said in NUT package:

                                      Is there anyway to silence the NUT error reporting I'm seeing?

                                      To my knowledge, you cannot silence the error. You are attempting to set a variable in the UPS snmp module that you do not have permission to change (battery.charge.low).

                                      Remove

                                      ignorelb
                                      override.battery.charge.low = 50

                                      from the advanced parameters.

                                      For snmp, you generally have to set variables in the ups using either upsrw (with snmp write access) or a proprietary application. Occasionally you can also use http/https.

                                      You can learn more in the archive of the nut users mailing list.

                                      1 Reply Last reply Reply Quote 0
                                      • Q
                                        q54e3w
                                        last edited by q54e3w

                                        That fixed that error, thank you, I can configure those values through my Eaton web configuration page as you suggested.
                                        I'm seeing different behavior with this Eaton 9px than my previous APC. Once the battery level falls below my predetermined level (87% for testing) the ups.status turns to OB OFF OB, ESXi shuts down VMs then itself, but pfSense doesn't ever initiate its own shut down. I have 'FINALDELAY 600' in my upsmon.conf additional parameters to give ESXi time to shutdown, however there no progress from pfSense reporting UPS UPS on battery.

                                        upsrw ups
                                        [battery.charge.low]
                                        Remaining battery level when UPS switches to LB (percent)
                                        Type: STRING
                                        Maximum length: 2
                                        Value: 87
                                        
                                        [outlet.desc]
                                        Outlet description
                                        Type: STRING
                                        Maximum length: 20
                                        Value: Main Outlet
                                        
                                        [ups.delay.shutdown]
                                        Interval to wait after shutdown with delay command (seconds)
                                        Type: STRING
                                        Maximum length: 6
                                        Value: 20
                                        
                                        [ups.delay.start]
                                        Interval to wait before (re)starting the load (seconds)
                                        Type: STRING
                                        Maximum length: 6
                                        Value: 30
                                        
                                        [ups.start.auto]
                                        UPS starts when mains is (re)applied
                                        Type: ENUM
                                        Option: "yes" SELECTED
                                        Option: "no"
                                        
                                        
                                        
                                        upsc ups
                                        ambient.humidity: 47.40
                                        ambient.temperature: 11.7
                                        battery.charge: 70.00
                                        battery.charge.low: 87
                                        battery.runtime: 12652.00
                                        battery.runtime.low: 13000.00
                                        battery.voltage: 49.00
                                        device.mfr: Eaton
                                        device.model: Eaton 9PX
                                        device.serial: GA18H32185
                                        device.type: ups
                                        driver.name: snmp-ups
                                        driver.parameter.pollinterval: 2
                                        driver.parameter.port: 192.168.10.52
                                        driver.parameter.synchronous: no
                                        driver.version: 2.7.4
                                        driver.version.data: mge MIB 0.5
                                        driver.version.internal: 0.97
                                        input.phases: 1.00
                                        input.transfer.reason: input voltage out of range
                                        outlet.desc: Main Outlet
                                        outlet.id: 0
                                        output.current: 2.00
                                        output.frequency: 60.00
                                        output.phases: 1.00
                                        output.voltage: 119.00
                                        ups.beeper.status: enabled
                                        ups.delay.shutdown: 20
                                        ups.delay.start: 30
                                        ups.firmware: 01.14.4257
                                        ups.firmware.aux: LB
                                        ups.load: 21.00
                                        ups.mfr: Eaton
                                        ups.model: Eaton 9PX
                                        ups.serial: 111122223333
                                        ups.start.auto: yes
                                        ups.status: OB OFF OB
                                        ups.test.result: done and passed
                                        ups.timer.reboot: -1.00
                                        ups.timer.shutdown: -1.00
                                        ups.timer.start: -1.00
                                        
                                        
                                        dennypageD 1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage @q54e3w
                                          last edited by

                                          @q54e3w Unless you are running NUT on pfSense as a NUT master with slaves on other systems, you should not be setting FINDELAY on pfSense. Also, 10 minutes is an incredibly long time...

                                          I'm not very knowledgable about Eaton, but you may also need to set some variables for the snmp driver. See the snmp-ups man page for detail on what is available. Perhaps the polling frequency is too short to constantly catch a shutdown pending situation.

                                          1 Reply Last reply Reply Quote 0
                                          • Q
                                            q54e3w
                                            last edited by q54e3w

                                            Thanks for the pointers @dennypage, my problem appears to be resolved although I still need to tweak some final timings. Sharing here for any one else who runs across this issue.
                                            The solution was that the snmp drivers 'auto' detection mode resulted in a less than optimal mibs parameter causing improper device reporting. The Eaton manual states that the Network-MS card is compatible with following MIBs:

                                            • MIB II (RFC 1213)
                                            • Internet Engineering Task Force (IETF) Standard UPS MIB (RFC 1628)
                                            • EATON Pulsar MIB (ex MGE) V1.7
                                            • EATON Powerware MIB (PowerMib)

                                            Selecting the 'pw' mib allowed me to access the correct parameter and using a SNMP v1 write enabled passphrase allowed adjusting the shutdown parameters (although I've reverted to setting these in the UPS web UI). Adding 'overidelb' was needed to prod the correct OB/LB needed to initiative the shutdown procedure.

                                            mibs = pw
                                            pollfreq = 15
                                            community = private
                                            ignorelb
                                            

                                            The 10 minute FINALDELAY I had used was because pfSense in my master node and I want pfSense to stay up whilst my ESXi hosts shutdown the various VMs to ensure routing across VLANs for storage requirements is available.

                                            thanks again for your support and maintenance of this package.