NUT package (2.8.0 and below)
-
@kevindd992002 This is a basic NUT issue rather than a package issue. You'll need to diagnose this at the NUT level, and probably follow up with the NUT forum. I'd suggest you start by examining the log entries for NUT...
-
So I am able to monitor and query the values of the two ups that power my firewall, by adding a second one at Advance Settings under ups.conf
Any tips on what files, and their location the status widget uses to be able to modify and display data for each of the ups. (Hopefully something as simple as adding a loop or hardcoding a link for the second entry).
-
@josepr The pfSense NUT package is designed to supervise/monitor a single UPS only.
I'm curious as to why you have two UPSs on your firewall... does you firewall hardware have dual power supplies connected to separate UPSs?
-
@dennypage
Two ups each ones feeds a pdu which feeds a dual power supply host and other dual power equipment on a small 12U rack.
I am comfortable with programming and some html so wanted to see if could modify my copy of the package locally on my machine and make it work. -
@josepr
So was able to find the widget php and for now hardcode the second ups, havent had the chance to play with php before but will try to make it so that it can read all ups from the ups.conf and do something like the traffic or gateway widget were i can select which to display, get a chance to learn php.
-
@josepr said in NUT package:
Two ups each ones feeds a pdu which feeds a dual power supply host and other dual power equipment on a small 12U rack.
I see. Old school cool. Given the lower cost of hardware these days, I don't see that much anymore. These days I usually see dual systems, each with their own UPS, set up as a fault tolerant or load balanced pair. But you probably have that as well.
Unfortunately, while NUT itself has support for multiple power sources, the pfSense NUT package does not support that configuration. The pfSense NUT package is single UPS only. It would take quite a bit of work to make it support multiples in the various (extensive) configurations, and there really hasn't been any interest. You are actually the first to ask about it.
Probably your best bet is to use one of your other systems to run NUT on, and have that system initiate a remote shutdown of pfSense when the time comes. Sorry.
-
@josepr
Well I have it working for at least a nice widget displaying all the info for the attached ups, which was my main goal so i can get an idea of their status in one page, dont really have it shutting down anything at the moment maybe will get to that later.For anyone that is interested all I did was:
Modified '/usr/local/pkg/nut/nut.inc'
Added two functions:function nut_conf() { global $config; $conf = &$config['installedpackages']['nut']['config'][0]; return $conf; } function list_ups() { $upss = array(); $config = nut_conf(); if (isset($config['name'])) { $upss[] = $config['name']; } if (isset($config['ups_conf'])) { $conf = parse_ini_string(base64_decode($config['ups_conf']), true); foreach ($conf as $name => $_conf) { $upss[] = $name; } } return $upss; }
and modified the start of the nut_ups_status function
function nut_ups_status($name = null) { global $config; $status = array(); $nut_config = &$config['installedpackages']['nut']['config'][0]; if (isset($nut_config['type'])) { $type = $nut_config['type']; } else { $type = 'disabled'; } if ($type == 'disabled') { $status['_summary'] = "Monitoring is not enabled"; return $status; } $ups = $name ?: $nut_config['name'];
Then i modified /usr/local/www/widgets/widgets/nut_status.widget.php
<?php require_once("/usr/local/www/widgets/include/nut_status.inc"); require_once("/usr/local/pkg/nut/nut.inc"); if ($_REQUEST && $_REQUEST['ajax']) { print_all_table(); #Get multiple tables instead of just one. exit; } function print_row($desc, $value) { #didnt touch } function print_row_pct($desc, $value) { #didnt touch } function print_table($name) { $status = nut_ups_status($name); ##Only added the $name parameter, the rest stayed the same } #New Function to print a table per UPS function print_all_table() { print '<table class="table table-bordered table-dark"> <tbody>'; foreach (list_ups() as $name) { print '<tr class="panel-title"><td><b>' . $name . '</b></td></tr>'; print '<tr><td><div">'; print '<table class="table table-striped table-hover table-condensed">'; print '<tbody>' . print_table($name) . '</tbody>'; print '</table>'; print '</div></td></tr>'; } print '</tbody></table>'; } ?> <div class="table-responsive" id = "nuttable"> <?php print_all_table() ?> </div> <script type="text/javascript"> #Didnt touch </script>
And then add my second ups under the ups.conf advanced settings.
-
@josepr It might be a good idea to focus on correct NUT configuration before worrying about the monitoring widget. It appears that you've set up a situation in which the pfSense box will shutdown if either UPS fails, which I'm pretty sure is not what you want. For the work that you're doing, it would be simpler to abandon the pfSense NUT package and just configure NUT directly. Of course, you'll loose the pretty widget, but it would be a lot safer.
The APC UPSs are SNMP based, and also have their own web interface. Is there a reason you are focused on having status displayed in pfSense widgets? Instead of using their built-in web monitoring? Or an SNMP web based monitor such as Librenms or the like?
-
@dennypage
Actions are not taken for the device configured at ups.conf, this is only for the upsd service which setups communications with devices and can also provide access to this devices to other remote services such as a remote upsmon instance in another server.
upsmon is the service that actually enforces action and it has its own configuration which the package only generates an entry for the UPS configured the normal way, I did add a two liner to the Advance part so that it acts when both UPS are down.Auto generated by the package for UPSMON
MONITOR ups-2 1 local-monitor **** master SHUTDOWNCMD "/sbin/shutdown -p +0" POWERDOWNFLAG /etc/killpower
With addition to the upsmon.conf at advance in gui
MONITOR ups-2 1 local-monitor **** master SHUTDOWNCMD "/sbin/shutdown -p +0" POWERDOWNFLAG /etc/killpower ###ADDED LINES upsmon.conf#### MONITOR ups-1 1 local-monitor2 **** master MINSUPPLIES 1
Did also have to add an extra user in upsd.users as the package generates a random password everytime it saves for local-monitor
[local-monitor2] password=**** upsmon master
This tells upsmon that it should monitor the 2 ups, that both UPS provide power for one PSU in the server and that it needs a minimum of one power supply to operate, so it is now fault tolerant (Will only conduct a shutdown if both UPS are down/critical power).
The reason i add them to PFSENSE is that it depends on both UPS so I wanted a way to make sure it reflected this and didnt try anything drastic when one UPS is offline.
It is my always on device and the last device to be shutdown and can it act as a ups provider to any other nut clients in other devices. -
@josepr said in NUT package:
This tells upsmon that it should monitor the 2 ups, that both UPS provide power for one PSU in the server and that it needs a minimum of one power supply to operate, so it is now fault tolerant (Will only conduct a shutdown if both UPS are down/critical power).
MINSUPPLIES was not shown in the configuration you posted previously.
-
@dennypage
Yes, but i also hadnt added
MONITOR ups-1 1 local-monitor2 **** master
to upsmon so it was not watching/monitoring the second ups. -
I have a NUT setup that used to work, but stopped working at some point (I don't know when)
UPS type:
snmpextra arguments:
pollfreq=1upsd.conf:
LISTEN pfsenseupsd.users:
[upsremote]
password = blablabla
upsmon masterlog:
Oct 5 19:24:07 php-fpm 352 /nut_settings.php: Beginning configuration backup to https://acb.netgate.com/save
Oct 5 19:24:08 upsmon 6682 Poll UPS [tripplite1] failed - Driver not connected
Oct 5 19:24:09 php-fpm 352 /nut_settings.php: End of configuration backup to https://acb.netgate.com/save (success).
Oct 5 19:24:09 php-fpm 352 /nut_settings.php: Stopping service nut
Oct 5 19:24:09 upsmon 6682 Signal 15: exiting
Oct 5 19:24:09 upsd 7295 User local-monitor@::1 logged out from UPS [tripplite1]
Oct 5 19:24:09 upsd 7295 mainloop: Interrupted system call
Oct 5 19:24:09 upsd 7295 Signal 15: exiting
Oct 5 19:24:09 php-fpm 352 /nut_settings.php: Starting service nut
Oct 5 19:24:09 upsmon 88547 Startup successful
Oct 5 19:24:10 upsd 89034 listening on pfsense port 3493
Oct 5 19:24:10 upsd 89034 listening on ::1 port 3493
Oct 5 19:24:10 upsd 89034 listening on 127.0.0.1 port 3493
Oct 5 19:24:10 upsd 89034 Can't connect to UPS [tripplite1] (snmp-ups-tripplite1): No such file or directory
Oct 5 19:24:10 upsd 89336 Startup successful
Oct 5 19:24:12 upsd 89336 User local-monitor@::1 logged into UPS [tripplite1]
Oct 5 19:24:12 upsmon 88697 Poll UPS [tripplite1] failed - Driver not connected
Oct 5 19:24:12 upsmon 88697 Communications with UPS tripplite1 lost
Oct 5 19:24:13 php 10742 nut_email.php: Message sent to logger@gentooserver.dehnel.info OK
Oct 5 19:24:17 upsmon 88697 Poll UPS [tripplite1] failed - Driver not connected
Oct 5 19:24:17 upsmon 88697 UPS tripplite1 is unavailable
Oct 5 19:24:18 php 19486 nut_email.php: Message sent to logger@gentooserver.dehnel.info OK -
@gooberpatrol66 You haven't included the pertinent portions of your config, but best guess based on the log is that you are simply not able to connect to the UPS.
- Be sure that you are referring to the UPS by address. Don't depend upon host name resolution for a UPS.
- Confirm that you can actually access the UPS with the SNMP credentials specified.
Unrelated, but a poll frequency of 1 is really overkill. The default of 5 works just fine. The lowest poll frequency recommended by NUT is 2.
-
@dennypage Hello(Sorry for my english)
pfeens 2.5.2 + Nut + UPS Ippon Back Basic 650 (connected Usb Driver Blazer).
Turned on nut and set it up
There was a problem with the definition UPS Ippon after reboot pfsens (Before restarting the UPS, it is determined).
-
There was a blackout in my house a few days ago. I've noticed a very weird behavior with my Eaton UPS while I was actually monitoring the shutdown process. Here are the logs:
Oct 11 11:49:14 kernel Origin="AuthenticAMD" Id=0x730f01 Family=0x16 Model=0x30 Stepping=1 Oct 11 11:49:14 kernel CPU: AMD GX-412TC SOC (998.15-MHz K8-class CPU) Oct 11 11:49:14 kernel VT(vga): resolution 640x480 Oct 11 11:49:14 kernel FreeBSD clang version 10.0.1 (git@github.com:llvm/llvm-project.git llvmorg-10.0.1-0-gef32c611aa2) Oct 11 11:49:14 kernel FreeBSD 12.2-STABLE fd0f54f44b5c(RELENG_2_5_0) pfSense amd64 Oct 11 11:49:14 kernel FreeBSD is a registered trademark of The FreeBSD Foundation. Oct 11 11:49:14 kernel The Regents of the University of California. All rights reserved. Oct 11 11:49:14 kernel Copyright (c) 1979, 1980, 1983, 1986, 1988, 1989, 1991, 1992, 1993, 1994 Oct 11 11:49:14 kernel Copyright (c) 1992-2020 The FreeBSD Project. Oct 11 11:49:14 kernel ---<<BOOT>>--- Oct 11 11:49:14 syslogd kernel boot file is /boot/kernel/kernel Oct 11 11:42:10 kernel done. Oct 11 09:48:27 shutdown 45407 power-down by root: Oct 11 09:48:25 upsd 61950 User monuser@192.168.10.10 logged into UPS [ups] Oct 11 09:48:22 upsmon 18273 Auto logout and shutdown proceeding Oct 11 09:48:22 upsmon 18273 Executing automatic power-fail shutdown Oct 11 09:48:21 upsd 61950 User monuser@192.168.10.10 logged out from UPS [ups] Oct 11 09:47:18 php 27924 nut_email.php: Message sent to kevindd992002@yahoo.com OK Oct 11 09:47:04 upsd 61950 Client local-monitor@::1 set FSD on UPS [ups] Oct 11 09:47:04 upsmon 18273 UPS ups battery is low
The weird behavior was that after the UPS gets a shutdown command from pfsense NUT, it shuts itself down, cuts power off from the load and then turns back on right away even though there is no power from the mains yet. And then it shuts itself down again and continues this cycle until the battery gets depleted. Any ideas what's causing this?
Also, at 9:48:21 I see a logout from one of the remote monitors, but why is there another login event at 9:48:25 right before the shutdown event by root at 09:48:27?
-
@kevindd992002 said in NUT package:
Any ideas what's causing this?
The BIOS of your pfSense uses the setting "Auto power on when power comes back".
So, when the power comes back, it will boot again.
This will loop until a) the power comes back and b) the battery is charged enough so NUT decides to stay 'on'.Easiest solution : don't auto boot when the power comes back. This means that the shut down is controlled, but human presence is needed to switch it on again.
Best solution : Have a talk with your USP. Ask it to power the oullets when a and b or ok.
This best solution is often not possible with a typical SoHO UPS. -
@gertjan said in NUT package:
@kevindd992002 said in NUT package:
Any ideas what's causing this?
The BIOS of your pfSense uses the setting "Auto power on when power comes back".
So, when the power comes back, it will boot again.
This will loop until a) the power comes back and b) the battery is charged enough so NUT decides to stay 'on'.Easiest solution : don't auto boot when the power comes back. This means that the shut down is controlled, but human presence is needed to switch it on again.
Best solution : Have a talk with your USP. Ask it to power the oullets when a and b or ok.
This best solution is often not possible with a typical SoHO UPS.Perhaps I should've been more clear with my post. This cycle happens when there are no power in the mains yet. So imagine the UPS being shutdown by pfsense and then it cuts power from its outlets and then supplies power again to them (from battery). Why would the UPS do this if it was instructed to stay off until power from the mains come back?
I have another UPS (APC) connected to another pfsense box and when it shuts down, it stays shutdown until the mains come back. After the mains come back, pfsense (and all other NUT clients) power on and NUT knows not to initiate another shutdown event even though the thresholds are still being reached because it knows that the UPS is using mains power. This avoids the cycle you are describing.
-
@andreymoiseev Can't tell anything without log info. Have you tried restarting the service? (first icon on the Status line)
-
@kevindd992002 said in NUT package:
Perhaps I should've been more clear with my post. This cycle happens when there are no power in the mains yet.
That's what I understood.
The UPS shuts down the outlets (probably because not enough energy in the battery to sustain a valid AC voltage.@kevindd992002 said in NUT package:
So imagine the UPS being shutdown by pfsense and then it cuts power from its outlets and then supplies power again to them (from battery). Why would the UPS do this if it was instructed to stay off until power from the mains come back?
I might be wrong, but NUT only gets info from the UPS. It isn't sending anything to it.
So NUT can't tell the UPS "do this when that happens".
It's the UPS that sends over a status of the UPS when it is asked to do so.
The answer contain online/offline status, and battery charge status, and some more details.
Based on the UPS status, NUT does all the action work.I've never seen an option like "if battery is lower then 10 % then shut down outlets" and "switch outlets back on when power is back and battery is more then 30 %".
Example : my UPS is called 'ups' in my pfSense.
[2.5.2-RELEASE][root@pfsense.my-network.tld]/root: /usr/local/bin/upsc ups@localhost battery.charge: 100 battery.charge.low: 10 battery.charge.warning: 50 battery.date: 2001/09/25 battery.mfr.date: 2019/06/25 battery.runtime: 828 battery.runtime.low: 120 battery.type: PbAc battery.voltage: 13.5 battery.voltage.nominal: 12.0 device.mfr: American Power Conversion device.model: Back-UPS XS 700U device.serial: 3B1926X61525 device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.synchronous: no driver.version: 2.7.4 driver.version.data: APC HID 0.96 driver.version.internal: 0.41 input.sensitivity: medium input.transfer.high: 300 input.transfer.low: 150 input.voltage: 232.0 input.voltage.nominal: 230 ups.beeper.status: disabled ups.delay.shutdown: 20 ups.firmware: 924.Z5 .I ups.firmware.aux: Z5 ups.load: 35 ups.mfr: American Power Conversion ups.mfr.date: 2019/06/25 ups.model: Back-UPS XS 700U ups.productid: 0002 ups.realpower.nominal: 390 ups.serial: 3B1926X61525 ups.status: OL ups.test.result: No test initiated ups.timer.reboot: 0 ups.timer.shutdown: -1 ups.vendorid: 051d
I can read these parameters but the thing is : can we set (some of) them ?
@kevindd992002 said in NUT package:
I have another UPS (APC) connected to another pfsense box and when it shuts down, it stays shutdown until the mains come back. After the mains come back, pfsense (and all other NUT clients) power on
That's seems the correct behaviour to me.
@kevindd992002 said in NUT package:
and NUT knows not to initiate another shutdown event even though the thresholds are still being reached because it knows that the UPS is using mains power. This avoids the cycle you are describing.
The thing is : NUT has does nothing to here.
The 'mains' is up - the 'battery is charging' as these are told to NUT when it asked the UPS for info.Btw : As you can see, I'm using also an APC. Not saying hey are the best, they 'work' pretty well.
-
@gertjan said in NUT package:
@kevindd992002 said in NUT package:
Perhaps I should've been more clear with my post. This cycle happens when there are no power in the mains yet.
That's what I understood.
The UPS shuts down the outlets (probably because not enough energy in the battery to sustain a valid AC voltage.Are you saying that when a blackout occurs, only the remote and local (pfsense) monitors shut down and the UPS continues to supply power to the outlets until the battery gets drained?
I have this arguments set and I'm not sure if they make a difference in the event when all monitors are already in shutdown state:
override.battery.charge.warning = 80
override.battery.charge.low = 70
override.battery.runtime.low = 420@kevindd992002 said in NUT package:
So imagine the UPS being shutdown by pfsense and then it cuts power from its outlets and then supplies power again to them (from battery). Why would the UPS do this if it was instructed to stay off until power from the mains come back?
I might be wrong, but NUT only gets info from the UPS. It isn't sending anything to it.
So NUT can't tell the UPS "do this when that happens".
It's the UPS that sends over a status of the UPS when it is asked to do so.
The answer contain online/offline status, and battery charge status, and some more details.
Based on the UPS status, NUT does all the action work.I've never seen an option like "if battery is lower then 10 % then shut down outlets" and "switch outlets back on when power is back and battery is more then 30 %".
I thought it does both. @dennypage can probably confirm but I thought NUT is able to shut down the UPS outlets. What you're saying makes sense though.
Example : my UPS is called 'ups' in my pfSense.
[2.5.2-RELEASE][root@pfsense.my-network.tld]/root: /usr/local/bin/upsc ups@localhost battery.charge: 100 battery.charge.low: 10 battery.charge.warning: 50 battery.date: 2001/09/25 battery.mfr.date: 2019/06/25 battery.runtime: 828 battery.runtime.low: 120 battery.type: PbAc battery.voltage: 13.5 battery.voltage.nominal: 12.0 device.mfr: American Power Conversion device.model: Back-UPS XS 700U device.serial: 3B1926X61525 device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.synchronous: no driver.version: 2.7.4 driver.version.data: APC HID 0.96 driver.version.internal: 0.41 input.sensitivity: medium input.transfer.high: 300 input.transfer.low: 150 input.voltage: 232.0 input.voltage.nominal: 230 ups.beeper.status: disabled ups.delay.shutdown: 20 ups.firmware: 924.Z5 .I ups.firmware.aux: Z5 ups.load: 35 ups.mfr: American Power Conversion ups.mfr.date: 2019/06/25 ups.model: Back-UPS XS 700U ups.productid: 0002 ups.realpower.nominal: 390 ups.serial: 3B1926X61525 ups.status: OL ups.test.result: No test initiated ups.timer.reboot: 0 ups.timer.shutdown: -1 ups.vendorid: 051d
I can read these parameters but the thing is : can we set (some of) them ?
I know in the past @dennypage confirmed that some of the parameters can be modified.
@kevindd992002 said in NUT package:
I have another UPS (APC) connected to another pfsense box and when it shuts down, it stays shutdown until the mains come back. After the mains come back, pfsense (and all other NUT clients) power on
That's seems the correct behaviour to me.
@kevindd992002 said in NUT package:
and NUT knows not to initiate another shutdown event even though the thresholds are still being reached because it knows that the UPS is using mains power. This avoids the cycle you are describing.
The thing is : NUT has does nothing to here.
The 'mains' is up - the 'battery is charging' as these are told to NUT when it asked the UPS for info.Btw : As you can see, I'm using also an APC. Not saying hey are the best, they 'work' pretty well.
I see. So since the UPS tells NUT it is using mains power, NUT doesn't do any of its power shutdown sequences, correct?