    NUT server and UPS general question

    General pfSense Questions
    6
    71
    12.9k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • N
      netboy @dennypage
      last edited by

      @dennypage Excellent point.
      First iteration (I am learning).... I need a visibility of all the UPS's. Right now I don't. I want to know how healthy the UPS's are and so on.....

      On second iteration (After I have learned a little).... I would like NUT to control shut down UPS 3

      UPS 1

      • Modem

      • Router

      • POE switches

      UPS 2

      • Dump Switches

      • HDHomerun

      • Raspberry PI which has NUT installed

      UPS 3

      • 3 servers

      UPS 4

      • Attached to NAS which can communicate to UPS

      I want UPS 3 to control shut down my servers. Is this possible using NUT (I know you are the package owner and are very knowledgeable). My servers are debian UBUNTU. UPS 1: I really do not care about control shut down because there is nothing to fail (like hard disk getting corrupted and so on ) and also they have the max run time. Regarding UPS 3 I really do not care because they are just switches. Worst case things attached to the switches will not work.

      What do you think? Can I make UBUNTU servers talk to NUT and control shut down?

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @netboy
        last edited by

        @netboy Yes, you can do all this with NUT. This would be more appropriate to the the NUT users list, but the general gist is this...

        UPS 1: Attach the UPS to some system and run NUT as monitor only (use 0 as the power value for upsmon).

        UPS 2: Run standard NUT Primary on the Pi.

        UPS 3: Pick a system to be the Primary and run a standard NUT Primary install on that system. Run NUT Secondary on the other systems using remote NUT to the Primary.

        UPS 4: Run NUT on the NAS. If Synology or QNAP, this is the standard supported UPS install.

        In addition to the above, run upsmon on the Pi to monitor all the UPSs and display status with cgi scripts. Look for upsstats.

        Lots of reading for you to do... ๐Ÿ˜€

        N 1 Reply Last reply Reply Quote 1
        • N
          netboy @dennypage
          last edited by

          @dennypage @dennypage said in NUT server and UPS general question:

          UPS 3: Pick a system to be the Primary and run a standard NUT Primary install on that system. Run NUT Secondary on the other systems using remote NUT to the Primary.

          Let me parse your reply ๐Ÿ˜•
          In my case 3 servers....Pick one server as PRIMARY say server 1 and install standard NUT on server 1. Install NUT secondary on server 2 and server 3. Run Remote NUT to the primary. I am going NUTS. In other words this UPS 3 is stand alone "farm" no connection to NUT installed in raspberry PI.

          UPS 1: Attach the UPS to some system and run NUT as monitor only (use 0 as the power value for upsmon).
          UPS 2: Run standard NUT Primary on the Pi.

          For above 2 scenario's Rasberry PI is to be used. The configuration for NUT in PI for UPS 1 is monitor only and UPS 2 is standard NUT as primary

          Have I understood it marginally?

          N dennypageD 2 Replies Last reply Reply Quote 0
          • N
            netboy @netboy
            last edited by

            @netboy dennypage, I did some reading......
            The UPS 3 has 3 servers and one of them is Openmediavault (OMV) and 2 of them or ubuntu.

            It so happens, OMV has a NUT package and I installed it after making sure my UPS is connected to OMV using USB (checked lsusb to make sure the UPS shows up). The package worked as standalone.

            The package has another option called REMOTE MONITORING (Enable remote monitoring of the local connected UPS.) which I believe is a server mode (or PRIMARY in your speak as I understand).
            So here is what I think are my next steps:

            • Enable server mode in OMV (with some username/pswd)

            • Install NUT client in server 2 and 3 (ubuntu) and point them to OMV using username/pswd (SECONDARY in your speak)

            And finagle it to work.

            Have I got it right so far?

            dennypageD 1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage @netboy
              last edited by

              @netboy said in NUT server and UPS general question:

              In my case 3 servers....Pick one server as PRIMARY say server 1 and install standard NUT on server 1. Install NUT secondary on server 2 and server 3. Run Remote NUT to the primary. I am going NUTS. In other words this UPS 3 is stand alone "farm" no connection to NUT installed in raspberry PI.

              Server 1 would be the NUT Primary (NUT's new term--previously called master), and would perform the actual control of the UPS. Server 2 & 3 would be Secondaries (previously called slaves), and take their instruction from the Primary. When the Primary says "time to shut down" the Secondaries shut down and disconnect from the Primary, after which the Primary shuts down which kills UPS power.

              Note that you can still "monitor" the the Server 1 UPS using NUT on another host (Pi). You would configure it as a Secondary, but use a power value of 0 to indicated that you are not actually connected to the UPS on Server 1. You can use this approach to monitor all the other UPSs from the Pi as well.

              N 2 Replies Last reply Reply Quote 0
              • dennypageD
                dennypage @netboy
                last edited by

                @netboy said in NUT server and UPS general question:

                It so happens, OMV has a NUT package and I installed it after making sure my UPS is connected to OMV using USB (checked lsusb to make sure the UPS shows up).

                Just about everyone has a NUT package. It's pretty universal.

                Have I got it right so far?

                I believe so.

                N 1 Reply Last reply Reply Quote 0
                • N
                  netboy @dennypage
                  last edited by

                  @dennypage Thank you.... shall read more and figure it out

                  1 Reply Last reply Reply Quote 0
                  • N
                    netboy @dennypage
                    last edited by

                    This post is deleted!
                    1 Reply Last reply Reply Quote 0
                    • N
                      netboy @dennypage
                      last edited by

                      @dennypage said in NUT server and UPS general question:

                      Server 1 would be the NUT Primary (NUT's new term--previously called master), and would perform the actual control of the UPS. Server 2 & 3 would be Secondaries (previously called slaves), and take their instruction from the Primary. When the Primary says "time to shut down" the Secondaries shut down and disconnect from the Primary, after which the Primary shuts down which kills UPS power.
                      Note that you can still "monitor" the the Server 1 UPS using NUT on another host (Pi). You would configure it as a Secondary, but use a power value of 0 to indicated that you are not actually connected to the UPS on Server 1. You can use this approach to monitor all the other UPSs from the Pi as well.

                      Very useful info....thanks

                      N 1 Reply Last reply Reply Quote 0
                      • N
                        netboy @netboy
                        last edited by netboy

                        @netboy dennypage I got everything working....

                        Now based on my success I would like to monitor the UPS attached to the Netgate router.

                        I earlier installed apc package and it worked fine. I uninstalled the same and installed NUT.

                        SSH into netgate and it reported the UPS.
                        [22.05-RELEASE][admin@router2100.xxx.local]/root: usbconfig
                        ugen0.1: <Marvell XHCI root HUB> at usbus0, cfg=0 md=HOST spd=SUPER (5.0Gbps) pwr=SAVE (0mA)
                        ugen1.1: <Marvell EHCI root HUB> at usbus1, cfg=0 md=HOST spd=HIGH (480Mbps) pwr=SAVE (0mA)
                        ugen1.2: <American Power Conversion Back-UPS ES 750G FW:841.I4 .D USB FW:I4> at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (2mA)

                        My config on the NUT in netgate is as follows:

                        5a7e9fdf-ed91-4dea-853c-fa1522b53a98-image.png

                        However I am not having any success!!

                        9f0d885f-b5d0-453d-ae30-9a47edd0d60a-image.png

                        Any tips for troubleshooting?

                        After some time in SSH I get this message:

                        d40b2c50-d338-438b-a9ea-d0d4c9cb6332-image.png Broadcast Message from root@router2100.480.local
                        (no tty) at 12:41 EST...

                        UPS netgateUPS is unavailable

                        dennypageD 1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage @netboy
                          last edited by

                          @netboy said in NUT server and UPS general question:

                          Any tips for troubleshooting?

                          Yes:

                          1. Remove everything from the Advanced settings section and leave it empty. [FYI: The lines you have are in the wrong section; The USB driver doesn't take a port. Some UPSs don't like to be polled too frequently.] Later, you can add lines to the "Additional configuration lines for upsd.users" section to allow remote access, but even then leave all the other sections empty.

                          2. If you haven't rebooted since you installed NUT, you need to do so. Alternatively, you can do an unplug and replug (see elsewhere in this thread), but the easiest thing to do is to reboot.

                          N 1 Reply Last reply Reply Quote 0
                          • N
                            netboy @dennypage
                            last edited by netboy

                            @dennypage Thanks
                            Followed your advice and it works now ....
                            e5aab3cc-5887-4a08-b410-e72de5115744-image.png
                            I added users to the upsd.users and "pointed" the hosts.conf and upsmon.conf on the raspberry pi.
                            The raspberry pi shows the drop down but when I select the one nothing shows up! Other drop down works like a charm.
                            Any other config I must change in netgate?

                            e0f5129c-0d32-4589-a5f4-42d477607868-image.png

                            The selection of "netgate UPS" does nothing and shows connection failure

                            dennypageD 1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage @netboy
                              last edited by

                              @netboy said in NUT server and UPS general question:

                              The selection of "netgate UPS" does nothing and shows connection failure

                              I note that in one location you have "netgateUPS" and in another you have "netgate UPS". FWIW, I recommend that you stay away from spaces in names.

                              N 1 Reply Last reply Reply Quote 0
                              • N
                                netboy @dennypage
                                last edited by netboy

                                @dennypage Hey dennypage the drop down shows the description as listed in Raspberry Pi hosts.conf

                                MONITOR netgateUPS@192.168.0.1 "Netgate UPS"

                                IMHO, I do not think this is the issue.

                                FYI, i have added the following user in netgate config:
                                [monslave]
                                password = {somepassword}
                                upsmon slave

                                Added the following in upsmon.conf in raspberry pi;

                                MONITOR netgateUPS@192.168.0.1 0 monslave {pswd for monslave} slave

                                dennypageD 1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage @netboy
                                  last edited by

                                  @netboy Please post your upsd.users and upsmon.conf from both systems.

                                  N 1 Reply Last reply Reply Quote 0
                                  • N
                                    netboy @dennypage
                                    last edited by netboy

                                    @dennypage
                                    Sure here we go...

                                    Masked password as xxxx, yyyy and zzzz - BTW there are no spaces in my password:

                                    netgate - upsd.users

                                    [admin]
                                    password = xxxxx
                                    actions = set
                                    actions = fsd
                                    instcmds = ALL

                                    [monmaster]
                                    password = yyyyy
                                    upsmon master

                                    [monslave]
                                    password = zzzzz
                                    upsmon slave

                                    pi- upsd.users

                                    [admin]
                                    password = nnnnnn
                                    actions = set
                                    actions = fsd
                                    instcmds = ALL

                                    [monmaster]
                                    password = uuuuuuu
                                    upsmon master

                                    [monslave]
                                    password = xxxxx
                                    upsmon slave

                                    netgate - upsmon.conf
                                    blanks no entries

                                    pi - upsmon.conf
                                    MONITOR netgateUPS@192.168.0.1 0 monslave zzzzz slave

                                    Am I missing MONITOR entries in upsmon.conf in netgate?

                                    dennypageD 1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage @netboy
                                      last edited by

                                      @netboy said in NUT server and UPS general question:

                                      netgate - upsmon.conf
                                      blanks no entries

                                      Based upon your prior screenshots, upsmon.conf on the pfSense system cannot be empty.

                                      Also, please post ups.conf from both systems.

                                      N 1 Reply Last reply Reply Quote 0
                                      • N
                                        netboy @dennypage
                                        last edited by

                                        @dennypage
                                        I added the following to

                                        netgate - upsmon.conf
                                        MONITOR netgateUPS@localhost 1 monmaster yyyyy master

                                        negate - ups.conf
                                        blanks no entries

                                        pi- ups.conf
                                        [powerStrip]
                                        driver = usbhid-ups
                                        port = auto
                                        vendorid = "051d"
                                        productid = "0002"
                                        desc = "APC BE600M1 600VA UPS"

                                        dennypageD 1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage @netboy
                                          last edited by

                                          @netboy said in NUT server and UPS general question:

                                          I added the following to
                                          netgate - upsmon.conf
                                          MONITOR netgateUPS@localhost 1 monmaster yyyyy master
                                          negate - ups.conf
                                          blanks no entries

                                          Something is wrong. ups.conf cannot be empty, and you should not need to edit upsmon.conf.

                                          Let's restart from the ground up and make sure we have a known, stable base.

                                          Go to Services -> UPS -> Settings.

                                          • Set "UPS Type" to "Local USB"
                                          • Set "UPS Name" to "ups"
                                          • Uncheck the "Enable notifications" box
                                          • Set "Driver" to "usbhid".
                                          • Clear any content in "Extra Arguments to driver"
                                          • Clear any content in all sections of "Advanced sections"

                                          After doing this, press save.

                                          Then, log in via terminal and execute the following:

                                          cat /usr/local/etc/nut/ups.conf
                                          cat /usr/local/etc/nut/upsd.conf
                                          cat /usr/local/etc/nut/upsd.users
                                          cat /usr/local/etc/nut/upsmon.conf
                                          

                                          And post the complete output of each.

                                          N 1 Reply Last reply Reply Quote 1
                                          • N
                                            netboy @dennypage
                                            last edited by netboy

                                            @dennypage
                                            masked passwords

                                            [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/ups.conf
                                            [ups]
                                            driver=usbhid-ups
                                            port=auto
                                            [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/upsd.conf
                                            LISTEN 127.0.0.1
                                            LISTEN ::1
                                            [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/upsd.users
                                            [admin]
                                            password=xxxxx
                                            actions=set
                                            instcmds=all
                                            [local-monitor]
                                            password=xxxxx
                                            upsmon master
                                            [22.05-RELEASE][admin@router2100.tttt.local]/root: cat /usr/local/etc/nut/upsmon.conf
                                            MONITOR ups 1 local-monitor xxxxx master
                                            SHUTDOWNCMD "/sbin/shutdown -p +0"
                                            POWERDOWNFLAG /etc/killpower
                                            [22.05-RELEASE][admin@router2100.tttt.local]/root:

                                            dennypageD 1 Reply Last reply Reply Quote 0