    More than one IPSec tunnel phase1 is fine, but adding another phase1 prevents an existing tunnel from re-establishing a connection
    17 Posts 4 Posters 3.4k Views 4 Watching
    • lifeboyL Offline
      lifeboy
      I have 5 different tunnels set up with IPSec in host-to-host config, which all run stable and without obvious problems.
      When I add a new tunnel phase1 (con10), all other phase1's stay connected, but as soon as I drop the con5 connection and try to re-establish it, it keeps on attempting to connect, but never succeeds. I can drop any other tunnel and it will immediately reconnect on the first try, but the last one previously added does not connect again.
      If I disable the phase 2 connections and also the the phase 1, then I can enable the tunnel in the config and all it well. It's when I enable the phase1 that the problem occurs with the con5 connection.
      This is weird and I'm at a loss for why this happens. I'm not event at the stage where I actually establish a connection with the far site on this link yet!
      How can this be?
      lifeboyL 1 Reply Last reply Reply Quote 0
      • lifeboyL Offline
        lifeboy @lifeboy
        I have attached ipsec.log
        It records what happens when I do the following:
        1. con10's status is disabled.
        2. con5's status is enabled and connected
        3. I enable con10 and con5 stays connected
        4. I then disconnect con5. It immediately attempts to reconnect, but fails and just shows "connecting" in the UI IPsec status
        5. I then disable con10 again and con5 connects immediately.
        BTW: Where is a disabled ipsec tunnel's config stored? Even a grep of the content of the pfSense is unable to locate it?? When I enable the tunnel it's added to /var/etc/ipsec/swanctl.conf, but from where?
        The config of both con5 and con10 are below:
        con5 {
                        # P1 (ikeid 5): Client5
                        fragmentation = yes
                        unique = replace
                        version = 2
                        proposals = aes256-sha256-modp2048
                        dpd_delay = 10s
                        rekey_time = 25920s
                        reauth_time = 0s
                        over_time = 2880s
                        rand_time = 2880s
                        encap = no
                        mobike = no
                        local_addrs = 197.214.xxx.yyy
                        remote_addrs = 196.250.xxx.yyy
                        local {
                                id = 197.214.xxx.yyy
                                auth = psk
                        remote {
                                id = %any
                                auth = psk
                        children {
                                con5 {
                                        # P2 (reqid 3): RC01 network
                                        mode = tunnel
                                        policies = yes
                                        life_time = 3600s
                                        rekey_time = 3240s
                                        rand_time = 360s
                                        start_action = trap
                                        remote_ts = 192.168.0.0/24
                                        local_ts = 192.168.152.0/29
                                        esp_proposals = aes256-sha256-modp2048
                                        dpd_action = trap
        con10 {
                        # P1 (ikeid 10): Client10
                        fragmentation = yes
                        unique = replace
                        version = 2
                        proposals = aes256gcm128-sha256-modp2048,aes256-sha256-modp2048
                        dpd_delay = 10s
                        rekey_time = 25920s
                        reauth_time = 0s
                        over_time = 2880s
                        rand_time = 2880s
                        encap = no
                        mobike = no
                        remote_addrs = 165.165.xxx.yyy
                        local {
                                auth = psk
                        remote {
                                id = %any
                                auth = psk
        • lifeboyL lifeboy referenced this topic on
        • lifeboyL Offline
          lifeboy @lifeboy
          Has anyone here ever experienced something like this? It seems @Gblenn is experiencing the same (or very similar) behaviour as posted here.
          @jimp, is it possible that a recent upgrade introduced some bug?
          • lifeboyL Offline
            lifeboy @lifeboy
            Interestingly: With con10 enabled I can disconnect any of the other connections and they will reconnect immediately. Only when I disconnect con5, is it not able to reconnect.
            The other connections are configured to use AES_GCM_16 (128), whereas con5 uses AES_CBC (256). Could that cause this link not to be able to re-establish ifself?
            • lifeboyL Offline
              lifeboy @lifeboy
              Figured out what is happening, but this seems like a bug that gets triggered by something we don't know yet.
              Looking at the /var/etc/ipsec/swanctl.conf, I note the following behaviour:
              1. There are multiple active connection configured in they are listed, which the last being con10.
              2. Con10 will connect fine in this scenario.
              3. If I enable (in the pfSense UI), con9, it will be inserted into the swanctl.conf file after the con10 configuration.
              4. Once con10 is not the last connection configurated in swanctl.conf, it doesn't connect anymore.
              5. I can work around the issue by enabling con9, establishing the connection and then disabling the config. The connection stays up and then I can connect con10.
              This is not normal, but I don't know how to resolve this.
              Below is the swanctl.conf file without con9 active (I have cut the secrets and public ip's)
              # This file is automatically generated. Do not edit
              connections {
              	bypass {
              		remote_addrs = 127.0.0.1
              		children {
              			bypasslan {
              				local_ts = 192.168.131.0/24
              				remote_ts = 192.168.131.0/24
              				mode = pass
              				start_action = trap
              	con3 {
              		# P1 (ikeid 3): customer1 - link1
              		fragmentation = yes
              		unique = replace
              		version = 2
              		proposals = aes128gcm128-sha256-modp2048,aes256gcm128-sha256-modp2048
              		dpd_delay = 10s
              		rekey_time = 77760s
              		reauth_time = 0s
              		over_time = 8640s
              		rand_time = 8640s
              		encap = no
              		mobike = no
              		remote_addrs = 105.27.aaa.bbb
              		local {
              			id = 197.214.119.130
              			auth = psk
              		remote {
              			id = 192.168.0.2
              			auth = psk
              		children {
              			con3 {
              				# P2 (reqid 9): M/Monit to Office LAN
              				# P2 (reqid 7): Unify to Office LAN
              				# P2 (reqid 6): GTS1 to Office LAN
              				mode = tunnel
              				policies = yes
              				life_time = 43196s
              				rekey_time = 38876s
              				rand_time = 4320s
              				start_action = trap
              				remote_ts = 172.16.3.0/24,172.16.3.0/24,172.16.3.0/24
              				local_ts = 192.168.131.191/32,192.168.131.177,192.168.131.174
              				esp_proposals = aes256gcm128-modp2048,aes256gcm96-modp2048,aes256gcm64-modp2048,aes128gcm128-modp2048,aes128gcm96-modp2048,aes128gcm64-modp2048
              				dpd_action = trap
              	con4 {
              		# P1 (ikeid 4): customer1 - link2
              		fragmentation = yes
              		unique = replace
              		version = 2
              		dpd_delay = 10s
              		rekey_time = 77760s
              		reauth_time = 0s
              		over_time = 8640s
              		rand_time = 8640s
              		encap = no
              		mobike = no
              		remote_addrs = 41.164.aaa.bbb
              		local {
              			auth = psk
              		remote {
              			id = 41.164.fff.ccc
              			auth = psk
              		children {
              			con4 {
              				# P2 (reqid 10): M/Monit to Office LAN backup
              				# P2 (reqid 8): Unify to Office LAN
              				# P2 (reqid 5): GTS1 to Office LAN
              				mode = tunnel
              				policies = yes
              				life_time = 43196s
              				rekey_time = 38876s
              				rand_time = 4320s
              				start_action = trap
              				local_ts = 192.168.131.191/32,192.168.131.177/32,192.168.131.174/32
              				dpd_action = trap
              	con10 {
              		# P1 (ikeid 10): Greenway Farm
              		fragmentation = yes
              		unique = replace
              		version = 2
              		dpd_delay = 10s
              		rekey_time = 544320s
              		reauth_time = 0s
              		over_time = 60480s
              		rand_time = 60480s
              		encap = no
              		mobike = no
              		remote_addrs = 165.165.bbb.ddd
              		local {
              			auth = psk
              		remote {
              			id = %any
              			auth = psk
              		children {
              			con10 {
              				# P2 (reqid 17): Greenway server
              				# P2 (reqid 16): Greenway server
              				# P2 (reqid 15): Greenway server
              				# P2 (reqid 14): Greenway server
              				# P2 (reqid 11): Greenway server
              				mode = tunnel
              				policies = yes
              				life_time = 604800s
              				rand_time = 60480s
              				start_action = trap
              				remote_ts = 10.10.3.0/24,10.10.4.0/24,192.168.3.0/24,10.10.2.0/24,192.168.1.0/24
              				local_ts = 192.168.153.0/24,192.168.153.0/24,192.168.153.0/24,192.168.153.0/24,192.168.153.0/24
              				esp_proposals = aes128gcm128,aes128gcm96,aes128gcm64
              				dpd_action = trap
              secrets {
              	ike-0 {
              		secret = <cut>
              		id-0 = %any
              		id-1 = 192.168.0.2
              	ike-1 {
              		secret = <cut>
              		id-0 = %any
              		id-1 = 41.164.ccc.ddd
              	ike-2 {
              		secret = <cut>
              		id-0 = %any
              		id-1 = %any
              • lifeboyL Offline
                lifeboy @lifeboy
                Here is the scanctl.conf file with the con9 enabled:
                connections {
                        bypass {
                                children {
                                        bypasslan {
                                                mode = pass
                                                start_action = trap
                        con3 {
                                fragmentation = yes
                                unique = replace
                                version = 2
                                dpd_delay = 10s
                                rekey_time = 77760s
                                reauth_time = 0s
                                over_time = 8640s
                                rand_time = 8640s
                                encap = no
                                mobike = no
                                local {
                                        auth = psk
                                remote {
                                        id = 192.168.0.2
                                        auth = psk
                                children {
                                        con3 {
                                                mode = tunnel
                                                policies = yes
                                                life_time = 43196s
                                                rekey_time = 38876s
                                                rand_time = 4320s
                                                start_action = trap
                                                dpd_action = trap
                        con4 {
                                fragmentation = yes
                                unique = replace
                                version = 2
                                dpd_delay = 10s
                                rekey_time = 77760s
                                reauth_time = 0s
                                over_time = 8640s
                                rand_time = 8640s
                                encap = no
                                mobike = no
                                local {
                                        auth = psk
                                remote {
                                        id = 41.164.aaa.bbb
                                        auth = psk
                                children {
                                        con4 {
                                                mode = tunnel
                                                policies = yes
                                                life_time = 43196s
                                                rekey_time = 38876s
                                                rand_time = 4320s
                                                start_action = trap
                                                dpd_action = trap
                        con10 {
                                fragmentation = yes
                                unique = replace
                                version = 2
                                dpd_delay = 10s
                                reauth_time = 0s
                                over_time = 60480s
                                rand_time = 60480s
                                encap = no
                                mobike = no
                                local {
                                        auth = psk
                                remote {
                                        id = %any
                                        auth = psk
                                children {
                                        con10 {
                                                mode = tunnel
                                                policies = yes
                                                life_time = 604800s
                                                rand_time = 60480s
                                                start_action = trap
                                                dpd_action = trap
                        con9 {
                                # P1 (ikeid 9): Reliance Compost
                                fragmentation = yes
                                unique = replace
                                version = 2
                                proposals = aes128gcm128-sha256-modp2048,aes128-sha256-modp2048
                                dpd_delay = 10s
                                reauth_time = 0s
                                over_time = 60480s
                                rand_time = 60480s
                                encap = no
                                mobike = no
                                remote_addrs = 196.250.eee.fff
                                local {
                                                mode = tunnel
                                                policies = yes
                                                life_time = 43196s
                                                rekey_time = 38876s
                                                rand_time = 4320s
                                                start_action = trap
                                                dpd_action = trap
                        con10 {
                                fragmentation = yes
                                unique = replace
                                version = 2
                                dpd_delay = 10s
                                reauth_time = 0s
                                over_time = 60480s
                                rand_time = 60480s
                                encap = no
                                mobike = no
                                local {
                                        auth = psk
                                remote {
                                        id = %any
                                        auth = psk
                                children {
                                        con10 {
                                                mode = tunnel
                                                policies = yes
                                                life_time = 604800s
                                                rand_time = 60480s
                                                start_action = trap
                                                dpd_action = trap
                        con9 {
                                fragmentation = yes
                                unique = replace
                                version = 2
                                dpd_delay = 10s
                                reauth_time = 0s
                                over_time = 60480s
                                rand_time = 60480s
                                encap = no
                                mobike = no
                                local {
                                        auth = psk
                                remote {
                                        id = %any
                                        auth = psk
                                children {
                                        con9 {
                                                # P2 (reqid 13): RC Subnet
                                                mode = tunnel
                                                policies = yes
                                                life_time = 3600s
                                                rekey_time = 3240s
                                                rand_time = 360s
                                                start_action = trap
                                                esp_proposals = aes128gcm128-modp2048,aes128gcm96-modp2048,aes128gcm64-modp2048
                                                dpd_action = trap
                secrets {
                        ike-0 {
                                secret = <cut>
                                id-0 = %any
                                id-1 = 192.168.0.2
                        ike-1 {
                                secret = <cut>
                                id-0 = %any
                                id-1 = 41.164.68.170
                        ike-2 {
                                secret = <cut>
                                id-0 = %any
                                id-1 = %any
                        ike-3 {
                                secret = <cut>
                                id-0 = %any
                                id-1 = %any
                So see now that my synopses was not quite correct. The con9 connection is now twice in the file. I suspect this causes problems?
                This seems to be a pfSense bug rather than something in the strongswan then?
                • lifeboyL Offline
                  lifeboy @lifeboy
                  After some enabling and disabling, I know have only one config per configured connection in swanctl.conf, but the behaviour has not changed. I don't know why, since I didn't really make any significant changes, but that's what is like now.
                  The connection for con10 cannot be established when the config for con9 is present (after the config for con10 in the file). If con10 is the last, then it can be established.
                  con9 is site-to-site with a RouterOS device.
                  con10 is site-to-site with a Sophos device.
                  The other 2 (con3 and con4) are to a Fortigate and can be disconnected and reconnected on demand.
                  @jimp, should I open a bug report for this? I don't want to make noise in redmine if it's a false alarm, so please advise if you can.
                  lifeboyL 2 Replies Last reply Reply Quote 0
                  • lifeboyL Offline
                    lifeboy @lifeboy
                    • jimpJ Offline
                      When something like this happens it tends to be one of two things:
                      1. There is something in the two configurations which conflicts so only one of the two is unique from strongSwan's point of view.
                      2. Something internal to strongSwan has gotten confused and you need to stop it and start it again (not restart, as that functions differently).
                      In either of those cases it's not a bug per se, so unless you can narrow it down further it likely doesn't warrant a Redmine issue since there wouldn't be anything actionable on our part.
                      Do not Chat/PM for help!
                      • lifeboyL Offline
                        lifeboy @lifeboy
                        UPDATE: After some more experimentation it turns out that the position of the connection in the config file it not relevant. If both con9 and con10 are enabled, then con9 cannot connect. When con10 is disabled (ie, removed from the config file), con9 can connect.
                        When con10 alone is in the config file, it connects succesfully, but if both con9 and con10 are present, then neither connects.
                        This is driving me a little crazy here... especially since I cannot see from the logs what the cause may be.
                        • lifeboyL Offline
                          lifeboy @jimp
                          @jimp The start vs restart is something I will do after hours tonight to see if it makes a difference. I have up to this point only used restart. I did notice that restart does not drop established connections.
                          wrt the connnection configs and a possible conflict: I have only used the UI to create these connection parameters, not didn't hack around in the swanctl.conf file. Where are the "disabled" connections stored? I have not been able to find that even with a grep search.
                          • jimpJ Offline
                            The configuration data is all stored in config.xml which on the installation is held in /conf/config.xml.
                            • lifeboyL Offline
                              lifeboy @jimp
                              @jimp
                              We stopped and started the IPsec service, but the bahaviour is the same.
                              If one config is in the file, the service starts.
                              con9 present alone: con9 connects automatically (far side is RouterOS)
                              com10 present alone: con10 connects if far side is restarted manually, but not automatically (far side is Sophos).
                              If both con9 and 10 are present, neither connection starts.
                              Below are two configurations from the swanctl.conf file. There's not overlap or conflict that I can see, but maybe I'm missing something?
                                   con9 {
                                          # P1 (ikeid 9): RC
                                          fragmentation = yes
                                          unique = replace
                                          version = 2
                                          dpd_delay = 10s
                                          reauth_time = 0s
                                          over_time = 60480s
                                          rand_time = 60480s
                                          encap = no
                                          mobike = no
                                          remote_addrs = 196.250.abc.def
                                          local {
                                                  auth = psk
                                          remote {
                                                  id = %any
                                                  auth = psk
                                          children {
                                                  con9 {
                                                          mode = tunnel
                                                          policies = yes
                                                          life_time = 3600s
                                                          rekey_time = 3240s
                                                          rand_time = 360s
                                                          start_action = trap
                                                          dpd_action = trap
                                  con10 {
                                          # P1 (ikeid 10): G
                                          fragmentation = yes
                                          unique = replace
                                          version = 2
                                          reauth_time = 0s
                                          over_time = 60480s
                                          rand_time = 60480s
                                          encap = no
                                          mobike = no
                                          remote_addrs = 165.165.cde.fgh
                                          local {
                                                  auth = psk
                                          remote {
                                                  id = %any
                                                  auth = psk
                                          children {
                                                  con10 {
                                                          # P2 (reqid 17): G server
                                                          # P2 (reqid 16): G server
                                                          # P2 (reqid 15): G server
                                                          # P2 (reqid 14): G server
                                                          # P2 (reqid 11): G server
                                                          mode = tunnel
                                                          policies = yes
                                                          life_time = 604800s
                                                          rand_time = 60480s
                                                          start_action = trap
                                                          dpd_action = clear
                              • jimpJ Offline
                                Your problem is almost certainly because both of those have a remote ID of %any and are using pre-shared keys.
                                strongSwan references pre-shared keys by associating them with a remote identifier. With both of those tunnels enabled, it would have both keys listed for the %any ID, so it's unpredictable which (if either) would ever match.
                                Fix the remote IDs and both will probably work.
                                M lifeboyL 2 Replies Last reply Reply Quote 2
                                  michmoor LAYER 8 Rebel Alliance @jimp
                                  @jimp nice.
                                  i have been following this out of curiosity. I have been a bit worried about the stability of IPsec on the platform based on my current experience so this has been an interesting post to follow. I would've never thought about the remote id being a problem. Makes sense
                                  Wireless: Unifi, Aruba IAP
                                  JNCIP,CCNP Enterprise
                                  • lifeboyL Offline
                                    lifeboy @jimp
                                    @jimp, you're quite correct about the peer identifier. (No surprise there! ๐Ÿ˜ )
                                    Thanks for pointing that out. Although we need to finally test the one link after hours tonight, the "g" link is already working with both configs enabled.
                                      Gblenn @michmoor
                                      @michmoor said in More than one IPSec tunnel phase1 is fine, but adding another phase1 prevents an existing tunnel from re-establishing a connection:
                                      @jimp nice.
                                      Indeed an interesting finding and definitely something to investigate to see if it resolves my issue...