    Nut GUI does not select correct driver

    Scheduled Pinned Locked Moved 2.0-RC Snapshot Feedback and Problems - RETIRED
    4 Posts 3 Posters 2.3k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • L
      ldpaniak
      last edited by

      When configuring network UPS tools (nut) from the web GUI, selecting APC Back-UPS Pro USB creates a config file /usr/local/etc/nut/ups.conf with:

      driver=newhidups

      This is not the driver listed for that device in /usr/local/etc/nut/driver.list

      Back-UPS Pro USB  usbhid-ups

      Manually editing ups.conf to change to driver=usbhid-ups  gives a config that works with my Powerware 9130 whereas the newhidups driver does not.

      The GUI driver selection system appears to be broken.

      1 Reply Last reply Reply Quote 0
      • C
        ColdFusion
        last edited by

        This occurs also in 1.23, not just 2.0

        1 Reply Last reply Reply Quote 0
        • jimpJ
          jimp Rebel Alliance Developer Netgate
          last edited by

          NUT is known not to work on 2.0, really. It's on the list of things to fix, but will take a little time as it requires updating to a new version of NUT which had some configuration file differences.

          Remember: Upvote with the 👍 button for any user/post you find to be helpful, informative, or deserving of recognition!

          Need help fast? Netgate Global Support!

          Do not Chat/PM for help!

          1 Reply Last reply Reply Quote 0
          • L
            ldpaniak
            last edited by

            Also, not surprisingly, the manually modified config is overwritten on reboot.  I guess there is an xml file somewhere to be changed.

            The current NUT machinery works - at least for my UPS.  The problem is with the GUI/xml/config layer not doing what it claims to do.