    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.1m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • 4
      4o4rh @occamsrazor
      last edited by

      @occamsrazor no. the more I thought about the problem, I put it on the back burner.

      • I have a dumb battery on the J1900
      • I have an APC smart UPS on the NAS upstairs
      • in between are a couple of switches.

      a) if I shut the J1900 down after x minutes due to loss of comms,
      I wouldn't be able to restart it because you can't use the netgear switches as a WakeOnLAN for provider

      b) I am now using ZFS as pfsense the file system and I should get about 30-60min with the battery.
      If the outage is longer, the ZFS should provide a more resilient recovery (I think). I can then simply use the PowerOn Restore BIOS option to force the restart.

      On balance, I decided it was easier to take the risk of a long outage and get the benefit of an autorestart. Of course, it would have been a different story if i could have used the netgear switches to trigger WakeOnLAN for the pfsense box

      1 Reply Last reply Reply Quote 0
      • DaddyGoD
        DaddyGo
        last edited by DaddyGo

        NUT (2.7.4_20) with CyberPower RMCARD205 incorrect decimal point (0.1) vari.: battery.runtime

        Problem with CyberPower RMCARD205 + NUT installations, maybe it's time to switch to 2.8 😊 ( https://www.freshports.org/sysutils/nut ), as the "snmp-ups" driver does not include this type either.
        The problem with this wrong value is that, the shutdown threshold slips by, say, from a few minute (20%) - to a few hour :) and thus, - the UPS protection does not work in real time.
        (because it "thinks" there are 5 hours left in the batteries, but in fact there are only 5 minutes left)

        I repeat, only with this network SNMP card which we use RMCARD205 and unfortunately with the old driver set "driver.list" - snmp-ups...

        OLD "snmp-ups" file in pfS inst driver.list NUT.:

        2022-10-29_13h53_36.jpg

        RMCARD205 web interface:

        2022-10-28_19h11_11.jpg

        pfS NUT console:

        2022-10-28_19h11_23.jpg

        According to new compatibility:

        2022-10-29_14h20_03.jpg

        Cats bury it so they can't see it!
        (You know what I mean if you have a cat)

        dennypageD 1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @DaddyGo
          last edited by

          @daddygo said in NUT package:

          maybe it's time to switch to 2.8

          Pending pull request and redmine issue.

          DaddyGoD 1 Reply Last reply Reply Quote 2
          • DaddyGoD
            DaddyGo @dennypage
            last edited by

            @dennypage

            Hi Denny,

            Super then we thought of one (2.8) and hope it will happen quickly as we have purchased 10 pcs. 1.5KVA UPS units with RMCARD205.
            (I say softly - yeah, my fault for not checking the pfS NUT package and the RMACARD drivers first)

            Anyway thanks for your sacrificial work with this package, I have been watching it for a while...šŸ˜‰

            Cats bury it so they can't see it!
            (You know what I mean if you have a cat)

            1 Reply Last reply Reply Quote 1
            • dennypageD dennypage referenced this topic on
            • dennypageD dennypage referenced this topic on
            • dennypageD dennypage referenced this topic on
            • V
              Viper_Rus
              last edited by

              This post is deleted!
              1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage
                last edited by

                @Viper_Rus i assume you found the answer to supporting Synology elsewhere in the thread.

                M 1 Reply Last reply Reply Quote 0
                • M
                  mrsunfire @dennypage
                  last edited by mrsunfire

                  Iā€˜m having the issue that I get a shutdown loop after the UPS battery is empty.

                  pfSense shutdown as expected. After power restores the UPD turns on and pfSense boots up. Couple of seconds later the UPS is doing battery check. This seems to trigger pfSense to shutdown again and turns of UPS aswell. This loop continues until I unplug communication to the UPS and wait that battery gets fully charged.

                  You can see here that the input power is available but the UPS is getting the signal from pfSense to not charge. After couple of seconds pfSense and UPS shutdown.

                  Screenshot 2022-12-11 103342.jpg

                  Netgate 6100 MAX

                  dennypageD 1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage @mrsunfire
                    last edited by dennypage

                    @mrsunfire please post your config. And your UPS model.

                    M 1 Reply Last reply Reply Quote 0
                    • M
                      mrsunfire @dennypage
                      last edited by

                      @dennypage Config is vanilla (no change). UPS is APC Backups Pro 550 via USB.

                      Netgate 6100 MAX

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @mrsunfire
                        last edited by

                        @mrsunfire Hmm... I would have expected there to be some config change, either in the NUT package or in the UPS, as the UPS should not be bringing the load back on that quickly (0%). Nor would I expect it to show "On Line" and "Discharging" like that unless a calibration cycle were underway.

                        Speaking thereof, have you run a battery calibration recently? Perhaps the battery is dead...

                        Lastly, can you post the output of upsrw?

                        M 1 Reply Last reply Reply Quote 0
                        • M
                          mrsunfire @dennypage
                          last edited by

                          @dennypage No calibration. I wo der why UPS switches back on battery the moment I connect pfSense.
                          Whats the command for that output?

                          Netgate 6100 MAX

                          dennypageD JonathanLeeJ 2 Replies Last reply Reply Quote 0
                          • dennypageD
                            dennypage @mrsunfire
                            last edited by

                            @mrsunfire How old it the UPS and battery?

                            Please post the output of upsrw. If you aren't familiar with that, you can find examples in this thread.

                            1 Reply Last reply Reply Quote 1
                            • JonathanLeeJ
                              JonathanLee @mrsunfire
                              last edited by

                              @mrsunfire I was having weird issues in the last and it turned out to be a bad battery not the software.

                              Make sure to upvote

                              M 1 Reply Last reply Reply Quote 0
                              • M
                                mrsunfire @JonathanLee
                                last edited by mrsunfire

                                @jonathanlee Yes I already ordered new batteries before continue further testing.

                                I also did edit upsmon.conf and removed "SHUTDOWNCMD "/sbin/shutdown -h +0"". Unfortunately after reboot this setting is back there. How to proper edit that file? My goal in the first step was to not shutdown the pfSense at all.

                                Netgate 6100 MAX

                                GertjanG dennypageD 2 Replies Last reply Reply Quote 0
                                • GertjanG
                                  Gertjan @mrsunfire
                                  last edited by

                                  @mrsunfire said in NUT package:

                                  Unfortunately after reboot this setting is back there. How to proper edit that file? My goal in the first step was to not shutdown the pfSense at all.

                                  Fast answer : you can't.
                                  As the GUI states, this is what gets inserted in that file :

                                  44d2f9e1-c368-4eac-a908-5b362a7caf96-image.png

                                  And this is what gets inserted upfront by the GUI interface, even when you leave that bloc empty :

                                  /usr/local/pkg/nut/nut.inc line 250->252

                                  ( so, edit that file and do whatever you want ^^ )

                                  No "help me" PM's please. Use the forum, the community will thank you.
                                  Edit : and where are the logs ??

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage @mrsunfire
                                    last edited by

                                    @mrsunfire said in NUT package:

                                    I also did edit upsmon.conf and removed "SHUTDOWNCMD "/sbin/shutdown -h +0"". Unfortunately after reboot this setting is back there.

                                    You can't. If you want to prevent NUT operation (shutdown and everything else), change the UPS Type to disabled until you replace the battery.

                                    1 Reply Last reply Reply Quote 0
                                    • D
                                      darkcorner
                                      last edited by

                                      I have an APC Back-UPS BX2200MI connected and configured in pfSense.
                                      Everything seems to work fine.
                                      But how and where can I customize the shutdown delay?
                                      I want it to turn off when the battery guarantees me no more than 10 minutes of electricity.
                                      If within these 10 minutes the current returns, what happens?
                                      What if pfSense has shut down in the meantime? The BIOS is configured for the PC to turn on when the power returns; is this enough?

                                      dennypageD D 2 Replies Last reply Reply Quote 0
                                      • dennypageD
                                        dennypage @darkcorner
                                        last edited by

                                        @darkcorner said in NUT package:

                                        But how and where can I customize the shutdown delay?
                                        I want it to turn off when the battery guarantees me no more than 10 minutes of electricity.

                                        NUT will automatically shut the system down when the UPS declares a low battery situation. It is best to leave this alone and let the UPS and NUT do their jobs.

                                        1 Reply Last reply Reply Quote 0
                                        • D
                                          DannyBoy2k @darkcorner
                                          last edited by

                                          @darkcorner If your UPS allows you to, you can configure battery.runtime.low to the amount of time you want the UPS to declare a critical condition. Unfortunately, a lot of UPSes don't allow you to configure this. If they do, you should be able to see and adjust the setting with the upsc command.
                                          https://networkupstools.org/docs/man/upsc.html

                                          1 Reply Last reply Reply Quote 0
                                          • D
                                            darkcorner
                                            last edited by darkcorner

                                            @dennypage
                                            @DannyBoy2k
                                            Thanks for your answers.

                                            The UPS USB cable is connected to pfSense, but it covers multiple PCs/servers that need to shut down automatically.
                                            So, pfSense is the Master of NUT and on these PCs/Servers I'm installing tools configured as NUT Slave.

                                            TrueNAS is configured as "Slave" in its NUT service, but it doesn't seem to notice the presence of the Master.
                                            On a Win10 Pro PC I mounted WinNUT-Client and it gives me a login failure error for authentication.
                                            (If it's not the right software, can you suggest me some other client?)

                                            For all, the port is the standard one (3493).
                                            In Windows10 I turned off its Windows Defender Firewall.
                                            On pfSense there are two rules in LAN and DMZ for LAN-Net and DMZ-Net which allows any to any with any protocol.
                                            In pfSense, with Diagnostic - Test Ports the port seems open, but from console telnet 127.0.0.1:3493 or (localhost:3493) reports the error "Name does not resolve".
                                            On PC Win10 telnet LAN-NIC-Address:3493 reports error "Could not open connection to host. on port 23: Connection failed"

                                            As NUT users I am using both admin and local-monitor with the password present in /usr/local/etc/nut/upsd.users.

                                            GertjanG dennypageD 2 Replies Last reply Reply Quote 0