    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.1m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • GertjanG
      Gertjan @renegade
      last edited by

      @renegade

      You've checked "Enable notifications" :

      bd6eefb5-83f8-45e1-9f24-3f8173b2d0f8-image.png

      ?

      No "help me" PM's please. Use the forum, the community will thank you.
      Edit : and where are the logs ??

      1 Reply Last reply Reply Quote 0
      • occamsrazorO
        occamsrazor @Teken
        last edited by occamsrazor

        @gwaitsi said in NUT package:

        @Teken did you look at my post above?

        http://rogerprice.org/NUT/ConfigExamples.A5.pdf
        i believe the scenario you require is covered in the examples.

        I was also told the scenario i wanted is not supported....just needed to change from a bash based script to a shell based on and everything turned on.

        @teken or @gwaitsi - Did you ever find a way to do this - read the status from multiple UPS units into NUT? I just made a post along similar lines before finding these messages. But that rogerprice.org website seems to be down now, did either of you by chance save that PDF?

        pfSense CE on Qotom Q355G4 8GB RAM/60GB SSD
        Ubiquiti Unifi wired and wireless network, APC UPSs
        Mac OSX and IOS devices, QNAP NAS

        4 1 Reply Last reply Reply Quote 0
        • 4
          4o4rh @occamsrazor
          last edited by

          @occamsrazor no. the more I thought about the problem, I put it on the back burner.

          • I have a dumb battery on the J1900
          • I have an APC smart UPS on the NAS upstairs
          • in between are a couple of switches.

          a) if I shut the J1900 down after x minutes due to loss of comms,
          I wouldn't be able to restart it because you can't use the netgear switches as a WakeOnLAN for provider

          b) I am now using ZFS as pfsense the file system and I should get about 30-60min with the battery.
          If the outage is longer, the ZFS should provide a more resilient recovery (I think). I can then simply use the PowerOn Restore BIOS option to force the restart.

          On balance, I decided it was easier to take the risk of a long outage and get the benefit of an autorestart. Of course, it would have been a different story if i could have used the netgear switches to trigger WakeOnLAN for the pfsense box

          1 Reply Last reply Reply Quote 0
          • DaddyGoD
            DaddyGo
            last edited by DaddyGo

            NUT (2.7.4_20) with CyberPower RMCARD205 incorrect decimal point (0.1) vari.: battery.runtime

            Problem with CyberPower RMCARD205 + NUT installations, maybe it's time to switch to 2.8 😊 ( https://www.freshports.org/sysutils/nut ), as the "snmp-ups" driver does not include this type either.
            The problem with this wrong value is that, the shutdown threshold slips by, say, from a few minute (20%) - to a few hour :) and thus, - the UPS protection does not work in real time.
            (because it "thinks" there are 5 hours left in the batteries, but in fact there are only 5 minutes left)

            I repeat, only with this network SNMP card which we use RMCARD205 and unfortunately with the old driver set "driver.list" - snmp-ups...

            OLD "snmp-ups" file in pfS inst driver.list NUT.:

            2022-10-29_13h53_36.jpg

            RMCARD205 web interface:

            2022-10-28_19h11_11.jpg

            pfS NUT console:

            2022-10-28_19h11_23.jpg

            According to new compatibility:

            2022-10-29_14h20_03.jpg

            Cats bury it so they can't see it!
            (You know what I mean if you have a cat)

            dennypageD 1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage @DaddyGo
              last edited by

              @daddygo said in NUT package:

              maybe it's time to switch to 2.8

              Pending pull request and redmine issue.

              DaddyGoD 1 Reply Last reply Reply Quote 2
              • DaddyGoD
                DaddyGo @dennypage
                last edited by

                @dennypage

                Hi Denny,

                Super then we thought of one (2.8) and hope it will happen quickly as we have purchased 10 pcs. 1.5KVA UPS units with RMCARD205.
                (I say softly - yeah, my fault for not checking the pfS NUT package and the RMACARD drivers first)

                Anyway thanks for your sacrificial work with this package, I have been watching it for a while...šŸ˜‰

                Cats bury it so they can't see it!
                (You know what I mean if you have a cat)

                1 Reply Last reply Reply Quote 1
                • dennypageD dennypage referenced this topic on
                • dennypageD dennypage referenced this topic on
                • dennypageD dennypage referenced this topic on
                • V
                  Viper_Rus
                  last edited by

                  This post is deleted!
                  1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage
                    last edited by

                    @Viper_Rus i assume you found the answer to supporting Synology elsewhere in the thread.

                    M 1 Reply Last reply Reply Quote 0
                    • M
                      mrsunfire @dennypage
                      last edited by mrsunfire

                      Iā€˜m having the issue that I get a shutdown loop after the UPS battery is empty.

                      pfSense shutdown as expected. After power restores the UPD turns on and pfSense boots up. Couple of seconds later the UPS is doing battery check. This seems to trigger pfSense to shutdown again and turns of UPS aswell. This loop continues until I unplug communication to the UPS and wait that battery gets fully charged.

                      You can see here that the input power is available but the UPS is getting the signal from pfSense to not charge. After couple of seconds pfSense and UPS shutdown.

                      Screenshot 2022-12-11 103342.jpg

                      Netgate 6100 MAX

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @mrsunfire
                        last edited by dennypage

                        @mrsunfire please post your config. And your UPS model.

                        M 1 Reply Last reply Reply Quote 0
                        • M
                          mrsunfire @dennypage
                          last edited by

                          @dennypage Config is vanilla (no change). UPS is APC Backups Pro 550 via USB.

                          Netgate 6100 MAX

                          dennypageD 1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @mrsunfire
                            last edited by

                            @mrsunfire Hmm... I would have expected there to be some config change, either in the NUT package or in the UPS, as the UPS should not be bringing the load back on that quickly (0%). Nor would I expect it to show "On Line" and "Discharging" like that unless a calibration cycle were underway.

                            Speaking thereof, have you run a battery calibration recently? Perhaps the battery is dead...

                            Lastly, can you post the output of upsrw?

                            M 1 Reply Last reply Reply Quote 0
                            • M
                              mrsunfire @dennypage
                              last edited by

                              @dennypage No calibration. I wo der why UPS switches back on battery the moment I connect pfSense.
                              Whats the command for that output?

                              Netgate 6100 MAX

                              dennypageD JonathanLeeJ 2 Replies Last reply Reply Quote 0
                              • dennypageD
                                dennypage @mrsunfire
                                last edited by

                                @mrsunfire How old it the UPS and battery?

                                Please post the output of upsrw. If you aren't familiar with that, you can find examples in this thread.

                                1 Reply Last reply Reply Quote 1
                                • JonathanLeeJ
                                  JonathanLee @mrsunfire
                                  last edited by

                                  @mrsunfire I was having weird issues in the last and it turned out to be a bad battery not the software.

                                  Make sure to upvote

                                  M 1 Reply Last reply Reply Quote 0
                                  • M
                                    mrsunfire @JonathanLee
                                    last edited by mrsunfire

                                    @jonathanlee Yes I already ordered new batteries before continue further testing.

                                    I also did edit upsmon.conf and removed "SHUTDOWNCMD "/sbin/shutdown -h +0"". Unfortunately after reboot this setting is back there. How to proper edit that file? My goal in the first step was to not shutdown the pfSense at all.

                                    Netgate 6100 MAX

                                    GertjanG dennypageD 2 Replies Last reply Reply Quote 0
                                    • GertjanG
                                      Gertjan @mrsunfire
                                      last edited by

                                      @mrsunfire said in NUT package:

                                      Unfortunately after reboot this setting is back there. How to proper edit that file? My goal in the first step was to not shutdown the pfSense at all.

                                      Fast answer : you can't.
                                      As the GUI states, this is what gets inserted in that file :

                                      44d2f9e1-c368-4eac-a908-5b362a7caf96-image.png

                                      And this is what gets inserted upfront by the GUI interface, even when you leave that bloc empty :

                                      /usr/local/pkg/nut/nut.inc line 250->252

                                      ( so, edit that file and do whatever you want ^^ )

                                      No "help me" PM's please. Use the forum, the community will thank you.
                                      Edit : and where are the logs ??

                                      1 Reply Last reply Reply Quote 0
                                      • dennypageD
                                        dennypage @mrsunfire
                                        last edited by

                                        @mrsunfire said in NUT package:

                                        I also did edit upsmon.conf and removed "SHUTDOWNCMD "/sbin/shutdown -h +0"". Unfortunately after reboot this setting is back there.

                                        You can't. If you want to prevent NUT operation (shutdown and everything else), change the UPS Type to disabled until you replace the battery.

                                        1 Reply Last reply Reply Quote 0
                                        • D
                                          darkcorner
                                          last edited by

                                          I have an APC Back-UPS BX2200MI connected and configured in pfSense.
                                          Everything seems to work fine.
                                          But how and where can I customize the shutdown delay?
                                          I want it to turn off when the battery guarantees me no more than 10 minutes of electricity.
                                          If within these 10 minutes the current returns, what happens?
                                          What if pfSense has shut down in the meantime? The BIOS is configured for the PC to turn on when the power returns; is this enough?

                                          dennypageD D 2 Replies Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage @darkcorner
                                            last edited by

                                            @darkcorner said in NUT package:

                                            But how and where can I customize the shutdown delay?
                                            I want it to turn off when the battery guarantees me no more than 10 minutes of electricity.

                                            NUT will automatically shut the system down when the UPS declares a low battery situation. It is best to leave this alone and let the UPS and NUT do their jobs.

                                            1 Reply Last reply Reply Quote 0