    • dennypageD
      dennypage @dmitri
      last edited by

      @dmitri said in NUT Package (2.8.1 and above):

      I've added "RUN_AS_USER root" to the upsmon.conf and "user=root" to ups.conf. But those didn't have any effect.

      FYI, if you are using a remote nut connection, you are not running upsd.

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @dmitri
        last edited by

        @dmitri said in NUT Package (2.8.1 and above):

        I didn't update by hand, used the Package Manager. But, I think I know what may have happened: I was trying to update to CE 2.7.1-RC and changed the branch (even though I'm still on 2.7), and that may have caused the new NUT package to show up.

        Okay, now that makes more sense.

        The upsmon from 2.8.1 isn't going to be able to start in a 2.7.0 system because libraries that it needs, such as OpenSSL 3, are not there.

        D 1 Reply Last reply Reply Quote 0
        • D
          dmitri @dennypage
          last edited by

          @dennypage

          @dennypage said in NUT Package (2.8.1 and above):

          FYI, if you are using a remote nut connection, you are not running upsd.

          Yeah, I guess I was just shooting in the dark at this point :). I've since removed those lines.

          After upgrading to 2.7.1-RC the issues went away. Thanks for the help!

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @dmitri
            last edited by

            @dmitri said in NUT Package (2.8.1 and above):

            After upgrading to 2.7.1-RC the issues went away.

            Are you running NUT 2.8.1 there?

            D 1 Reply Last reply Reply Quote 0
            • D
              dmitri @dennypage
              last edited by

              @dennypage Just double checked, yes 2.8.1 NUT package on 2.7.1-RC.

              1 Reply Last reply Reply Quote 1
              • S
                sgnoc
                last edited by sgnoc

                @dennypage I've done some additional testing. Initially when I tried the updated package I was receiving connection lost/established messages. I've restarted pfSense, removed all nut packages, reinstalled nut (pfsense-pkg-nut, and the nut package itself), removed nut, installed the nut-devel-2023.10.07_01 and restarted the service.

                I then did some testing and grabbed some logs. So far I haven't received any more connection lost notices, but they were sporadic over an hour timeframe. Here are the logs/info, in case you see anything that jumps out. I do see no matching INFO_* value for OID listed for a bunch of different OID values (in the log).

                [23.09-RELEASE][admin@netgate]/tmp/acme: upsc CyberPowerCP2200
                battery.charge: 100
                battery.current: 3.50
                battery.date: 12/22/2022
                battery.runtime: 3300
                battery.runtime.elapsed: 0
                battery.voltage: 81.10
                battery.voltage.nominal: 72
                device.contact: Shaun
                device.description: UPS SNMP Card
                device.location: Basement
                device.mfr: CYBERPOWER
                device.model: OL2200RTXL2U
                device.serial: WBGEP2000038
                device.type: ups
                driver.debug: 0
                driver.flag.allow_killpower: 0
                driver.name: snmp-ups
                driver.parameter.pollinterval: 2
                driver.parameter.port: 10.10.5.10
                driver.parameter.synchronous: auto
                driver.state: quiet
                driver.version: 2.8.0.1
                driver.version.data: cyberpower MIB 0.55
                driver.version.internal: 1.30
                input.frequency: 60
                input.transfer.reason: noTransfer
                input.voltage: 123
                output.current: 3.50
                output.frequency: 60
                output.voltage: 120.20
                ups.delay.reboot: 0
                ups.delay.shutdown: 180
                ups.delay.start: 0
                ups.firmware: S1A14
                ups.id: CP2200
                ups.load: 19
                ups.mfr: CYBERPOWER
                ups.model: OL2200RTXL2U
                ups.serial: WBGEP2000038
                ups.status: OL
                ups.temperature: 34
                ups.test.date: 11/12/2023
                ups.test.result: Ok
                
                [23.09-RELEASE][admin@netgate]/tmp/acme: snmpwalk -v 1 -c public 10.10.5.10 SNMPv2-SMI::enterprises.3808.1.1.1
                SNMPv2-SMI::enterprises.3808.1.1.1.1.1.1.0 = STRING: "OL2200RTXL2U"
                SNMPv2-SMI::enterprises.3808.1.1.1.1.1.2.0 = STRING: "CP2200"
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.1.0 = STRING: "S1A14"
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.3.0 = STRING: "WBGEP2000038"
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.4.0 = STRING: "1.4.0"
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.5.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.6.0 = INTEGER: 2200
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.7.0 = INTEGER: 1800
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.8.0 = INTEGER: 180
                SNMPv2-SMI::enterprises.3808.1.1.1.1.2.9.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.2.1.1.0 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.2.1.2.0 = Timeticks: (0) 0:00:00.00
                SNMPv2-SMI::enterprises.3808.1.1.1.2.1.3.0 = STRING: "12/22/2022"
                SNMPv2-SMI::enterprises.3808.1.1.1.2.1.4.0 = INTEGER: 36
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.1.0 = Gauge32: 100
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.2.0 = Gauge32: 811
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.3.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.4.0 = Timeticks: (330000) 0:55:00.00
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.5.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.8.0 = INTEGER: 72
                SNMPv2-SMI::enterprises.3808.1.1.1.2.2.9.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.3.1.1.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.3.2.1.0 = Gauge32: 1230
                SNMPv2-SMI::enterprises.3808.1.1.1.3.2.2.0 = Gauge32: 1232
                SNMPv2-SMI::enterprises.3808.1.1.1.3.2.3.0 = Gauge32: 1230
                SNMPv2-SMI::enterprises.3808.1.1.1.3.2.4.0 = Gauge32: 600
                SNMPv2-SMI::enterprises.3808.1.1.1.3.2.5.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.3.2.6.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.4.1.1.0 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.4.1.2.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.4.1.3.0 = STRING: "40~70 Hz"
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.1.0 = Gauge32: 1200
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.2.0 = INTEGER: 600
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.3.0 = Gauge32: 19
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.4.0 = Gauge32: 35
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.5.0 = Gauge32: 342
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.6.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.4.2.7.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.1.0 = INTEGER: 24
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.1 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.2 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.3 = INTEGER: 3
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.4 = INTEGER: 4
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.5 = INTEGER: 5
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.6 = INTEGER: 6
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.7 = INTEGER: 7
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.8 = INTEGER: 8
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.9 = INTEGER: 9
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.10 = INTEGER: 10
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.11 = INTEGER: 11
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.12 = INTEGER: 12
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.13 = INTEGER: 13
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.14 = INTEGER: 14
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.1.15 = INTEGER: 15
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.1 = STRING: "Outlet1"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.2 = STRING: "Outlet2"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.3 = STRING: "Outlet3"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.4 = STRING: "Outlet4"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.5 = STRING: "Outlet5"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.6 = STRING: "Outlet6"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.7 = STRING: "Outlet7"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.8 = STRING: "Outlet8"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.9 = STRING: "Outlet9"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.10 = STRING: "Outlet10"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.11 = STRING: "Outlet11"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.12 = STRING: "Outlet12"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.13 = STRING: "Outlet13"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.14 = STRING: "Outlet14"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.2.15 = STRING: "Outlet15"
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.1 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.2 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.3 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.4 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.5 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.6 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.7 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.8 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.9 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.10 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.11 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.12 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.13 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.14 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.3.15 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.1 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.2 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.3 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.4 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.5 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.6 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.7 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.8 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.9 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.10 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.11 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.12 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.13 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.14 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.1.2.1.4.15 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.1.0 = INTEGER: 120
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.4.0 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.9.0 = Timeticks: (0) 0:00:00.00
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.10.0 = Timeticks: (18000) 0:03:00.00
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.11.0 = Timeticks: (18000) 0:03:00.00
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.13.0 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.14.0 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.15.0 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.16.0 = INTEGER: 0
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.17.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.18.0 = INTEGER: 20
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.19.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.5.2.20.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.6.2.1.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.6.2.2.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.6.2.3.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.6.2.5.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.6.2.6.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.7.2.2.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.7.2.3.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.7.2.4.0 = STRING: "11/12/2023"
                SNMPv2-SMI::enterprises.3808.1.1.1.7.2.6.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.7.2.7.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.7.2.8.0 = NULL
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.1.1 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.1.2 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.1.3 = INTEGER: 3
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.1.4 = INTEGER: 4
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.1.5 = INTEGER: 5
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.2.1 = INTEGER: 4
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.2.2 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.2.3 = INTEGER: 3
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.2.4 = INTEGER: 4
                SNMPv2-SMI::enterprises.3808.1.1.1.8.1.1.1.2.5 = INTEGER: 2
                SNMPv2-SMI::enterprises.3808.1.1.1.10.1.0 = INTEGER: 1
                SNMPv2-SMI::enterprises.3808.1.1.1.10.2.0 = Gauge32: 34
                

                Here is the file with the output (ran for about 100 seconds) from: /usr/local/libexec/nut/snmp-ups -a ups -DDDDDD 2>&1 | tee /tmp/out
                output.txt

                I'm hoping the restart and reinstall of everything fixed whatever was causing the connection losts messages, but I'll update again if they reoccur.

                Update about 2 hours later: The reboot and uninstall/reinstall of all NUT packages (to the devel package) seemed to do the trick. I haven't had a single connection lost notice since then. No idea why it was having issues after I tried the devel package, but it seems to be good now.

                1 Reply Last reply Reply Quote 1
                • T
                  tman222
                  last edited by

                  Upgraded to the new NUT package (2.8.2) and I'm happy to report that I was able to remove the interruptonly flag and now see no more disconnects on the USB connected Cyberpower UPS. Thanks @dennypage for all your hard work updating and maintaining this pfSense package.

                  dennypageD 1 Reply Last reply Reply Quote 1
                  • dennypageD
                    dennypage @tman222
                    last edited by

                    @tman222 said in NUT Package (2.8.1 and above):

                    Thanks @dennypage for all your hard work updating and maintaining this pfSense package.

                    You are most welcome

                    1 Reply Last reply Reply Quote 0
                    • evertE
                      evert @dennypage
                      last edited by

                      @dennypage said in NUT Package (2.8.1 and above):

                      Call for testing!

                      We are in a testing/feedback phase for the 2.8.1 pfSense NUT package. Many of you have experienced issues with the 2.8.0 version and are running custom builds. I would like to ask you to test the new package prior to a general release.

                      The 2.8.1 packages are available from the Redmine issue here. In order to install the package, you must be running 23.09. Be sure to select the correct package for your architecture.

                      Can you tell me where I can get the previous package? I'm on 23.05.1 and upgraded NUT to 2.8.2 yesterday. Package management let me do this, even though NUT 2.8.2 apparently doesn't work with 23.05.1. Result: a busted nut...
                      (I'll upgrade to 23.09 soon, but I can't do this during office hours)

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • GertjanG
                        Gertjan @Unoptanio
                        last edited by

                        @Unoptanio said in NUT Package (2.8.1 and above):

                        maybe I found it, can you confirm?
                        nano /boot/loader.conf

                        Not that file, as pfSense can wipe / purge / empty / modify / do whatever it wants with the content.

                        Read System Tunables and you'll find the one you need : /boot/loader.conf.local

                        No "help me" PM's please. Use the forum, the community will thank you.
                        Edit : and where are the logs ??

                        1 Reply Last reply Reply Quote 1
                        • dennypageD
                          dennypage @evert
                          last edited by

                          @evert said in NUT Package (2.8.1 and above):

                          @
                          Can you tell me where I can get the previous package? I'm on 23.05.1 and upgraded NUT to 2.8.2 yesterday. Package management let me do this, even though NUT 2.8.2 apparently doesn't work with 23.05.1. Result: a busted nut...
                          (I'll upgrade to 23.09 soon, but I can't do this during office hours)

                          It shouldn’t show up in 23.05.1. Did you switch update streams? Best I can suggest is to remove the package and reinstall.

                          evertE 1 Reply Last reply Reply Quote 1
                          • S
                            sgnoc
                            last edited by

                            @dennypage I got prompted on package manager that 2.8.2 was available and upgraded. Since then, I've started receiving the communication lost and established. I'm running a CyberPower UPS. I tried to put the nut-devel-2023.10.07_1.pkg back on, but it doesn't seem to be working with the other portion of NUT that was installed with 2.8.2. Was 2.8.2 the fix or is that still a version that hasn't been patched yet?

                            What's my best bet to get this working again until a permanent fix is available? Thanks!

                            dennypageD 1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage @sgnoc
                              last edited by

                              @sgnoc 2.8.2 of the pfSense package is the final release version.

                              The content of the underlying NUT package, nut-devel-2023.10.07_1, is the same as the prerelease test version. The only change in the new pfSense package (pfSense-pkg-nut-2.8.2) is that it states a dependency on nut-devel-2023.10.07_1 instead of nut-2.8.0.

                              A current install on 23.09 should show this:

                              [23.09-RELEASE][root@fw]/root: pkg info | grep nut
                              nut-devel-2023.10.07_1         Network UPS Tools
                              pfSense-pkg-nut-2.8.2          Network UPS Tools
                              [23.09-RELEASE][root@fw]/root: 
                              
                              S 1 Reply Last reply Reply Quote 0
                              • S
                                sgnoc @dennypage
                                last edited by

                                @dennypage I'm showing both of those packages, but oddly enough I'm now getting sporadic lost communication notices again, where I was not with the patch before this 2.8.2 update.

                                It's only happening a few times a day, but it is consistently a lost communication notice, exactly 3 seconds later a second lost communication notice and 5 seconds after that an established communication notice. I've already uninstalled and reinstalled to see if that would do it. I'll try and dig around to see why this may have happened from the patch to this update, since there shouldn't be a difference.

                                1 Reply Last reply Reply Quote 0
                                • Q
                                  q54e3w
                                  last edited by

                                  All working with 2.8.2 here with Eaton 9PX3000. Only change required was subdriver changing from pw to eaton_pw_nm2. Thanks @dennypage for maintaining this package, super appreciated.

                                  dennypageD 1 Reply Last reply Reply Quote 1
                                  • dennypageD
                                    dennypage @q54e3w
                                    last edited by

                                    @q54e3w I appreciate you saying that. Thanks.

                                    1 Reply Last reply Reply Quote 0
                                    • evertE
                                      evert @dennypage
                                      last edited by

                                      @dennypage said in NUT Package (2.8.1 and above):

                                      @evert said in NUT Package (2.8.1 and above):

                                      @
                                      Can you tell me where I can get the previous package? I'm on 23.05.1 and upgraded NUT to 2.8.2 yesterday. Package management let me do this, even though NUT 2.8.2 apparently doesn't work with 23.05.1. Result: a busted nut...
                                      (I'll upgrade to 23.09 soon, but I can't do this during office hours)

                                      It shouldn’t show up in 23.05.1. Did you switch update streams? Best I can suggest is to remove the package and reinstall.

                                      We are on the regular 'Latest Stable Version' branch. Ah well, I came in early today and updated the whole thing to 23.09 and that resolved my issues 😎

                                      And... Lo and behold! Our UPS is finally having a proper connection to the pfSense box 🤗

                                      1 Reply Last reply Reply Quote 0
                                      • evertE
                                        evert
                                        last edited by

                                        A bit confused by the versioning: pfSense now has nut 2.8.2, but the official NUT release is 2.8.1 if I interpret this page correctly.

                                        What happens when the official NUT release hits 2.8.2?

                                        dennypageD 1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage @evert
                                          last edited by

                                          @evert Yea, we had a little oops at the end, and a commit went in that should not have. The published version of the pfSense package itself shows as 2.8.2. By the time I discovered it, it was too late to change it.

                                          It should stay 2.8.2 (2.8.2_1, 2.8.2_2, 2.8.2_3...) until 2.8.3 or 3.0.0 is released.

                                          UnoptanioU 1 Reply Last reply Reply Quote 0
                                          • UnoptanioU
                                            Unoptanio @dennypage
                                            last edited by Unoptanio

                                            @dennypage

                                            Good morning,
                                            I updated to pfsense 2.7.1 with Nut ver 2.8.2

                                            The quirk is always inserted in the boot loader.
                                            hw.usb.quirk.0="0x04b4 0x5500 0x0000 0xffff UQ_HID_IGNORE"

                                            I confirm that the Riello VST1100 UPS is working well without disconnection of the USB port

                                            Soon I will also let you know for the "Riello Sentinel Pro 2200" and "Riello Sentinel Dual SDU 6Kw" models

                                            For Riello VST1100:

                                            UPS Detail
                                            
                                            This table contains all the variables reported by the UPS via the upsc command. Note that many UPSs report only a subset of the available variables. Also note that some UPSs, particularly those using usbhid, may report an incorrect value for a variable. This is generally not a cause for concern. For additional information, see the Network UPS Tools site
                                            
                                            Variable	Value
                                            battery.capacity	9
                                            battery.charge	100
                                            battery.runtime	5940
                                            battery.voltage	27.4
                                            battery.voltage.nominal	24
                                            device.mfr	RPS S.p.a.
                                            device.model	ULC2
                                            device.serial	
                                            device.type	ups
                                            driver.debug	0
                                            driver.flag.allow_killpower	0
                                            driver.name	riello_usb
                                            driver.parameter.pollinterval	2
                                            driver.parameter.port	auto
                                            driver.parameter.synchronous	auto
                                            driver.state	updateinfo
                                            driver.version	2.8.0.1
                                            driver.version.internal	0.10
                                            driver.version.usb	libusb-1.0.0 (API: 0x1000102)
                                            input.bypass.frequency	50.00
                                            input.bypass.voltage	230
                                            input.frequency	50.00
                                            input.voltage	230
                                            output.frequency	50.00
                                            output.frequency.nominal	50.0
                                            output.L1.current	0
                                            output.L1.power	0
                                            output.L1.realpower	0
                                            output.L2.current	0
                                            output.L2.power	0
                                            output.L2.realpower	0
                                            output.L3.current	0
                                            output.L3.power	0
                                            output.L3.realpower	0
                                            output.power.percent	12
                                            output.voltage	230
                                            output.voltage.nominal	230
                                            ups.delay.reboot	5
                                            ups.delay.shutdown	5
                                            ups.firmware	SWM039-01-04
                                            ups.load	12
                                            ups.mfr	RPS S.p.a.
                                            ups.model	ULC2
                                            ups.power.nominal	1100
                                            ups.productid	5500
                                            ups.realpower.nominal	880
                                            ups.serial	
                                            ups.status	OL
                                            ups.temperature	42
                                            ups.vendorid	04b4
                                            

                                            pfSensePlus24.03 2U BareMetal Asrock Industrial IMB-X1314MicroATX
                                            CPU: i7-13700@5.2GHz, RAM:32GB ECC, n°2 Samsung 870EVO SATA 2.5” SSD 1TB (ZFS) Raid1
                                            n°3 Intel i225-LM 2500/1000/100Mbps, n°1 NIC Intel i350-T4V2 10/100/1000 Mbps 4*GLAN, n°1 Intel X520-DA2

                                            1 Reply Last reply Reply Quote 1