    Would ignorelb work on socomec double on-line conversion UPS

    Scheduled Pinned Locked Moved UPS Tools
    15 Posts 2 Posters 2.3k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage @chewie
      last edited by dennypage

      @chewie The ignorelb directive instructs NUT to ignore it if the UPS reports a low battery condition. This is probably the most misused directive in NUT.

      You should not use ignorelb unless your UPS prematurely declares a low battery immediately after mains fail.


      Moving on...

      You can ignore the battery voltage reporting issue. It is a common issue with the blazer driver, and it isn't used for anything anyway. If it bothers you, look at setting the battery.packs value.

      Before you do anything, the first thing you need to know is do you actually have a problem to begin with? Synology units don't actually shut down anymore, they go into a safe mode. So, is the UPS cutting power before the Synology reaches safe mode? If so, is the UPS running out of battery? Or is it because there is too short of a delay following the low battery declaration? Or is it because the UPS cuts power too quickly after being instructed to do so?

      If you actually have a problem...

      Things you will want to know: How long does it take for your Synology to get to safe mode? How low (runtime) does the UPS go before declaring a low battery? How long does your UPS wait to cut power after receiving the command to do so?

      If at all possible you want to configure the variables governing runtime battery reserve and/or delays in the UPS itself. If your UPS does not offer this ability, then you can start down the path of configuration for NUT. Begin by looking at the HOSTSYNC and FINALDELAY variables.

      C 1 Reply Last reply Reply Quote 1
      • C
        chewie @dennypage
        last edited by chewie

        @dennypage
        Hello, sorry for the late response, had to find time to do further reading on nut in between work. Since the 2kva socomec is being used for another equipment, i was hesitant to use it for nut shutdown tests. I had to borrow an old APC Back-UPS XS 650CI and replace its battery. With as usbhid driver, ups status on pfsense shows this...

        Screenshot 2024-07-31 034828.png

        It couldnt determine the ups load with the new battery installed.The APC is rated at 650VA and the load is a 135watt psu for pfsense and around 236 watts for synology, providing more than 30% of load, suppose to be enough for nut to show the load on the gui, but probably need to run battery calibration yet.

        With just the upsd.conf modified for LISTEN interface and the upsd.users modified for synology, pulling the cord out of
        the wall shows the following power-off times...

        • pfsense - 48 secs
        • synology - 89.05 secs
        • apc ups - 91.58 secs

        Is this a normal behavior with pfsense shutting down first followed by the synology then the ups? I thought it was the other way around, synology first before pfsense.

        I think the synology and pfsense has shutdown gracefully without me modifying HOSTSYNC and FINALDEALY. Do I still have to modify them to keep enough reserves for the battery and extend its life? Re-plugging the ups to the wall outlet, has re-started synology, pfsense and ups successfully and a battery charge at 98.

        I have to return the APC, and purchase another socomec for its double on-line feature, but before our group would do so, the least available socomec wattage with double-on line conversion is 1 kva, basing on the poweroff times above would it be possible to modify the the variables to at least shutdown pfsense and synology at 90% battery charge on a socomec?

        I revisited the UPS menu on the 2 kva socomec and does not offer modification on battery reserves and delays, So I am back with nut.

        I re-tested the socomec with nut on the raspberry Pi, hoping to extrapolate the poweroff times from the APC and modify socomec's shutdown behavior, this time it showed a driver of...

        [nutdev1]
                driver = "nutdrv_qx"
                port = "auto"
                vendorid = "0665"
                productid = "5161"
                bus = "001"
        
        

        the only difference with the blazer driver was that nutdrv_qx showed only a battery charge of 91 as oppose to 100 with the blazer driver. Here are the variables...

        
        Init SSL without certificate database
        battery.charge: 91
        battery.energysave: no
        battery.packs: 1
        battery.protection: yes
        battery.runtime: 20400
        battery.voltage: 54.70
        battery.voltage.nominal: 48.0
        device.model: WPHVT2K0
        device.type: ups
        driver.name: nutdrv_qx
        driver.parameter.bus: 001
        driver.parameter.pollfreq: 30
        driver.parameter.pollinterval: 15
        driver.parameter.port: auto
        driver.parameter.productid: 5161
        driver.parameter.synchronous: auto
        driver.parameter.vendorid: 0665
        driver.version: 2.8.0
        driver.version.data: Voltronic 0.06
        driver.version.internal: 0.32
        driver.version.usb: libusb-1.0.26 (API: 0x1000109)
        input.current.nominal: 8.0
        input.frequency: 60.2
        input.frequency.high: 63.0
        input.frequency.low: 57.0
        input.frequency.nominal: 60.0
        input.phases: 1
        input.transfer.high: 242
        input.transfer.high.max: 254
        input.transfer.high.min: 237
        input.transfer.low: 218
        input.transfer.low.max: 223
        input.transfer.low.min: 206
        input.voltage: 225.5
        input.voltage.nominal: 230.0
        output.current: 0.0
        output.current.nominal: 8
        output.frequency: 60.2
        output.frequency.nominal: 60.0
        output.phases: 1
        output.power.maximum.percent: 0
        output.power.minimum.percent: 0
        output.powerfactor: 0.8
        output.voltage: 229.5
        output.voltage.nominal: 230.0
        ups.beeper.status: enabled
        ups.delay.shutdown: 30
        ups.delay.start: 180
        ups.firmware: 01036.05
        ups.firmware.aux: P01
        ups.load: 0
        ups.power.nominal: 2000
        ups.productid: 5161
        ups.start.auto: yes
        ups.start.battery: yes
        ups.status: OL
        ups.temperature: 24.0
        ups.type: online
        ups.vendorid: 0665
        

        The modifiable variables with upsrw socomec@localhost

        [battery.energysave]
        Switch off when running on battery and no/low load
        Type: ENUM NUMBER
        Option: "no" SELECTED
        Option: "yes"
        
        [battery.packs]
        Number of battery packs
        Type: RANGE NUMBER
        Option: "1-99" SELECTED
        
        [battery.protection]
        Prevent deep discharge of battery
        Type: ENUM NUMBER
        Option: "no"
        Option: "yes" SELECTED
        
        [input.frequency.high]
        Maximum input line frequency (Hz)
        Type: RANGE NUMBER
        Option: "63-70" SELECTED
        
        [input.frequency.low]
        Minimum input line frequency (Hz)
        Type: RANGE NUMBER
        Option: "50-57" SELECTED
        
        [input.transfer.high]
        High voltage transfer point (V)
        Type: RANGE NUMBER
        Option: "237-254" SELECTED
        
        [input.transfer.low]
        Low voltage transfer point (V)
        Type: RANGE NUMBER
        Option: "206-223" SELECTED
        
        [ups.delay.shutdown]
        Interval to wait after shutdown with delay command (seconds)
        Type: RANGE NUMBER
        Option: "12-5940" SELECTED
        
        [ups.delay.start]
        Interval to wait before (re)starting the load (seconds)
        Type: RANGE NUMBER
        Option: "0-599940" SELECTED
        
        [ups.start.auto]
        UPS starts when mains is (re)applied
        Type: ENUM NUMBER
        Option: "no"
        Option: "yes" SELECTED
        
        [ups.start.battery]
        Allow to start UPS from battery
        Type: ENUM NUMBER
        Option: "no"
        Option: "yes" SELECTED
        

        and upscmd -l socomec@localhost

        Instant commands supported on UPS [socomec]:
        
        beeper.disable - Disable the UPS beeper
        beeper.enable - Enable the UPS beeper
        beeper.toggle - Toggle the UPS beeper
        bypass.start - Put the UPS in bypass mode
        bypass.stop - Take the UPS out of bypass mode
        load.off - Turn off the load immediately
        load.on - Turn on the load immediately
        shutdown.return - Turn off the load and return when power is back
        shutdown.stayoff - Turn off the load and remain off
        shutdown.stop - Stop a shutdown in progress
        test.battery.start - Start a battery test
        test.battery.start.deep - Start a deep battery test
        test.battery.start.quick - Start a quick battery test
        test.battery.stop - Stop the battery test
        

        It seems that you can not instruct socomec to shutdown at 90 battery charge or assign a battery run time.
        Do I still need to modify HOSTSYNC and FINALDELAY based on the poweroff times on the APC? Our goal is hopefully to shutdown pfsense, synology and socomec at 90 battery charge. I am hesitant of copying scripts from various sites and running them on pfsense though. I suppose I can use the raspberry pi as nut master instead and run the scripts and make pfsense and synology run as nut slaves.

        Thank you again for your time.

        dennypageD 1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @chewie
          last edited by

          @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

          With just the upsd.conf modified for LISTEN interface and the upsd.users modified for synology, pulling the cord out of
          the wall shows the following power-off times...

          pfsense - 48 secs
          synology - 89.05 secs
          apc ups - 91.58 secs
          Is this a normal behavior with pfsense shutting down first followed by the synology then the ups? I thought it was the other way around, synology first before pfsense.

          The server waits for clients to initiate their shutdown (indicated by the client logging out of the server) rather than complete their shutdown. The server has no way to know how long a client actually takes to complete the shutdown. Once all clients have logged out, the server initiates its own shutdown following a short delay (FINALDELAY).

          pfSense generally shuts down relatively quickly, while Synology shuts down very slowly. So yes, it's reasonable to expect that pfSense would complete its shutdown before the Synology does. Variable ups.delay.shutdown can be used to cover this. You could also use FINALDELAY, but since your UPS has the capability to control the power off delay I would use that instead.

          One question: you list a "power-off" for the Synology of 89 seconds. Was this an actual power off, or achievement of quiescent mode?

          WRT the socomec, I expect the UPS vendor knows what they are doing, so setting battery.protection to true is probably sufficient to maintain battery life. Also, be sure to set ups.delay.shutdown to a sufficient value to cover the Synology's shutdown. Maybe 100-120 seconds.

          As to where you run the server, you can run the server on pfSense or on the pi. Which system is more reliable? If you choose the pi, keep in mind that it may shut down even faster than pfSense. If so, you'll need to allow a little extra time. The only thing I would not do is to use the Synology as the master. 😊

          HTH

          C 2 Replies Last reply Reply Quote 0
          • C
            chewie @dennypage
            last edited by chewie

            This post is deleted!
            1 Reply Last reply Reply Quote 0
            • C
              chewie @dennypage
              last edited by chewie

              @dennypage

              Regarding the synology quiescent mode, I am not sure about this. I just have my settings same as server on
              time before server enters standby mode under the UPS tab of the synology. Would gladly check it if you could
              show me how. Perhaps under var/log/messages on synology?

              Do i put this line in the ups conf or in the extra arguments to driver to control ther power off delay?

              ups.delay.shutdown = 120
              

              or is it,

              offdelay = 120
              

              in Extra Arguments to driver

              or should i issue this command via the cli?

              upsrw -s ups.delay.shutdown =120

              Is there way of making the soscomec shutdown immediately just for testing purposes? Since the scomec is 2 kva, it may
              take forever for it to shutdown wtih just the Pi as its load. Mindful of your advice to use igbnorelb only when UPS
              declares battery immediately after the mains fail?

              Luckily, I did read your post on why not to run nut master on synology...

              Thank you very much

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage @chewie
                last edited by

                @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                Regarding the synology quiescent mode, I am not sure about this. I just have my settings same as server on
                time before server enters standby mode under the UPS tab of the synology. Would gladly check it if you could
                show me how. Perhaps under var/log/messages on synology?

                Standby mode is quiescent mode. Older version of Synology would actually power off, now they just shut down all the services and sit there.

                @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                or should i issue this command via the cli?

                upsrw -s ups.delay.shutdown =120

                This.

                @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                Is there way of making the soscomec shutdown immediately just for testing purposes? Since the scomec is 2 kva, it may
                take forever for it to shutdown wtih just the Pi as its load.

                You can instruct the UPS to power off immediately via a NUT command, but that's different than the UPS declaring LB (Low Battery).

                C 1 Reply Last reply Reply Quote 0
                • C
                  chewie @dennypage
                  last edited by

                  @dennypage thank you again

                  dennypageD 1 Reply Last reply Reply Quote 1
                  • dennypageD
                    dennypage @chewie
                    last edited by

                    @chewie Most welcome!

                    1 Reply Last reply Reply Quote 0
                    • C
                      chewie
                      last edited by chewie

                      @dennypage said in Would ignorelb work on socomec double on-line conversion UPS:

                      This.

                      upsrw -s ups.delay.shutdown =120
                      

                      doesn 't seem to persist across reboots. The ups dealy shutdown goes back to the deafualt value of 30. should i use the ..

                      offdelay = 120
                      

                      in ExtraArgument to driver instead? This one seem to persist across reboots.

                      Thank you again.

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @chewie
                        last edited by

                        @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                        doesn 't seem to persist across reboots. The ups dealy shutdown goes back to the deafualt value of 30.

                        Can you clarify what you mean by "Across reboots"?

                        Does this refer to the reboot of the OS? Or reboot of the UPS? Or the restart of the NUT daemon or NUT UPS driver?

                        C 1 Reply Last reply Reply Quote 0
                        • C
                          chewie @dennypage
                          last edited by

                          @dennypage said in Would ignorelb work on socomec double on-line conversion UPS:

                          Can you clarify what you mean by "Across reboots"?

                          Does this refer to the reboot of the OS? Or reboot of the UPS? Or the restart of the NUT daemon or NUT UPS driver?

                          Restarting the Daemon successfully showed the delay shutdown at 120 but not when you reboot the OS.

                          dennypageD 1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @chewie
                            last edited by dennypage

                            @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                            Restarting the Daemon successfully showed the delay shutdown at 120 but not when you reboot the OS.

                            Okay, that's kinda weird. Only thing I can think of would be that the UPS is reseting when the USB resets. You can confirm by pulling the USB cable out for a 5-10 seconds, and then plugging it back in.

                            [Edit: By "restarting the Daemon" you mean completely restarting NUT, yes?]

                            C 1 Reply Last reply Reply Quote 0
                            • C
                              chewie @dennypage
                              last edited by

                              @dennypage I apologize, this is what i did...

                              upsrw -s ups.delay.shutdown =120
                              

                              and immediately the delay shutdown was set to 120 without me restarting nut with the circular arrow on the top right corner of pfsense. But the moment i hit that arrow the delay shutdown goes back to its original value of 30. Rebooting pfsense would still show the value at 30. I must be doing something wrong or not understanding something. Thank you very much

                              dennypageD 1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage @chewie
                                last edited by

                                @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                                @dennypage I apologize, this is what i did...

                                upsrw -s ups.delay.shutdown =120
                                

                                and immediately the delay shutdown was set to 120 without me restarting nut with the circular arrow on the top right corner of pfsense. But the moment i hit that arrow the delay shutdown goes back to its original value of 30. Rebooting pfsense would still show the value at 30.

                                Apologies for the delay, I've been busy/offline.

                                So I expect what is happening is that the NUT driver is resetting the shutdown delay on start, even though you have not specified a value. Lots of little quirks like this in NUT drivers.

                                So yes, I would recommend setting the offdelay parameter in the Extra Arguments to driver section. You can confirm that it is correctly setting the value in the UPS by using the upsrw command to read from the UPS after restarting NUT.

                                1 Reply Last reply Reply Quote 0