    Would ignorelb work on socomec double on-line conversion UPS

    Scheduled Pinned Locked Moved UPS Tools
    15 Posts 2 Posters 2.3k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage @chewie
      last edited by

      @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

      With just the upsd.conf modified for LISTEN interface and the upsd.users modified for synology, pulling the cord out of
      the wall shows the following power-off times...

      pfsense - 48 secs
      synology - 89.05 secs
      apc ups - 91.58 secs
      Is this a normal behavior with pfsense shutting down first followed by the synology then the ups? I thought it was the other way around, synology first before pfsense.

      The server waits for clients to initiate their shutdown (indicated by the client logging out of the server) rather than complete their shutdown. The server has no way to know how long a client actually takes to complete the shutdown. Once all clients have logged out, the server initiates its own shutdown following a short delay (FINALDELAY).

      pfSense generally shuts down relatively quickly, while Synology shuts down very slowly. So yes, it's reasonable to expect that pfSense would complete its shutdown before the Synology does. Variable ups.delay.shutdown can be used to cover this. You could also use FINALDELAY, but since your UPS has the capability to control the power off delay I would use that instead.

      One question: you list a "power-off" for the Synology of 89 seconds. Was this an actual power off, or achievement of quiescent mode?

      WRT the socomec, I expect the UPS vendor knows what they are doing, so setting battery.protection to true is probably sufficient to maintain battery life. Also, be sure to set ups.delay.shutdown to a sufficient value to cover the Synology's shutdown. Maybe 100-120 seconds.

      As to where you run the server, you can run the server on pfSense or on the pi. Which system is more reliable? If you choose the pi, keep in mind that it may shut down even faster than pfSense. If so, you'll need to allow a little extra time. The only thing I would not do is to use the Synology as the master. 😊

      HTH

      C 2 Replies Last reply Reply Quote 0
      • C
        chewie @dennypage
        last edited by chewie

        This post is deleted!
        1 Reply Last reply Reply Quote 0
        • C
          chewie @dennypage
          last edited by chewie

          @dennypage

          Regarding the synology quiescent mode, I am not sure about this. I just have my settings same as server on
          time before server enters standby mode under the UPS tab of the synology. Would gladly check it if you could
          show me how. Perhaps under var/log/messages on synology?

          Do i put this line in the ups conf or in the extra arguments to driver to control ther power off delay?

          ups.delay.shutdown = 120
          

          or is it,

          offdelay = 120
          

          in Extra Arguments to driver

          or should i issue this command via the cli?

          upsrw -s ups.delay.shutdown =120

          Is there way of making the soscomec shutdown immediately just for testing purposes? Since the scomec is 2 kva, it may
          take forever for it to shutdown wtih just the Pi as its load. Mindful of your advice to use igbnorelb only when UPS
          declares battery immediately after the mains fail?

          Luckily, I did read your post on why not to run nut master on synology...

          Thank you very much

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @chewie
            last edited by

            @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

            Regarding the synology quiescent mode, I am not sure about this. I just have my settings same as server on
            time before server enters standby mode under the UPS tab of the synology. Would gladly check it if you could
            show me how. Perhaps under var/log/messages on synology?

            Standby mode is quiescent mode. Older version of Synology would actually power off, now they just shut down all the services and sit there.

            @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

            or should i issue this command via the cli?

            upsrw -s ups.delay.shutdown =120

            This.

            @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

            Is there way of making the soscomec shutdown immediately just for testing purposes? Since the scomec is 2 kva, it may
            take forever for it to shutdown wtih just the Pi as its load.

            You can instruct the UPS to power off immediately via a NUT command, but that's different than the UPS declaring LB (Low Battery).

            C 1 Reply Last reply Reply Quote 0
            • C
              chewie @dennypage
              last edited by

              @dennypage thank you again

              dennypageD 1 Reply Last reply Reply Quote 1
              • dennypageD
                dennypage @chewie
                last edited by

                @chewie Most welcome!

                1 Reply Last reply Reply Quote 0
                • C
                  chewie
                  last edited by chewie

                  @dennypage said in Would ignorelb work on socomec double on-line conversion UPS:

                  This.

                  upsrw -s ups.delay.shutdown =120
                  

                  doesn 't seem to persist across reboots. The ups dealy shutdown goes back to the deafualt value of 30. should i use the ..

                  offdelay = 120
                  

                  in ExtraArgument to driver instead? This one seem to persist across reboots.

                  Thank you again.

                  dennypageD 1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage @chewie
                    last edited by

                    @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                    doesn 't seem to persist across reboots. The ups dealy shutdown goes back to the deafualt value of 30.

                    Can you clarify what you mean by "Across reboots"?

                    Does this refer to the reboot of the OS? Or reboot of the UPS? Or the restart of the NUT daemon or NUT UPS driver?

                    C 1 Reply Last reply Reply Quote 0
                    • C
                      chewie @dennypage
                      last edited by

                      @dennypage said in Would ignorelb work on socomec double on-line conversion UPS:

                      Can you clarify what you mean by "Across reboots"?

                      Does this refer to the reboot of the OS? Or reboot of the UPS? Or the restart of the NUT daemon or NUT UPS driver?

                      Restarting the Daemon successfully showed the delay shutdown at 120 but not when you reboot the OS.

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @chewie
                        last edited by dennypage

                        @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                        Restarting the Daemon successfully showed the delay shutdown at 120 but not when you reboot the OS.

                        Okay, that's kinda weird. Only thing I can think of would be that the UPS is reseting when the USB resets. You can confirm by pulling the USB cable out for a 5-10 seconds, and then plugging it back in.

                        [Edit: By "restarting the Daemon" you mean completely restarting NUT, yes?]

                        C 1 Reply Last reply Reply Quote 0
                        • C
                          chewie @dennypage
                          last edited by

                          @dennypage I apologize, this is what i did...

                          upsrw -s ups.delay.shutdown =120
                          

                          and immediately the delay shutdown was set to 120 without me restarting nut with the circular arrow on the top right corner of pfsense. But the moment i hit that arrow the delay shutdown goes back to its original value of 30. Rebooting pfsense would still show the value at 30. I must be doing something wrong or not understanding something. Thank you very much

                          dennypageD 1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @chewie
                            last edited by

                            @chewie said in Would ignorelb work on socomec double on-line conversion UPS:

                            @dennypage I apologize, this is what i did...

                            upsrw -s ups.delay.shutdown =120
                            

                            and immediately the delay shutdown was set to 120 without me restarting nut with the circular arrow on the top right corner of pfsense. But the moment i hit that arrow the delay shutdown goes back to its original value of 30. Rebooting pfsense would still show the value at 30.

                            Apologies for the delay, I've been busy/offline.

                            So I expect what is happening is that the NUT driver is resetting the shutdown delay on start, even though you have not specified a value. Lots of little quirks like this in NUT drivers.

                            So yes, I would recommend setting the offdelay parameter in the Extra Arguments to driver section. You can confirm that it is correctly setting the value in the UPS by using the upsrw command to read from the UPS after restarting NUT.

                            1 Reply Last reply Reply Quote 0