    ONLINE LOW BATTERY message

    UPS Tools
    5
    29
    1.9k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • N
      netboy
      last edited by

      I had a power outage, and two of my UPS are reporting the subject message. They show 100% charged - How to troubleshoot this?

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @netboy
        last edited by

        @netboy said in ONLINE LOW BATTERY message:

        I had a power outage, and two of my UPS are reporting the subject message. They show 100% charged - How to troubleshoot this?

        There is Insufficient information above to provide you with a meaningful response.

        If you are using NUT, please provide the contents of the NUT status page (Services / UPS / Status) and explain the issue you see.

        N 1 Reply Last reply Reply Quote 0
        • N
          netboy @dennypage
          last edited by

          @dennypage
          Sorry. Here is the screenshot
          a961e7f8-0dba-4b05-bf71-2f6ec07ccf29-image.png

          Is this really low battery - how to be sure? I get tons of message from netgatge that "UPS ups battery is low" - How do I suppress this message till I change the batter (assuming the battery is not charging)

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @netboy
            last edited by

            @netboy You cut off the status detail.

            Rather than a picture, you can just post the text. If it's easier, you can also get the information by running the command

            upsc ups
            

            FWIW, just looking at the summary status it appears that the UPS does indeed have a serious issue. It's reporting the battery as being 100% charged, and a load level of 8%, but only 114 seconds of runtime. Either something is wrong with the UPS unit itself, or the battery is in dire need of replacement. Depending upon how frequently you experience power outages, most UPS batteries should be replaced every 3 years or so. How old is the battery?

            You can suppress further messages by turning off Notifications in the UPS settings (Services / UPS / Settings).

            N 1 Reply Last reply Reply Quote 0
            • N
              netboy @dennypage
              last edited by

              @dennypage pretty old 2012...maybe time to replace battery - thinking of getting one of these 1000VA/800W UPS Battery Backup and Surge Protector, Backup Battery Power Supply with LiFePO4 Battery, BMS & Cooling Fan, Lithium Battery of 10 Years Lifespan, 8 Outlets, AVR, LCD Display

              What is your opinion of goldmate?
              The issue is this goldmate is not compatible with NUT server.
              Do you think I should change the battery and call it a day?

              T provelsP dennypageD 3 Replies Last reply Reply Quote 0
              • T
                tedquade @netboy
                last edited by

                @netboy Change the battery.
                Ted

                1 Reply Last reply Reply Quote 1
                • provelsP
                  provels @netboy
                  last edited by

                  @netboy My APCs are 2012, too. I just change batteries. Think they're on their third set. Amazon has replacements for low prices. Fine for home use.

                  Peder

                  MAIN - pfSense+ 24.11-RELEASE - Adlink MXE-5401, i7, 16 GB RAM, 64 GB SSD. 500 GB HDD for SyslogNG
                  BACKUP - pfSense+ 23.01-RELEASE - Hyper-V Virtual Machine, Gen 1, 2 v-CPUs, 3 GB RAM, 8GB VHDX (Dynamic)

                  1 Reply Last reply Reply Quote 1
                  • dennypageD
                    dennypage @netboy
                    last edited by

                    @netboy said in ONLINE LOW BATTERY message:

                    pretty old 2012...maybe time to replace battery
                    ...
                    Do you think I should change the battery and call it a day?

                    A 12 year old battery?!? Yes, change the battery. And set a reminder to do it again in 3-5 years. No more than 5 years.

                    FWIW, APC has some very nice Lithium UPSs. But replacing the UPS is a lot more expensive than changing the battery a couple of times.

                    N 2 Replies Last reply Reply Quote 0
                    • N
                      netboy @dennypage
                      last edited by

                      @dennypage Thanks - I did order the ORIGINAL APC battery from amazon (sold directly by Amazon )

                      1 Reply Last reply Reply Quote 0
                      • N
                        netboy @dennypage
                        last edited by

                        @dennypage I replaced the battery with APC original battery from Amazon and it is now approx 6+ hours and the nut server seems to be stuck with the old config.

                        Any idea how to troubleshoot this issue?

                        Thanks

                        0bf2220f-ddd6-46c5-a0fc-a152a5328d35-image.png e9d0b101-2907-4f95-ae83-3dfbeb64a102-image.png

                        w0wW dennypageD 2 Replies Last reply Reply Quote 0
                        • w0wW
                          w0w @netboy
                          last edited by

                          @netboy
                          If it has already been charging for more than 16 hours and still won't work, you can try the solution found here.

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @netboy
                            last edited by

                            @netboy said in ONLINE LOW BATTERY message:

                            I replaced the battery with APC original battery from Amazon and it is now approx 6+ hours and the nut server seems to be stuck with the old config.

                            See the line that says:

                            ups.status                      OL LB
                            

                            That indicates that your UPS is (still) actively reporting low battery.

                            You may need to perform an action on the UPS itself to reset the bad battery state. Either a self-test or a reboot. Check your UPS's manual.

                            Btw, while you're at it you probably want to set the battery date. Check the upsrw command to see if you can set the field called [battery.date] field. If not, then you will have to do it on the UPS itself.

                            N 1 Reply Last reply Reply Quote 0
                            • N
                              netboy @dennypage
                              last edited by

                              @dennypage said in ONLINE LOW BATTERY message:

                              self-test

                              Ok did a manual reeset (I belive press and hold start button and it blinkcs for 20 seconds or so).
                              Now the status says low battery and charging

                              7533c77e-6367-4f0f-8cd3-6ff8eea29585-image.png

                              884cd96d-8342-44e5-b314-4a63002ed553-image.png

                              N 1 Reply Last reply Reply Quote 0
                              • N
                                netboy @netboy
                                last edited by

                                @netboy Back to status OL LB - How to reset BE850G - any idea ? The manual does not detail how to reset

                                T w0wW 2 Replies Last reply Reply Quote 0
                                • T
                                  tedquade @netboy
                                  last edited by

                                  @netboy Leave it on to charge for 16 hours or so before passing judgment. I just installed a new APC UPS and instructions say so.

                                  Ted

                                  N 1 Reply Last reply Reply Quote 0
                                  • N
                                    netboy @tedquade
                                    last edited by

                                    @tedquade said in ONLINE LOW BATTERY message:

                                    @netboy Leave it on to charge for 16 hours or so before passing judgment. I just installed a new APC UPS and instructions say so.

                                    Ted

                                    Ok patience is warranted on my part

                                    1 Reply Last reply Reply Quote 0
                                    • provelsP
                                      provels
                                      last edited by provels

                                      Just throwing this out here. If you cannot change the battery replacement date from the console (like me!), you can download a copy of APC's PowerChute Personal Edition and use it to set the date from a Windows PC.
                                      d700fca5-d982-4697-8ae4-3e829a55201b-image.png

                                      Peder

                                      MAIN - pfSense+ 24.11-RELEASE - Adlink MXE-5401, i7, 16 GB RAM, 64 GB SSD. 500 GB HDD for SyslogNG
                                      BACKUP - pfSense+ 23.01-RELEASE - Hyper-V Virtual Machine, Gen 1, 2 v-CPUs, 3 GB RAM, 8GB VHDX (Dynamic)

                                      N 1 Reply Last reply Reply Quote 0
                                      • N
                                        netboy @provels
                                        last edited by

                                        @provels said in ONLINE LOW BATTERY message:

                                        Just throwing this out here. If you cannot change the battery replacement date from the console (like me!), you can download a copy of APC's PowerChute Personal Edition and use it to set the date from a Windows PC.
                                        d700fca5-d982-4697-8ae4-3e829a55201b-image.png

                                        I have UPS attached to pfsense netgatge 2100 - I am aware of powerchute software - the only problem is I have to take a WINDOWS PC / LAPTOP and then install the software and connect to the battery. I might do this if 16 hours have passed. Any way thanks for the suggestion

                                        1 Reply Last reply Reply Quote 0
                                        • w0wW
                                          w0w @netboy
                                          last edited by

                                          @netboy said in ONLINE LOW BATTERY message:

                                          How to reset BE850G - any idea ? The manual does not detail how to reset

                                          From link I've posted above. In case you didn't read that or missed:

                                          instructions from APC's e-mail support:

                                          1. Disconnect any attached load.
                                          2. Turn off the UPS
                                          3. Unplug the UPS from the wall socket.
                                          4. Disconnect the UPS internal battery.
                                          5. Push and hold the "On" button on the UPS for 5 seconds.
                                          6. Reconnect internal battery.
                                          7. Plug UPS in to known good power source.
                                          8. Turn the UPS ON.
                                          N 1 Reply Last reply Reply Quote 0
                                          • N
                                            netboy @w0w
                                            last edited by

                                            @w0w said in ONLINE LOW BATTERY message:

                                            @netboy said in ONLINE LOW BATTERY message:

                                            How to reset BE850G - any idea ? The manual does not detail how to reset

                                            From link I've posted above. In case you didn't read that or missed:

                                            instructions from APC's e-mail support:

                                            1. Disconnect any attached load.
                                            2. Turn off the UPS
                                            3. Unplug the UPS from the wall socket.
                                            4. Disconnect the UPS internal battery.
                                            5. Push and hold the "On" button on the UPS for 5 seconds.
                                            6. Reconnect internal battery.
                                            7. Plug UPS in to known good power source.
                                            8. Turn the UPS ON.

                                            I am aware of the above instructions for Easy-UPS - unfortunately I guess this does not apply to BE750G unless somebody says I am wrong!

                                            w0wW 1 Reply Last reply Reply Quote 0