    • D
      dbaio
      last edited by

      @Criggie:

      I've just switched back to a hardware firewall from a VM, and have tried setting up my old APC smartups 620 again.  This used to work in the past, but for the life of me I can't get the config right.

      Hi.
      Could you try this config:

      UPS CABLE: 940-0095A
      UPS TYPE / Device: apcsmart /dev/cuau0

      –
      Danilo G. Baio (dbaio)

      1 Reply Last reply Reply Quote 0
      • D
        dbaio
        last edited by

        @biggsy:

        Thanks.

        I know the NUT package has been around for quite a long time but I've been using apcupsd in a Windows VM for a couple of years.  This package is just what I need in a similar build I'm doing for a friend, provided I can figure out the script to execute on low battery.

        Soon, I want  make an improvement for let you change these scripts:

        killpower)
          commfailure)
          commok)
          powerout)
          onbattery)
          offbattery)
          mainsback)
          failing)
          timeout)
          loadlimit)
          runlimit)
          doreboot)
          doshutdown)
          annoyme)
          emergency)
          changeme)
          remotedown)
          startselftest)
          endselftest)
          battdetach)
          battattach)

        For now, you need to change manually or create your script on pfSense box.

        Example for pfSense 2.1 amd64:

        create the script:
        touch /usr/pbi/apcupsd-amd64/etc/apcupsd/doshutdown

        edit it:
        vi /usr/pbi/apcupsd-amd64/etc/apcupsd/doshutdown

        change the permissions:
        chmod +x /usr/pbi/apcupsd-amd64/etc/apcupsd/doshutdown

        create a symbolic link:
        ln -s /usr/pbi/apcupsd-amd64/etc/apcupsd/doshutdown /usr/local/etc/apcupsd/

        Thanks

        –
        Danilo G. Baio (dbaio)

        1 Reply Last reply Reply Quote 0
        • M
          Mr. Jingles
          last edited by

          G'day Danilo  ;D

          Could I ask a question? I have an APC-UPS (SmartUPS 1000), which connects to a Synology NAS via a USB-cable which has some (I don't know which one yet, but Synology runs Linux) UPS-server running. So the APC-UPS sends a signal to the Synology when there is a power problem, after which the Synology can shut down itself and the other Synology NAS-ses I have via LAN. Would your package be able to act as a slave towards the Synology also? As in:
          APC-UPS: power problem signal to Synology NAS 1
          –----------> Synology NAS 1 (UPS server monitoring software)
          -------------------------------> signal to other Synologies: shutdown
          -------------------------------> signal to pfSense: shutdown

          If so, what would be the settings in your package to accomplish this? I have been poking around, but to be honest: I have no clue  :-[

          Thank you in advance for your answer  ;D

          Bye,

          ups004.jpg
          ups004.jpg_thumb

          6 and a half billion people know that they are stupid, agressive, lower life forms.

          1 Reply Last reply Reply Quote 0
          • D
            dbaio
            last edited by

            @Hollander:

            G'day Danilo  ;D

            Could I ask a question? I have an APC-UPS (SmartUPS 1000), which connects to a Synology NAS via a USB-cable which has some (I don't know which one yet, but Synology runs Linux) UPS-server running. So the APC-UPS sends a signal to the Synology when there is a power problem, after which the Synology can shut down itself and the other Synology NAS-ses I have via LAN. Would your package be able to act as a slave towards the Synology also? As in:
            APC-UPS: power problem signal to Synology NAS 1
            –----------> Synology NAS 1 (UPS server monitoring software)
            -------------------------------> signal to other Synologies: shutdown
            -------------------------------> signal to pfSense: shutdown

            Hi Hollander.

            searching on google, looks like you can install apcupsd on synology, but seems that you need to make some modifications. (I can't help you with that ).

            If you can run apcupsd on synology, then you can integrate with others systems running apcupsd.

            Sorry for not helping too much.

            –
            Danilo G. Baio (dbaio)

            1 Reply Last reply Reply Quote 0
            • C
              Criggie
              last edited by

              @dbaio:

              Could you try this config:
              UPS CABLE: 940-0095A
              UPS TYPE / Device: apcsmart /dev/cuau0

              Same kind of thing again

              Jan  3 21:18:27 pfsense apcupsd[27864]: Lock file data error: X<ec><ff><ff><ff>^?
              Jan  3 21:18:27 pfsense apcupsd[27864]: apcupsd FATAL ERROR in apcupsd.c at line 285 Failed to acquire device lock file
              Jan  3 21:18:27 pfsense apcupsd[27864]: Lock file data error: M-^@ <da><fd>Jan  3 21:18:27 pfsense apcupsd[27864]: apcupsd error shutdown completed

              [2.1-RELEASE][root@pfsense.criggie.org.nz]/root(10): ls -la /dev/cuau0*
              crw-rw–--  1 root  dialer    0,  40 Dec 28 23:16 /dev/cuau0
              crw-rw----  1 uucp  dialer    0,  41 Dec 28 22:06 /dev/cuau0.init
              crw-rw----  1 uucp  dialer    0,  42 Dec 28 22:06 /dev/cuau0.lock

              How do I find out what's using /dev/cuau0?  Normally I'd run fuser or lsof but they're not available.</fd></da></ff></ff></ff></ec>

              1 Reply Last reply Reply Quote 0
              • K
                KaneR
                last edited by

                Hi,

                Many thanks for the package.

                It looks like it has been compiled without snmp support, see below:

                php: /pkg_edit.php: The command '/usr/local/etc/rc.d/apcupsd.sh restart' returned exit code '1', the output was 'Stopping APC UPS Daemon… No matching processes were found Starting APC UPS Daemon... apcupsd FATAL ERROR in apcupsd.c at line 259 Apcupsd cannot continue without a valid driver. Apcupsd driver snmplite not found. The available apcupsd drivers are: dumb apcsmart net usb pcnet Most likely, you need to add --enable-snmplite to your ./configure options. '

                Can this be changed?

                Thanks

                Kane

                1 Reply Last reply Reply Quote 0
                • G
                  gogol
                  last edited by

                  @Hollander:

                  G'day Danilo  ;D

                  Could I ask a question? I have an APC-UPS (SmartUPS 1000), which connects to a Synology NAS via a USB-cable which has some (I don't know which one yet, but Synology runs Linux) UPS-server running. So the APC-UPS sends a signal to the Synology when there is a power problem, after which the Synology can shut down itself and the other Synology NAS-ses I have via LAN. Would your package be able to act as a slave towards the Synology also? As in:
                  APC-UPS: power problem signal to Synology NAS 1
                  –----------> Synology NAS 1 (UPS server monitoring software)
                  -------------------------------> signal to other Synologies: shutdown
                  -------------------------------> signal to pfSense: shutdown

                  If so, what would be the settings in your package to accomplish this? I have been poking around, but to be honest: I have no clue  :-[

                  Thank you in advance for your answer  ;D

                  Bye,
                  [/quote]

                  I have done this with the NUT package. The USB cable from my backups ES700 is connected to a Synology NAS and this NAS acts as a server for my Pfsense box.
                  Works like a charm:

                  • On your NAS check shutdown UPS and enable Network UPS Server

                  • In Permitted disk stations enter IP adres of your Pfsense box (Lan IP address in most cases)

                  • In the NUT package settings set Remote UPS

                  • And Remote NUT ups settings set name to "ups", Remote address to you NAS IP, User "monuser" and Password "secret"

                  Thats all there is. But don't forget that with a power failure your network doesn't have power too, so your switch must be connected to the UPS too (that's what I forgot while testing) :D

                  1 Reply Last reply Reply Quote 0
                  • M
                    Mr. Jingles
                    last edited by

                    @gogol:

                    @Hollander:

                    G'day Danilo  ;D

                    Could I ask a question? I have an APC-UPS (SmartUPS 1000), which connects to a Synology NAS via a USB-cable which has some (I don't know which one yet, but Synology runs Linux) UPS-server running. So the APC-UPS sends a signal to the Synology when there is a power problem, after which the Synology can shut down itself and the other Synology NAS-ses I have via LAN. Would your package be able to act as a slave towards the Synology also? As in:
                    APC-UPS: power problem signal to Synology NAS 1
                    –----------> Synology NAS 1 (UPS server monitoring software)
                    -------------------------------> signal to other Synologies: shutdown
                    -------------------------------> signal to pfSense: shutdown

                    If so, what would be the settings in your package to accomplish this? I have been poking around, but to be honest: I have no clue  :-[

                    Thank you in advance for your answer  ;D

                    Bye,
                    [/quote]

                    I have done this with the NUT package. The USB cable from my backups ES700 is connected to a Synology NAS and this NAS acts as a server for my Pfsense box.
                    Works like a charm:

                    • On your NAS check shutdown UPS and enable Network UPS Server

                    • In Permitted disk stations enter IP adres of your Pfsense box (Lan IP address in most cases)

                    • In the NUT package settings set Remote UPS

                    • And Remote NUT ups settings set name to "ups", Remote address to you NAS IP, User "monuser" and Password "secret"

                    Thats all there is. But don't forget that with a power failure your network doesn't have power too, so your switch must be connected to the UPS too (that's what I forgot while testing) :D

                    Thank you Gogol for the very clear instructions, very kind of you  ;D

                    Of course, knowing me, it didn't work  :-[

                    ( ;D)

                    I will open a new thread in order not to hijack Danilo's thread. Perhaps you'd be willing to look in that new thread? (I'll post it here once I've created it). EDIT: new thread is here: http://forum.pfsense.org/index.php/topic,71121.msg388428.html#msg388428

                    Thank you  ;D

                    6 and a half billion people know that they are stupid, agressive, lower life forms.

                    1 Reply Last reply Reply Quote 0
                    • D
                      dbaio
                      last edited by

                      The package was updated. (apcupsd-3.14.10_1 pkg v0.2)

                      • Fixed snmp.

                      • Added device option.

                      • Added script to send alerts if you have smtp notifications enabled and mailreport package.

                      If you use pcnet on the Upstype field, the parameters need to be on same field.
                      If you use snmp, the parameters need to be on device field.

                      –
                      Danilo G. Baio (dbaio)

                      1 Reply Last reply Reply Quote 0
                      • M
                        McFuzz
                        last edited by

                        Hello!

                        Love the UPS monitoring feature; very nice!

                        Question/request though - it is possible to get email notifications when the power is cut out?

                        Thanks!

                        1 Reply Last reply Reply Quote 0
                        • D
                          doktornotor Banned
                          last edited by

                          @McFuzz:

                          Question/request though - it is possible to get email notifications when the power is cut out?

                          May I suggest reading the previous post, right above yours?

                          1 Reply Last reply Reply Quote 0
                          • M
                            McFuzz
                            last edited by

                            @doktornotor:

                            @McFuzz:

                            Question/request though - it is possible to get email notifications when the power is cut out?

                            May I suggest reading the previous post, right above yours?

                            blind, i am :D

                            1 Reply Last reply Reply Quote 0
                            • M
                              McFuzz
                              last edited by

                              So I am hitting a bit of a weird issue…

                              Upgraded to 2.1.2 and all was well; apcupsd worked fine with my USB based APC UPS.

                              Then all of the sudden, I started getting the operation timed out error when clicking on the status tab. Checking the logs, I see this:

                              
                              2014-04-10 21:21:48 -0700  Lock file data error: Xìÿÿÿ^?
                              2014-04-10 21:21:48 -0700  apcupsd FATAL ERROR in apcupsd.c at line 285
                              Failed to acquire device lock file
                              2014-04-10 21:21:48 -0700  Lock file data error: Ø^ËB
                              2014-04-10 21:21:48 -0700  apcupsd error shutdown completed
                              
                              

                              Tried restarting the service, reinstalling, rebooting, removing, rebooting, reinstalling… no dice.

                              Then, I just put a random string in the 'Device' field (the one right above 'Poll Time') - not to confuse with 'USB Type / Device' field which shows "usb BLANK"

                              Now I see this:

                              
                              2014-04-10 21:27:50 -0700  apcupsd FATAL ERROR in generic-usb.c at line 674
                              Cannot find UPS device --
                              For a link to detailed USB trouble shooting information,
                              please see <http: www.apcupsd.com="" support.html="">.
                              2014-04-10 21:27:50 -0700  apcupsd error shutdown completed</http:> 
                              

                              For testing sake - I installed NUT and it seems to be working just fine.

                              So, any ideas of why apcupsd ceased to work? :(

                              1 Reply Last reply Reply Quote 0
                              • D
                                dbaio
                                last edited by

                                Before, We had just one field to be filled: UPS Type / Device.
                                Now, We have Device field separated.

                                For pcnet config, parameters need to be just on UPS Type field.
                                With snmp, the parameters need to be on device field.

                                How was your config before the upgrade?

                                –
                                Danilo G. Baio (dbaio)

                                1 Reply Last reply Reply Quote 0
                                • D
                                  dbaio
                                  last edited by

                                  @McFuzz:

                                  Hello!

                                  Love the UPS monitoring feature; very nice!

                                  Question/request though - it is possible to get email notifications when the power is cut out?

                                  Thanks!

                                  Hi.

                                  You need to configure smtp email notifications on pfSense and install mailreport package (just install it).
                                  After that, apcupsd will send email alerts to you.

                                  –
                                  Danilo G. Baio (dbaio)

                                  1 Reply Last reply Reply Quote 0
                                  • M
                                    McFuzz
                                    last edited by

                                    @dbaio:

                                    Before, We had just one field to be filled: UPS Type / Device.
                                    Now, We have Device field separated.

                                    For pcnet config, parameters need to be just on UPS Type field.
                                    With snmp, the parameters need to be on device field.

                                    How was your config before the upgrade?

                                    Config was as attached (of course service was enabled; I disabled it for now since I am using NUT). All other settings are left at default.

                                    ![Screen Shot 2014-04-11 at 9.28.52 AM.png_thumb](/public/imported_attachments/1/Screen Shot 2014-04-11 at 9.28.52 AM.png_thumb)
                                    ![Screen Shot 2014-04-11 at 9.28.52 AM.png](/public/imported_attachments/1/Screen Shot 2014-04-11 at 9.28.52 AM.png)

                                    1 Reply Last reply Reply Quote 0
                                    • D
                                      dbaio
                                      last edited by

                                      @McFuzz:

                                      Config was as attached (of course service was enabled; I disabled it for now since I am using NUT). All other settings are left at default.

                                      When you have a chance, on UPSType / Device put just "usb" and try again.

                                      –
                                      Danilo G. Baio (dbaio)

                                      1 Reply Last reply Reply Quote 0
                                      • M
                                        McFuzz
                                        last edited by

                                        @dbaio:

                                        @McFuzz:

                                        Config was as attached (of course service was enabled; I disabled it for now since I am using NUT). All other settings are left at default.

                                        When you have a chance, on UPSType / Device put just "usb" and try again.

                                        Unfortunately that did not help :\ still have the same problem:

                                        
                                        2014-04-11 13:58:04 -0700  Lock file data error: X����
                                        2014-04-11 13:58:04 -0700  apcupsd FATAL ERROR in apcupsd.c at line 285
                                        Failed to acquire device lock file
                                        2014-04-11 13:58:04 -0700  Lock file data error: ؋B
                                        2014-04-11 13:58:04 -0700  apcupsd error shutdown completed
                                        
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • D
                                          dbaio
                                          last edited by

                                          Could you collect all the log?

                                          On Diagnostics –> Command Prompt

                                          cat /var/log/apcupsd.events

                                          Use a pastebin like pastebin.ca

                                          Thank you.

                                          @McFuzz:

                                          @dbaio:

                                          @McFuzz:

                                          Config was as attached (of course service was enabled; I disabled it for now since I am using NUT). All other settings are left at default.

                                          When you have a chance, on UPSType / Device put just "usb" and try again.

                                          Unfortunately that did not help :\ still have the same problem:

                                          
                                          2014-04-11 13:58:04 -0700  Lock file data error: X����
                                          2014-04-11 13:58:04 -0700  apcupsd FATAL ERROR in apcupsd.c at line 285
                                          Failed to acquire device lock file
                                          2014-04-11 13:58:04 -0700  Lock file data error: ؋B
                                          2014-04-11 13:58:04 -0700  apcupsd error shutdown completed
                                          
                                          

                                          –
                                          Danilo G. Baio (dbaio)

                                          1 Reply Last reply Reply Quote 0
                                          • M
                                            McFuzz
                                            last edited by

                                            @dbaio:

                                            Could you collect the log?

                                            On Diagnostics –> Command Prompt

                                            cat /var/log/apcupsd.events

                                            Use a pastebin like pastebin.ca

                                            Thank you.

                                            @McFuzz:

                                            @dbaio:

                                            @McFuzz:

                                            Config was as attached (of course service was enabled; I disabled it for now since I am using NUT). All other settings are left at default.

                                            When you have a chance, on UPSType / Device put just "usb" and try again.

                                            Unfortunately that did not help :\ still have the same problem:

                                            
                                            2014-04-11 13:58:04 -0700  Lock file data error: X����
                                            2014-04-11 13:58:04 -0700  apcupsd FATAL ERROR in apcupsd.c at line 285
                                            Failed to acquire device lock file
                                            2014-04-11 13:58:04 -0700  Lock file data error: ؋B
                                            2014-04-11 13:58:04 -0700  apcupsd error shutdown completed
                                            
                                            

                                            Log here:

                                            http://pastebin.com/9e347baC

                                            The log is as-of yesterday.

                                            1 Reply Last reply Reply Quote 0