Netgate Discussion Forum
    • Categories
    • Recent
    • Tags
    • Popular
    • Users
    • Search
    • Register
    • Login

    Apcupsd 3.14.10 on pfSense 2.1.5 (amd64)

    Scheduled Pinned Locked Moved pfSense Packages
    21 Posts 5 Posters 9.0k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • M
      mir
      last edited by

      What is the contents of: /usr/pbi/apcupsd-amd64/etc/apcupsd/apcupsd.conf

      1 Reply Last reply Reply Quote 0
      • P
        PARC
        last edited by

        Certainly…

        $ cat /usr/pbi/apcupsd-amd64/etc/apcupsd/apcupsd.conf
        ## apcupsd.conf v1.1 ##
        # 
        #  for apcupsd release 3.14.10 (13 September 2011) - freebsd
        #
        # "apcupsd" POSIX config file
        
        #
        # ========= General configuration parameters ============
        #
        
        # UPSNAME xxx
        #   Use this to give your UPS a name in log files and such. This
        #   is particulary useful if you have multiple UPSes. This does not
        #   set the EEPROM. It should be 8 characters or less.
        UPSNAME UPS02
        
        # UPSCABLE <cable>
        #   Defines the type of cable connecting the UPS to your computer.
        #
        #   Possible generic choices for <cable> are:
        #     simple, smart, ether, usb
        #
        #   Or a specific cable model number may be used:
        #     940-0119A, 940-0127A, 940-0128A, 940-0020B,
        #     940-0020C, 940-0023A, 940-0024B, 940-0024C,
        #     940-1524C, 940-0024G, 940-0095A, 940-0095B,
        #     940-0095C, M-04-02-2000
        #
        UPSCABLE ether
        
        # To get apcupsd to work, in addition to defining the cable
        # above, you must also define a UPSTYPE, which corresponds to
        # the type of UPS you have (see the Description for more details).
        # You must also specify a DEVICE, sometimes referred to as a port.
        # For USB UPSes, please leave the DEVICE directive blank. For
        # other UPS types, you must specify an appropriate port or address.
        #
        # UPSTYPE   DEVICE           Description
        # apcsmart  /dev/tty**       Newer serial character device, appropriate for 
        #                            SmartUPS models using a serial cable (not USB).
        #
        # usb       <blank>          Most new UPSes are USB. A blank DEVICE
        #                            setting enables autodetection, which is
        #                            the best choice for most installations.
        #
        # net       hostname:port    Network link to a master apcupsd through apcupsd's 
        #                            Network Information Server. This is used if the
        #                            UPS powering your computer is connected to a 
        #                            different computer for monitoring.
        #
        # snmp      hostname:port:vendor:community
        #                            SNMP network link to an SNMP-enabled UPS device.
        #                            Hostname is the ip address or hostname of the UPS 
        #                            on the network. Vendor can be can be "APC" or 
        #                            "APC_NOTRAP". "APC_NOTRAP" will disable SNMP trap 
        #                            catching; you usually want "APC". Port is usually 
        #                            161\. Community is usually "private".
        #
        # netsnmp   hostname:port:vendor:community
        #                            OBSOLETE
        #                            Same as SNMP above but requires use of the 
        #                            net-snmp library. Unless you have a specific need
        #                            for this old driver, you should use 'snmp' instead.
        #
        # dumb      /dev/tty**       Old serial character device for use with 
        #                            simple-signaling UPSes.
        #
        # pcnet     ipaddr:username:passphrase:port
        #                            PowerChute Network Shutdown protocol which can be 
        #                            used as an alternative to SNMP with the AP9617 
        #                            family of smart slot cards. ipaddr is the IP 
        #                            address of the UPS management card. username and 
        #                            passphrase are the credentials for which the card 
        #                            has been configured. port is the port number on 
        #                            which to listen for messages from the UPS, normally 
        #                            3052\. If this parameter is empty or missing, the 
        #                            default of 3052 will be used.
        #
        UPSTYPE net
        DEVICE <my.netop.ip.here>: <myport># POLLTIME <int>
        #   Interval (in seconds) at which apcupsd polls the UPS for status. This
        #   setting applies both to directly-attached UPSes (UPSTYPE apcsmart, usb, 
        #   dumb) and networked UPSes (UPSTYPE net, snmp). Lowering this setting
        #   will improve apcupsd's responsiveness to certain events at the cost of
        #   higher CPU utilization. The default of 60 is appropriate for most
        #   situations.
        POLLTIME 30
        
        # LOCKFILE <path to="" lockfile="">
        #   Path for device lock file. Not used on Win32.
        LOCKFILE /var/lock
        
        # SCRIPTDIR <path to="" script="" directory="">
        #   Directory in which apccontrol and event scripts are located.
        SCRIPTDIR /usr/local/etc/apcupsd
        
        # PWRFAILDIR <path to="" powerfail="" directory="">
        #   Directory in which to write the powerfail flag file. This file
        #   is created when apcupsd initiates a system shutdown and is
        #   checked in the OS halt scripts to determine if a killpower
        #   (turning off UPS output power) is required.
        PWRFAILDIR /var/run
        
        # NOLOGINDIR <path to="" nologin="" directory="">
        #   Directory in which to write the nologin file. The existence
        #   of this flag file tells the OS to disallow new logins.
        NOLOGINDIR /var/run
        
        #
        # ======== Configuration parameters used during power failures ==========
        #
        
        # The ONBATTERYDELAY is the time in seconds from when a power failure
        #   is detected until we react to it with an onbattery event.
        #
        #   This means that, apccontrol will be called with the powerout argument
        #   immediately when a power failure is detected.  However, the
        #   onbattery argument is passed to apccontrol only after the 
        #   ONBATTERYDELAY time.  If you don't want to be annoyed by short
        #   powerfailures, make sure that apccontrol powerout does nothing
        #   i.e. comment out the wall.
        ONBATTERYDELAY 6
        
        # 
        # Note: BATTERYLEVEL, MINUTES, and TIMEOUT work in conjunction, so
        # the first that occurs will cause the initation of a shutdown.
        #
        
        # If during a power failure, the remaining battery percentage
        # (as reported by the UPS) is below or equal to BATTERYLEVEL, 
        # apcupsd will initiate a system shutdown.
        BATTERYLEVEL 5
        
        # If during a power failure, the remaining runtime in minutes 
        # (as calculated internally by the UPS) is below or equal to MINUTES,
        # apcupsd, will initiate a system shutdown.
        MINUTES 1
        
        # If during a power failure, the UPS has run on batteries for TIMEOUT
        # many seconds or longer, apcupsd will initiate a system shutdown.
        # A value of 0 disables this timer.
        #
        #  Note, if you have a Smart UPS, you will most likely want to disable
        #    this timer by setting it to zero. That way, you UPS will continue
        #    on batteries until either the % charge remaing drops to or below BATTERYLEVEL,
        #    or the remaining battery runtime drops to or below MINUTES.  Of course,
        #    if you are testing, setting this to 60 causes a quick system shutdown
        #    if you pull the power plug.   
        #  If you have an older dumb UPS, you will want to set this to less than
        #    the time you know you can run on batteries.
        TIMEOUT 0
        
        #  Time in seconds between annoying users to signoff prior to
        #  system shutdown. 0 disables.
        ANNOY 0
        
        # Initial delay after power failure before warning users to get
        # off the system.
        ANNOYDELAY 60
        
        # The condition which determines when users are prevented from
        # logging in during a power failure.
        # NOLOGON <string> [ disable | timeout | percent | minutes | always ]
        NOLOGON disable
        
        # If KILLDELAY is non-zero, apcupsd will continue running after a
        # shutdown has been requested, and after the specified time in
        # seconds attempt to kill the power. This is for use on systems
        # where apcupsd cannot regain control after a shutdown.
        # KILLDELAY <seconds>  0 disables
        KILLDELAY 0
        
        #
        # ==== Configuration statements for Network Information Server ====
        #
        
        # NETSERVER [ on | off ] on enables, off disables the network
        #  information server. If netstatus is on, a network information
        #  server process will be started for serving the STATUS and
        #  EVENT data over the network (used by CGI programs).
        NETSERVER on
        
        # NISIP <dotted notation="" ip="" address="">
        #  IP address on which NIS server will listen for incoming connections.
        #  This is useful if your server is multi-homed (has more than one
        #  network interface and IP address). Default value is 0.0.0.0 which
        #  means any incoming request will be serviced. Alternatively, you can
        #  configure this setting to any specific IP address of your server and 
        #  NIS will listen for connections only on that interface. Use the
        #  loopback address (127.0.0.1) to accept connections only from the
        #  local machine.
        NISIP 0.0.0.0
        
        # NISPORT <port> default is 3551 as registered with the IANA
        #  port to use for sending STATUS and EVENTS data over the network.
        #  It is not used unless NETSERVER is on. If you change this port,
        #  you will need to change the corresponding value in the cgi directory
        #  and rebuild the cgi programs.
        NISPORT <myport>
        
        # If you want the last few EVENTS to be available over the network
        # by the network information server, you must define an EVENTSFILE.
        EVENTSFILE /var/log/apcupsd.events
        
        # EVENTSFILEMAX <kilobytes>
        #  By default, the size of the EVENTSFILE will be not be allowed to exceed
        #  10 kilobytes.  When the file grows beyond this limit, older EVENTS will
        #  be removed from the beginning of the file (first in first out).  The
        #  parameter EVENTSFILEMAX can be set to a different kilobyte value, or set
        #  to zero to allow the EVENTSFILE to grow without limit.
        EVENTSFILEMAX 10
        
        #
        # ========== Configuration statements used if sharing =============
        #            a UPS with more than one machine
        
        #
        # Remaining items are for ShareUPS (APC expansion card) ONLY
        #
        
        # UPSCLASS [ standalone | shareslave | sharemaster ]
        #   Normally standalone unless you share an UPS using an APC ShareUPS
        #   card.
        UPSCLASS standalone
        
        # UPSMODE [ disable | share ]
        #   Normally disable unless you share an UPS using an APC ShareUPS card.
        UPSMODE disable
        
        #
        # ===== Configuration statements to control apcupsd system logging ========
        #
        
        # Time interval in seconds between writing the STATUS file; 0 disables
        STATTIME 0
        
        # Location of STATUS file (written to only if STATTIME is non-zero)
        STATFILE /var/log/apcupsd.status
        
        # LOGSTATS [ on | off ] on enables, off disables
        # Note! This generates a lot of output, so if         
        #       you turn this on, be sure that the
        #       file defined in syslog.conf for LOG_NOTICE is a named pipe.
        #  You probably do not want this on.
        LOGSTATS off
        
        # Time interval in seconds between writing the DATA records to
        #   the log file. 0 disables.
        DATATIME 0
        
        # FACILITY defines the logging facility (class) for logging to syslog. 
        #          If not specified, it defaults to "daemon". This is useful 
        #          if you want to separate the data logged by apcupsd from other
        #          programs.
        #FACILITY DAEMON
        
        #
        # ========== Configuration statements used in updating the UPS EPROM =========
        #
        
        #
        # These statements are used only by apctest when choosing "Set EEPROM with conf
        # file values" from the EEPROM menu. THESE STATEMENTS HAVE NO EFFECT ON APCUPSD.
        #
        
        # UPS name, max 8 characters 
        #UPSNAME UPS_IDEN
        
        # Battery date - 8 characters
        #BATTDATE mm/dd/yy
        
        # Sensitivity to line voltage quality (H cause faster transfer to batteries)  
        # SENSITIVITY H M L        (default = H)
        #SENSITIVITY H
        
        # UPS delay after power return (seconds)
        # WAKEUP 000 060 180 300   (default = 0)
        #WAKEUP 60
        
        # UPS Grace period after request to power off (seconds)
        # SLEEP 020 180 300 600    (default = 20)
        #SLEEP 180
        
        # Low line voltage causing transfer to batteries
        # The permitted values depend on your model as defined by last letter 
        #  of FIRMWARE or APCMODEL. Some representative values are:
        #    D 106 103 100 097
        #    M 177 172 168 182
        #    A 092 090 088 086
        #    I 208 204 200 196     (default = 0 => not valid)
        #LOTRANSFER  208
        
        # High line voltage causing transfer to batteries
        # The permitted values depend on your model as defined by last letter 
        #  of FIRMWARE or APCMODEL. Some representative values are:
        #    D 127 130 133 136
        #    M 229 234 239 224
        #    A 108 110 112 114
        #    I 253 257 261 265     (default = 0 => not valid)
        #HITRANSFER 253
        
        # Battery charge needed to restore power
        # RETURNCHARGE 00 15 50 90 (default = 15)
        #RETURNCHARGE 15
        
        # Alarm delay 
        # 0 = zero delay after pwr fail, T = power fail + 30 sec, L = low battery, N = never
        # BEEPSTATE 0 T L N        (default = 0)
        #BEEPSTATE T
        
        # Low battery warning delay in minutes
        # LOWBATT 02 05 07 10      (default = 02)
        #LOWBATT 2
        
        # UPS Output voltage when running on batteries
        # The permitted values depend on your model as defined by last letter 
        #  of FIRMWARE or APCMODEL. Some representative values are:
        #    D 115
        #    M 208
        #    A 100
        #    I 230 240 220 225     (default = 0 => not valid)
        #OUTPUTVOLTS 230
        
        # Self test interval in hours 336=2 weeks, 168=1 week, ON=at power on
        # SELFTEST 336 168 ON OFF  (default = 336)
        #SELFTEST 336</kilobytes></myport></port></dotted></seconds></string></path></path></path></path></int></myport></my.netop.ip.here></blank></cable></cable>
        

        For those interested, here is the output of acpaccess for the local and remote services.

        $ apcaccess status localhost: <myport>APC      : 001,018,0476
        DATE     : 2014-12-08 18:32:31 +0000  
        HOSTNAME : pfsense.localdomain
        VERSION  : 3.14.10 (13 September 2011) freebsd
        UPSNAME  : UPS02
        CABLE    : Ethernet Link
        DRIVER   : NETWORK UPS Driver
        UPSMODE  : Net Slave
        STARTTIME: 2014-12-08 18:32:11 +0000  
        STATUS   : COMMLOST 
        MBATTCHG : 5 Percent
        MINTIMEL : 1 Minutes
        MAXTIME  : 0 Seconds
        NUMXFERS : 0
        TONBATT  : 0 seconds
        CUMONBATT: 0 seconds
        XOFFBATT : N/A
        STATFLAG : 0x07000100 Status Flag
        END APC  : 2014-12-08 23:57:10 +0000</myport>
        
        $ apcaccess status <my.netops.ip.here>: <port>APC      : 001,045,1178
        DATE     : 2014-12-08 15:57:54 -0800  
        HOSTNAME : my.netops.fqdn
        VERSION  : 3.14.8 (16 January 2010) gentoo
        UPSNAME  : UPSO2
        CABLE    : USB Cable
        MODEL    : Smart-UPS 2200 XL 
        UPSMODE  : ShareUPS Master
        STARTTIME: 2013-09-29 20:45:42 -0700  
        SHARE    : ShareUPS
        STATUS   : ONLINE 
        LINEV    : 117.3 Volts
        LOADPCT  :  94.9 Percent Load Capacity
        BCHARGE  : 100.0 Percent
        TIMELEFT :  85.0 Minutes
        MBATTCHG : -1 Percent
        MINTIMEL : 2 Minutes
        MAXTIME  : 0 Seconds
        OUTPUTV  : 117.3 Volts
        SENSE    : High
        DWAKE    : -01 Seconds
        DSHUTD   : 090 Seconds
        LOTRANS  : 106.0 Volts
        HITRANS  : 127.0 Volts
        RETPCT   : 000.0 Percent
        ITEMP    : 22.5 C Internal
        ALARMDEL : Always
        BATTV    : 55.4 Volts
        LINEFREQ : 60.0 Hz
        LASTXFER : Automatic or explicit self test
        NUMXFERS : 42
        XONBATT  : 2014-12-07 18:55:45 -0800  
        TONBATT  : 0 seconds
        CUMONBATT: 321 seconds
        XOFFBATT : 2014-12-07 18:55:52 -0800  
        LASTSTEST: 2014-12-07 18:55:45 -0800  
        SELFTEST : NO
        STESTI   : 14 days
        STATFLAG : 0x07000008 Status Flag
        SERIALNO : JS1047018233
        BATTDATE : 2010-11-19
        NOMOUTV  : 120 Volts
        NOMBATTV :  48.0 Volts
        FIRMWARE : 690.19.D USB FW:7.4
        APCMODEL : Smart-UPS 2200 XL 
        END APC  : 2014-12-08 15:57:58 -0800</port></my.netops.ip.here>
        
        1 Reply Last reply Reply Quote 0
        • M
          mir
          last edited by

          LOCKFILE option should have /var/tmp
          You have /var/lock which does not exist by default.

          1 Reply Last reply Reply Quote 0
          • P
            PARC
            last edited by

            I toggled this setting during my troubleshooting… sadly, changing it back to the /var/tmp default has no effect, but I appreciate the suggestion.

            1 Reply Last reply Reply Quote 0
            • M
              mir
              last edited by

              Have you tried running this from the command line: /usr/local/etc/rc.d/apcupsd.sh

              To see want errors you get?

              1 Reply Last reply Reply Quote 0
              • P
                PARC
                last edited by

                I've been starting and stopping the daemon from the command line. Whether or not it's started or stopped, that command doesn't produce any output, nor does it drop anything into the log:

                [2.1.5-RELEASE][admin@pfsense.localdomain]/var/log(20): /usr/local/etc/rc.d/apcupsd.sh stop
                Stopping APC UPS Daemon...
                [2.1.5-RELEASE][admin@pfsense.localdomain]/var/log(21): /usr/local/etc/rc.d/apcupsd.sh
                [2.1.5-RELEASE][admin@pfsense.localdomain]/var/log(22): /usr/local/etc/rc.d/apcupsd.sh start
                Starting APC UPS Daemon...
                [2.1.5-RELEASE][admin@pfsense.localdomain]/var/log(23): /usr/local/etc/rc.d/apcupsd.sh
                Broadcast Message from admin@pfsense.localdomain
                        (no tty) at 21:00 UTC...
                
                Communications with UPS lost. 
                [2.1.5-RELEASE][admin@pfsense.localdomain]/var/log(24): cat /var/log/apcupsd.events
                ...
                2014-12-09 20:59:43 +0000  apcupsd exiting, signal 15
                2014-12-09 20:59:43 +0000  apcupsd shutdown succeeded
                2014-12-09 21:00:09 +0000  apcupsd 3.14.10 (13 September 2011) freebsd startup succeeded
                2014-12-09 21:00:14 +0000  Communications with UPS lost.
                
                
                1 Reply Last reply Reply Quote 0
                • M
                  mir
                  last edited by

                  Any contents in this file?
                  /var/log/apcupsd.events

                  1 Reply Last reply Reply Quote 0
                  • D
                    dbaio
                    last edited by

                    I think this is a problem similar with pcnet.

                    If you use pcnet on the Upstype field, the parameters need to be on same field, not in DEVICE.

                    Try to do the same.

                    –
                    Danilo G. Baio (dbaio)

                    1 Reply Last reply Reply Quote 0
                    • P
                      PARC
                      last edited by

                      Thanks dbaio… this hadn't occurred to me. All my other apcupsd instances have the conf files configured by hand with net as the UPSTYPE and _<my.netop.ip.here>: <myport>_as the DEVICE.

                      After making this change, the relevant section in the conf file now looks like so:

                      
                      ...
                      #
                      UPSTYPE net <my.netop.ip.here>: <myport>#DEVICE
                      ...</myport></my.netop.ip.here> 
                      

                      Sadly, after restart, the service still isn't able to consume the UPS data over the network.</myport></my.netop.ip.here>

                      1 Reply Last reply Reply Quote 0
                      • D
                        dbaio
                        last edited by

                        Hi.

                        I've tried here and "net" doesn't have the simular bug like "pcnet", thanks for trying.

                        Change your UPS Class and UPS Mode to Share Master and Share and try it again, please.

                        Regards.

                        –
                        Danilo G. Baio (dbaio)

                        1 Reply Last reply Reply Quote 0
                        • D
                          dbaio
                          last edited by

                          Maybe apcaccess uses all settings (standalone | shareslave | sharemaster)

                          $ apcaccess status <my.netops.ip.here>: <port>[snip]
                          UPSMODE  : ShareUPS Master 
                          SHARE    : ShareUPS
                          STATUS   : ONLINE 
                          [snip]</port></my.netops.ip.here>
                          

                          –
                          Danilo G. Baio (dbaio)

                          1 Reply Last reply Reply Quote 0
                          • P
                            PARC
                            last edited by

                            Hi Danilo,

                            Thanks for the suggestion. I gave this a try as well, but sadly those changes didn't work either.

                            If I can find a similar version of apcupsd I'm going to try installing it on a linux machine behind pfSense to see if this is an issue with this specific version of apcupsd and the net connectivity I'm using.

                            Cheers,
                            Greg

                            1 Reply Last reply Reply Quote 0
                            • D
                              dbaio
                              last edited by

                              @PARC:

                              Hi Danilo,

                              Thanks for the suggestion. I gave this a try as well, but sadly those changes didn't work either.

                              If I can find a similar version of apcupsd I'm going to try installing it on a linux machine behind pfSense to see if this is an issue with this specific version of apcupsd and the net connectivity I'm using.

                              Cheers,
                              Greg

                              Thank you for your time.

                              I submitted a PR and I asked for build the new binaries (3.14.12).

                              Best Regards.

                              –
                              Danilo G. Baio (dbaio)

                              1 Reply Last reply Reply Quote 0
                              • M
                                mk96
                                last edited by

                                Actually same here, after a couple of seconds after system start a broadcast appears:
                                "Communications with UPS lost"
                                My config uses PCNET driver,

                                apcupsd.events:

                                2015-01-08 22:24:48 +0100  apcupsd FATAL ERROR in newups.c at line 103
                                Mutex lock failure. ERR=Resource deadlock avoided
                                2015-01-08 22:24:48 +0100  apcupsd FATAL ERROR in newups.c at line 103
                                Mutex lock failure. ERR=Resource deadlock avoided
                                2015-01-08 22:24:48 +0100  apcupsd FATAL ERROR in newups.c at line 103
                                Mutex lock failure. ERR=Resource deadlock avoided
                                2015-01-08 22:25:28 +0100  apcupsd 3.14.10 (13 September 2011) freebsd startup succeeded
                                2015-01-08 22:26:28 +0100  Communications with UPS lost.
                                2015-01-08 22:32:11 +0100  apcupsd exiting, signal 15
                                2015-01-08 22:32:11 +0100  apcupsd shutdown succeeded
                                2015-01-08 22:32:25 +0100  apcupsd 3.14.10 (13 September 2011) freebsd startup succeeded
                                2015-01-08 22:32:25 +0100  apcupsd exiting, signal 15
                                2015-01-08 22:32:30 +0100  apcupsd 3.14.10 (13 September 2011) freebsd startup succeeded
                                2015-01-08 22:33:30 +0100  Communications with UPS lost.
                                2015-01-08 22:35:33 +0100  apcupsd exiting, signal 15
                                2015-01-08 22:35:38 +0100  apcupsd 3.14.10 (13 September 2011) freebsd startup succeeded
                                2015-01-08 22:35:38 +0100  apcupsd exiting, signal 15
                                2015-01-08 22:35:43 +0100  apcupsd 3.14.10 (13 September 2011) freebsd startup succeeded
                                2015-01-08 22:36:43 +0100  Communications with UPS lost.
                                
                                

                                On the other installation works fine using serial cable, but this one with this strange issue uses an APC MNC2 card AP9631

                                1 Reply Last reply Reply Quote 0
                                • M
                                  mk96
                                  last edited by

                                  Seems it is solved by adding the IP of the PFsense box to the powerchute clients in the web interface of the AP9631 NMC card

                                  1 Reply Last reply Reply Quote 0
                                  • S
                                    sensemann
                                    last edited by

                                    hello,

                                    I ve the same problem.

                                    even with the correct config / IP , in the webinterface and  /usr/pbi/apcupsd-amd64/etc/apcupsd/apcupsd.conf  it doenst work, I only get this error:

                                    /usr/local/sbin: apcaccess

                                    Error contacting apcupsd @ localhost:3551: Operation timed out

                                    But this is working:

                                    apcaccess -h 192.168.2.1:3551

                                    using apcupsd-3.14.12_1  with pfSense 2.2-R.

                                    Any ideas?

                                    1 Reply Last reply Reply Quote 0
                                    • D
                                      dbaio
                                      last edited by

                                      The command apcaccess tries to connect through many ways(SNMP, PCNET with auth, PCNET without auth and others), seeing the log you can know how it did.

                                      You need to check your config on the UPS (pcnet) - PowerChute Network Shutdown.

                                      Some tips from apcupsd.com:

                                      UPSCABLE ether
                                      UPSTYPE pcnet
                                      DEVICE ipaddr:user:passphrase
                                      UPSCLASS standalone
                                      UPSMODE disable
                                      

                                      The DEVICE setting specifies the IP address of the UPS as well as the username and authentication passphrase to use. Note th
                                      at the username and passphrase are not the Web/SNMP login credentials. They are separate settings. The default username on a new card is "apc" and the default passphrase is "admin user phrase". To change the passphrase, log in to the Web UI and go to the UPS tab, then to PowerChute -> Configuration. (This assumes firmware v3.3.1. Other versions may place the setting elsewhere.) The password must be a minimum of 15 characters long. The web UI will silently ignore shorter passwords and does not give an error message. There is no apparent way to change the username.

                                      Note that you may leave DEVICE blank and Apcupsd will accept information from any PCNET UPS on the network, however it will be very insecure since an attacker could easily send packets crafted to cause your server to shut down. Using the ipaddr, user, and passphrase will prevent this behavior.

                                      http://www.apcupsd.com/manual/manual.html#powerchute-network-shutdown-driver-pcnet

                                      Also, you can add the IP of pfSense box to the powerchute clients in the web interface like @mk96 saied.

                                      Regards

                                      –
                                      Danilo G. Baio (dbaio)

                                      1 Reply Last reply Reply Quote 0
                                      • S
                                        sensemann
                                        last edited by

                                        hi, I tryd to change "net" to "pcnet" - but it doesnt help. I guess there`s a bug between pfSende web-GUI and apcaccess…

                                        1 Reply Last reply Reply Quote 0
                                        • D
                                          dbaio
                                          last edited by

                                          @sensemann:

                                          hi, I tryd to change "net" to "pcnet" - but it doesnt help. I guess there`s a bug between pfSende web-GUI and apcaccess…

                                          You were right, it was improved.

                                          https://forum.pfsense.org/index.php?topic=89901.0

                                          –
                                          Danilo G. Baio (dbaio)

                                          1 Reply Last reply Reply Quote 0
                                          • P
                                            PARC
                                            last edited by

                                            Hello all,

                                            Just wanted to mention that I noticed a new version of the apcupsd package was available; I uninstalled the previous package and installed the new one. That resolved this issue.

                                            Hooray!

                                            Cheers,
                                            Greg

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post
                                            Copyright 2025 Rubicon Communications LLC (Netgate). All rights reserved.