    • dennypageD
      dennypage
      last edited by

      Several questions:

      What messages are in the system log? Look for messages from upsd, upsmon, upsdrvctl, blazer*.
      What are the contents of /usr/local/etc/nut/ups.conf and upsd.conf?
      What nut processes are running? (ps -axuwww | grep ups)
      Does anything change if you restart the nut service via the nut status page or the services page?
      Have you successfully tested this specific ups model with nut previously?

      @johnabbot:

      I'm running a generic asian ups with the following

      (Various USB)
      UPSilon 2000 software blazer_usb langid_fix=0x409

      It installed perfectly, looks great, unfortunately it gives me

      "Failed to retrieve status"

      1 Reply Last reply Reply Quote 0
      • S
        Starrbuck
        last edited by

        USB type:  Local USB
        Driver:  usbhid

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          Hey Starrbuck, I sent you an update that should address your ram disk issue. Please let me know that it works for you. Thanks.

          1 Reply Last reply Reply Quote 0
          • S
            Starrbuck
            last edited by

            Got it, thanks!

            1 Reply Last reply Reply Quote 0
            • S
              Starrbuck
              last edited by

              @dennypage:

              Hey Starrbuck, I sent you an update that should address your ram disk issue. Please let me know that it works for you. Thanks.

              The ramdisk issue is corrected.  Upon rebooting the package started up normally and the status looks fine.

              1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage
                last edited by

                Good to hear. Thanks again for testing.

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  w0w, I may have an approach that will address the SNMP unreachable on startup issue issue. Give me a couple of days, and I'll let you know. In the mean time, please test the existing beta2 version. Thanks.

                  1 Reply Last reply Reply Quote 0
                  • w0wW
                    w0w
                    last edited by

                    UPS Status — OFF, but displayed battery charge and load are OK.
                    Fixed with an extra argument for driver.
                    mibs=ietf
                    Looks much better now :)
                    Good job!

                    P.S. Don't look at I/O Voltage at first picture, it's Powercom firmware bug that could not be fixed anyway.

                    nut1.jpg
                    nut1.jpg_thumb
                    nut2.jpg
                    nut2.jpg_thumb

                    1 Reply Last reply Reply Quote 0
                    • w0wW
                      w0w
                      last edited by

                      Can I request some features for package? (lowest priority in your list) :)
                      1. I want shutdown pfsense before battery get LOW condition, for example after running 5 minutes on battery, I have seen some implementations using internal nut scripting, but not for pfsense. Feature is very similar to what APCUPSD already have for years.
                      2. It would be good to kill UPS power, sending command to shutdown UPS, like APCUPSD doing it.

                      BTW I am using APCUPSD on windows for the same UPS.

                      1 Reply Last reply Reply Quote 0
                      • J
                        johnabbot
                        last edited by

                        @dennypage:

                        Several questions:

                        What messages are in the system log? Look for messages from upsd, upsmon, upsdrvctl, blazer*.

                        upsmon 73821 Poll UPS [sunpac] failed - Driver not connected
                        upsd 71207 Can't connect to UPS [sunpac] (blazer_usb-sunpac): No such file or directory

                        What are the contents of /usr/local/etc/nut/ups.conf and upsd.conf?

                        sunpac]
                        driver=blazer_usb
                        port=auto
                        langid_fix=0x4095
                        subdriver=krauler
                        productid=1234
                        vendorid=0925

                        LISTEN 127.0.0.1
                        LISTEN ::1

                        What nut processes are running? (ps -axuwww | grep ups)

                        ps -axuwww | grep ups
                        root    71207  0.0  0.0  20712    2368  -  Ss    6:10PM    0:00.24 /usr/local/sbin/upsd -u root
                        root    72651  0.0  0.0  16612    2308  -  Is    6:10PM    0:00.00 /usr/local/sbin/upsmon
                        uucp    73821  0.0  0.0  16612    2340  -  S    6:10PM    0:00.20 /usr/local/sbin/upsmon
                        root    58229  0.0  0.0  18740    2240  0  S+    9:44PM    0:00.00 grep ups

                        Does anything change if you restart the nut service via the nut status page or the services page?

                        No

                        Have you successfully tested this specific ups model with nut previously?

                        No

                        @johnabbot:

                        I'm running a generic asian ups with the following

                        (Various USB)
                        UPSilon 2000 software blazer_usb langid_fix=0x409

                        It installed perfectly, looks great, unfortunately it gives me

                        "Failed to retrieve status"

                        1 Reply Last reply Reply Quote 0
                        • w0wW
                          w0w
                          last edited by

                          I have "tecnoware" UPS, some ERA series but not the same as listed in NUT supported devices. It have similar behavior to yours,  johnabbot
                          Playing with driver options not helped, strange… but UPSilon 2000 works under windows environment at least.

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage
                            last edited by

                            John, it looks like the usb information for the ups doesn't match. I would recommend dumping the usb information on the device and heading over to the NUT forums with it. You can dump the usb information with the following command on the console:

                            usbconfig dump_device_desc

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              I've sent out beta 3. You do not need to remove the beta 1/2 package before installing the beta 3 package. Note that it is normal that the nut service is stopped during the install–you will need to restart the service after the install completes.

                              Again, thank you for all your help!

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage
                                last edited by

                                w0w, with the beta 3 release you should be able to address the SNMP unreachable on startup issue issue. Add the following lines to ups.conf in the advanced section:

                                maxretry=60
                                  retrydelay=60

                                This will result in a retry every minute for an hour. Be careful how you use this.

                                See the ups.conf man page for more information.

                                1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage
                                  last edited by

                                  I believe NUT already handles this. Have a look at the man page for the apcsmart driver. Pretty rich configuration options for power handling in there.

                                  @w0w:

                                  It would be good to kill UPS power, sending command to shutdown UPS, like APCUPSD doing it.

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    Hey John, just wondering if you had a chance to dump the usb config to check the vendor and product id?

                                    @johnabbot:

                                    driver=blazer_usb
                                    port=auto
                                    langid_fix=0x4095
                                    subdriver=krauler
                                    productid=1234
                                    vendorid=0925

                                    1 Reply Last reply Reply Quote 0
                                    • w0wW
                                      w0w
                                      last edited by

                                      dennypage
                                      Thanks, looks like b3 works. UPS reconnects if no connection at startup or if it lost.

                                      @dennypage:

                                      I believe NUT already handles this. Have a look at the man page for the apcsmart driver. Pretty rich configuration options for power handling in there.

                                      @w0w:

                                      It would be good to kill UPS power, sending command to shutdown UPS, like APCUPSD doing it.

                                      I don't use apcsmart driver, I use SNMP. I think I'll try

                                      something like " /usr/local/ups/sbin/upsdrvctl shutdown" later to check if this works.

                                      Thanks again about tip for ups.conf, shame on me. :)

                                      1 Reply Last reply Reply Quote 0
                                      • T
                                        timotl
                                        last edited by

                                        w0w

                                        If that works to kill the UPS, you can add this to rc.shutdown and it will send the command if NUT shuts down the system
                                        I use the system patches package to keep it there across updates.

                                        
                                        if (test -f /etc/killpower)
                                            then
                                                echo "Shutting down UPS power..."
                                                /usr/local/sbin/upsdrvctl shutdown
                                            fi
                                        
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          Glad it works. No shame btw, it wasn't possible to do in beta 2. Both config and script changes were needed to support it.

                                          @w0w:

                                          Thanks, looks like b3 works. UPS reconnects if no connection at startup or if it lost.

                                          Thanks again about tip for ups.conf, shame on me. :)

                                          1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            Pull request created: https://github.com/pfsense/FreeBSD-ports/pull/155

                                            1 Reply Last reply Reply Quote 0