    • M
      McFuzz
      last edited by

      @dennypage:

      You did a save of the NUT settings after ticking the checkbox, yes?

      Please post the contents of /usr/local/etc/nut/upsmon.conf.

      Yup - I did.

      Here are the contents of upsmon.conf - I did not modify it yet; want to first get the defaults working:

      
      MONITOR BX1300G 1 monuser a620bdded832fb08439a master
      SHUTDOWNCMD "/sbin/shutdown -p +0"
      POWERDOWNFLAG /etc/killpower
      NOTIFYCMD /usr/local/pkg/nut/nut_email.php
      NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
      NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
      NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
      NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
      NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
      NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
      NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
      NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
      NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
      NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
      
      

      Naturally, I browsed through nut_email.php and noticed that it is referencing to a file called notices.inc:

      
      require_once("notices.inc");
      
      

      However - can't find that file anywhere…

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage
        last edited by

        @McFuzz:

        Naturally, I browsed through nut_email.php and noticed that it is referencing to a file called notices.inc:

        
        require_once("notices.inc");
        
        

        However - can't find that file anywhere…

        You should find this as /etc/inc/notices.inc.

        The contents of upsmon.conf look fine. Please run the following:

        echo "hello" | /usr/local/pkg/nut/nut_email.php
        

        What happens?

        1 Reply Last reply Reply Quote 0
        • M
          McFuzz
          last edited by

          @dennypage:

          @McFuzz:

          Naturally, I browsed through nut_email.php and noticed that it is referencing to a file called notices.inc:

          
          require_once("notices.inc");
          
          

          However - can't find that file anywhere…

          You should find this as /etc/inc/notices.inc.

          The contents of upsmon.conf look fine. Please run the following:

          echo "hello" | /usr/local/pkg/nut/nut_email.php
          

          What happens?

          Yup - notices.inc is in /etc/inc

          Attempted to execute the command - all I got was an email that simply had a timestamp; nothing else… was I supposed to see "hello" in the body?

          1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage
            last edited by

            Sorry, my bad. It should have been:

            /usr/local/pkg/nut/nut_email.php hello
            

            And yes, the content of the email should be like this:

            Fri, 07 Oct 2016 00:09:55 -0700
            hello
            

            If you receive this, it means that your email notifications are working.

            1 Reply Last reply Reply Quote 0
            • M
              McFuzz
              last edited by

              @dennypage:

              Sorry, my bad. It should have been:

              /usr/local/pkg/nut/nut_email.php hello
              

              And yes, the content of the email should be like this:

              Fri, 07 Oct 2016 00:09:55 -0700
              hello
              

              If you receive this, it means that your email notifications are working.

              Yup - that worked; got an email with "hello" in it.

              So what's wrong with the automatic notifications? :(

              I just tried it again (saved the settings, for a good measure) - yanked the power off the UPS so it goes on battery power… got the notification within the shell session, but no email :(

              1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage
                last edited by

                Assuming that your email notifications are working…

                When you pulled the cord, how long did you wait? If you were logged into pfSense, did you see a wall announcement?

                When you go to Services / UPS / Status with the cord pulled, what do you see?

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  Are you affected by this bug?

                  https://forum.pfsense.org/index.php?topic=115349.msg646251#msg646251
                  https://forum.pfsense.org/index.php?topic=115349.msg646466#msg646466

                  1 Reply Last reply Reply Quote 0
                  • M
                    McFuzz
                    last edited by

                    @dennypage:

                    Assuming that your email notifications are working…

                    When you pulled the cord, how long did you wait? If you were logged into pfSense, did you see a wall announcement?

                    When you go to Services / UPS / Status with the cord pulled, what do you see?

                    I just gave it another shot:

                    • Disconnected power
                    • pfsense shell session indicated the UPS being on battery
                    • UI dashboard as well as Services -> UPS both indicated the UPS needed attention (and showed it discharging)
                    • Waited a minute and plugged back in
                    • Shell session indicated the UPS was back on line power practically right away
                    • UI dashboard reflected power restoration and shows the UPS as charging.
                    1 Reply Last reply Reply Quote 0
                    • M
                      McFuzz
                      last edited by

                      @dennypage:

                      Are you affected by this bug?

                      https://forum.pfsense.org/index.php?topic=115349.msg646251#msg646251
                      https://forum.pfsense.org/index.php?topic=115349.msg646466#msg646466

                      Hooray! That worked!!!!!

                      Thank you :)

                      So yeah - I guess I am affected :x

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage
                        last edited by

                        You're welcome. I'm glad it worked for you.

                        1 Reply Last reply Reply Quote 0
                        • E
                          endy66
                          last edited by

                          Since yesterday, i have also an brand new UPS, one from CyberPower. I installed the nut package and everything is working as expected. Thanks to this thread, i could set the override.battery.charge.low to shutdown my pfsense earlier.
                          But now i have one question, i don't know, if this is the rigt Forum to ask this: I want to shutdown a Linux/Debian Server, which should get the data from the pfsense. So i have added in the upsd.users inside the box of the nut Settings the following:

                          
                          [client]
                          password = mypass
                          upsmon slave
                          
                          

                          And in the upsd.conf box

                          
                          LISTEN 192.168.1.1
                          
                          

                          On the Server i installed the nut-Client package (apt-get install nut-Client). With this command

                          
                          upsc CyberPower_USV@192.168.1.1
                          
                          

                          i can get all the data from the pfsense (UPS)

                          But how can i make, that the Server also shuts down, when the pfsense box is shutting down?

                          EDIT// Everything is working now, i had to set the MODE=netclient on the Server.

                          But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

                          
                          ignorelb
                          override.battery.charge.low = 50
                          override.battery.runtime.low = 1200
                          
                          

                          BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

                          Best Regards

                          1 Reply Last reply Reply Quote 0
                          • A
                            alanper
                            last edited by

                            Firstly, thanks for a great and extremely useful package.
                            I'm having a problem with the NUT package on my pfSense deployment.  When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.  Any ideas?

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              @endy66:

                              But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

                              
                              ignorelb
                              override.battery.charge.low = 50
                              override.battery.runtime.low = 1200
                              
                              

                              BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

                              The section entitled "Additional configuration lines for ups.conf" in Advanced settings is for global directives. The values you are trying to set are UPS specific arguments. UPS specific arguments should be entered in the section above that says "Extra Arguments to driver"

                              Sorry this isn't clear. I'll have a look at clarifying.

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage
                                last edited by

                                @alanper:

                                When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                                Can you clarify some things please?

                                What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                                When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                                If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                                Thanks

                                1 Reply Last reply Reply Quote 0
                                • E
                                  endy66
                                  last edited by

                                  @dennypage:

                                  @alanper:

                                  When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                                  Can you clarify some things please?

                                  What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                                  When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                                  If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                                  Thanks

                                  Thank you very much for the help, it works perfectly! :)

                                  One last question i  have:

                                  When my UPS reaches the Limit which i set, my Server (slave) and my pfsense box are shutting down. But when do they (especally the pfsense box), boot again? Does the UPS Needs to dischagre completely to cut the power from the devices and then after power restore they get the power and boot again (with bios Setting ac restore)?

                                  Best Regards

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    Did you mean to quote a different posting?

                                    @endy66:

                                    @dennypage:

                                    @alanper:

                                    When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                                    Can you clarify some things please?

                                    What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                                    When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                                    If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                                    Thanks

                                    Thank you very much for the help, it works perfectly! :)

                                    One last question i  have:

                                    When my UPS reaches the Limit which i set, my Server (slave) and my pfsense box are shutting down. But when do they (especally the pfsense box), boot again? Does the UPS Needs to dischagre completely to cut the power from the devices and then after power restore they get the power and boot again (with bios Setting ac restore)?

                                    Best Regards

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      @endy66:

                                      When my UPS reaches the Limit which i set, my Server (slave) and my pfsense box are shutting down. But when do they (especally the pfsense box), boot again? Does the UPS Needs to dischagre completely to cut the power from the devices and then after power restore they get the power and boot again (with bios Setting ac restore)?

                                      A simplified description of what happens with NUT when shutdown time arrives: The master sends a message to all slaves saying "initiate shutdown"; the master sends a command to the UPS saying "wait X seconds, then turn load power off"; the master initiates a local shutdown; the UPS turns off load power. When the mains return, the UPS restores load power, and the attached systems boot.

                                      If possible, network systems attached to a UPS should be configured to always boot when power is applied. Otherwise, you can run into problems with shutdown vs power off.

                                      1 Reply Last reply Reply Quote 0
                                      • E
                                        endy66
                                        last edited by

                                        Oops, yes sorry i quoted the wrong post. Thank you for the clarification. As i set the override.battery.charge.low to 50%, does my pfsense then power off the UPS? And can i set this "delay-value"? or can i see this somewhere? Because i waited about 10mins after my pfsense and my Server are shutdown, but the UPS did not power off.

                                        Best Regards

                                        1 Reply Last reply Reply Quote 0
                                        • O
                                          openletter
                                          last edited by

                                          The latest update for NUT has a link to view the changelog:

                                          https://github.com/pfsense/FreeBSD-ports/commits/devel/sysutils/pfSense-pkg-nut

                                          I have been getting the "This page is taking way too long to load." page from GitHub for the past few days.

                                          How about updating the first post of this thread with each new changelog?

                                          pfSense 2.4.3-RELEASE (amd64) installed to PC on Samsung 860 EVO mSATA 256 GB SSD with Supermicro X11SBA-LN4F, Intel Pentium N3700, 4 GB RAM, 4 mobo 10/100/1000, 1 PCIe 10/100/1000 x4 NIC (HP NC364T), and APC Smart-UPS SMT1500.

                                          1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            @endy66:

                                            As i set the override.battery.charge.low to 50%, does my pfsense then power off the UPS? And can i set this "delay-value"? or can i see this somewhere? Because i waited about 10mins after my pfsense and my Server are shutdown, but the UPS did not power off.

                                            You control this with the "offdelay" parameter to the driver. See the NUT usbhib-ups man page for information. Setting this controls the variable "ups.delay.shutdown". You can read about the various variable in the NUT Variables man page.

                                            1 Reply Last reply Reply Quote 0