    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.5m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage
      last edited by

      Assuming that your email notifications are working…

      When you pulled the cord, how long did you wait? If you were logged into pfSense, did you see a wall announcement?

      When you go to Services / UPS / Status with the cord pulled, what do you see?

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage
        last edited by

        Are you affected by this bug?

        https://forum.pfsense.org/index.php?topic=115349.msg646251#msg646251
        https://forum.pfsense.org/index.php?topic=115349.msg646466#msg646466

        1 Reply Last reply Reply Quote 0
        • M
          McFuzz
          last edited by

          @dennypage:

          Assuming that your email notifications are working…

          When you pulled the cord, how long did you wait? If you were logged into pfSense, did you see a wall announcement?

          When you go to Services / UPS / Status with the cord pulled, what do you see?

          I just gave it another shot:

          • Disconnected power
          • pfsense shell session indicated the UPS being on battery
          • UI dashboard as well as Services -> UPS both indicated the UPS needed attention (and showed it discharging)
          • Waited a minute and plugged back in
          • Shell session indicated the UPS was back on line power practically right away
          • UI dashboard reflected power restoration and shows the UPS as charging.
          1 Reply Last reply Reply Quote 0
          • M
            McFuzz
            last edited by

            @dennypage:

            Are you affected by this bug?

            https://forum.pfsense.org/index.php?topic=115349.msg646251#msg646251
            https://forum.pfsense.org/index.php?topic=115349.msg646466#msg646466

            Hooray! That worked!!!!!

            Thank you :)

            So yeah - I guess I am affected :x

            1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage
              last edited by

              You're welcome. I'm glad it worked for you.

              1 Reply Last reply Reply Quote 0
              • E
                endy66
                last edited by

                Since yesterday, i have also an brand new UPS, one from CyberPower. I installed the nut package and everything is working as expected. Thanks to this thread, i could set the override.battery.charge.low to shutdown my pfsense earlier.
                But now i have one question, i don't know, if this is the rigt Forum to ask this: I want to shutdown a Linux/Debian Server, which should get the data from the pfsense. So i have added in the upsd.users inside the box of the nut Settings the following:

                
                [client]
                password = mypass
                upsmon slave
                
                

                And in the upsd.conf box

                
                LISTEN 192.168.1.1
                
                

                On the Server i installed the nut-Client package (apt-get install nut-Client). With this command

                
                upsc CyberPower_USV@192.168.1.1
                
                

                i can get all the data from the pfsense (UPS)

                But how can i make, that the Server also shuts down, when the pfsense box is shutting down?

                EDIT// Everything is working now, i had to set the MODE=netclient on the Server.

                But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

                
                ignorelb
                override.battery.charge.low = 50
                override.battery.runtime.low = 1200
                
                

                BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

                Best Regards

                1 Reply Last reply Reply Quote 0
                • A
                  alanper
                  last edited by

                  Firstly, thanks for a great and extremely useful package.
                  I'm having a problem with the NUT package on my pfSense deployment.  When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.  Any ideas?

                  1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage
                    last edited by

                    @endy66:

                    But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

                    
                    ignorelb
                    override.battery.charge.low = 50
                    override.battery.runtime.low = 1200
                    
                    

                    BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

                    The section entitled "Additional configuration lines for ups.conf" in Advanced settings is for global directives. The values you are trying to set are UPS specific arguments. UPS specific arguments should be entered in the section above that says "Extra Arguments to driver"

                    Sorry this isn't clear. I'll have a look at clarifying.

                    1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage
                      last edited by

                      @alanper:

                      When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                      Can you clarify some things please?

                      What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                      When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                      If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                      Thanks

                      1 Reply Last reply Reply Quote 0
                      • E
                        endy66
                        last edited by

                        @dennypage:

                        @alanper:

                        When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                        Can you clarify some things please?

                        What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                        When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                        If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                        Thanks

                        Thank you very much for the help, it works perfectly! :)

                        One last question i  have:

                        When my UPS reaches the Limit which i set, my Server (slave) and my pfsense box are shutting down. But when do they (especally the pfsense box), boot again? Does the UPS Needs to dischagre completely to cut the power from the devices and then after power restore they get the power and boot again (with bios Setting ac restore)?

                        Best Regards

                        1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage
                          last edited by

                          Did you mean to quote a different posting?

                          @endy66:

                          @dennypage:

                          @alanper:

                          When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                          Can you clarify some things please?

                          What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                          When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                          If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                          Thanks

                          Thank you very much for the help, it works perfectly! :)

                          One last question i  have:

                          When my UPS reaches the Limit which i set, my Server (slave) and my pfsense box are shutting down. But when do they (especally the pfsense box), boot again? Does the UPS Needs to dischagre completely to cut the power from the devices and then after power restore they get the power and boot again (with bios Setting ac restore)?

                          Best Regards

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage
                            last edited by

                            @endy66:

                            When my UPS reaches the Limit which i set, my Server (slave) and my pfsense box are shutting down. But when do they (especally the pfsense box), boot again? Does the UPS Needs to dischagre completely to cut the power from the devices and then after power restore they get the power and boot again (with bios Setting ac restore)?

                            A simplified description of what happens with NUT when shutdown time arrives: The master sends a message to all slaves saying "initiate shutdown"; the master sends a command to the UPS saying "wait X seconds, then turn load power off"; the master initiates a local shutdown; the UPS turns off load power. When the mains return, the UPS restores load power, and the attached systems boot.

                            If possible, network systems attached to a UPS should be configured to always boot when power is applied. Otherwise, you can run into problems with shutdown vs power off.

                            1 Reply Last reply Reply Quote 0
                            • E
                              endy66
                              last edited by

                              Oops, yes sorry i quoted the wrong post. Thank you for the clarification. As i set the override.battery.charge.low to 50%, does my pfsense then power off the UPS? And can i set this "delay-value"? or can i see this somewhere? Because i waited about 10mins after my pfsense and my Server are shutdown, but the UPS did not power off.

                              Best Regards

                              1 Reply Last reply Reply Quote 0
                              • O
                                openletter
                                last edited by

                                The latest update for NUT has a link to view the changelog:

                                https://github.com/pfsense/FreeBSD-ports/commits/devel/sysutils/pfSense-pkg-nut

                                I have been getting the "This page is taking way too long to load." page from GitHub for the past few days.

                                How about updating the first post of this thread with each new changelog?

                                pfSense 2.4.3-RELEASE (amd64) installed to PC on Samsung 860 EVO mSATA 256 GB SSD with Supermicro X11SBA-LN4F, Intel Pentium N3700, 4 GB RAM, 4 mobo 10/100/1000, 1 PCIe 10/100/1000 x4 NIC (HP NC364T), and APC Smart-UPS SMT1500.

                                1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage
                                  last edited by

                                  @endy66:

                                  As i set the override.battery.charge.low to 50%, does my pfsense then power off the UPS? And can i set this "delay-value"? or can i see this somewhere? Because i waited about 10mins after my pfsense and my Server are shutdown, but the UPS did not power off.

                                  You control this with the "offdelay" parameter to the driver. See the NUT usbhib-ups man page for information. Setting this controls the variable "ups.delay.shutdown". You can read about the various variable in the NUT Variables man page.

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    @dennypage:

                                    @alanper:

                                    When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                                    Can you clarify some things please?

                                    What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                                    When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                                    If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                                    Thanks

                                    Alanper, did you get your issue resolved?

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      @openletter:

                                      The latest update for NUT has a link to view the changelog:

                                      https://github.com/pfsense/FreeBSD-ports/commits/devel/sysutils/pfSense-pkg-nut

                                      I have been getting the "This page is taking way too long to load." page from GitHub for the past few days.

                                      How about updating the first post of this thread with each new changelog?

                                      It will be updated if there is something meaningful in a new version. The update released last week was solely to remove the orphan "NUT" menu item that would occur if the old package was not removed before install as discussed earlier in this thread. You can view the diff directly here.

                                      1 Reply Last reply Reply Quote 0
                                      • A
                                        alanper
                                        last edited by

                                        @dennypage:

                                        @dennypage:

                                        @alanper:

                                        When I click on Services->UPS I get an alert "Status Alert: The UPS requires attention".  The NUT service is setup as a Remote NUT Server.  The service is connecting fine to the UPS as I can see values and graphs being populated (correctly).  The service is working as expected as well, as when I drop power to the UPS, NUT detects it and does what it is setup to do.  Yet I still get the "Status Alert: The UPS requires attention" every time I go to Services->UPS.

                                        Can you clarify some things please?

                                        What do you mean by "The NUT service is setup as a Remote NUT Server"? Is the UPS attached to the pfSense host or to another host?

                                        When you say "I can see values and graphs", are you seeing this on the Services / UPS / Status page?

                                        If present, can you post the content of the UPS Detail section of Services / UPS / Status?

                                        Thanks

                                        Alanper, did you get your issue resolved?

                                        Sorry for the delayed response.  Trying to catch up on everything…
                                        I have attached screenshots of my UPS status and settings page.  Yep, seeing the values on the UPS Status page.  The UPS is not attached to the pfSense host, it is attached to another host on the local network.

                                        Capture2.PNG
                                        Capture2.PNG_thumb
                                        Capture1.PNG
                                        Capture1.PNG_thumb

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          @alanper:

                                          I have attached screenshots of my UPS status and settings page.  Yep, seeing the values on the UPS Status page.

                                          The warning that the UPS requires attention appears to be correct. Note that the status is "On line, Bypass"? Bypass is bad. Bypass means that the UPS inverter has been bypassed and will not take over if the mains fail. If you scroll down to the bottom of the UPS Detail section, you should see a field titled "ups.alarm" which will hopefully give you a better indication of why bypass is active.

                                          I'm surprised that there wouldn't be an alarm going off on the thing.

                                          1 Reply Last reply Reply Quote 0
                                          • A
                                            alanper
                                            last edited by

                                            @dennypage:

                                            @alanper:

                                            I have attached screenshots of my UPS status and settings page.  Yep, seeing the values on the UPS Status page.

                                            The warning that the UPS requires attention appears to be correct. Note that the status is "On line, Bypass"? Bypass is bad. Bypass means that the UPS inverter has been bypassed and will not take over if the mains fail. If you scroll down to the bottom of the UPS Detail section, you should see a field titled "ups.alarm" which will hopefully give you a better indication of why bypass is active.

                                            I'm surprised that there wouldn't be an alarm going off on the thing.

                                            For all intents and purposes, the UPS is functioning correctly (aside from the bypass status reading).  I am using a generic UPS driver for NUT (it was a trial and error process at the time to find a driver that worked as there was none from the UPS manufacturer), perhaps that is the cause for the "incorrect" bypass reading (I say incorrect because if I disconnect the mains the UPS functions correctly).  Anyway, it's not a major problem for me as it is just aesthetics for now.

                                            1 Reply Last reply Reply Quote 0