    • dennypageD
      dennypage
      last edited by

      NUT itself doesn't invoke self-tests on a schedule. This is done by the UPS itself.

      There are usually configuration parameters that can be viewed and modified in the UPS. The complete list of NUT variables can be found here. Note that a given UPS model will generally only offer a small subset of these variables. Use the upsrw command to discover the list of variables you can modify. For your particular issue, the variable you are looking to modify is ups.test.interval.

      Further information on running commands can be found here. Be careful.

      1 Reply Last reply Reply Quote 0
      • C
        cozkramer
        last edited by

        Thanks Denny!

        After using upsrw, and only getting three outlet switch options, a delay shutdown and ups.id as modifiable, I fear a call to TrippLite is in order..

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          Your UPS is a network model, yes? If so, is there anything that is connecting to the UPS that could be initiating the self test?

          1 Reply Last reply Reply Quote 0
          • C
            cozkramer
            last edited by

            No, it's the non-network model..  I've got two usb cables plugged into it..  One to a (stupid) Windows 7 machine I need for Photography work, and the other goes to the BSD rig..  I've slightly cheated a little here, the cable is plugged into a freenas machine and I have pfsense nut talking to nut on the nas.  It's all bsd nuts though and so apparently they can't do anything but report it seems and I know the people here are nicer.  =)

            Here's a link to the unit I have https://www.tripplite.com/smartpro-120v-2.2kva-1.6kw-line-interactive-ups-tower-snmpwebcard-option-usb-db9-serial~SMART2200VS/

            If you know of a way to replace Lightroom on a *Nix/BSD System, I'm all ears!

            Thanks Danny!

            1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage
              last edited by

              Different story then. NUT doesn't initiate a self-test by default, and the pfSense NUT package doesn't initiate a self-test, but that doesn't mean that the FreeNAS NUT package isn't doing it or that Windows isn't doing it. Before calling Tripplite, I would disconnect all but one USB or RS-232 cable and test each system stand-alone to see if it still happens.

              I can't help you with Windows I'm afraid. I stopped running Windows around the XP timeframe.  For a nice and cuddly Unix UI environment, I use Mac. As I recall, Lightroom runs a bit better on Mac than Windows. Adobe used to let you turn your Windows license in and get a Mac license in exchange, but I don't know if they still do that.

              First time in my life someone has referred to me as one of the nicer people. :)

              -Denny

              1 Reply Last reply Reply Quote 0
              • C
                cozkramer
                last edited by

                It's always a different story when Microcrap is involved, isn't it….  I'd love to drop kick them to next century, but I refuse to give Apple any money.  I've never liked how the OS was setup and you're stuck with whatever they let you have.  but that's another topic, lol..

                I've removed any trace of ups software from wincrap, and I may disable the service on the nas rig for a day and see, seem easier than trying to reach cables.. :/

                I would have thought that the NUT service is the same on both PF and FreeNas and thus has the same functionality/or lack thereof.  Incorrect presumption?

                I've been a light user of *Nix/BSD since Slackware 4ish iirc and FreeBSD 3ish, I've just never been able to drop win as the software wasn't there for *nix/bsd.  Now the only holdup is LR, and running LR under a VM just doesn't get it done, tried that recently..

                These days, Adobe wants you to pay them monthly for their software, and if you refuse and buy the standalone, they remove features...  bastids..

                First time for everything!  :)  Anyone that can take what could be a stupid and/or silly question/issue and reply with helpful info in a concise manner gets my nice vote...  8)

                -Scott

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  @cozkramer:

                  I would have thought that the NUT service is the same on both PF and FreeNas and thus has the same functionality/or lack thereof.  Incorrect presumption?

                  The NUT distribution itself is the same, but the package that configures and runs it is quite different. If you look at your pfSense system, you will see two packages:

                  nut-2.7.4_1                    Network UPS Tools
                  pfSense-pkg-nut-2.7.4_4        Network UPS Tools
                  
                  

                  The first one is the NUT package itself and the second one the the pfSense package for NUT. The pfSense package is what controls the NUT configuration and starts the NUT service.

                  1 Reply Last reply Reply Quote 0
                  • C
                    cozkramer
                    last edited by

                    Thanks Denny for some clarification there.

                    Is it wrong of me to then presume that pfSense has a control package for every add-on service/package?

                    If that's the case, is it possible to run other freebsd packages separately?

                    Thanks again!  Hope I'm not too ot or anything.

                    1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage
                      last edited by

                      The list of supported packages for your pfSense version can be found in System / Package Manager / Available Packages. There are a good number of excellent FreeBSD packages directly supported in pfSense.

                      There are also many packages that are in FreeBSD that are not directly supported in pfSense. If you are interested in installing FreeBSD packages that are not directly supported by pfSense, you can search the forums for instructions on how to do this. In general, I would recommend against using unsupported packages unless 1) you have a very strong need for the package on your firewall, and 2) you are extremely confident of the security implications of having the package running on your firewall.

                      1 Reply Last reply Reply Quote 0
                      • C
                        cozkramer
                        last edited by

                        I indeed know and run many of the great packages in the package manager, a couple don't seem to like me too much, but that's another topic.

                        I've been very thrilled with how well all the Devs and supporters have made pfSense, it's been great so far the last couple months.  I was merely wondering and curious if the standard ports tree was supported considering pfSense having it's own controller packages.

                        I completely agree with both of your conditions of usage, if it ain't broke don't fix it, and if you don't know wth your doing, don't do it.  It's why we have Allow All on the WAN right?  ::) :P

                        Thanks again for all the time and help Denny!

                        1 Reply Last reply Reply Quote 0
                        • P
                          Per Hansson
                          last edited by

                          Is there any support for graphs like apcupsd has on IPCOP?
                          See attachments, really like how they make a daily, weekly, monthly & yearly graph for the stats that can be taken from the UPS:

                          temperature and battery voltage
                          min. / max. line voltage
                          remaining runtime
                          supplying voltage
                          load capacity
                          min. /max. battery charge
                          

                          Attached two example graphs.

                          Temperature.png
                          Temperature.png_thumb
                          ![Line Voltage.png](/public/imported_attachments/1/Line Voltage.png)
                          ![Line Voltage.png_thumb](/public/imported_attachments/1/Line Voltage.png_thumb)

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage
                            last edited by

                            Not at this time.

                            1 Reply Last reply Reply Quote 0
                            • P
                              Per Hansson
                              last edited by

                              Ok, would be awsome if it could be added!
                              Still run an old IPCOP box just for that reason, would be nice to switch it to pfSense :)

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage
                                last edited by

                                @Per:

                                Ok, would be awsome if it could be added!
                                Still run an old IPCOP box just for that reason, would be nice to switch it to pfSense :)

                                Yes, it would be nice to have. However, I wouldn't view this is a sufficient reason to stay with IPCop as the IPCop distribution really isn't being kept up to date. Security is more important that voltage monitoring.

                                1 Reply Last reply Reply Quote 0
                                • GertjanG
                                  Gertjan
                                  last edited by

                                  @dennypage:

                                  … Security is more important that voltage monitoring.

                                  Like this :
                                  pfSense is handling my network flux.
                                  My UPS is monitoring all the 'electric' stuff - and exposing its finding by snmp. I use NUT just for the 'shutdown properly' when power goes to zero …

                                  No "help me" PM's please. Use the forum, the community will thank you.
                                  Edit : and where are the logs ??

                                  1 Reply Last reply Reply Quote 0
                                  • B
                                    bdf0506
                                    last edited by

                                    I'm having issues with NUT shutting down the pfSense, but it is NOT shutting down the UPS after the pfSesnse shuts down.

                                    I am using a CyberPower UPS, with all default settings of the NUT package in pfSense. I am using the driver of 'usbhid-ups'. It is able to monitor the UPS without any issue.

                                    From an ssh console of pfSense, if i issue 'upsdrvctl shutdown' it will shut down the UPS, so at least I know the driver works properly. But how do I get it so that it will shutdown the pfSense physical server, and then shutdown the UPS immediately after? It seems like it should just "work" based on what I've read about NUT, but perhaps I am missing a setting.

                                    The reason I need it to behave this way is that if the UPS battery is good for 30 minutes, pfSense shuts down after 20 minutes. Then there is 10 minutes battery remaining - and if power resumes before the UPS is fully depleted, there is no way for the pfSense server to know that power was restored, and it will stay in an off situation, requiring human intervention.

                                    Thanks!

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      bdf0506, can you please confirm that you haven't modified any of the system or nut scripts by hand? I will have a look at this, but it will be about a week before I can.

                                      1 Reply Last reply Reply Quote 0
                                      • B
                                        bdf0506
                                        last edited by

                                        Thanks for the reply. I've added a LISTEN section into upsd.conf for another device to query NUT, but that is all. Everything else should be the default.

                                        I'm not convinced this is an issue with the pfsense port of NUT, but perhaps its a NUT configuration setting all together that I am missing. I have noticed that some of the files - especially upsmon.conf are missing a lot of values vs the sample file, but maybe some of those fields are just the default fields.

                                        Here's the config files that I have:

                                        
                                        [2.3.4-RELEASE][root@pfSense.home]/root: cat /usr/local/etc/nut/ups.conf
                                        
                                        [ups]
                                        driver=usbhid-ups
                                        port=auto
                                        
                                        
                                        
                                        [2.3.4-RELEASE][root@pfSense.home]/root: cat /usr/local/etc/nut/upsd.conf
                                        LISTEN 127.0.0.1
                                        LISTEN ::1
                                        
                                        LISTEN 192.168.10.1 3493
                                        
                                        
                                        
                                        [2.3.4-RELEASE][root@pfSense.home]/root: cat /usr/local/etc/nut/upsmon.conf
                                        MONITOR ups 1 monuser 615fdd64b1d37893a33d master
                                        SHUTDOWNCMD "/sbin/shutdown -p +0"
                                        POWERDOWNFLAG /etc/killpower
                                        NOTIFYCMD /usr/local/pkg/nut/nut_email.php
                                        NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
                                        NOTIFYFLAG FSD    SYSLOG+WALL+EXEC
                                        NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                                        NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
                                        NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
                                        NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
                                        
                                        
                                        
                                        [2.3.4-RELEASE][root@pfSense.home]/root: cat /usr/local/etc/nut/upsd.users
                                        [admin]
                                        password=ca21ff457d2db2f4d776
                                        actions=set
                                        instcmds=all
                                        [monuser]
                                        password=615fdd64b1d37893a33d
                                        upsmon master
                                        
                                        

                                        And here is an output of my actual ups device, showing that NUT is working and can connect to it.

                                        
                                        [2.3.4-RELEASE][root@pfSense.home]/root: upsc ups@localhost
                                        battery.charge: 28
                                        battery.charge.low: 10
                                        battery.charge.warning: 20
                                        battery.mfr.date: CPS
                                        battery.runtime: 714
                                        battery.runtime.low: 300
                                        battery.type: PbAcid
                                        battery.voltage: 12.9
                                        battery.voltage.nominal: 12
                                        device.mfr: CPS
                                        device.model: EC650LCD
                                        device.type: ups
                                        driver.name: usbhid-ups
                                        driver.parameter.pollfreq: 30
                                        driver.parameter.pollinterval: 2
                                        driver.parameter.port: auto
                                        driver.parameter.synchronous: no
                                        driver.version: 2.7.4
                                        driver.version.data: CyberPower HID 0.4
                                        driver.version.internal: 0.41
                                        input.transfer.high: 142
                                        input.transfer.low: 100
                                        input.voltage: 123.0
                                        input.voltage.nominal: 120
                                        output.voltage: 123.0
                                        ups.beeper.status: enabled
                                        ups.delay.shutdown: 20
                                        ups.delay.start: 30
                                        ups.load: 16
                                        ups.mfr: CPS
                                        ups.model: EC650LCD
                                        ups.productid: 0501
                                        ups.realpower.nominal: 390
                                        ups.status: OL CHRG
                                        ups.test.result: No test initiated
                                        ups.timer.shutdown: -60
                                        ups.timer.start: 0
                                        ups.vendorid: 0764
                                        
                                        
                                        
                                        [2.3.4-RELEASE][root@pfSense.home]/root: upsdrvctl -t shutdown
                                        Network UPS Tools - UPS driver controller 2.7.4
                                        *** Testing mode: not calling exec/kill
                                           0.000000
                                        If you're not a NUT core developer, chances are that you're told to enable debugging
                                        to see why a driver isn't working for you. We're sorry for the confusion, but this is
                                        the 'upsdrvctl' wrapper, not the driver you're interested in.
                                        
                                        Below you'll find one or more lines starting with 'exec:' followed by an absolute
                                        path to the driver binary and some command line option. This is what the driver
                                        starts and you need to copy and paste that line and append the debug flags to that
                                        line (less the 'exec:' prefix).
                                        
                                           0.000219     Shutdown UPS: ups
                                           0.000240     exec:  /usr/local/libexec/nut/usbhid-ups -a ups -k
                                        
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • R
                                          reqman
                                          last edited by

                                          In package manager, I can see nut is installed, but there is an orange warning "Newer version available", followed by a "Package is configured but not (fully) installed". No update button exists. See attached screenshot.

                                          Something I must do here?


                                          images upload

                                          1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            There is nothing you need to do. What you are seeing below the blue line is actually the legend for the entire package list. I.E. what the icons and colors mean. If you only have one package installed, it can be visually confusing.

                                            1 Reply Last reply Reply Quote 0