      But it doesn't log the timer starting if the UPS goes on battery for example?

      I have no way to test this unfortunately.

      Steve

      4 1 Reply Last reply Reply Quote 0
      • 4
        4o4rh @stephenw10
        last edited by

        @stephenw10 so here is my config

        upsmon.conf

        NOTIFYCMD /usr/local/sbin/upssched
        POLLFREQ 5
        POLLFREQALERT 5
        HOSTSYNC 15
        DEADTIME 15
        
        NOTIFYMSG ONLINE   "UPS %s: On line power."
        NOTIFYMSG ONBATT   "UPS %s: On battery."
        NOTIFYMSG LOWBATT  "UPS %s: Battery is low."
        NOTIFYMSG REPLBATT "UPS %s: Battery needs to be replaced."
        NOTIFYMSG FSD      "UPS %s: Forced shutdown in progress."
        NOTIFYMSG SHUTDOWN "Auto logout and shutdown proceeding."
        NOTIFYMSG COMMOK   "UPS %s: Communications (re-)established."
        NOTIFYMSG COMMBAD  "UPS %s: Communications lost."
        NOTIFYMSG NOCOMM   "UPS %s: Not available."
        NOTIFYMSG NOPARENT "upsmon parent dead, shutdown impossible."
        
        NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
        NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
        NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
        NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
        NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
        NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
        NOTIFYFLAG FSD      SYSLOG+WALL+EXEC
        NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
        NOTIFYFLAG REPLBATT SYSLOG+WALL
        NOTIFYFLAG NOPARENT SYSLOG+WALL
        
        RBWARNTIME 43200
        NOCOMMWARNTIME 300
        FINALDELAY 5
        

        upssched.conf (via filer package)

        CMDSCRIPT /usr/local/bin/upssched-cmd
        PIPEFN /var/db/nut/upssched.pipe
        LOCKFN /var/db/nut/upssched.lock
        
        AT ONBATT  * START-TIMER onbatt 300
        AT ONLINE  * CANCEL-TIMER onbatt online
        AT LOWBATT * EXECUTE lowbatt
        AT COMMBAD  * START-TIMER commbad 30
        AT COMMOK  * CANCEL-TIMER commbad commok
        AT NOCOMM * EXECUTE commbad
        AT FSD * EXECUTE powerdown
        AT SHUTDOWN * EXECUTE powerdown
        

        upssched-cmd

        #! /bin/sh
        
        UPS="ups"
        STATUS=$( upsc $UPS ups.status )
        CHARGE=$( upsc $UPS battery.charge )
        CHMSG="[$STATUS]:$CHARGE%"
        
        # upssched-cmd  --slave --
        logger -i -t upssched-cmd Calling upssched-cmd $1
        
        case $1 in
            online) 
            MSG="$UPS, $CHMSG - power supply has been restored."
            ;;
            onbatt)
            MSG="$UPS, $CHMSG - power failure - save your work!"
            ;;
            lowbatt) 
            MSG="$UPS, $CHMSG - shutdown now!"
            ;;
            *) 
            logger -i -t upssched-cmd "Bad arg: \"$1\", $CHMSG"
            exit 1
            ;;
        esac
        logger -i -t upssched-cmd $MSG
        

        log file is showing

        Nov 8 10:08:49 	upssched 	44022 	exec_cmd(/usr/local/bin/upssched-cmd online) returned 127
        Nov 8 10:08:49 	upssched-cmd 	44598 	UPS - power supply had been restored.
        Nov 8 10:08:49 	upssched-cmd 	44492 	Calling upssched-cmd online
        Nov 8 10:08:49 	upsmon 	61766 	UPS ups@nas.net.lan: On line power.
        Nov 8 10:08:44 	upssched 	22770 	exec_cmd(/usr/local/bin/upssched-cmd onbatt) returned 127
        Nov 8 10:08:44 	upssched-cmd 	23262 	UPS - power failure - save your work!
        Nov 8 10:08:44 	upssched-cmd 	23007 	Calling upssched-cmd onbatt
        Nov 8 10:08:44 	upsmon 	61766 	UPS ups@nas.net.lan: On battery. 
        

        what is the
        "upssched 44022 exec_cmd(/usr/local/bin/upssched-cmd online) returned 127"

        1 Reply Last reply Reply Quote 0
        • stephenw10S
          stephenw10 Netgate Administrator
          last edited by stephenw10

          That return code is usually telling you 'command not found' or similar.

          Did you try running those from the command line?

          The timer names seem to be defined in upper case but referenced as lower case.

          Steve

          4 1 Reply Last reply Reply Quote 0
          • 4
            4o4rh @stephenw10
            last edited by

            @stephenw10 script doesn't do anything.

            when running /usr/local/bin/upssched-cmd online, the prompt doesn't return and you have to ctl-c to break it.

            1 Reply Last reply Reply Quote 0
            • stephenw10S
              stephenw10 Netgate Administrator
              last edited by

              It doesn't even write anything to the logs?

              4 1 Reply Last reply Reply Quote 0
              • 4
                4o4rh @stephenw10
                last edited by 4o4rh

                @stephenw10 here is what shows in the log

                upssched 22770 exec_cmd(/usr/local/bin/upssched-cmd onbatt) returned 127
                upssched-cmd 23262 UPS - power failure - save your work!
                upssched-cmd 23007 Calling upssched-cmd onbatt
                upsmon 61766 UPS ups@nas.net.lan: On battery.

                after further searching, i found that some of the lines were missing the open bracket, but the bigger issue is, this is a bash script (which is not installed). I have no idea how to convert it to sh

                #!/usr/local/bin/bash -u
                logger -i -t upssched-cmd Calling upssched-cmd $1
                
                UPS="eapeups"
                STATUS=$( upsc $UPS ups.status )
                CHARGE=$( upsc $UPS battery.charge )
                CHMSG="[$STATUS]:$CHARGE%"
                
                case $1 in
                    (online)  MSG="$UPS, $CHMSG - power supply has been restored." ;;
                    (onbatt)  MSG="$UPS, $CHMSG - power failure - save your work!" ;;
                    (lowbatt) MSG="$UPS, $CHMSG - shutdown now!" ;;
                (*) logger -i -t upssched-cmd "Bad arg: \"$1\", $CHMSG"
                    exit 1 ;;
                esac
                logger -i -t upssched-cmd $MSG
                
                GertjanG 1 Reply Last reply Reply Quote 0
                • stephenw10S
                  stephenw10 Netgate Administrator
                  last edited by

                  You can install bash if you really need to.
                  What part fails id you use sh?

                  Steve

                  1 Reply Last reply Reply Quote 0
                  • GertjanG
                    Gertjan @4o4rh
                    last edited by

                    @gwaitsi said in UPSMON independent shutdown.:

                    but the bigger issue is, this is a bash script

                    Although bash is probably a more powerful shell, I guess the script's syntax could be re written in sh syntax.

                    No "help me" PM's please. Use the forum, the community will thank you.
                    Edit : and where are the logs ??

                    4 1 Reply Last reply Reply Quote 0
                    • 4
                      4o4rh @Gertjan
                      last edited by

                      @Gertjan is that something you could help with pls? i would have no clue as i am not familiar with either

                      1 Reply Last reply Reply Quote 0
                      • GertjanG
                        Gertjan
                        last edited by

                        First things first : extreme, but you won't regret it : do not use the build in GUI file editor.
                        Use a console or better : ssh access. You'll be having full control, you can see file permissions, attributes etc.

                        The GUI file editor is only used by experts ... and they probably use when they want to fly blind.

                        @gwaitsi said in UPSMON independent shutdown.:

                        but the bigger issue is, this is a bash script (which is not installed)

                        I'm experimenting right now with this upssched-cmd ....
                        See here https://dan.langille.org/2020/09/07/monitoring-your-ups-using-nut-on-freebsd/ for guidelines and the entire https://networkupstools.org/ .....

                        Be careful : you've seen that pfSense (re) creates /usr/local/etc/nut/upsmon.conf and other .conf files in that dircetory. Use the GUI NUT pages to add your own lines to these files.

                        No "help me" PM's please. Use the forum, the community will thank you.
                        Edit : and where are the logs ??

                        4 1 Reply Last reply Reply Quote 0
                        • 4
                          4o4rh @Gertjan
                          last edited by

                          @Gertjan hi, I created my files a linux text editor. I copied and pasted them into the filer package.

                          /usr/local/etc/nut/upssched.conf 	0644 	UPS Shutdown Scheduler Configuration 	
                          	 
                          /usr/local/bin/upssched-cmd 	0755 	UPS Shutdown Scheduler Command Script
                          

                          The extra upsmon script commands were added to the advanced tab.
                          the log clearly shows the script is being triggered, but just i don't know what i am doing with the scripts to be able to convert it.

                          GertjanG 1 Reply Last reply Reply Quote 0
                          • GertjanG
                            Gertjan @4o4rh
                            last edited by

                            @gwaitsi said in UPSMON independent shutdown.:

                            hi, I created my files a linux text editor

                            Again : use ssh directly, you'll feel @home right away.

                            I advise you to execute this on pfSEnse :

                            pkg install nano
                            

                            I guess you know who 'nano' is ;)

                            I don't know what you mean with

                            /usr/local/etc/nut/upssched.conf 	0644 	UPS Shutdown Scheduler Configuration 	
                            	 
                            /usr/local/bin/upssched-cmd 	0755 	UPS Shutdown Scheduler Command Script
                            

                            Btw : I have a Back-UPS 700 APC ups, hooked up using a USB cable.

                            These are my settings :

                            2ba8b960-d21b-43e2-9b1f-9587d85d8a98-image.png

                            upsmon.conf : the strict minimum, as the other settings in upsmon.conf will be set to default. see upsmon.conf.example for the values.

                            The upsd.conf contains the LAN IPv4 and IPv6, as my pfSense NUT us a UPS master - I have a disk station NAS being the NUT slave.

                            The upsd.users section shows the login details of the NAS.

                            My /usr/local/etc/nut/upssched.conf file :

                            -r-xr-xr-x   1 root  wheel    649 Nov 12 15:36 upssched-cmd
                            
                            CMDSCRIPT /usr/local/etc/nut/upssched-cmd
                            PIPEFN /var/db/nut/upssched.pipe
                            LOCKFN /var/db/nut/upssched.lock
                            
                            AT ONBATT  * START-TIMER onbatt 20
                            AT ONLINE  * CANCEL-TIMER onbatt online
                            AT LOWBATT * EXECUTE lowbatt
                            AT COMMBAD  * START-TIMER commbad 30
                            AT COMMOK  * CANCEL-TIMER commbad commok
                            AT NOCOMM * EXECUTE commbad
                            AT FSD * EXECUTE powerdown
                            AT SHUTDOWN * EXECUTE powerdown
                            

                            Take note of the location of the "CMDSCRIPT " file : /usr/local/etc/nut/upssched-cmd file

                            See also : "onbatt 20" which means that I receive notifications by mail etc after "20 sec" - not the default 300 seconds.

                            Here is /usr/local/etc/nut/upssched-cmd file :

                            #! /bin/sh
                            
                            UPS="ups"
                            STATUS=$( upsc $UPS ups.status )
                            CHARGE=$( upsc $UPS battery.charge )
                            CHMSG="[$STATUS]:$CHARGE%"
                            
                            # upssched-cmd  --slave --
                            logger -i -t upssched-cmd Calling upssched-cmd $1
                            
                            case $1 in
                                online) 
                                MSG="$UPS, $CHMSG - power supply has been restored."
                                ;;
                                onbatt)
                                MSG="$UPS, $CHMSG - power failure - save your work!"
                                ;;
                                lowbatt) 
                                MSG="$UPS, $CHMSG - shutdown now!"
                                ;;
                            	upsgone)
                            	MSG="$UPS, $CHMSG - UPS has been gone for awhile"
                            	;;
                                *) 
                                logger -i -t upssched-cmd "Bad arg: \"$1\", $CHMSG"
                                exit 1
                                ;;
                            esac
                            logger -i -t upssched-cmd $MSG
                            

                            This is logged when I pull the plug :

                            8a2f4877-c8d8-430e-bd7e-7b077eca8c8b-image.png

                            Read from bottom to top.
                            I received the mails.

                            No "help me" PM's please. Use the forum, the community will thank you.
                            Edit : and where are the logs ??

                            4 1 Reply Last reply Reply Quote 0
                            • 4
                              4o4rh @Gertjan
                              last edited by

                              @Gertjan said in UPSMON independent shutdown.:

                              #! /bin/sh

                              UPS="ups"
                              STATUS=$( upsc $UPS ups.status )
                              CHARGE=$( upsc $UPS battery.charge )
                              CHMSG="[$STATUS]:$CHARGE%"

                              upssched-cmd --slave --

                              logger -i -t upssched-cmd Calling upssched-cmd $1

                              case $1 in
                              online)
                              MSG="$UPS, $CHMSG - power supply has been restored."
                              ;;
                              onbatt)
                              MSG="$UPS, $CHMSG - power failure - save your work!"
                              ;;
                              lowbatt)
                              MSG="$UPS, $CHMSG - shutdown now!"
                              ;;
                              upsgone)
                              MSG="$UPS, $CHMSG - UPS has been gone for awhile"
                              ;;
                              *)
                              logger -i -t upssched-cmd "Bad arg: "$1", $CHMSG"
                              exit 1
                              ;;
                              esac
                              logger -i -t upssched-cmd $MSG

                              i will give it a shot.

                              fyi - If you use nano to create upssched.conf and upssched-cmd the files will be lost if you have to re-install.

                              If you install the "Filer" package, you can create those files under the Diagnostics menu and the contents will be saved to config.xml, so you can transfer the settings to a new install.

                              GertjanG 1 Reply Last reply Reply Quote 0
                              • stephenw10S
                                stephenw10 Netgate Administrator
                                last edited by

                                You can also use the included Easy Editor ee which provides much the same functionality as nano.

                                Steve

                                1 Reply Last reply Reply Quote 0
                                • GertjanG
                                  Gertjan @4o4rh
                                  last edited by

                                  @gwaitsi said in UPSMON independent shutdown.:

                                  If you install the "Filer" package,

                                  True ! In fact, discovered yesterday that "Filer" wasn't the build-in GUI editor ...
                                  I use the Notes package myself : for every change I made that can't be done with the GUI, thus stored for eternity, I take notes.
                                  This forces me to re read the documentation if I want to implement changes. Not only pfSense changes over time ;)

                                  @stephenw10 said in UPSMON independent shutdown.:

                                  ee

                                  I know. nano is just a personal preference, as it exists on all my pfSenses, and linux based servers. I'm trying to limit my have-to-know keyboard short-cut list to a minimum as I'm stilling suffering from the vi syndrome.

                                  No "help me" PM's please. Use the forum, the community will thank you.
                                  Edit : and where are the logs ??

                                  1 Reply Last reply Reply Quote 0
                                  • 4
                                    4o4rh
                                    last edited by

                                    So it is looking good so far, lost comms are from shutting down the service on truenas. forced shutdown from lost comms works.

                                    Still need to test how long the battery on the dumb ups will last. It should last much longer than the apc ups which gives me about an hour for power to be restored.

                                    i will have on rare occasions a use case when the power is gone for more than an hour and pfsense shuts down, but the battery doesn't die before power is restored. in such a use case, pfsense will need to be manually re-started.

                                    Anyone got any ideas?

                                    Nov 16 06:57:38 	upsmon 	98032 	UPS ups@nas.net.lan: Communications (re-)established.
                                    Nov 16 06:57:33 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                                    Nov 16 06:57:28 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                                    Nov 16 06:57:23 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                                    Nov 16 06:57:18 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                                    Nov 16 06:57:13 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                                    Nov 16 06:57:08 	upsmon 	98032 	UPS ups@nas.net.lan: Communications lost.
                                    Nov 16 06:57:08 	upsmon 	98032 	Poll UPS [ups@nas.net.lan] failed - Server disconnected
                                    Nov 16 06:56:48 	upsmon 	98032 	UPS ups@nas.net.lan: Communications (re-)established.
                                    Nov 16 06:56:43 	upsmon 	98032 	UPS ups@nas.net.lan: Communications lost.
                                    Nov 16 06:56:43 	upsmon 	98032 	Poll UPS [ups@nas.net.lan] failed - Server disconnected
                                    Nov 15 05:34:34 	upsmon 	98032 	UPS ups@nas.net.lan: On line power.
                                    Nov 15 05:34:29 	upsmon 	98032 	UPS ups@nas.net.lan: On battery.
                                    Nov 14 00:56:34 	upssched-cmd 		UPS on battery too long, forced shutdown
                                    

                                    final schedups-cmd

                                    #! /bin/sh
                                    #
                                    # This script should be called by upssched via the CMDSCRIPT directive.
                                    # Here is a quick example to show how to handle a bunch of possible
                                    # timer names with the help of the case structure.
                                    # This script may be replaced with another program without harm.
                                    # The first argument passed to your CMDSCRIPT is the name of the timer
                                    # from your AT lines.
                                    
                                    # upssched-cmd  --slave --
                                    
                                    case $1 in
                                        onbattery)
                                        	logger -t upssched-cmd "UPS on battery too long, forced shutdown"
                                        	/usr/local/sbin/upsmon -c fsd
                                        	;;
                                        lowbattery) 
                                        	logger -t upssched-cmd "UPS on battery critical, forced shutdown"
                                        	/usr/local/sbin/upsmon -c fsd
                                        	;;
                                        commbad)
                                        	logger -t upssched-cmd "UPS communications missing too long, forced shutdown"
                                        	/usr/local/sbin/upsmon -c fsd
                                        	;;
                                        powerdown)
                                        	logger -t upssched-cmd "UPS communications missing too long, forced shutdown"
                                        	/usr/local/sbin/upsmon -c fsd
                                        	;;
                                        *) 
                                        		logger -t upssched-cmd "Unrecognized command: $1"
                                        		;;
                                    esac
                                    
                                    GertjanG 1 Reply Last reply Reply Quote 1
                                    • GertjanG
                                      Gertjan @4o4rh
                                      last edited by

                                      @gwaitsi said in UPSMON independent shutdown.:

                                      Anyone got any ideas?

                                      What is is the question ?
                                      How to manually restart ?

                                      For the "AT ... timer commands", see the upssched.conf file.

                                      No "help me" PM's please. Use the forum, the community will thank you.
                                      Edit : and where are the logs ??

                                      4 1 Reply Last reply Reply Quote 0
                                      • 4
                                        4o4rh @Gertjan
                                        last edited by

                                        @Gertjan the ups on the pfsense (Qotom J1900) is like a power adapter with a battery e.g. it is dumb. pfsense is triggered via truenas server which has a apc ups connected to it.

                                        If the power comes back on before the pfsense powers down, all is good. it will run on battery and continue.

                                        If the pfsense shutdowns, but the ups battery doesn't deplete, the J1900 will never see a loss of power and therefore wont know to turn back on, so has to be manually started.

                                        Looking for ideas on how i could solve this scenario.

                                        1 Reply Last reply Reply Quote 0
                                        • GertjanG
                                          Gertjan
                                          last edited by

                                          @gwaitsi said in UPSMON independent shutdown.:

                                          J1900

                                          If the J1900 supports WOL .....

                                          No "help me" PM's please. Use the forum, the community will thank you.
                                          Edit : and where are the logs ??

                                          1 Reply Last reply Reply Quote 0
                                          • stephenw10S
                                            stephenw10 Netgate Administrator
                                            last edited by

                                            Yeah, WoL is probably the only option there without some additional hardware.