    UPSMON independent shutdown.

    Scheduled Pinned Locked Moved Hardware
    37 Posts 3 Posters 4.1k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • 4
      4o4rh @stephenw10
      last edited by 4o4rh

      @stephenw10 here is what shows in the log

      upssched 22770 exec_cmd(/usr/local/bin/upssched-cmd onbatt) returned 127
      upssched-cmd 23262 UPS - power failure - save your work!
      upssched-cmd 23007 Calling upssched-cmd onbatt
      upsmon 61766 UPS ups@nas.net.lan: On battery.

      after further searching, i found that some of the lines were missing the open bracket, but the bigger issue is, this is a bash script (which is not installed). I have no idea how to convert it to sh

      #!/usr/local/bin/bash -u
      logger -i -t upssched-cmd Calling upssched-cmd $1
      
      UPS="eapeups"
      STATUS=$( upsc $UPS ups.status )
      CHARGE=$( upsc $UPS battery.charge )
      CHMSG="[$STATUS]:$CHARGE%"
      
      case $1 in
          (online)  MSG="$UPS, $CHMSG - power supply has been restored." ;;
          (onbatt)  MSG="$UPS, $CHMSG - power failure - save your work!" ;;
          (lowbatt) MSG="$UPS, $CHMSG - shutdown now!" ;;
      (*) logger -i -t upssched-cmd "Bad arg: \"$1\", $CHMSG"
          exit 1 ;;
      esac
      logger -i -t upssched-cmd $MSG
      
      GertjanG 1 Reply Last reply Reply Quote 0
      • stephenw10S
        stephenw10 Netgate Administrator
        last edited by

        You can install bash if you really need to.
        What part fails id you use sh?

        Steve

        1 Reply Last reply Reply Quote 0
        • GertjanG
          Gertjan @4o4rh
          last edited by

          @gwaitsi said in UPSMON independent shutdown.:

          but the bigger issue is, this is a bash script

          Although bash is probably a more powerful shell, I guess the script's syntax could be re written in sh syntax.

          No "help me" PM's please. Use the forum, the community will thank you.
          Edit : and where are the logs ??

          4 1 Reply Last reply Reply Quote 0
          • 4
            4o4rh @Gertjan
            last edited by

            @Gertjan is that something you could help with pls? i would have no clue as i am not familiar with either

            1 Reply Last reply Reply Quote 0
            • GertjanG
              Gertjan
              last edited by

              First things first : extreme, but you won't regret it : do not use the build in GUI file editor.
              Use a console or better : ssh access. You'll be having full control, you can see file permissions, attributes etc.

              The GUI file editor is only used by experts ... and they probably use when they want to fly blind.

              @gwaitsi said in UPSMON independent shutdown.:

              but the bigger issue is, this is a bash script (which is not installed)

              I'm experimenting right now with this upssched-cmd ....
              See here https://dan.langille.org/2020/09/07/monitoring-your-ups-using-nut-on-freebsd/ for guidelines and the entire https://networkupstools.org/ .....

              Be careful : you've seen that pfSense (re) creates /usr/local/etc/nut/upsmon.conf and other .conf files in that dircetory. Use the GUI NUT pages to add your own lines to these files.

              No "help me" PM's please. Use the forum, the community will thank you.
              Edit : and where are the logs ??

              4 1 Reply Last reply Reply Quote 0
              • 4
                4o4rh @Gertjan
                last edited by

                @Gertjan hi, I created my files a linux text editor. I copied and pasted them into the filer package.

                /usr/local/etc/nut/upssched.conf 	0644 	UPS Shutdown Scheduler Configuration 	
                	 
                /usr/local/bin/upssched-cmd 	0755 	UPS Shutdown Scheduler Command Script
                

                The extra upsmon script commands were added to the advanced tab.
                the log clearly shows the script is being triggered, but just i don't know what i am doing with the scripts to be able to convert it.

                GertjanG 1 Reply Last reply Reply Quote 0
                • GertjanG
                  Gertjan @4o4rh
                  last edited by

                  @gwaitsi said in UPSMON independent shutdown.:

                  hi, I created my files a linux text editor

                  Again : use ssh directly, you'll feel @home right away.

                  I advise you to execute this on pfSEnse :

                  pkg install nano
                  

                  I guess you know who 'nano' is ;)

                  I don't know what you mean with

                  /usr/local/etc/nut/upssched.conf 	0644 	UPS Shutdown Scheduler Configuration 	
                  	 
                  /usr/local/bin/upssched-cmd 	0755 	UPS Shutdown Scheduler Command Script
                  

                  Btw : I have a Back-UPS 700 APC ups, hooked up using a USB cable.

                  These are my settings :

                  2ba8b960-d21b-43e2-9b1f-9587d85d8a98-image.png

                  upsmon.conf : the strict minimum, as the other settings in upsmon.conf will be set to default. see upsmon.conf.example for the values.

                  The upsd.conf contains the LAN IPv4 and IPv6, as my pfSense NUT us a UPS master - I have a disk station NAS being the NUT slave.

                  The upsd.users section shows the login details of the NAS.

                  My /usr/local/etc/nut/upssched.conf file :

                  -r-xr-xr-x   1 root  wheel    649 Nov 12 15:36 upssched-cmd
                  
                  CMDSCRIPT /usr/local/etc/nut/upssched-cmd
                  PIPEFN /var/db/nut/upssched.pipe
                  LOCKFN /var/db/nut/upssched.lock
                  
                  AT ONBATT  * START-TIMER onbatt 20
                  AT ONLINE  * CANCEL-TIMER onbatt online
                  AT LOWBATT * EXECUTE lowbatt
                  AT COMMBAD  * START-TIMER commbad 30
                  AT COMMOK  * CANCEL-TIMER commbad commok
                  AT NOCOMM * EXECUTE commbad
                  AT FSD * EXECUTE powerdown
                  AT SHUTDOWN * EXECUTE powerdown
                  

                  Take note of the location of the "CMDSCRIPT " file : /usr/local/etc/nut/upssched-cmd file

                  See also : "onbatt 20" which means that I receive notifications by mail etc after "20 sec" - not the default 300 seconds.

                  Here is /usr/local/etc/nut/upssched-cmd file :

                  #! /bin/sh
                  
                  UPS="ups"
                  STATUS=$( upsc $UPS ups.status )
                  CHARGE=$( upsc $UPS battery.charge )
                  CHMSG="[$STATUS]:$CHARGE%"
                  
                  # upssched-cmd  --slave --
                  logger -i -t upssched-cmd Calling upssched-cmd $1
                  
                  case $1 in
                      online) 
                      MSG="$UPS, $CHMSG - power supply has been restored."
                      ;;
                      onbatt)
                      MSG="$UPS, $CHMSG - power failure - save your work!"
                      ;;
                      lowbatt) 
                      MSG="$UPS, $CHMSG - shutdown now!"
                      ;;
                  	upsgone)
                  	MSG="$UPS, $CHMSG - UPS has been gone for awhile"
                  	;;
                      *) 
                      logger -i -t upssched-cmd "Bad arg: \"$1\", $CHMSG"
                      exit 1
                      ;;
                  esac
                  logger -i -t upssched-cmd $MSG
                  

                  This is logged when I pull the plug :

                  8a2f4877-c8d8-430e-bd7e-7b077eca8c8b-image.png

                  Read from bottom to top.
                  I received the mails.

                  No "help me" PM's please. Use the forum, the community will thank you.
                  Edit : and where are the logs ??

                  4 1 Reply Last reply Reply Quote 0
                  • 4
                    4o4rh @Gertjan
                    last edited by

                    @Gertjan said in UPSMON independent shutdown.:

                    #! /bin/sh

                    UPS="ups"
                    STATUS=$( upsc $UPS ups.status )
                    CHARGE=$( upsc $UPS battery.charge )
                    CHMSG="[$STATUS]:$CHARGE%"

                    upssched-cmd --slave --

                    logger -i -t upssched-cmd Calling upssched-cmd $1

                    case $1 in
                    online)
                    MSG="$UPS, $CHMSG - power supply has been restored."
                    ;;
                    onbatt)
                    MSG="$UPS, $CHMSG - power failure - save your work!"
                    ;;
                    lowbatt)
                    MSG="$UPS, $CHMSG - shutdown now!"
                    ;;
                    upsgone)
                    MSG="$UPS, $CHMSG - UPS has been gone for awhile"
                    ;;
                    *)
                    logger -i -t upssched-cmd "Bad arg: "$1", $CHMSG"
                    exit 1
                    ;;
                    esac
                    logger -i -t upssched-cmd $MSG

                    i will give it a shot.

                    fyi - If you use nano to create upssched.conf and upssched-cmd the files will be lost if you have to re-install.

                    If you install the "Filer" package, you can create those files under the Diagnostics menu and the contents will be saved to config.xml, so you can transfer the settings to a new install.

                    GertjanG 1 Reply Last reply Reply Quote 0
                    • stephenw10S
                      stephenw10 Netgate Administrator
                      last edited by

                      You can also use the included Easy Editor ee which provides much the same functionality as nano.

                      Steve

                      1 Reply Last reply Reply Quote 0
                      • GertjanG
                        Gertjan @4o4rh
                        last edited by

                        @gwaitsi said in UPSMON independent shutdown.:

                        If you install the "Filer" package,

                        True ! In fact, discovered yesterday that "Filer" wasn't the build-in GUI editor ...
                        I use the Notes package myself : for every change I made that can't be done with the GUI, thus stored for eternity, I take notes.
                        This forces me to re read the documentation if I want to implement changes. Not only pfSense changes over time ;)

                        @stephenw10 said in UPSMON independent shutdown.:

                        ee

                        I know. nano is just a personal preference, as it exists on all my pfSenses, and linux based servers. I'm trying to limit my have-to-know keyboard short-cut list to a minimum as I'm stilling suffering from the vi syndrome.

                        No "help me" PM's please. Use the forum, the community will thank you.
                        Edit : and where are the logs ??

                        1 Reply Last reply Reply Quote 0
                        • 4
                          4o4rh
                          last edited by

                          So it is looking good so far, lost comms are from shutting down the service on truenas. forced shutdown from lost comms works.

                          Still need to test how long the battery on the dumb ups will last. It should last much longer than the apc ups which gives me about an hour for power to be restored.

                          i will have on rare occasions a use case when the power is gone for more than an hour and pfsense shuts down, but the battery doesn't die before power is restored. in such a use case, pfsense will need to be manually re-started.

                          Anyone got any ideas?

                          Nov 16 06:57:38 	upsmon 	98032 	UPS ups@nas.net.lan: Communications (re-)established.
                          Nov 16 06:57:33 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                          Nov 16 06:57:28 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                          Nov 16 06:57:23 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                          Nov 16 06:57:18 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                          Nov 16 06:57:13 	upsmon 	98032 	UPS [ups@nas.net.lan]: connect failed: Connection failure: Connection refused
                          Nov 16 06:57:08 	upsmon 	98032 	UPS ups@nas.net.lan: Communications lost.
                          Nov 16 06:57:08 	upsmon 	98032 	Poll UPS [ups@nas.net.lan] failed - Server disconnected
                          Nov 16 06:56:48 	upsmon 	98032 	UPS ups@nas.net.lan: Communications (re-)established.
                          Nov 16 06:56:43 	upsmon 	98032 	UPS ups@nas.net.lan: Communications lost.
                          Nov 16 06:56:43 	upsmon 	98032 	Poll UPS [ups@nas.net.lan] failed - Server disconnected
                          Nov 15 05:34:34 	upsmon 	98032 	UPS ups@nas.net.lan: On line power.
                          Nov 15 05:34:29 	upsmon 	98032 	UPS ups@nas.net.lan: On battery.
                          Nov 14 00:56:34 	upssched-cmd 		UPS on battery too long, forced shutdown
                          

                          final schedups-cmd

                          #! /bin/sh
                          #
                          # This script should be called by upssched via the CMDSCRIPT directive.
                          # Here is a quick example to show how to handle a bunch of possible
                          # timer names with the help of the case structure.
                          # This script may be replaced with another program without harm.
                          # The first argument passed to your CMDSCRIPT is the name of the timer
                          # from your AT lines.
                          
                          # upssched-cmd  --slave --
                          
                          case $1 in
                              onbattery)
                              	logger -t upssched-cmd "UPS on battery too long, forced shutdown"
                              	/usr/local/sbin/upsmon -c fsd
                              	;;
                              lowbattery) 
                              	logger -t upssched-cmd "UPS on battery critical, forced shutdown"
                              	/usr/local/sbin/upsmon -c fsd
                              	;;
                              commbad)
                              	logger -t upssched-cmd "UPS communications missing too long, forced shutdown"
                              	/usr/local/sbin/upsmon -c fsd
                              	;;
                              powerdown)
                              	logger -t upssched-cmd "UPS communications missing too long, forced shutdown"
                              	/usr/local/sbin/upsmon -c fsd
                              	;;
                              *) 
                              		logger -t upssched-cmd "Unrecognized command: $1"
                              		;;
                          esac
                          
                          GertjanG 1 Reply Last reply Reply Quote 1
                          • GertjanG
                            Gertjan @4o4rh
                            last edited by

                            @gwaitsi said in UPSMON independent shutdown.:

                            Anyone got any ideas?

                            What is is the question ?
                            How to manually restart ?

                            For the "AT ... timer commands", see the upssched.conf file.

                            No "help me" PM's please. Use the forum, the community will thank you.
                            Edit : and where are the logs ??

                            4 1 Reply Last reply Reply Quote 0
                            • 4
                              4o4rh @Gertjan
                              last edited by

                              @Gertjan the ups on the pfsense (Qotom J1900) is like a power adapter with a battery e.g. it is dumb. pfsense is triggered via truenas server which has a apc ups connected to it.

                              If the power comes back on before the pfsense powers down, all is good. it will run on battery and continue.

                              If the pfsense shutdowns, but the ups battery doesn't deplete, the J1900 will never see a loss of power and therefore wont know to turn back on, so has to be manually started.

                              Looking for ideas on how i could solve this scenario.

                              1 Reply Last reply Reply Quote 0
                              • GertjanG
                                Gertjan
                                last edited by

                                @gwaitsi said in UPSMON independent shutdown.:

                                J1900

                                If the J1900 supports WOL .....

                                No "help me" PM's please. Use the forum, the community will thank you.
                                Edit : and where are the logs ??

                                1 Reply Last reply Reply Quote 0
                                • stephenw10S
                                  stephenw10 Netgate Administrator
                                  last edited by

                                  Yeah, WoL is probably the only option there without some additional hardware.

                                  Steve

                                  1 Reply Last reply Reply Quote 0
                                  • 4
                                    4o4rh
                                    last edited by

                                    sounds like a good idea fellas, just need to figure out how to do that now ;-)

                                    1 Reply Last reply Reply Quote 0
                                    • GertjanG
                                      Gertjan
                                      last edited by

                                      If your J-thing is a typical PC device, check the BIOS.
                                      WOL is nothing more a an always-on chip (activated as soon as there is some power) and simulates a press-power-on-the-button as soon as it sees it's own MAC 3 times in a packet load over the/a Ethernet interface, typically the LAN interface.

                                      If not : you found yourself yet another Rasberry/PI project ;)

                                      No "help me" PM's please. Use the forum, the community will thank you.
                                      Edit : and where are the logs ??

                                      1 Reply Last reply Reply Quote 0
                                      • 4
                                        4o4rh
                                        last edited by

                                        does anyone know how to set a netgear switch (GS108Tv3) up to provide the magic packet

                                        1 Reply Last reply Reply Quote 0
                                        • GertjanG
                                          Gertjan
                                          last edited by

                                          @gwaitsi said in UPSMON independent shutdown.:

                                          WOL for GS108Tv3

                                          => They should know it : https://community.netgear.com/t5/Smart-Plus-and-Smart-Pro-Managed/GS108Tv3-how-to-wake-up-pfsense-router/m-p/2007829
                                          If you need a fast answer : look in the Netgear's GUI or go for the manual.

                                          Bad start : Google doesn't know about it, so chances are great the router doesn't have WOL capabilities.

                                          No "help me" PM's please. Use the forum, the community will thank you.
                                          Edit : and where are the logs ??

                                          4 1 Reply Last reply Reply Quote 0
                                          • 4
                                            4o4rh @Gertjan
                                            last edited by

                                            @Gertjan couldn't find anything in the gui. there is a section on green ethernet, but it is not clear to me whether that causes broadcast magic packets. (i thought the specific mac address had to be used)

                                            1 Reply Last reply Reply Quote 0
                                            • First post