When I stop the apcupsd service and run apctest then select 10 battery calibration. It cause my router to reboot after reporting the calibration was aborted. My battery is only 1 year old, and all the other tests passed. APC backups 750.
-
S stephenw10 moved this topic from General pfSense Questions on
-
I'm running the 24.11-RELEASE (arm64) on a Netgate SG-1100.
-
@Vancejo1 said in apcupsd causes restart:
When I stop the apcupsd service and run apctest then select 10 battery calibration. It cause my router to reboot after reporting the calibration was aborted.
Is it really rebooting? Or does the UPS cut the power?
Check the logs to get sure.
I've seen the latter already, but with old batteries, however. -
@viragomann
Yes it definitely is rebooting, but not immediately. I was able to try it 3 more times before putty quit responding.Here is what shows in putty...
Select function number: 10
This test instructs the UPS to perform a battery calibration
operation and reports the result when the process completes.
The battery level must be at 100% and the load must be at least
10% to begin this test.Battery level is 100% -- OK
Load level is 14% -- OK
Clearing previous self test result...CLEAREDThe battery calibration should automatically end
when the battery level drops below about 25%.
This process can take minutes or hours, depending on
the size of your UPS and the load attached.Initiating battery calibration...INITIATED
Waiting for calibration to complete...
To abort the calibration, press ENTER.CALIBRATION COMPLETED
Result of last self test: ABORTED- Test kill UPS power
- Perform self-test
- Read last self-test result
- View/Change battery date
- View manufacturing date
- View/Change alarm behavior
- View/Change sensitivity
- View/Change low transfer voltage
- View/Change high transfer voltage
- Perform battery calibration
- Test alarm
- View/Change self-test interval
Q) Quit
Select function number: 10
This test instructs the UPS to perform a battery calibration
operation and reports the result when the process completes.
The battery level must be at 100% and the load must be at least
10% to begin this test.Battery level 99% is insufficient to run test.
- Test kill UPS power
- Perform self-test
- Read last self-test result
- View/Change battery date
- View manufacturing date
- View/Change alarm behavior
- View/Change sensitivity
- View/Change low transfer voltage
- View/Change high transfer voltage
- Perform battery calibration
- Test alarm
- View/Change self-test interval
Q) Quit
Select function number: 10
This test instructs the UPS to perform a battery calibration
operation and reports the result when the process completes.
The battery level must be at 100% and the load must be at least
10% to begin this test.Battery level 99% is insufficient to run test.
- Test kill UPS power
- Perform self-test
- Read last self-test result
- View/Change battery date
- View manufacturing date
- View/Change alarm behavior
- View/Change sensitivity
- View/Change low transfer voltage
- View/Change high transfer voltage
- Perform battery calibration
- Test alarm
- View/Change self-test interval
Q) Quit
Select function number: 10
This test instructs the UPS to perform a battery calibration
operation and reports the result when the process completes.
The battery level must be at 100% and the load must be at least
10% to begin this test.
Copyright 2025 Rubicon Communications LLC (Netgate). All rights reserved.