    NUT Package (2.8.1 and above)

    Scheduled Pinned Locked Moved UPS Tools
    296 Posts 41 Posters 159.1k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage @ghound
      last edited by

      @ghound said in NUT Package (2.8.1 and above):

      Output is to the console, should I redirect it to a file or will I be able to capture what you are looking for from console scrollback?

      I expect that you will want to direct it to a file so you don't loose it due to scrolling or other issues.

      1 Reply Last reply Reply Quote 0
      • G
        ghound @dennypage
        last edited by

        @dennypage said in NUT Package (2.8.1 and above):

        Can you run the driver by hand in debug mode via ssh please?

        First start the service, and then kill the driver:

        killall usbhid-ups
        Then, run the driver with debug:

        /usr/local/libexec/nut/usbhid-ups -DDDDDD -a TrippLite

        This is the result around the point when connection to the UPS was lost (around one day after the process was started):

        72245.572443	[D1] upsdrv_updateinfo...
        72245.599003	[D2] file_report_buffer: expected 4 bytes, but got 512 instead
        72245.599080	[D3] Report[err]: (512 bytes) => 32 00 00 09 00 00 00 00 f0 9f 6a 80 00 00 00 00
        72245.599112	[D3]  00 00 00 00 00 00 00 00 98 ea f4 45 48 49 3a c1 80 a0 6a 80 ff ff ff ff 40
        72245.599141	[D3]  9e 6a 80 00 00 00 00 14 b1 b6 83 00 00 00 00 4f 1e ef 65 00 00 00 00 00 50
        72245.599171	[D3]  27 00 00 00 00 00 00 00 00 00 00 00 00 00 00 60 27 00 00 00 00 00 02 00 00
        72245.599201	[D3]  00 00 00 00 00 00 60 27 00 00 00 00 00 41 3c 21 00 00 00 00 00 5c 8d 20 00
        72245.599230	[D3]  00 00 00 00 78 9f 6a 80 00 00 00 00 00 02 00 00 00 00 00 00 f0 a1 6a 80 00
        72245.599259	[D3]  00 00 00 30 9f 6a 80 00 00 00 00 f0 9e 6a 80 00 00 00 00 d8 ff ff ff 80 ff
        72245.599288	[D3]  ff ff 3f 9f 6a 80 00 00 00 00 b8 c3 c2 83 00 00 00 00 9a 9f 6a 80 00 00 00
        72245.599317	[D3]  00 00 00 00 00 dd 01 00 00 08 02 ff ff 00 00 00 00 78 9f 6a 80 00 00 00 00
        72245.599346	[D3]  ff 01 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72245.599414	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72245.599446	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72245.599476	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72245.599504	[D3]  52 25 8a 3f 98 ea f4 45 48 49 3a c1 00 9e 6a 80 00 00 00 00 cc 63 b7 83 00
        72245.599533	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 60 27 00 00 00 00 00 02 00 00 00 00 00
        72245.599562	[D3]  00 00 00 70 27 00 00 00 00 00 41 3c 21 00 00 00 00 00 0d 00 00 00 00 00 00
        72245.599591	[D3]  00 0d 00 00 00 00 00 00 00 68 9e 6a 80 00 00 00 00 4f 1e ef 65 00 00 00 00
        72245.599620	[D3]  f9 65 6b 7b 2f e6 eb 38 00 00 00 00 00 00 00 00 98 ea f4 45 48 49 3a c1 30
        72245.599649	[D3]  9e 6a 80 00 00 00 00 9c 5f b7 83 00 00 00 00 0d 00 00 00 00 00 00 00 00 00
        72245.599678	[D3]  00 00 00 00 00 00 68 9e 6a 80 00 00 00 00 a0 9e 6a 80 00 00 00 00 80 9e 6a
        72245.599704	[D3]  80 00 00 00 00 8c 61 b0 83 00 00 00 00 5c 8d 20 00 00 00 00 00
        72245.599732	[D1] Got 9 HID objects...
        72245.599752	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.599768	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.599781	[D5] Unit = 00000000, UnitExp = 0
        72245.599793	[D5] Exponent = 0
        72245.599808	[D5] hid_lookup_path: 00840004 -> UPS
        72245.599823	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.599837	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.599850	[D5] hid_lookup_path: 00840062 -> InternalFailure
        72245.599866	[D2] Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
        72245.599884	[D5] hu_find_infoval: found !commfault (value: 0)
        72245.599897	[D5] process_boolean_info: !commfault
        72245.599924	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.599938	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.599950	[D5] Unit = 00000000, UnitExp = 0
        72245.599961	[D5] Exponent = 0
        72245.599973	[D5] hid_lookup_path: 00840004 -> UPS
        72245.599986	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600000	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600013	[D5] hid_lookup_path: 00840069 -> ShutdownImminent
        72245.600028	[D2] Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
        72245.600044	[D5] hu_find_infoval: found !shutdownimm (value: 0)
        72245.600056	[D5] process_boolean_info: !shutdownimm
        72245.600076	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600089	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.600101	[D5] Unit = 00000000, UnitExp = 0
        72245.600112	[D5] Exponent = 0
        72245.600124	[D5] hid_lookup_path: 00840004 -> UPS
        72245.600138	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600151	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600167	[D5] hid_lookup_path: 008500d0 -> ACPresent
        72245.600183	[D2] Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
        72245.600197	[D5] hu_find_infoval: found online (value: 1)
        72245.600209	[D5] process_boolean_info: online
        72245.600227	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600240	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.600252	[D5] Unit = 00000000, UnitExp = 0
        72245.600263	[D5] Exponent = 0
        72245.600275	[D5] hid_lookup_path: 00840004 -> UPS
        72245.600288	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600301	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600315	[D5] hid_lookup_path: 00850042 -> BelowRemainingCapacityLimit
        72245.600330	[D2] Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
        72245.600345	[D5] hu_find_infoval: found !lowbatt (value: 0)
        72245.600356	[D5] process_boolean_info: !lowbatt
        72245.600374	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600394	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.600407	[D5] Unit = 00000000, UnitExp = 0
        72245.600418	[D5] Exponent = 0
        72245.600430	[D5] hid_lookup_path: 00840004 -> UPS
        72245.600444	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600457	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600470	[D5] hid_lookup_path: 00850046 -> FullyCharged
        72245.600486	[D2] Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
        72245.600501	[D5] hu_find_infoval: found fullycharged (value: 1)
        72245.600513	[D5] process_boolean_info: fullycharged
        72245.600535	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600548	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.600560	[D5] Unit = 00000000, UnitExp = 0
        72245.600571	[D5] Exponent = 0
        72245.600583	[D5] hid_lookup_path: 00840004 -> UPS
        72245.600596	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600609	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600623	[D5] hid_lookup_path: 00850044 -> Charging
        72245.600637	[D2] Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
        72245.600652	[D5] hu_find_infoval: found !chrg (value: 0)
        72245.600664	[D5] process_boolean_info: !chrg
        72245.600682	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600695	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.600707	[D5] Unit = 00000000, UnitExp = 0
        72245.600718	[D5] Exponent = 0
        72245.600730	[D5] hid_lookup_path: 00840004 -> UPS
        72245.600744	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600757	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600770	[D5] hid_lookup_path: 00850045 -> Discharging
        72245.600785	[D2] Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
        72245.600800	[D5] hu_find_infoval: found !dischrg (value: 0)
        72245.600811	[D5] process_boolean_info: !dischrg
        72245.600829	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600842	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.600854	[D5] Unit = 00000000, UnitExp = 0
        72245.600865	[D5] Exponent = 0
        72245.600877	[D5] hid_lookup_path: 00840004 -> UPS
        72245.600890	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.600903	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.600917	[D5] hid_lookup_path: 00850047 -> FullyDischarged
        72245.600931	[D2] Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
        72245.600946	[D5] hu_find_infoval: found !depleted (value: 0)
        72245.600958	[D5] process_boolean_info: !depleted
        72245.600979	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.600993	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.601005	[D5] Unit = 00000000, UnitExp = 0
        72245.601017	[D5] Exponent = 0
        72245.601029	[D5] hid_lookup_path: 00840004 -> UPS
        72245.601042	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72245.601055	[D5] hid_lookup_path: 00840002 -> PresentStatus
        72245.601069	[D5] hid_lookup_path: 0085004b -> NeedReplacement
        72245.601084	[D2] Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
        72245.601099	[D5] hu_find_infoval: found !replacebatt (value: 0)
        72245.601111	[D5] process_boolean_info: !replacebatt
        72245.601129	[D1] Quick update...
        72245.601144	[D4] Entering libusb_get_report
        72245.601911	[D3] Report[get]: (3 bytes) => 61 ff ff
        72245.601975	[D5] PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
        72245.601991	[D5] Unit = 00001001, UnitExp = 0
        72245.602004	[D5] Exponent = 0
        72245.602021	[D2] Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
        72245.602051	[D4] Entering libusb_get_report
        72245.602892	[D3] Report[get]: (3 bytes) => 15 ff ff
        72245.602944	[D5] PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
        72245.602958	[D5] Unit = 00001001, UnitExp = 0
        72245.602972	[D5] Exponent = 0
        72245.602988	[D2] Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
        72245.603016	[D4] Entering libusb_get_report
        72245.603890	[D3] Report[get]: (3 bytes) => 17 ff ff
        72245.603934	[D5] PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
        72245.603948	[D5] Unit = 00001001, UnitExp = 0
        72245.603961	[D5] Exponent = 0
        72245.603978	[D2] Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
        72245.604013	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.604027	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.604040	[D5] Unit = 00000000, UnitExp = 0
        72245.604051	[D5] Exponent = 0
        72245.604067	[D2] Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
        72245.604080	[D5] hu_find_infoval: found online (value: 1)
        72245.604092	[D5] process_boolean_info: online
        72245.604111	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.604124	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.604136	[D5] Unit = 00000000, UnitExp = 0
        72245.604148	[D5] Exponent = 0
        72245.604162	[D2] Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
        72245.604175	[D5] hu_find_infoval: found !lowbatt (value: 0)
        72245.604187	[D5] process_boolean_info: !lowbatt
        72245.604205	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.604218	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.604230	[D5] Unit = 00000000, UnitExp = 0
        72245.604241	[D5] Exponent = 0
        72245.604256	[D2] Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
        72245.604268	[D5] hu_find_infoval: found fullycharged (value: 1)
        72245.604280	[D5] process_boolean_info: fullycharged
        72245.604302	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.604315	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.604327	[D5] Unit = 00000000, UnitExp = 0
        72245.604339	[D5] Exponent = 0
        72245.604353	[D2] Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
        72245.604366	[D5] hu_find_infoval: found !chrg (value: 0)
        72245.604392	[D5] process_boolean_info: !chrg
        72245.604409	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.604423	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.604435	[D5] Unit = 00000000, UnitExp = 0
        72245.604446	[D5] Exponent = 0
        72245.604460	[D2] Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
        72245.604473	[D5] hu_find_infoval: found !dischrg (value: 0)
        72245.604484	[D5] process_boolean_info: !dischrg
        72245.604502	[D3] Report[buf]: (4 bytes) => 32 00 00 09
        72245.604515	[D5] PhyMax = 0, PhyMin = 0, LogMax = 1, LogMin = 0
        72245.604527	[D5] Unit = 00000000, UnitExp = 0
        72245.604538	[D5] Exponent = 0
        72245.604552	[D2] Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
        72245.604565	[D5] hu_find_infoval: found !depleted (value: 0)
        72245.604576	[D5] process_boolean_info: !depleted
        72245.604640	[D5] send_to_all: SETINFO driver.state "quiet"
        72245.604783	[D6] send_to_all: write 29 bytes to socket 9 succeeded (ret=29): SETINFO driver.state "quiet"
        
        72247.581943	[D5] send_to_all: SETINFO driver.state "updateinfo"
        72247.582155	[D6] send_to_all: write 34 bytes to socket 9 succeeded (ret=34): SETINFO driver.state "updateinfo"
        
        72247.582177	[D1] upsdrv_updateinfo...
        72247.647068	[D2] file_report_buffer: expected 2 bytes, but got 512 instead
        72247.647148	[D3] Report[err]: (512 bytes) => 34 64 00 00 00 00 00 00 f0 9f 6a 80 00 00 00 00
        72247.647180	[D3]  00 00 00 00 00 00 00 00 98 ea f4 45 48 49 3a c1 80 a0 6a 80 ff ff ff ff 40
        72247.647210	[D3]  9e 6a 80 00 00 00 00 14 b1 b6 83 00 00 00 00 51 1e ef 65 00 00 00 00 00 50
        72247.647239	[D3]  27 00 00 00 00 00 00 00 00 00 00 00 00 00 00 60 27 00 00 00 00 00 02 00 00
        72247.647268	[D3]  00 00 00 00 00 00 60 27 00 00 00 00 00 41 3c 21 00 00 00 00 00 5c 8d 20 00
        72247.647297	[D3]  00 00 00 00 78 9f 6a 80 00 00 00 00 00 02 00 00 00 00 00 00 f0 a1 6a 80 00
        72247.647326	[D3]  00 00 00 30 9f 6a 80 00 00 00 00 f0 9e 6a 80 00 00 00 00 d8 ff ff ff 80 ff
        72247.647355	[D3]  ff ff 3f 9f 6a 80 00 00 00 00 b8 c3 c2 83 00 00 00 00 9a 9f 6a 80 00 00 00
        72247.647388	[D3]  00 00 00 00 00 dd 01 00 00 08 02 ff ff 00 00 00 00 78 9f 6a 80 00 00 00 00
        72247.647418	[D3]  ff 01 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72247.647448	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72247.647477	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72247.647506	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
        72247.647534	[D3]  3f 78 09 41 98 ea f4 45 48 49 3a c1 00 9e 6a 80 00 00 00 00 cc 63 b7 83 00
        72247.647564	[D3]  00 00 00 00 00 00 00 00 00 00 00 00 60 27 00 00 00 00 00 02 00 00 00 00 00
        72247.647593	[D3]  00 00 00 70 27 00 00 00 00 00 41 3c 21 00 00 00 00 00 0d 00 00 00 00 00 00
        72247.647622	[D3]  00 0d 00 00 00 00 00 00 00 68 9e 6a 80 00 00 00 00 51 1e ef 65 00 00 00 00
        72247.647653	[D3]  93 e8 dc 78 a4 e7 69 3b 00 00 00 00 00 00 00 00 98 ea f4 45 48 49 3a c1 30
        72247.647682	[D3]  9e 6a 80 00 00 00 00 9c 5f b7 83 00 00 00 00 0d 00 00 00 00 00 00 00 00 00
        72247.647710	[D3]  00 00 00 00 00 00 68 9e 6a 80 00 00 00 00 a0 9e 6a 80 00 00 00 00 80 9e 6a
        72247.647737	[D3]  80 00 00 00 00 8c 61 b0 83 00 00 00 00 5c 8d 20 00 00 00 00 00
        72247.647764	[D1] Got 1 HID objects...
        72247.647781	[D3] Report[buf]: (2 bytes) => 34 64
        72247.647797	[D5] PhyMax = 0, PhyMin = 0, LogMax = 255, LogMin = 0
        72247.647810	[D5] Unit = 00000000, UnitExp = 0
        72247.647822	[D5] Exponent = 0
        72247.647837	[D5] hid_lookup_path: 00840004 -> UPS
        72247.647852	[D5] hid_lookup_path: 00840024 -> PowerSummary
        72247.647867	[D5] hid_lookup_path: 00850066 -> RemainingCapacity
        72247.647884	[D2] Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
        72247.647919	[D1] Quick update...
        72247.647935	[D4] Entering libusb_get_report
        72247.648925	[D3] Report[get]: (3 bytes) => 61 ff ff
        72247.648983	[D5] PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
        72247.649032	[D5] Unit = 00001001, UnitExp = 0
        72247.649047	[D5] Exponent = 0
        72247.649064	[D2] Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
        72247.649095	[D4] Entering libusb_get_report
        72247.649932	[D3] Report[get]: (3 bytes) => 15 ff ff
        72247.649995	[D5] PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
        72247.650010	[D5] Unit = 00001001, UnitExp = 0
        72247.650023	[D5] Exponent = 0
        72247.650041	[D2] Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
        72247.650072	[D4] Entering libusb_get_report
        72247.727371	nut_libusb_get_report: No device
        72247.727469	[D1] Can't retrieve Report 17: Interrupted system call
        72247.727532	[D5] send_to_all: SETINFO driver.state "reconnect.trying"
        72247.727733	[D6] send_to_all: write 40 bytes to socket 9 succeeded (ret=40): SETINFO driver.state "reconnect.trying"
        
        72247.727777	[D5] send_to_all: SETINFO driver.state "quiet"
        72247.727879	[D6] send_to_all: write 29 bytes to socket 9 succeeded (ret=29): SETINFO driver.state "quiet"
        
        72249.583257	[D5] send_to_all: SETINFO driver.state "updateinfo"
        72249.583466	[D6] send_to_all: write 34 bytes to socket 9 succeeded (ret=34): SETINFO driver.state "updateinfo"
        
        72249.583501	[D1] upsdrv_updateinfo...
        72249.583516	[D1] Got to reconnect!
        72249.583543	[D5] send_to_all: SETINFO driver.state "reconnect.trying"
        72249.583569	[D6] send_to_all: write 40 bytes to socket 9 succeeded (ret=40): SETINFO driver.state "reconnect.trying"
        
        72249.583596	[D4] Closing comm_driver previous handle
        72249.586916	[D4] ===================================================================
        72249.586973	[D4]  device has been disconnected, try to reconnect
        72249.586987	[D4] ===================================================================
        72249.586999	[D4] Opening comm_driver ...
        72249.587552	[D2] Checking device 1 of 3 (0000/0000)
        72249.587798	[D1] nut_libusb_open: invalid libusb bus number 0
        72249.587882	[D2] - VendorID: 0000
        72249.587897	[D2] - ProductID: 0000
        72249.587910	[D2] - Manufacturer: Generic
        72249.587922	[D2] - Product: XHCI root HUB
        72249.587934	[D2] - Serial Number: unknown
        72249.587946	[D2] - Bus: 000
        72249.587957	[D2] - Bus Port: unknown
        72249.587968	[D2] - Device: 001
        72249.587980	[D2] - Device release number: 0100
        72249.587991	[D2] Trying to match device
        72249.588013	[D2] match_function_subdriver (non-SHUT mode): matching a device...
        72249.588048	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
        72249.588062	[D2] Device does not match - skipping
        72249.588150	[D2] Checking device 2 of 3 (0000/0000)
        72249.588301	[D1] nut_libusb_open: invalid libusb bus number 0
        72249.588361	[D2] - VendorID: 0000
        72249.588384	[D2] - ProductID: 0000
        72249.588397	[D2] - Manufacturer: Marvell
        72249.588409	[D2] - Product: EHCI root HUB
        72249.588421	[D2] - Serial Number: unknown
        72249.588432	[D2] - Bus: 001
        72249.588443	[D2] - Bus Port: unknown
        72249.588454	[D2] - Device: 001
        72249.588466	[D2] - Device release number: 0100
        72249.588477	[D2] Trying to match device
        72249.588496	[D2] match_function_subdriver (non-SHUT mode): matching a device...
        72249.588525	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
        72249.588539	[D2] Device does not match - skipping
        72249.588619	[D2] Checking device 3 of 3 (09AE/3024)
        72249.743398	[D1] nut_libusb_open get iManufacturer failed, retrying...
        72249.893627	[D1] nut_libusb_open get iManufacturer failed, retrying...
        72250.048371	[D1] nut_libusb_open get iManufacturer failed, retrying...
        72250.198508	[D1] nut_libusb_open get iProduct failed, retrying...
        72250.347839	[D1] nut_libusb_open get iProduct failed, retrying...
        72250.499443	[D1] nut_libusb_open get iProduct failed, retrying...
        72250.649305	[D1] nut_libusb_open get iSerialNumber failed, retrying...
        72250.803444	[D1] nut_libusb_open get iSerialNumber failed, retrying...
        72250.955470	[D1] nut_libusb_open get iSerialNumber failed, retrying...
        72250.955570	[D2] - VendorID: 09ae
        72250.955585	[D2] - ProductID: 3024
        72250.955597	[D2] - Manufacturer: unknown
        72250.955609	[D2] - Product: unknown
        72250.955621	[D2] - Serial Number: unknown
        72250.955633	[D2] - Bus: 001
        72250.955644	[D2] - Bus Port: 001
        72250.955655	[D2] - Device: 002
        72250.955667	[D2] - Device release number: 0002
        72250.955679	[D2] Trying to match device
        72250.955704	[D2] match_function_subdriver (non-SHUT mode): matching a device...
        72250.955744	[D3] match_function_regex: matching a device...
        72250.955766	[D3] match_function_exact: matching a device...
        72250.955782	[D2] match_function_exact: failed match of Vendor: (null) != Tripp Lite
        72250.955795	[D2] Device does not match - skipping
        72250.955954	[D2] libusb1: No appropriate HID device found
        72250.955978	libusb1: Could not open any HID devices: insufficient permissions on everything
        72250.955994	[D4] Opening comm_driver returns ret=-1
        72250.956021	[D5] send_to_all: SETINFO driver.state "quiet"
        72250.956052	[D6] send_to_all: write 29 bytes to socket 9 succeeded (ret=29): SETINFO driver.state "quiet"
        
        72250.956067	[D5] send_to_all: DATASTALE
        72250.956086	[D6] send_to_all: write 10 bytes to socket 9 succeeded (ret=10): DATASTALE
        
        72251.588983	[D5] send_to_all: SETINFO driver.state "updateinfo"
        72251.589141	[D6] send_to_all: write 34 bytes to socket 9 succeeded (ret=34): SETINFO driver.state "updateinfo"
        
        72251.589165	[D1] upsdrv_updateinfo...
        72251.589179	[D1] Got to reconnect!
        72251.589201	[D5] send_to_all: SETINFO driver.state "reconnect.trying"
        72251.589225	[D6] send_to_all: write 40 bytes to socket 9 succeeded (ret=40): SETINFO driver.state "reconnect.trying"
        
        72251.589247	[D4] Not closing comm_driver previous handle: already closed
        72251.589260	[D4] ===================================================================
        72251.589272	[D4]  device has been disconnected, try to reconnect
        72251.589284	[D4] ===================================================================
        72251.589296	[D4] Opening comm_driver ...
        72251.589870	[D2] Checking device 1 of 3 (0000/0000)
        72251.590057	[D1] nut_libusb_open: invalid libusb bus number 0
        72251.590139	[D2] - VendorID: 0000
        72251.590154	[D2] - ProductID: 0000
        72251.590166	[D2] - Manufacturer: Generic
        72251.590178	[D2] - Product: XHCI root HUB
        72251.590190	[D2] - Serial Number: unknown
        72251.590203	[D2] - Bus: 000
        72251.590214	[D2] - Bus Port: unknown
        72251.590226	[D2] - Device: 001
        72251.590237	[D2] - Device release number: 0100
        72251.590249	[D2] Trying to match device
        72251.590271	[D2] match_function_subdriver (non-SHUT mode): matching a device...
        72251.590307	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
        72251.590322	[D2] Device does not match - skipping
        72251.590444	[D2] Checking device 2 of 3 (0000/0000)
        72251.590658	[D1] nut_libusb_open: invalid libusb bus number 0
        72251.590755	[D2] - VendorID: 0000
        72251.590771	[D2] - ProductID: 0000
        72251.590785	[D2] - Manufacturer: Marvell
        72251.590797	[D2] - Product: EHCI root HUB
        72251.590809	[D2] - Serial Number: unknown
        72251.590821	[D2] - Bus: 001
        72251.590832	[D2] - Bus Port: unknown
        72251.590843	[D2] - Device: 001
        72251.590855	[D2] - Device release number: 0100
        72251.590867	[D2] Trying to match device
        72251.590886	[D2] match_function_subdriver (non-SHUT mode): matching a device...
        72251.590918	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
        72251.590932	[D2] Device does not match - skipping
        72251.591030	[D2] Checking device 3 of 3 (09AE/3024)
        72251.745371	[D1] nut_libusb_open get iManufacturer failed, retrying...
        72251.895872	[D1] nut_libusb_open get iManufacturer failed, retrying...
        72252.050367	[D1] nut_libusb_open get iManufacturer failed, retrying...
        72252.205384	[D1] nut_libusb_open get iProduct failed, retrying...
        72252.359364	[D1] nut_libusb_open get iProduct failed, retrying...
        72252.513419	[D1] nut_libusb_open get iProduct failed, retrying...
        72252.667482	[D1] nut_libusb_open get iSerialNumber failed, retrying...
        72252.820954	[D1] nut_libusb_open get iSerialNumber failed, retrying...
        72252.971389	[D1] nut_libusb_open get iSerialNumber failed, retrying...
        72252.971473	[D2] - VendorID: 09ae
        72252.971489	[D2] - ProductID: 3024
        72252.971501	[D2] - Manufacturer: unknown
        72252.971516	[D2] - Product: unknown
        72252.971528	[D2] - Serial Number: unknown
        72252.971540	[D2] - Bus: 001
        72252.971551	[D2] - Bus Port: 001
        72252.971563	[D2] - Device: 002
        72252.971574	[D2] - Device release number: 0002
        72252.971586	[D2] Trying to match device
        72252.971609	[D2] match_function_subdriver (non-SHUT mode): matching a device...
        72252.971645	[D3] match_function_regex: matching a device...
        72252.971663	[D3] match_function_exact: matching a device...
        72252.971678	[D2] match_function_exact: failed match of Vendor: (null) != Tripp Lite
        72252.971690	[D2] Device does not match - skipping
        72252.971846	[D2] libusb1: No appropriate HID device found
        72252.971869	libusb1: Could not open any HID devices: insufficient permissions on everything
        72252.971885	[D4] Opening comm_driver returns ret=-1
        72252.971912	[D5] send_to_all: SETINFO driver.state "quiet"
        72252.972008	[D6] send_to_all: write 29 bytes to socket 9 succeeded (ret=29): SETINFO driver.state "quiet"
        
        dennypageD 1 Reply Last reply Reply Quote 0
        • G
          ghound @dennypage
          last edited by

          @dennypage said in NUT Package (2.8.1 and above):

          Can you run the driver by hand in debug mode via ssh please?

          First start the service, and then kill the driver:

          killall usbhid-ups
          Then, run the driver with debug:

          /usr/local/libexec/nut/usbhid-ups -DDDDDD -a TrippLite

          FYI - this is the output when I tried to manually restart the driver after connection was lost:

             0.002954	[D2] Initializing an USB-connected UPS with library libusb-1.0.0 (API: 0x1000102) (NUT subdriver name='USB communication driver (libusb 1.0)' ver='0.46')
             0.003874	[D2] Checking device 1 of 3 (0000/0000)
             0.004670	[D1] nut_libusb_open: invalid libusb bus number 0
             0.004804	[D2] - VendorID: 0000
             0.004821	[D2] - ProductID: 0000
             0.004833	[D2] - Manufacturer: Generic
             0.004845	[D2] - Product: XHCI root HUB
             0.004856	[D2] - Serial Number: unknown
             0.004868	[D2] - Bus: 000
             0.004878	[D2] - Bus Port: unknown
             0.004889	[D2] - Device: 001
             0.004901	[D2] - Device release number: 0100
             0.004912	[D2] Trying to match device
             0.004934	[D2] match_function_subdriver (non-SHUT mode): matching a device...
             0.004978	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
             0.004991	[D2] Device does not match - skipping
             0.005115	[D2] Checking device 2 of 3 (0000/0000)
             0.005340	[D1] nut_libusb_open: invalid libusb bus number 0
             0.005432	[D2] - VendorID: 0000
             0.005447	[D2] - ProductID: 0000
             0.005458	[D2] - Manufacturer: Marvell
             0.005470	[D2] - Product: EHCI root HUB
             0.005481	[D2] - Serial Number: unknown
             0.005492	[D2] - Bus: 001
             0.005502	[D2] - Bus Port: unknown
             0.005513	[D2] - Device: 001
             0.005525	[D2] - Device release number: 0100
             0.005535	[D2] Trying to match device
             0.005554	[D2] match_function_subdriver (non-SHUT mode): matching a device...
             0.005596	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
             0.005610	[D2] Device does not match - skipping
             0.005713	[D2] Checking device 3 of 3 (09AE/3024)
             0.156567	[D1] nut_libusb_open get iManufacturer failed, retrying...
             0.310568	[D1] nut_libusb_open get iManufacturer failed, retrying...
             0.461572	[D1] nut_libusb_open get iManufacturer failed, retrying...
             0.608445	[D1] nut_libusb_open get iProduct failed, retrying...
             0.762543	[D1] nut_libusb_open get iProduct failed, retrying...
             0.912962	[D1] nut_libusb_open get iProduct failed, retrying...
             1.066550	[D1] nut_libusb_open get iSerialNumber failed, retrying...
             1.218542	[D1] nut_libusb_open get iSerialNumber failed, retrying...
             1.369116	[D1] nut_libusb_open get iSerialNumber failed, retrying...
             1.369185	[D2] - VendorID: 09ae
             1.369200	[D2] - ProductID: 3024
             1.369214	[D2] - Manufacturer: unknown
             1.369226	[D2] - Product: unknown
             1.369238	[D2] - Serial Number: unknown
             1.369249	[D2] - Bus: 001
             1.369261	[D2] - Bus Port: 001
             1.369273	[D2] - Device: 002
             1.369285	[D2] - Device release number: 0002
             1.369296	[D2] Trying to match device
             1.369319	[D2] match_function_subdriver (non-SHUT mode): matching a device...
             1.369424	[D3] match_function_regex: matching a device...
             1.369447	[D2] Device matches
             1.369460	[D2] Reading configuration descriptor 1 of 1
             1.369848	[D3] libusb_kernel_driver_active() returned 0: Success
             1.369919	[D2] Claimed interface 0 successfully
             1.369944	[D3] nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
             1.446624	[D2] Unable to get HID descriptor (No device)
             1.446696	[D3] HID descriptor length (method 1) -1
             1.446713	[D4] i=0, extra[i]=09, extra[i+1]=21
             1.446736	[D3] HID descriptor, method 2: (9 bytes) => 09 21 11 01 21 01 22 75 03
             1.446775	[D3] HID descriptor length (method 2) 885
             1.446789	[D2] HID descriptor length 885
             1.523598	[D2] Unable to get Report descriptor: Input/output error
             1.523845	[D2] libusb1: No appropriate HID device found
             1.524098	libusb1: Could not open any HID devices: insufficient permissions on everything
             1.524142	No matching HID UPS found
             1.524226	[D5] send_to_all: SETINFO driver.state "cleanup.exit"
             1.524248	upsnotify: failed to notify about state 4: no notification tech defined, will not spam more about it
          

          And this was the initial good manual startup:

          0.002990	[D2] Initializing an USB-connected UPS with library libusb-1.0.0 (API: 0x1000102) (NUT subdriver name='USB communication driver (libusb 1.0)' ver='0.46')
             0.003801	[D2] Checking device 1 of 3 (0000/0000)
             0.004569	[D1] nut_libusb_open: invalid libusb bus number 0
             0.004704	[D2] - VendorID: 0000
             0.004723	[D2] - ProductID: 0000
             0.004734	[D2] - Manufacturer: Generic
             0.004745	[D2] - Product: XHCI root HUB
             0.004757	[D2] - Serial Number: unknown
             0.004768	[D2] - Bus: 000
             0.004778	[D2] - Bus Port: unknown
             0.004789	[D2] - Device: 001
             0.004800	[D2] - Device release number: 0100
             0.004810	[D2] Trying to match device
             0.004832	[D2] match_function_subdriver (non-SHUT mode): matching a device...
             0.004876	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
             0.004888	[D2] Device does not match - skipping
             0.005006	[D2] Checking device 2 of 3 (0000/0000)
             0.005231	[D1] nut_libusb_open: invalid libusb bus number 0
             0.005323	[D2] - VendorID: 0000
             0.005337	[D2] - ProductID: 0000
             0.005349	[D2] - Manufacturer: Marvell
             0.005360	[D2] - Product: EHCI root HUB
             0.005371	[D2] - Serial Number: unknown
             0.005381	[D2] - Bus: 001
             0.005391	[D2] - Bus Port: unknown
             0.005402	[D2] - Device: 001
             0.005412	[D2] - Device release number: 0100
             0.005422	[D2] Trying to match device
             0.005442	[D2] match_function_subdriver (non-SHUT mode): matching a device...
             0.005476	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
             0.005489	[D2] Device does not match - skipping
             0.005585	[D2] Checking device 3 of 3 (09AE/3024)
             0.018725	[D2] - VendorID: 09ae
             0.018775	[D2] - ProductID: 3024
             0.018789	[D2] - Manufacturer: Tripp Lite
             0.018800	[D2] - Product: ECO850LCD       
             0.018811	[D2] - Serial Number: 3216CV4BC87F303175
             0.018822	[D2] - Bus: 001
             0.018832	[D2] - Bus Port: 001
             0.018843	[D2] - Device: 002
             0.018853	[D2] - Device release number: 0002
             0.018864	[D2] Trying to match device
             0.018884	[D2] match_function_subdriver (non-SHUT mode): matching a device...
             0.018983	[D3] match_function_regex: matching a device...
             0.019006	[D2] Device matches
          
          1 Reply Last reply Reply Quote 0
          • G
            ghound @dennypage
            last edited by

            @dennypage said in NUT Package (2.8.1 and above):

            First start the service, and then kill the driver:

            killall usbhid-ups
            Then, run the driver with debug:

            /usr/local/libexec/nut/usbhid-ups -DDDDDD -a TrippLite

            Here is system log after disconnecting / reconnecting USB cable:

            Mar 11 11:40:04	upsmon	8414	Poll UPS [TrippLite] failed - Driver not connected
            Mar 11 11:40:01	kernel		 uhid0: <Tripp Lite ECO850LCD, class 0/0, rev 2.00/0.02, addr 2> on usbus1
            Mar 11 11:40:01	kernel		uhid0 on uhub1
            Mar 11 11:40:01	kernel		ugen1.2: <Tripp Lite ECO850LCD> at usbus1
            Mar 11 11:39:59	upsmon	8414	Poll UPS [TrippLite] failed - Driver not connected
            Mar 11 11:39:54	upsmon	8414	Poll UPS [TrippLite] failed - Driver not connected
            Mar 11 11:39:49	upsmon	8414	Poll UPS [TrippLite] failed - Driver not connected
            Mar 11 11:39:48	kernel		ugen1.2: <Tripp Lite ECO850LCD> at usbus1 (disconnected)
            Mar 11 11:39:44	upsmon	8414	Poll UPS [TrippLite] failed - Driver not connected
            

            After disconnecting / reconnecting USB cable and manual driver start, UPS is available again:

               0.002865	[D2] Initializing an USB-connected UPS with library libusb-1.0.0 (API: 0x1000102) (NUT subdriver name='USB communication driver (libusb 1.0)' ver='0.46')
               0.003797	[D2] Checking device 1 of 3 (0000/0000)
               0.004739	[D1] nut_libusb_open: invalid libusb bus number 0
               0.004878	[D2] - VendorID: 0000
               0.004897	[D2] - ProductID: 0000
               0.004909	[D2] - Manufacturer: Generic
               0.004920	[D2] - Product: XHCI root HUB
               0.004932	[D2] - Serial Number: unknown
               0.004943	[D2] - Bus: 000
               0.004953	[D2] - Bus Port: unknown
               0.004963	[D2] - Device: 001
               0.004974	[D2] - Device release number: 0100
               0.004985	[D2] Trying to match device
               0.005008	[D2] match_function_subdriver (non-SHUT mode): matching a device...
               0.005052	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
               0.005065	[D2] Device does not match - skipping
               0.005194	[D2] Checking device 2 of 3 (0000/0000)
               0.005421	[D1] nut_libusb_open: invalid libusb bus number 0
               0.005517	[D2] - VendorID: 0000
               0.005532	[D2] - ProductID: 0000
               0.005543	[D2] - Manufacturer: Marvell
               0.005554	[D2] - Product: EHCI root HUB
               0.005565	[D2] - Serial Number: unknown
               0.005576	[D2] - Bus: 001
               0.005586	[D2] - Bus Port: unknown
               0.005596	[D2] - Device: 001
               0.005607	[D2] - Device release number: 0100
               0.005617	[D2] Trying to match device
               0.005637	[D2] match_function_subdriver (non-SHUT mode): matching a device...
               0.005669	[D2] match_function_subdriver (non-SHUT mode): failed to match a subdriver to vendor and/or product ID
               0.005682	[D2] Device does not match - skipping
               0.005775	[D2] Checking device 3 of 3 (09AE/3024)
               0.018671	[D2] - VendorID: 09ae
               0.018723	[D2] - ProductID: 3024
               0.018736	[D2] - Manufacturer: Tripp Lite
               0.018748	[D2] - Product: ECO850LCD       
               0.018762	[D2] - Serial Number: 3216CV4BC87F303175
               0.018774	[D2] - Bus: 001
               0.018784	[D2] - Bus Port: 001
               0.018794	[D2] - Device: 002
               0.018805	[D2] - Device release number: 0002
               0.018816	[D2] Trying to match device
               0.018843	[D2] match_function_subdriver (non-SHUT mode): matching a device...
               0.018946	[D3] match_function_regex: matching a device...
               0.018967	[D2] Device matches
            
            1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage @ghound
              last edited by

              @ghound said in NUT Package (2.8.1 and above):

              72251.591030 [D2] Checking device 3 of 3 (09AE/3024)
              72251.745371 [D1] nut_libusb_open get iManufacturer failed, retrying...
              72251.895872 [D1] nut_libusb_open get iManufacturer failed, retrying...
              72252.050367 [D1] nut_libusb_open get iManufacturer failed, retrying...
              72252.205384 [D1] nut_libusb_open get iProduct failed, retrying...
              72252.359364 [D1] nut_libusb_open get iProduct failed, retrying...
              72252.513419 [D1] nut_libusb_open get iProduct failed, retrying...
              72252.667482 [D1] nut_libusb_open get iSerialNumber failed, retrying...
              72252.820954 [D1] nut_libusb_open get iSerialNumber failed, retrying...
              72252.971389 [D1] nut_libusb_open get iSerialNumber failed, retrying...
              72252.971473 [D2] - VendorID: 09ae
              72252.971489 [D2] - ProductID: 3024
              72252.971501 [D2] - Manufacturer: unknown
              72252.971516 [D2] - Product: unknown
              72252.971528 [D2] - Serial Number: unknown
              72252.971540 [D2] - Bus: 001
              72252.971551 [D2] - Bus Port: 001
              72252.971563 [D2] - Device: 002
              72252.971574 [D2] - Device release number: 0002
              72252.971586 [D2] Trying to match device
              72252.971609 [D2] match_function_subdriver (non-SHUT mode): matching a device...
              72252.971645 [D3] match_function_regex: matching a device...
              72252.971663 [D3] match_function_exact: matching a device...
              72252.971678 [D2] match_function_exact: failed match of Vendor: (null) != Tripp Lite
              72252.971690 [D2] Device does not match - skipping

              @ghound said in NUT Package (2.8.1 and above):

              0.005713 [D2] Checking device 3 of 3 (09AE/3024)
              0.156567 [D1] nut_libusb_open get iManufacturer failed, retrying...
              0.310568 [D1] nut_libusb_open get iManufacturer failed, retrying...
              0.461572 [D1] nut_libusb_open get iManufacturer failed, retrying...
              0.608445 [D1] nut_libusb_open get iProduct failed, retrying...
              0.762543 [D1] nut_libusb_open get iProduct failed, retrying...
              0.912962 [D1] nut_libusb_open get iProduct failed, retrying...
              1.066550 [D1] nut_libusb_open get iSerialNumber failed, retrying...
              1.218542 [D1] nut_libusb_open get iSerialNumber failed, retrying...
              1.369116 [D1] nut_libusb_open get iSerialNumber failed, retrying...
              1.369185 [D2] - VendorID: 09ae
              1.369200 [D2] - ProductID: 3024
              1.369214 [D2] - Manufacturer: unknown
              1.369226 [D2] - Product: unknown
              1.369238 [D2] - Serial Number: unknown
              1.369249 [D2] - Bus: 001
              1.369261 [D2] - Bus Port: 001
              1.369273 [D2] - Device: 002
              1.369285 [D2] - Device release number: 0002

              For some reason we are loosing the ability to query device manufacturer and product. That it is persistent indicates that there is a problem in the kernel's USB drivers or the hardware itself. Unfortunately this is well outside of NUT's control.

              Looking at your usbconfig output, the one thing I would recommend is to try a different USB port on the host. Something that connects to bus0 (generic XHCI) rather than bus1 (Marvell EHCI).

              G 1 Reply Last reply Reply Quote 0
              • G
                ghound @dennypage
                last edited by

                @dennypage said in NUT Package (2.8.1 and above):

                For some reason we are loosing the ability to query device manufacturer and product. That it is persistent indicates that there is a problem in the kernel's USB drivers or the hardware itself. Unfortunately this is well outside of NUT's control.

                Looking at your usbconfig output, the one thing I would recommend is to try a different USB port on the host. Something that connects to bus0 (generic XHCI) rather than bus1 (Marvell EHCI).

                Thank you for looking at all the logs. This is a Netgate SG1100 box, so I connected to the USB3 port at ugen0.1: <Generic XHCI root HUB> at usbus0 – Bus:000 Bus Port: 002; vice my original connection to the USB2 port at ugen1.1: <Marvell EHCI root HUB> at usbus1 – Bus:001 Bus Port: 001. Again, connection was lost after around one day of operation. I do have another SG1100 I can try. Any other troubleshooting ideas? Thank you.

                Log USB3 port connection:

                   0.007864	[D2] Checking device 3 of 3 (09AE/3024)
                   0.010883	[D2] - VendorID: 09ae
                   0.010949	[D2] - ProductID: 3024
                   0.010964	[D2] - Manufacturer: Tripp Lite
                   0.010976	[D2] - Product: ECO850LCD       
                   0.010987	[D2] - Serial Number: 3216CV4BC87F303175
                   0.010998	[D2] - Bus: 000
                   0.011009	[D2] - Bus Port: 002
                   0.011019	[D2] - Device: 002
                   0.011030	[D2] - Device release number: 0002
                   0.011041	[D2] Trying to match device
                   0.011062	[D2] match_function_subdriver (non-SHUT mode): matching a device...
                   0.011164	[D3] match_function_regex: matching a device...
                   0.011185	[D2] Device matches
                
                
                dennypageD 1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage @ghound
                  last edited by

                  @ghound said in NUT Package (2.8.1 and above):

                  0.007864 [D2] Checking device 3 of 3 (09AE/3024)
                  0.010883 [D2] - VendorID: 09ae
                  0.010949 [D2] - ProductID: 3024
                  0.010964 [D2] - Manufacturer: Tripp Lite
                  0.010976 [D2] - Product: ECO850LCD
                  0.010987 [D2] - Serial Number: 3216CV4BC87F303175
                  0.010998 [D2] - Bus: 000
                  0.011009 [D2] - Bus Port: 002
                  0.011019 [D2] - Device: 002
                  0.011030 [D2] - Device release number: 0002

                  This looks correct (working). Manufacturer and Product are identifiable. If this subsequently fails, to confirm that the issue is the same as experienced on the other port, I would need to see what the driver says when it isn't working. Also interested to see the output of "usbconfig -v" when it isn't working.

                  G 1 Reply Last reply Reply Quote 0
                  • G
                    ghound @dennypage
                    last edited by

                    @dennypage said in NUT Package (2.8.1 and above):

                    This looks correct (working). Manufacturer and Product are identifiable. If this subsequently fails, to confirm that the issue is the same as experienced on the other port, I would need to see what the driver says when it isn't working. Also interested to see the output of "usbconfig -v" when it isn't working.

                    Below is result of usbconfig -v when the connection is not working (on USB3 port):

                    [23.09.1-RELEASE][admin@router01.localr01]/dev/usb: usbconfig -v
                    ugen0.1: <Generic XHCI root HUB> at usbus0, cfg=0 md=HOST spd=SUPER (5.0Gbps) pwr=SAVE (0mA)
                    ugen0.1.0: uhub0: <Generic XHCI root HUB, class 9/0, rev 3.00/1.00, addr 1>
                    
                      bLength = 0x0012
                      bDescriptorType = 0x0001
                      bcdUSB = 0x0300
                      bDeviceClass = 0x0009  <HUB>
                      bDeviceSubClass = 0x0000
                      bDeviceProtocol = 0x0003
                      bMaxPacketSize0 = 0x0009
                      idVendor = 0x0000
                      idProduct = 0x0000
                      bcdDevice = 0x0100
                      iManufacturer = 0x0001  <Generic>
                      iProduct = 0x0002  <XHCI root HUB>
                      iSerialNumber = 0x0000  <no string>
                      bNumConfigurations = 0x0001
                    
                    
                     Configuration index 0
                    
                        bLength = 0x0009
                        bDescriptorType = 0x0002
                        wTotalLength = 0x001f
                        bNumInterfaces = 0x0001
                        bConfigurationValue = 0x0001
                        iConfiguration = 0x0000  <no string>
                        bmAttributes = 0x0040
                        bMaxPower = 0x0000
                    
                        Interface 0
                          bLength = 0x0009
                          bDescriptorType = 0x0004
                          bInterfaceNumber = 0x0000
                          bAlternateSetting = 0x0000
                          bNumEndpoints = 0x0001
                          bInterfaceClass = 0x0009  <HUB>
                          bInterfaceSubClass = 0x0000
                          bInterfaceProtocol = 0x0000
                          iInterface = 0x0000  <no string>
                    
                         Endpoint 0
                            bLength = 0x0007
                            bDescriptorType = 0x0005
                            bEndpointAddress = 0x0081  <IN>
                            bmAttributes = 0x0003  <INTERRUPT>
                            wMaxPacketSize = 0x0002
                            bInterval = 0x00ff
                            bRefresh = 0x0000
                            bSynchAddress = 0x0000
                    
                          Additional Descriptor
                    
                          bLength = 0x06
                          bDescriptorType = 0x30
                          bDescriptorSubType = 0x00
                           RAW dump:
                           0x00 | 0x06, 0x30, 0x00, 0x00, 0x00, 0x00
                    
                    
                    
                    
                    ugen1.1: <Marvell EHCI root HUB> at usbus1, cfg=0 md=HOST spd=HIGH (480Mbps) pwr=SAVE (0mA)
                    ugen1.1.0: uhub1: <Marvell EHCI root HUB, class 9/0, rev 2.00/1.00, addr 1>
                    
                      bLength = 0x0012
                      bDescriptorType = 0x0001
                      bcdUSB = 0x0200
                      bDeviceClass = 0x0009  <HUB>
                      bDeviceSubClass = 0x0000
                      bDeviceProtocol = 0x0001
                      bMaxPacketSize0 = 0x0040
                      idVendor = 0x0000
                      idProduct = 0x0000
                      bcdDevice = 0x0100
                      iManufacturer = 0x0001  <Marvell>
                      iProduct = 0x0002  <EHCI root HUB>
                      iSerialNumber = 0x0000  <no string>
                      bNumConfigurations = 0x0001
                    
                    
                     Configuration index 0
                    
                        bLength = 0x0009
                        bDescriptorType = 0x0002
                        wTotalLength = 0x0019
                        bNumInterfaces = 0x0001
                        bConfigurationValue = 0x0001
                        iConfiguration = 0x0000  <no string>
                        bmAttributes = 0x0040
                        bMaxPower = 0x0000
                    
                        Interface 0
                          bLength = 0x0009
                          bDescriptorType = 0x0004
                          bInterfaceNumber = 0x0000
                          bAlternateSetting = 0x0000
                          bNumEndpoints = 0x0001
                          bInterfaceClass = 0x0009  <HUB>
                          bInterfaceSubClass = 0x0000
                          bInterfaceProtocol = 0x0000
                          iInterface = 0x0000  <no string>
                    
                         Endpoint 0
                            bLength = 0x0007
                            bDescriptorType = 0x0005
                            bEndpointAddress = 0x0081  <IN>
                            bmAttributes = 0x0003  <INTERRUPT>
                            wMaxPacketSize = 0x0008
                            bInterval = 0x00ff
                            bRefresh = 0x0000
                            bSynchAddress = 0x0000
                    
                    
                    
                    ugen0.2: <Tripp Lite ECO850LCD> at usbus0, cfg=0 md=HOST spd=FULL (12Mbps) pwr=ON (100mA)
                    
                      bLength = 0x0012
                      bDescriptorType = 0x0001
                      bcdUSB = 0x0200
                      bDeviceClass = 0x0000  <Probed by interface class>
                      bDeviceSubClass = 0x0000
                      bDeviceProtocol = 0x0000
                      bMaxPacketSize0 = 0x0040
                      idVendor = 0x09ae
                      idProduct = 0x3024
                      bcdDevice = 0x0002
                      iManufacturer = 0x0003  <retrieving string failed>
                      iProduct = 0x0001  <retrieving string failed>
                      iSerialNumber = 0x0005  <retrieving string failed>
                      bNumConfigurations = 0x0001
                    
                    
                     Configuration index 0
                    
                        bLength = 0x0009
                        bDescriptorType = 0x0002
                        wTotalLength = 0x0022
                        bNumInterfaces = 0x0001
                        bConfigurationValue = 0x0001
                        iConfiguration = 0x0000  <no string>
                        bmAttributes = 0x00a0
                        bMaxPower = 0x0032
                    
                        Interface 0
                          bLength = 0x0009
                          bDescriptorType = 0x0004
                          bInterfaceNumber = 0x0000
                          bAlternateSetting = 0x0000
                          bNumEndpoints = 0x0001
                          bInterfaceClass = 0x0003  <HID device>
                          bInterfaceSubClass = 0x0000
                          bInterfaceProtocol = 0x0000
                          iInterface = 0x0000  <no string>
                    
                          Additional Descriptor
                    
                          bLength = 0x09
                          bDescriptorType = 0x21
                          bDescriptorSubType = 0x11
                           RAW dump:
                           0x00 | 0x09, 0x21, 0x11, 0x01, 0x21, 0x01, 0x22, 0x75,
                           0x08 | 0x03
                    
                         Endpoint 0
                            bLength = 0x0007
                            bDescriptorType = 0x0005
                            bEndpointAddress = 0x0081  <IN>
                            bmAttributes = 0x0003  <INTERRUPT>
                            wMaxPacketSize = 0x0040
                            bInterval = 0x00ff
                            bRefresh = 0x0000
                            bSynchAddress = 0x0000
                    
                    
                    
                    
                    Broadcast Message from root@router01.localr01
                            (no tty) at 16:01 EDT...
                    
                    UPS TrippLite is unavailable
                    
                    dennypageD 1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage @ghound
                      last edited by

                      @ghound said in NUT Package (2.8.1 and above):

                      iManufacturer = 0x0003 <retrieving string failed>
                      iProduct = 0x0001 <retrieving string failed>
                      iSerialNumber = 0x0005 <retrieving string failed>

                      It was worth a shot.

                      Can you confirm that this behavior started following an upgrade of pfSense?

                      G 1 Reply Last reply Reply Quote 0
                      • G
                        ghound @dennypage
                        last edited by

                        @dennypage said in NUT Package (2.8.1 and above):

                        Can you confirm that this behavior started following an upgrade of pfSense?

                        Behavior has persisted through several updates. (In fact, UPS has never not had this issue from its first day out of the box.)

                        dennypageD 1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage @ghound
                          last edited by

                          @ghound said in NUT Package (2.8.1 and above):

                          Behavior has persisted through several updates. (In fact, UPS has never not had this issue from its first day out of the box.)

                          Okay, I'm confused. Please detail what previous version/date that the problem did not occur, and what version/date began to occurr.

                          G 1 Reply Last reply Reply Quote 0
                          • G
                            ghound @dennypage
                            last edited by

                            @dennypage said in NUT Package (2.8.1 and above):

                            Okay, I'm confused. Please detail what previous version/date that the problem did not occur, and what version/date began to occurr.

                            TrippLite UPS was purchased new in May '23 and connected to SG-1100 (23.05 / 2.8.0_2). You gave me a few tips to properly load usbhid-ups. Once usbhid-ups loaded correctly, after a few days, UPS lost connection (so the UPS has never operated without the lost connection problem every few days). At the time, I believed this was the "lost connection" problem mentioned in the thread. The problem has persisted from first connection to today. SG-1100 is currently 23.09.1 and Nut 2.8.2_1.

                            dennypageD 1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage @ghound
                              last edited by

                              @ghound said in NUT Package (2.8.1 and above):

                              TrippLite UPS was purchased new in May '23 and connected to SG-1100 (23.05 / 2.8.0_2). You gave me a few tips to properly load usbhid-ups. Once usbhid-ups loaded correctly, after a few days, UPS lost connection (so the UPS has never operated without the lost connection problem every few days). At the time, I believed this was the "lost connection" problem mentioned in the thread. The problem has persisted from first connection to today. SG-1100 is currently 23.09.1 and Nut 2.8.2_1.

                              Ah, okay. It's never operated correctly. I had misunderstood that it was a regression.

                              P 1 Reply Last reply Reply Quote 0
                              • P
                                pvk1 @dennypage
                                last edited by

                                @dennypage Sorry if this is the wrong place. I migrated the configuration to a Netgate 4200. I have NUT package 2.8.2_1. It had permission errors. After including user=root in the ups.conf section (as suggested by you in the previous track) it started working. It also worked on the previous system.
                                Schermafbeelding 2024-03-30 091809.png

                                dennypageD 2 Replies Last reply Reply Quote 0
                                • dennypageD
                                  dennypage @pvk1
                                  last edited by

                                  @pvk1 Ownership of the /var/db/nut directory is incorrect. The following command will fix that:

                                  chown -R nut:nut /var/db/nut
                                  

                                  The errors for /usr/local/etc/nut are more of an issue. Those files should be accessed prior to switching to user "nut". What version of pfSense are you running? What does

                                  pkg info | grep nut
                                  

                                  report? Thx.

                                  P 1 Reply Last reply Reply Quote 0
                                  • P
                                    pvk1 @dennypage
                                    last edited by

                                    @dennypage
                                    I am running: 23.09.1-RELEASE (amd64)

                                    pkg info:

                                    nut-devel-2024.01.03 Network UPS Tools
                                    pfSense-pkg-nut-2.8.2_1 Network UPS Tools

                                    thx

                                    dennypageD 1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage @pvk1
                                      last edited by

                                      @pvk1 Can you post the output of the the following commands please?

                                      ls -l /var/db/nut
                                      ls -l /usr/local/etc/nut
                                      

                                      Thanks

                                      P 1 Reply Last reply Reply Quote 0
                                      • P
                                        pvk1 @dennypage
                                        last edited by

                                        @dennypage Hi, thx

                                        ls -l /var/db/nut
                                        total 0
                                        ls: /var/db/nut: Permission denied

                                        ls -l /usr/local/etc/nut
                                        total 143
                                        -rw-r--r-- 1 root wheel 15136 Mar 4 22:00 cmdvartab
                                        -rw-r--r-- 1 root wheel 98236 Mar 4 22:00 driver.list
                                        -rw-r--r-- 1 root wheel 1071 Mar 4 22:00 hosts.conf
                                        -rw-r--r-- 1 root wheel 1071 Mar 4 22:00 hosts.conf.sample
                                        -rw-r--r-- 1 root wheel 4774 Mar 4 22:00 nut.conf
                                        -rw-r--r-- 1 root wheel 4774 Mar 4 22:00 nut.conf.sample
                                        -rw-r----- 1 root wheel 124 Apr 1 18:43 ups.conf
                                        -rw-r--r-- 1 root wheel 9845 Mar 4 22:00 ups.conf.sample
                                        -rw-r----- 1 root wheel 28 Apr 1 18:43 upsd.conf
                                        -rw-r--r-- 1 root wheel 9199 Mar 4 22:00 upsd.conf.sample
                                        -rw-r----- 1 root wheel 167 Apr 1 18:43 upsd.users
                                        -rw-r--r-- 1 root wheel 2349 Mar 4 22:00 upsd.users.sample
                                        -rw-r----- 1 root wheel 530 Apr 1 18:43 upsmon.conf
                                        -rw-r--r-- 1 root wheel 24735 Mar 4 22:00 upsmon.conf.sample
                                        -rw-r--r-- 1 root wheel 4217 Mar 4 22:00 upssched.conf
                                        -rw-r--r-- 1 root wheel 4217 Mar 4 22:00 upssched.conf.sample
                                        -rw-r--r-- 1 root wheel 1871 Mar 4 22:00 upsset.conf
                                        -rw-r--r-- 1 root wheel 1871 Mar 4 22:00 upsset.conf.sample
                                        -rw-r--r-- 1 root wheel 6861 Mar 4 22:00 upsstats-single.html
                                        -rw-r--r-- 1 root wheel 6861 Mar 4 22:00 upsstats-single.html.sample
                                        -rw-r--r-- 1 root wheel 4096 Mar 4 22:00 upsstats.html
                                        -rw-r--r-- 1 root wheel 4096 Mar 4 22:00 upsstats.html.sample

                                        GertjanG dennypageD 2 Replies Last reply Reply Quote 0
                                        • GertjanG
                                          Gertjan @pvk1
                                          last edited by

                                          @pvk1 said in NUT Package (2.8.1 and above):

                                          ls: /var/db/nut: Permission denied

                                          Strange.
                                          You are root, right ?

                                          [24.03-BETA][root@pfSense.bhf.tld]/root: whoami
                                          root
                                          

                                          No "help me" PM's please. Use the forum, the community will thank you.
                                          Edit : and where are the logs ??

                                          1 Reply Last reply Reply Quote 1
                                          • dennypageD
                                            dennypage @pvk1
                                            last edited by

                                            @pvk1 said in NUT Package (2.8.1 and above):

                                            ls -l /var/db/nut
                                            total 0
                                            ls: /var/db/nut: Permission denied

                                            As @Gertjan noted, you need to run the commands as root.

                                            P 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post