    Notification: UPS ups battery is low

    Scheduled Pinned Locked Moved UPS Tools
    16 Posts 2 Posters 3.0k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD Offline
      dennypage @fjmp24
      last edited by

      @fjmp24 said in Notification: UPS ups battery is low:

      I receive the notification "UPS ups battery is low" and I don't understand why.
      I changed the battery without success.
      I changed UPS (EATON ELLIPSE PRO 850) to a more powerful one without success.

      You indicated that you have 3 systems powered by the UPS, however your post does not include the notification that you are referring to, nor any information about the circumstance when the notification occurs or which system it originates from.

      Btw, unless you are trying to address a very specific problem, you should not have the items in the "Extra Arguments to driver" section. Specifically, setting "ignorelb" and specifying runtimes is almost always a mistake, although a commonly made one. Likely the only one that should be there is the shutdown delay, but that only if you need more than 20 seconds to completely a shutdown on one of the systems. My expectation is that would probably only apply if you are running the Synology as a remote client to pfSense.

      F 2 Replies Last reply Reply Quote 0
      • F Offline
        fjmp24 @dennypage
        last edited by

        This post is deleted!
        1 Reply Last reply Reply Quote 0
        • F Offline
          fjmp24 @dennypage
          last edited by

          @dennypage Thanks I deleted override.battery.runtime.low and override.battery.runtime.warn and I don't receive notifications anymore. But I have another questions.

          1. When I cut power to my NUT, pfsense sends a shutdown when my NUT have :
          • runtime is equal to 0:01:41
          • battery charge is equal to 19%
            Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300
          1. Once my devices have been shutdown, the NUT runs for about 1 minute and displays the runtime. Then it doesn't display runtime and works about 0:02:49. I don't understand how it works.An idea ?

          Below my configuration:

          battery.charge	9
          battery.charge.low	20
          battery.runtime	355
          battery.type	PbAc
          device.mfr	EATON
          device.model	Ellipse PRO 650
          device.serial	P354L18GBN
          device.type	ups
          driver.debug	0
          driver.flag.allow_killpower	0
          driver.flag.ignorelb	enabled
          driver.name	usbhid-ups
          driver.parameter.override.ups.delay.shutdown	300
          driver.parameter.pollfreq	30
          driver.parameter.pollinterval	2
          driver.parameter.port	auto
          driver.parameter.synchronous	auto
          driver.state	quiet
          driver.version	2.8.0.1
          driver.version.data	MGE HID 1.46
          driver.version.internal	0.52
          driver.version.usb	libusb-1.0.0 (API: 0x1000102)
          input.frequency	50.0
          input.transfer.high	285
          input.transfer.low	165
          input.voltage	225.0
          input.voltage.extended	no
          outlet.1.desc	PowerShare Outlet 1
          outlet.1.id	2
          outlet.1.status	on
          outlet.1.switchable	no
          outlet.2.desc	PowerShare Outlet 2
          outlet.2.id	3
          outlet.2.status	on
          outlet.2.switchable	no
          outlet.desc	Main Outlet
          outlet.id	1
          outlet.switchable	no
          output.frequency	50.0
          output.frequency.nominal	50
          output.voltage	227.0
          output.voltage.nominal	230
          ups.beeper.status	enabled
          ups.delay.shutdown	300
          ups.delay.start	30
          ups.firmware	01.16.0020
          ups.load	7
          ups.mfr	EATON
          ups.model	Ellipse PRO 650
          ups.power	49
          ups.power.nominal	650
          ups.productid	ffff
          ups.realpower	18
          ups.serial	P354L18GBN
          ups.status	OL LB
          ups.timer.shutdown	-1
          ups.timer.start	-1
          ups.vendorid	0463
          

          Thank you for your help and sorry for my newbie's questions.

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD Offline
            dennypage @fjmp24
            last edited by

            @fjmp24 said in Notification: UPS ups battery is low:

            • runtime is equal to 0:01:41
            • battery charge is equal to 19%
              Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300

            NUT initiates a shutdown when the UPS declares that the battery is low (LB). The decision regarding a low battery is made by the UPS itself. Some UPSs have configurable LB levels, and some have fixed LB levels. If your UPS has a configurable LB level, this is configured by the battery.charge.low variable. 20% is a common default.

            When performing a shutdown, one of the last steps is for the OS (pfSense) to instruction the UPS to cut the power. After receiving that command, the UPS waits a short period of time before it actually turns off the power. The purpose of this delay is to allow the OS to complete its shutdown before power is cut. Some UPSs have configurable delays, and some have fixed delays. If your UPS has a configurable delay, this is configured by the ups.delay.shutdown variable. 20 seconds is a common default.

            F 1 Reply Last reply Reply Quote 0
            • stephenw10S stephenw10 moved this topic from pfSense Packages on
            • F Offline
              fjmp24 @dennypage
              last edited by

              @dennypage Thank you for your help

              F 1 Reply Last reply Reply Quote 0
              • F Offline
                fjmp24 @fjmp24
                last edited by

                Hi,

                I did a test to see if my UPS is working properly. I could see that it wasn't :-(
                The UPS cuts the power very quickly (about 1 minute), which means, for example, my NAS doesn't have time to shut down properly.
                My setup was working before. I updated pfSense. The problem might be coming from there.

                UPS Detail

                Variable 	Value
                battery.charge	100
                battery.charge.low	20
                battery.runtime	1417
                battery.type	PbAc
                device.mfr	EATON
                device.model	Ellipse PRO 650
                device.serial	P354L18GBN
                device.type	ups
                driver.debug	0
                driver.flag.allow_killpower	0
                driver.flag.ignorelb	enabled
                driver.name	usbhid-ups
                driver.parameter.override.ups.delay.shutdown	90
                driver.parameter.pollfreq	30
                driver.parameter.pollinterval	2
                driver.parameter.port	auto
                driver.parameter.synchronous	auto
                driver.state	updateinfo
                driver.version	2.8.2
                driver.version.data	MGE HID 1.46
                driver.version.internal	0.53
                driver.version.usb	libusb-1.0.0 (API: 0x1000102)
                input.frequency	50.0
                input.transfer.high	285
                input.transfer.low	165
                input.voltage	229.0
                input.voltage.extended	no
                outlet.1.desc	PowerShare Outlet 1
                outlet.1.id	2
                outlet.1.status	on
                outlet.1.switchable	no
                outlet.2.desc	PowerShare Outlet 2
                outlet.2.id	3
                outlet.2.status	on
                outlet.2.switchable	no
                outlet.desc	Main Outlet
                outlet.id	1
                outlet.switchable	no
                output.frequency	50.0
                output.frequency.nominal	50
                output.voltage	230.0
                output.voltage.nominal	230
                ups.beeper.status	enabled
                ups.delay.shutdown	90
                ups.delay.start	30
                ups.firmware	01.16.0020
                ups.load	19
                ups.mfr	EATON
                ups.model	Ellipse PRO 650
                ups.power	114
                ups.power.nominal	650
                ups.productid	ffff
                ups.realpower	76
                ups.serial	P354L18GBN
                ups.status	OL
                ups.timer.shutdown	-1
                ups.timer.start	-1
                ups.vendorid	0463
                

                Extra Arguments to driver

                ignorelb
                override.ups.delay.shutdown = 90
                

                Do you have an idea ? Sorry I'm newbie Thanks.

                dennypageD 1 Reply Last reply Reply Quote 0
                • dennypageD Offline
                  dennypage @fjmp24
                  last edited by

                  @fjmp24 How old is the battery? Have you done a calibration test?

                  F 1 Reply Last reply Reply Quote 0
                  • F Offline
                    fjmp24 @dennypage
                    last edited by

                    @dennypage I changed the battery this year. I don't understand : "Have you done a calibration test" ?

                    dennypageD 1 Reply Last reply Reply Quote 0
                    • dennypageD Offline
                      dennypage @fjmp24
                      last edited by

                      @fjmp24 said in Notification: UPS ups battery is low:

                      I don't understand : "Have you done a calibration test" ?

                      Most UPSs have a "battery calibration test", "runtime calibration test", etc. You are looking for a test that runs the load off of the battery (without cutting mains) to see how the battery behaves under actual load.

                      Btw, you should remove the ignorelb directive from the Extra Arguments to driver section. Unless you have a very old UPS that signals low battery whenever the UPS is on battery. You almost certainly do not have such a UPS.

                      F 1 Reply Last reply Reply Quote 0
                      • F Offline
                        fjmp24 @dennypage
                        last edited by

                        @dennypage My UPD indicate runtime: 18:21

                        dennypageD 1 Reply Last reply Reply Quote 0
                        • dennypageD Offline
                          dennypage @fjmp24
                          last edited by

                          @fjmp24 said in Notification: UPS ups battery is low:

                          @dennypage My UPD indicate runtime: 18:21

                          Yes, but that may be completely inaccurate, especially with bad batteries. That's why you run a calibration test.

                          F 1 Reply Last reply Reply Quote 0
                          • F Offline
                            fjmp24 @dennypage
                            last edited by

                            @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                            I don't understand anything :-((

                            dennypageD 1 Reply Last reply Reply Quote 0
                            • dennypageD Offline
                              dennypage @fjmp24
                              last edited by

                              @fjmp24 said in Notification: UPS ups battery is low:

                              @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                              I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                              Also, you do not have anything in the Advanced settings section, correct?

                              As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                              F 1 Reply Last reply Reply Quote 0
                              • F Offline
                                fjmp24 @dennypage
                                last edited by

                                I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                                Ok, I will test without ignorelb directive.

                                Also, you do not have anything in the Advanced settings section, correct?

                                Yes

                                As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                                I find anything I will search tomorow

                                1 Reply Last reply Reply Quote 0