Netgate Discussion Forum
    • Categories
    • Recent
    • Tags
    • Popular
    • Users
    • Search
    • Register
    • Login

    Notification: UPS ups battery is low

    Scheduled Pinned Locked Moved UPS Tools
    20 Posts 2 Posters 3.2k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD Offline
      dennypage @fjmp24
      last edited by

      @fjmp24 said in Notification: UPS ups battery is low:

      I don't understand : "Have you done a calibration test" ?

      Most UPSs have a "battery calibration test", "runtime calibration test", etc. You are looking for a test that runs the load off of the battery (without cutting mains) to see how the battery behaves under actual load.

      Btw, you should remove the ignorelb directive from the Extra Arguments to driver section. Unless you have a very old UPS that signals low battery whenever the UPS is on battery. You almost certainly do not have such a UPS.

      F 1 Reply Last reply Reply Quote 0
      • F Offline
        fjmp24 @dennypage
        last edited by

        @dennypage My UPD indicate runtime: 18:21

        dennypageD 1 Reply Last reply Reply Quote 0
        • dennypageD Offline
          dennypage @fjmp24
          last edited by

          @fjmp24 said in Notification: UPS ups battery is low:

          @dennypage My UPD indicate runtime: 18:21

          Yes, but that may be completely inaccurate, especially with bad batteries. That's why you run a calibration test.

          F 1 Reply Last reply Reply Quote 0
          • F Offline
            fjmp24 @dennypage
            last edited by

            @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

            I don't understand anything :-((

            dennypageD 1 Reply Last reply Reply Quote 0
            • dennypageD Offline
              dennypage @fjmp24
              last edited by

              @fjmp24 said in Notification: UPS ups battery is low:

              @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

              I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

              Also, you do not have anything in the Advanced settings section, correct?

              As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

              F 1 Reply Last reply Reply Quote 0
              • F Offline
                fjmp24 @dennypage
                last edited by

                I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                Ok, I will test without ignorelb directive.

                Also, you do not have anything in the Advanced settings section, correct?

                Yes

                As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                I find anything I will search tomorow

                F 1 Reply Last reply Reply Quote 0
                • F Offline
                  fjmp24 @fjmp24
                  last edited by

                  If I remove ignorelb directive, my UPS shuts down after 16 seconds

                  F dennypageD 2 Replies Last reply Reply Quote 0
                  • F Offline
                    fjmp24 @fjmp24
                    last edited by

                    My UPD do an automatic battery test regularly to warn when a replacement of the current battery needs to be carried out.

                    1 Reply Last reply Reply Quote 0
                    • dennypageD Offline
                      dennypage @fjmp24
                      last edited by

                      @fjmp24 said in Notification: UPS ups battery is low:

                      If I remove ignorelb directive, my UPS shuts down after 16 seconds

                      This means your UPS is signaling a low battery. Either your battery is bad, or your UPS is bad. Most likely battery, but you never know. I suggest reaching out to Eaton support.

                      F 1 Reply Last reply Reply Quote 1
                      • F Offline
                        fjmp24 @dennypage
                        last edited by

                        @dennypage I tested it with a new UPS and I no longer have the problem. It was the UPS that wasn't working properly.

                        Thanks for your help.

                        1 Reply Last reply Reply Quote 0
                        • First post
                          Last post
                        Copyright 2025 Rubicon Communications LLC (Netgate). All rights reserved.