    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.1m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • F
      f34rinc
      last edited by

      @dennypage:

      Do you have confidence in the USB chipset on the mother board? Is it a recent MB? I don't see it's identification in the usb dump. It's not an external hub is it?
      Also, how old is the UPS? If it's not recent, have you tried the tripplite driver?

      I do not have confidence in the USB chipset the box is a Leonovo M90 3246-A2U from 2010 and I was able to find it uses Platform Controller Hub (PCH) for PCI, ethernet and USB.  I've also switched between the USB 2 and USB 3 ports, different cables.  I can only get usbconfig to show TRIPP LITE UPS Tripp Lite.

      No external USB hub (eww)

      I just purchased the UPS July 2017

      I do plan to get new hardware in the next year or possibly sooner, I dont know if it would be worth it to try and get a PCI\PCIe usb card with a better chipset.

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage
        last edited by

        @bulldog5:

        Hi, I'm running a Cyberpower UPS, and getting random email notifications saying LOWBATT

        I've had a couple of Cyberpowers. I found them to be a bit flakey, particularly when the battery needs replacing. It could be happening when the unit does its short self test. I would perform a self test, followed by a runtime calibration to check the battery.

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          @f34rinc:

          I do not have confidence in the USB chipset the box is a Leonovo M90 3246-A2U from 2010 and I was able to find it uses Platform Controller Hub (PCH) for PCI, ethernet and USB.  I've also switched between the USB 2 and USB 3 ports, different cables.  I can only get usbconfig to show TRIPP LITE UPS Tripp Lite.

          No external USB hub (eww)

          Normally I would recommend against an external hub, but in this case it's worth a try to test with an external (powered) hub because it will be a different bridge chip.

          1 Reply Last reply Reply Quote 0
          • F
            f34rinc
            last edited by

            @dennypage:

            Normally I would recommend against an external hub, but in this case it's worth a try to test with an external (powered) hub because it will be a different bridge chip.

            Thanks, is there a certain bridge chip manufacture I should try or avoid ?

            1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage
              last edited by

              @f34rinc:

              Thanks, is there a certain bridge chip manufacture I should try or avoid ?

              Sorry, I'm not knowledgeable enough to make a recommendation.

              1 Reply Last reply Reply Quote 0
              • B
                bulldog5
                last edited by

                @dennypage:

                @f34rinc:

                I do not have confidence in the USB chipset the box is a Leonovo M90 3246-A2U from 2010 and I was able to find it uses Platform Controller Hub (PCH) for PCI, ethernet and USB.  I've also switched between the USB 2 and USB 3 ports, different cables.  I can only get usbconfig to show TRIPP LITE UPS Tripp Lite.

                No external USB hub (eww)

                Normally I would recommend against an external hub, but in this case it's worth a try to test with an external (powered) hub because it will be a different bridge chip.

                I'm trying to figure out how to do this?  Its connected directly to pfSense with just NUT. Is there a upsc command to imitate a selftest?  The units not even a year old =(

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  You use "upscmd" to do self tests and the like. A list of the potential commands is available here.

                  This command

                  upscmd -l <upsname>will provide a list of available commands for the specific UPS.</upsname>

                  1 Reply Last reply Reply Quote 0
                  • B
                    bulldog5
                    last edited by

                    So i ran a deep battery test, and it passes every time. Is there anything diagnostic wise i could do to see what's going on at the time it reports LOWBATT, because as far as i can tell its never low.  This just started happening after I upgraded pfSense to the latest version 2.4.4, If i remember, i was on 2.3.2.  Something has changed in the way pfsense is handling this across these versions.

                    1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage
                      last edited by

                      @bulldog5:

                      This just started happening after I upgraded pfSense to the latest version 2.4.4, If i remember, i was on 2.3.2.  Something has changed in the way pfsense is handling this across these versions.

                      Can you clarify the version information please? The latest version of pfSense is 2.3.4. Version 2.4 of pfSense is still in development (beta). The latest version of the nut package is 2.7.4_4, which uses underlying nut version 2.7.4_1. Thanks.

                      Btw, unless you were previously running pfSense 2.2.X or below, I'm guessing that the "something changed with nut" may be coincidental. This stuff hasn't changed much in the last year. The underlying release of nut for pfSense, version 2.7.4, was introduced in pfSense 2.3.0. The current generation of the nut package, version 2.7.4, was introduced shortly thereafter. Note that the prior generation nut package, 2.3.X, didn't have the ability to send email notifications so you would have only noticed LOWBATT messages if you scanned the system log.

                      1 Reply Last reply Reply Quote 0
                      • B
                        bulldog5
                        last edited by

                        @dennypage:

                        @bulldog5:

                        This just started happening after I upgraded pfSense to the latest version 2.4.4, If i remember, i was on 2.3.2.  Something has changed in the way pfsense is handling this across these versions.

                        Can you clarify the version information please? The latest version of pfSense is 2.3.4. Version 2.4 of pfSense is still in development (beta). The latest version of the nut package is 2.7.4_4, which uses underlying nut version 2.7.4_1. Thanks.

                        Btw, unless you were previously running pfSense 2.2.X or below, I'm guessing that the "something changed with nut" may be coincidental. This stuff hasn't changed much in the last year. The underlying release of nut for pfSense, version 2.7.4, was introduced in pfSense 2.3.0. The current generation of the nut package, version 2.7.4, was introduced shortly thereafter. Note that the prior generation nut package, 2.3.X, didn't have the ability to send email notifications so you would have only noticed LOWBATT messages if you scanned the system log.

                        Ok sorry, let me clear that up, I'm on the latest version now of 2.3.4.  Previously on 2.3.2, never had a single LOWBATT alert. Back checked email, July 9th I upgrade to 2.3.4, alerts start rolling in since, randomly.  Is something polling differently now?

                        1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage
                          last edited by

                          @bulldog5:

                          @dennypage:

                          Btw, unless you were previously running pfSense 2.2.X or below, I'm guessing that the "something changed with nut" may be coincidental. This stuff hasn't changed much in the last year. The underlying release of nut for pfSense, version 2.7.4, was introduced in pfSense 2.3.0. The current generation of the nut package, version 2.7.4, was introduced shortly thereafter. Note that the prior generation nut package, 2.3.X, didn't have the ability to send email notifications so you would have only noticed LOWBATT messages if you scanned the system log.

                          Ok sorry, let me clear that up, I'm on the latest version now of 2.3.4.  Previously on 2.3.2, never had a single LOWBATT alert. Back checked email, July 9th I upgrade to 2.3.4, alerts start rolling in since, randomly.  Is something polling differently now?

                          The only scenario I can think of would be having an earlier version of pfSense and the nut package installed, then installing 2.3.2 and not reinstalling the packages until the upgrade to 2.3.4.

                          If this was the case, there would have been two changes. First would have been the underlying nut version going from 2.7.3 to 2.7.4. Second would have been the nut package going from 2.3.X to 2.7.4. If this happened, it should have been pretty obvious because the nut package would have put up a banner about settings migration and forced the migrated settings to be explicitly saved before it would start. Nut email notifications are also off by default, so at some point they had to be explicitly enabled as well.

                          For nut, the release notes are here. Nothing in particular jumps out at me, but I'm not a nut developer. For the nut package, there hasn't been much since the introduction of 2.7.4, which is when the ability to configure email was introduced. Overall, my best guess is that the LOWBATT thing has been happening all along and it wasn't noticed in the system logs until email notifications were enabled because it didn't impair operation.

                          So I guess the key questions to think about are: Was there a nut configuration migration performed? If so, when? And when were email notifications enabled?

                          1 Reply Last reply Reply Quote 0
                          • B
                            bulldog5
                            last edited by

                            @dennypage:

                            @bulldog5:

                            @dennypage:

                            Btw, unless you were previously running pfSense 2.2.X or below, I'm guessing that the "something changed with nut" may be coincidental. This stuff hasn't changed much in the last year. The underlying release of nut for pfSense, version 2.7.4, was introduced in pfSense 2.3.0. The current generation of the nut package, version 2.7.4, was introduced shortly thereafter. Note that the prior generation nut package, 2.3.X, didn't have the ability to send email notifications so you would have only noticed LOWBATT messages if you scanned the system log.

                            Ok sorry, let me clear that up, I'm on the latest version now of 2.3.4.  Previously on 2.3.2, never had a single LOWBATT alert. Back checked email, July 9th I upgrade to 2.3.4, alerts start rolling in since, randomly.  Is something polling differently now?

                            The only scenario I can think of would be having an earlier version of pfSense and the nut package installed, then installing 2.3.2 and not reinstalling the packages until the upgrade to 2.3.4.

                            If this was the case, there would have been two changes. First would have been the underlying nut version going from 2.7.3 to 2.7.4. Second would have been the nut package going from 2.3.X to 2.7.4. If this happened, it should have been pretty obvious because the nut package would have put up a banner about settings migration and forced the migrated settings to be explicitly saved before it would start. Nut email notifications are also off by default, so at some point they had to be explicitly enabled as well.

                            For nut, the release notes are here. Nothing in particular jumps out at me, but I'm not a nut developer. For the nut package, there hasn't been much since the introduction of 2.7.4, which is when the ability to configure email was introduced. Overall, my best guess is that the LOWBATT thing has been happening all along and it wasn't noticed in the system logs until email notifications were enabled because it didn't impair operation.

                            So I guess the key questions to think about are: Was there a nut configuration migration performed? If so, when? And when were email notifications enabled?

                            Email notifications have been on all along, I'd get OL and OB notifications during switches, but never random LOWBATTs until after the upgrade, nut package has been on 2.7.4.  I just don't see why its sending LOWBATT, when it never comes off 100%, LOWBATT shouldn't even come out until past 70% or so and if it was actually discharging, it sure wouldn't come back to 100% that quick.  I'm going to try moving NUT master servers and see if it continues, before trying a rollback as another experiment.

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              Do you have another UPS to test with by chance?

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage
                                last edited by

                                @bulldog5:

                                Email notifications have been on all along, I'd get OL and OB notifications during switches, but never random LOWBATTs until after the upgrade, nut package has been on 2.7.4.  I just don't see why its sending LOWBATT, when it never comes off 100%, LOWBATT shouldn't even come out until past 70% or so and if it was actually discharging, it sure wouldn't come back to 100% that quick.

                                Okay, so no changes in the nut version or the nut package. Presuming the same UPS the entire time.

                                Just for completeness, can you post output from the following two commands?

                                upsc <upsname>upsrw <upsname>Thanks</upsname></upsname>

                                1 Reply Last reply Reply Quote 0
                                • B
                                  bulldog5
                                  last edited by

                                  @dennypage:

                                  @bulldog5:

                                  Email notifications have been on all along, I'd get OL and OB notifications during switches, but never random LOWBATTs until after the upgrade, nut package has been on 2.7.4.  I just don't see why its sending LOWBATT, when it never comes off 100%, LOWBATT shouldn't even come out until past 70% or so and if it was actually discharging, it sure wouldn't come back to 100% that quick.

                                  Okay, so no changes in the nut version or the nut package. Presuming the same UPS the entire time.

                                  Just for completeness, can you post output from the following two commands?

                                  upsc <upsname>upsrw <upsname>Thanks</upsname></upsname>

                                  battery.charge: 100
                                  battery.charge.low: 50
                                  battery.charge.warning: 20
                                  battery.mfr.date: CPS
                                  battery.runtime: 960
                                  battery.runtime.low: 600
                                  battery.type: PbAcid
                                  battery.voltage: 24.0
                                  battery.voltage.nominal: 24
                                  device.mfr: CPS
                                  device.model: OR1500PFCRT2U
                                  device.type: ups
                                  driver.flag.ignorelb: enabled
                                  driver.name: usbhid-ups
                                  driver.parameter.pollfreq: 30
                                  driver.parameter.pollinterval: 2
                                  driver.parameter.port: /dev/ugen0.6
                                  driver.parameter.synchronous: no
                                  driver.version: 2.7.4
                                  driver.version.data: CyberPower HID 0.4
                                  driver.version.internal: 0.41
                                  input.transfer.high: 139
                                  input.transfer.low: 88
                                  input.voltage: 118.0
                                  input.voltage.nominal: 120
                                  output.voltage: 118.0
                                  ups.beeper.status: enabled
                                  ups.delay.shutdown: 20
                                  ups.delay.start: 30
                                  ups.load: 58
                                  ups.mfr: CPS
                                  ups.model: OR1500PFCRT2U
                                  ups.productid: 0601
                                  ups.realpower.nominal: 900
                                  ups.status: OL
                                  ups.test.result: Done and passed
                                  ups.timer.shutdown: -60
                                  ups.timer.start: -60
                                  ups.vendorid: 0764

                                  [input.transfer.high]
                                  High voltage transfer point (V)
                                  Type: STRING
                                  Maximum length: 10
                                  Value: 139

                                  [input.transfer.low]
                                  Low voltage transfer point (V)
                                  Type: STRING
                                  Maximum length: 10
                                  Value: 88

                                  [ups.delay.shutdown]
                                  Interval to wait after shutdown with delay command (seconds)
                                  Type: STRING
                                  Maximum length: 10
                                  Value: 20

                                  [ups.delay.start]
                                  Interval to wait before (re)starting the load (seconds)
                                  Type: STRING
                                  Maximum length: 10
                                  Value: 30

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    @bulldog5:

                                    battery.charge.low: 50
                                    battery.charge.warning: 20

                                    I didn't look at all the variables, but this one is an issue: battery.charge.warning should be higher than battery.charge.low.

                                    What is being set in the Extra Arguments to driver section? Anything in the Advanced section?

                                    1 Reply Last reply Reply Quote 0
                                    • B
                                      bulldog5
                                      last edited by

                                      @dennypage:

                                      @bulldog5:

                                      battery.charge.low: 50
                                      battery.charge.warning: 20

                                      I didn't look at all the variables, but this one is an issue: battery.charge.warning should be higher than battery.charge.low.

                                      What is being set in the Extra Arguments to driver section? Anything in the Advanced section?

                                      Driver Extra Args:

                                      port = /dev/ugen0.6
                                      ignorelb
                                      override.battery.charge.low = 50
                                      override.battery.runtime.low = 600

                                      upsmon.conf

                                      RUN_AS_USER root

                                      upsd.conf

                                      LISTEN 10.10.0.1

                                      upsd.users

                                      [monitor]
                                      password = *************
                                      upsmon slave

                                      1 Reply Last reply Reply Quote 0
                                      • J
                                        jg3
                                        last edited by

                                        Hello,

                                        Is it possible to have the NUT daemon monitor and manage two UPSes?

                                        I have a CyberPower1500 and a CyberPower1350 in my set-up and the pfSense firewall is the only bare-metal box (everything else is an ESXi server).  I want to have each of the other systems query the NUT daemon on the pfSense for the status of the UPS that host is connected to.  (the UPSes are on different circuits so there are scenarios where one goes down but not both)

                                        What I don't know is how to set these configurations.  I see there are a number of advanced options in the UI, I'm a little lost as to where to start.  Has anyone done this before?  I'd like to do it via the pfSense UI so my configs will survive upgrades and reinstalls, rather than being hidden down in config files.

                                        To make this work I figure I need to pass options for additional configurations here so that the port of each UPS is listed explicitly:

                                        
                                        [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: cat /usr/local/etc/nut/ups.conf
                                        [CyberPower1500]
                                        driver=usbhid-ups
                                        port=auto
                                        
                                        

                                        …and here so that each UPS has an explicit TCP port for communication with the remote servers.:

                                        
                                        [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: cat /usr/local/etc/nut/upsd.conf
                                        LISTEN 127.0.0.1
                                        LISTEN ::1
                                        
                                        

                                        …  I'm really not sure what I need to do or what will happen automatically here:

                                        
                                        [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: cat /usr/local/etc/nut/upsmon.conf
                                        MONITOR CyberPower1500 1 monuser f0e07165bec481f09a93 master
                                        SHUTDOWNCMD "/sbin/shutdown -p +0"
                                        POWERDOWNFLAG /etc/killpower
                                        NOTIFYCMD /usr/local/pkg/nut/nut_email.php
                                        NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
                                        NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
                                        NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                                        NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
                                        NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
                                        NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
                                        NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
                                        
                                        

                                        Here's the USB information .. the difference I can see is the "ugen1.[2|3]" but everything else is the same?  How do I identify/label the port?

                                        [2.3.4-RELEASE][admin@pfsense.thirtynineohsix]/root: usbconfig dump_device_desc
                                        ugen0.1: <uhci root="" hub="" intel="">at usbus0, cfg=0 md=HOST spd=FULL (12Mbps) pwr=SAVE (0mA)
                                        
                                         [ details from four root hubs elided ]
                                        
                                        ugen1.2: <cp 1500c="" cps="">at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (50mA)
                                        
                                          bLength = 0x0012
                                          bDescriptorType = 0x0001
                                          bcdUSB = 0x0110
                                          bDeviceClass = 0x0000  <probed by="" interface="" class="">bDeviceSubClass = 0x0000
                                          bDeviceProtocol = 0x0000
                                          bMaxPacketSize0 = 0x0008
                                          idVendor = 0x0764
                                          idProduct = 0x0501
                                          bcdDevice = 0x0001
                                          iManufacturer = 0x0003  <cps>iProduct = 0x0001  < CP 1500C>
                                          iSerialNumber = 0x0000  <no string="">bNumConfigurations = 0x0001
                                        
                                        ugen1.3: <cp 1350c="" cps="">at usbus1, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (50mA)
                                        
                                          bLength = 0x0012
                                          bDescriptorType = 0x0001
                                          bcdUSB = 0x0110
                                          bDeviceClass = 0x0000  <probed by="" interface="" class="">bDeviceSubClass = 0x0000
                                          bDeviceProtocol = 0x0000
                                          bMaxPacketSize0 = 0x0008
                                          idVendor = 0x0764
                                          idProduct = 0x0501
                                          bcdDevice = 0x0001
                                          iManufacturer = 0x0003  <cps>iProduct = 0x0001  < CP 1350C>
                                          iSerialNumber = 0x0000  <no string="">bNumConfigurations = 0x0001</no></cps></probed></cp></no></cps></probed></cp></uhci> 
                                        

                                        I'm okay if only one shows up in the UPS widget, it's more important that the respective machines know how to validate their power source.

                                        Thanks for any insights …

                                        --jg3

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          @bulldog5:

                                          Driver Extra Args:

                                          port = /dev/ugen0.6
                                          ignorelb
                                          override.battery.charge.low = 50
                                          override.battery.runtime.low = 600

                                          The ups is at 58% load, or approximately 610 watts. Expected runtime of 14-15 min according to Cyber. So the shutdown should be triggered approximately 5 min after mains go offline.

                                          One of the notes in the nut documentation on ignorelb is that some UPSs generate a LB indication almost immediately after loss of mains. In the context of general Cyberpower flakiness, I can see this happening either from loss of mains, high/low transfer, or maybe even a UPS initiated self test. Even though it would not initiate a shutdown with your configuration, nut would still generate a notification if the UPS sent a LB alert. Is it possible this is happening?

                                          In terms of timing, did the load level change around the time of the upgrade? Or Driver Extra arguments?

                                          1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            @jg3:

                                            Is it possible to have the NUT daemon monitor and manage two UPSes?

                                            There is no way to do this in the UI. Sorry.

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post