Netgate Discussion Forum
    • Categories
    • Recent
    • Tags
    • Popular
    • Users
    • Search
    • Register
    • Login

    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.2m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • dennypageD
      dennypage @flu
      last edited by

      @flu Yes, this happens because when an interface flaps, pfSense restarts all add-on services. The reason for this is that pfSense itself does not have direct knowledge of what dependencies the services have on interfaces (if any).

      F 1 Reply Last reply Reply Quote 0
      • F
        flu @dennypage
        last edited by

        @dennypage
        many thanks for the explanation.
        I guess the nut package could be changed so that it does not send messages like "Communications with UPS UPS lost" and "UPS UPS is unavailable" every time it gets restarted by pfsense?

        dennypageD 1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @flu
          last edited by

          @flu The email comes from NUT itself, rather than the pfSense NUT package. And from NUT's point of view, the connection to the UPS is actually being lost. This will be triggered by something that affects the USB or serial connectivity being restarted or reloaded underneath NUT. NUT doesn't know why the connection failed, it just knows that it failed so it sends the email. You should be able to see the order of events in the system log if you want to understand more about what is happening.

          1 Reply Last reply Reply Quote 0
          • K
            kevindd992002 @dennypage
            last edited by

            @dennypage So here's what I noticed recently in my system logs after receiving UPS communication lost and established emails:

            Feb 19 04:33:53 	php-cgi 		nut_email.php: Message sent to kevindd992002@yahoo.com OK
            Feb 19 04:33:49 	php-cgi 		nut_email.php: Message sent to kevindd992002@yahoo.com OK
            Feb 19 04:33:46 	upsmon 	43175 	Communications with UPS ups established
            Feb 19 04:33:44 	upsd 	86349 	UPS [ups] data is no longer stale
            Feb 19 04:33:41 	upsmon 	43175 	Communications with UPS ups lost
            Feb 19 04:33:41 	upsmon 	43175 	Poll UPS [ups] failed - Data stale
            Feb 19 04:33:41 	kernel 		ugen0.2: <EATON 5E> at usbus0
            Feb 19 04:33:38 	kernel 		ugen0.2: <EATON 5E> at usbus0 (disconnected)
            Feb 19 04:33:37 	upsd 	86349 	Data for UPS [ups] is stale - check driver
            

            What does "data is stale" even mean? And why does this happen intermittently?

            GertjanG 1 Reply Last reply Reply Quote 0
            • GertjanG
              Gertjan @kevindd992002
              last edited by

              @kevindd992002 said in NUT package:

              What does "data is stale" even mean? And why does this happen intermittently?

              Probably because :
              Feb 19 04:33:38 kernel ugen0.2: <EATON 5E> at usbus0 (disconnected)
              Feb 19 04:33:37 upsd 86349 Data for UPS [ups] is stale - check driver

              which says to me that the link between the driver (NUT ?) and the UPS device (cable, whatever) isn't "stable".

              No "help me" PM's please. Use the forum, the community will thank you.
              Edit : and where are the logs ??

              K 1 Reply Last reply Reply Quote 0
              • K
                kevindd992002 @Gertjan
                last edited by

                @Gertjan said in NUT package:

                @kevindd992002 said in NUT package:

                What does "data is stale" even mean? And why does this happen intermittently?

                Probably because :
                Feb 19 04:33:38 kernel ugen0.2: <EATON 5E> at usbus0 (disconnected)
                Feb 19 04:33:37 upsd 86349 Data for UPS [ups] is stale - check driver

                which says to me that the link between the driver (NUT ?) and the UPS device (cable, whatever) isn't "stable".

                Right but it's just weird that it happens randomly. It's not the UPS and cable because those were replaced already. I also tried using another usb port on the apu2c4 to no avail. There are only 2 usb ports available. Maybe the hub itself? How can you tell for sure though?

                dennypageD 1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage @kevindd992002
                  last edited by

                  @kevindd992002 It's either the host end or the UPS end. On the host end, it can be hardware (bridge controller) or software (kernel driver). On the UPS end it would just be a flakey USB implementation.

                  What I generally recommend to people having these types of issues:

                  • Try a different port on the host that uses a different bridge chip. Favor ports that are USB 2 as USB 3 ports usually have more problems.
                  • If you have a USB hub between the host and the UPS, try removing it.
                  • If you don't have a USB hub between the host and the UPS, try adding one.
                  • Try a different USB hub that uses a different bridge chip.
                  • Try a different UPS model.
                  • Try a different host model.

                  Regarding the apu2c4, you might find this an interesting read.

                  Bonne chance

                  1 Reply Last reply Reply Quote 0
                  • Q
                    q54e3w
                    last edited by

                    @dennypage I'm seeing the following log entries under 2.4.5, anything to be concerned about?

                    Apr 16 07:09:28	upsmon	92379	Communications with UPS UPS established
                    Apr 16 07:09:28	upsd	33793	User local-monitor@127.0.0.1 logged into UPS [UPS]
                    Apr 16 07:09:23	upsmon	92379	Communications with UPS UPS lost
                    Apr 16 07:09:23	upsmon	92379	Poll UPS [UPS] failed - Write error: Permission denied
                    Apr 16 07:09:21	nginx		2020/04/16 07:09:21 [crit] 11971#100993: *62736 SSL_write() failed (13: Permission denied) while processing HTTP/2 connection, client: 192.168.20.115, server: 0.0.0.0:4433
                    Apr 16 07:08:43	upsmon	92379	Communications with UPS UPS established
                    Apr 16 07:08:43	upsd	33793	User local-monitor@127.0.0.1 logged into UPS [UPS]
                    Apr 16 07:08:38	upsmon	92379	Communications with UPS UPS lost
                    Apr 16 07:08:38	upsmon	92379	Poll UPS [UPS] failed - Write error: Permission denied
                    
                    dennypageD 2 Replies Last reply Reply Quote 0
                    • dennypageD
                      dennypage @q54e3w
                      last edited by

                      @q54e3w Can you provide information on your NUT configuration please?

                      1 Reply Last reply Reply Quote 0
                      • Q
                        q54e3w
                        last edited by

                        UPS is a network connected Eaton 9PX with Network Card 2.

                        UPS Type: Remote SNMP
                        UPS Name: UPS
                        Notifications: Enabled

                        Driver Settings
                        Remote IP: 192.168.10.42
                        Extra args:
                        mibs = pw
                        pollfreq = 15
                        ignorelb

                        Advanced Settings
                        FINALDELAY 180
                        Addition configuration lines for ups.conf = LISTEN 192.168.10.1
                        Additional ups.users
                        [remoteuser]
                        password = mysupersecretpassword
                        upsmon slave

                        This provides the following status

                        UPS Status
                        Name: UPS@localhost
                        Summary status: On line
                        Runtime (H:M:S): 5:17:00
                        UPS Load:
                        36.00%
                        Battery charge:
                        100.00%
                        Battery voltage: 52.00
                        Input frequency: 60.00

                        1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage @q54e3w
                          last edited by

                          @q54e3w said in NUT package:

                          Poll UPS [UPS] failed - Write error: Permission denied

                          Is there anything that precedes this entry in the log? Perhaps something similar to this?

                          Q 1 Reply Last reply Reply Quote 0
                          • Q
                            q54e3w @dennypage
                            last edited by

                            @dennypage said in NUT package:

                            Is there anything that precedes this entry in the log? Perhaps something similar to this?

                            No, no other errors or messages from upsd/upsmon above or below that one. First sign of trouble is the Poll UPS failed.

                            dennypageD 1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage @q54e3w
                              last edited by

                              @q54e3w said in NUT package:

                              @dennypage said in NUT package:

                              Is there anything that precedes this entry in the log? Perhaps something similar to this?

                              No, no other errors or messages from upsd/upsmon above or below that one. First sign of trouble is the Poll UPS failed.

                              I wasn’t asking about other upsd/upsmon messages, rather I was asking about messages associated with links flapping, DHCP activities, etc. Similar to the logs in the link above.

                              1 Reply Last reply Reply Quote 0
                              • Q
                                q54e3w
                                last edited by

                                ahhhh, gotcha. There was another issue with UPnP that I resolved and thats when I noticed these entries. I'll keep an eye on it but as I haven't seen a repeat maybe it was related. Thank you.

                                1 Reply Last reply Reply Quote 0
                                • K
                                  kevindd992002
                                  last edited by

                                  @dennypage Why is it that in the NUT GUI I see different set of parameters shown between my two pfsense boxes (same version of pfsense, same hardware, same NUT version, different UPS but both USB):

                                  9aa33efe-6eac-4042-9246-31ff6fe2b983-image.png

                                  69a471ce-7e56-4929-ac85-6ba247eb3f51-image.png

                                  I'm missing battery voltage and last test result on the second one. Is this normal?

                                  dennypageD 1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage @kevindd992002
                                    last edited by

                                    @kevindd992002 said in NUT package:

                                    @dennypage Why is it that in the NUT GUI I see different set of parameters shown between my two pfsense boxes (same version of pfsense, same hardware, same NUT version, different UPS but both USB):

                                    I'm missing battery voltage and last test result on the second one. Is this normal?

                                    Not unusual. NUT only reports what what the UPS reports.

                                    1 Reply Last reply Reply Quote 0
                                    • GertjanG
                                      Gertjan
                                      last edited by Gertjan

                                      True.
                                      This wouldn't be very assuring :

                                      ff53a6fb-d976-4b1d-8368-10e3450bf821-image.png

                                      ( image is fake of course )

                                      No "help me" PM's please. Use the forum, the community will thank you.
                                      Edit : and where are the logs ??

                                      1 Reply Last reply Reply Quote 0
                                      • K
                                        kevindd992002
                                        last edited by

                                        Ok, that makes sense.

                                        Any idea what can causes a UPS battery low notification even though I don't see a UPS on battery message first? Here's what I get in the system logs:

                                        f78d92a0-dde1-4a24-80d0-87ec47b25e2e-image.png

                                        I've noticed this come and go since a few days ago and I don't know why. I was receiving email notifications about a batt low condition even without an on batt notification first. These are the settings I have:

                                        f554aa69-3e23-4f79-b960-6c0833783769-image.png

                                        eb698fb0-faff-4b96-b94a-21d0e380bdc2-image.png

                                        I don't see the charge.warning and charge.low that high. But what do you think?

                                        Also, how can I set the UPS (after a shutdown condition) to wait for a few minutes before it turns everything back on? Sort of a delay?

                                        GertjanG 1 Reply Last reply Reply Quote 0
                                        • GertjanG
                                          Gertjan @kevindd992002
                                          last edited by

                                          @kevindd992002 said in NUT package:

                                          causes a UPS battery low notification even though I don't see a UPS on battery message first?

                                          If a battery was a perfect device, it couldn't be low. But they are not. They always die .... which start with the tension that starts dropping. It isn't needed to be on battery to see that happen.
                                          It could also be the charging electronics that adapts it's loading tension, because the load current start to rise for some reason.

                                          Also, the "UPS battery low notification" could also be a generic message from the UPS that is shown "as is" by NUT.

                                          @kevindd992002 said in NUT package:

                                          Also, how can I set the UPS (after a shutdown condition) to wait for a few minutes before it turns everything back on? Sort of a delay?

                                          You should add a question to your question :
                                          Does my UPS supports this ?
                                          And if the answer is yes, ask another yourself another question : Is it possible with NUT and the UPS driver to communicate such a setting ?
                                          If yes, then yes, it can be done.
                                          How ? Dono. Up to you to search for it.

                                          Btw : the pfSense widget is nice to see the situation.
                                          But UPS's (batteries) should be observed over (very long) time spans. Use tools like this to see more info.

                                          No "help me" PM's please. Use the forum, the community will thank you.
                                          Edit : and where are the logs ??

                                          K 1 Reply Last reply Reply Quote 0
                                          • K
                                            kevindd992002 @Gertjan
                                            last edited by

                                            @Gertjan said in NUT package:

                                            @kevindd992002 said in NUT package:

                                            causes a UPS battery low notification even though I don't see a UPS on battery message first?

                                            If a battery was a perfect device, it couldn't be low. But they are not. They always die .... which start with the tension that starts dropping. It isn't needed to be on battery to see that happen.
                                            It could also be the charging electronics that adapts it's loading tension, because the load current start to rise for some reason.

                                            Also, the "UPS battery low notification" could also be a generic message from the UPS that is shown "as is" by NUT.

                                            That's the answer I'm expecting. I completely know that batteries tend to die, especially in hot climates. I just thought there's an issue with NUT or something because it was fine a few days ago. There was just a blackout a few weeks ago where the battery was fully depleted in about 10 minutes so I knew it was working fine.

                                            @kevindd992002 said in NUT package:

                                            Also, how can I set the UPS (after a shutdown condition) to wait for a few minutes before it turns everything back on? Sort of a delay?

                                            You should add a question to your question :
                                            Does my UPS supports this ?
                                            And if the answer is yes, ask another yourself another question : Is it possible with NUT and the UPS driver to communicate such a setting ?
                                            If yes, then yes, it can be done.
                                            How ? Dono. Up to you to search for it.

                                            Btw : the pfSense widget is nice to see the situation.
                                            But UPS's (batteries) should be observed over (very long) time spans. Use tools like this to see more info.

                                            Yes, I have to search if my UPS supports it. And yes, I'm sure NUT and the USB ups driver can communicate this setting. I read about it somewhere but cannot find that specific post anymore. This is why I posted here. I guess I have to search harder.

                                            What is that pfsense widget you've linked? Is it a package or something? I'm not seeing such a widget in the available widgets section.

                                            GertjanG 1 Reply Last reply Reply Quote 0