    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.8m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • F
      flu @dennypage
      last edited by

      @dennypage
      many thanks for the explanation.
      I guess the nut package could be changed so that it does not send messages like "Communications with UPS UPS lost" and "UPS UPS is unavailable" every time it gets restarted by pfsense?

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @flu
        last edited by

        @flu The email comes from NUT itself, rather than the pfSense NUT package. And from NUT's point of view, the connection to the UPS is actually being lost. This will be triggered by something that affects the USB or serial connectivity being restarted or reloaded underneath NUT. NUT doesn't know why the connection failed, it just knows that it failed so it sends the email. You should be able to see the order of events in the system log if you want to understand more about what is happening.

        1 Reply Last reply Reply Quote 0
        • K
          kevindd992002 @dennypage
          last edited by

          @dennypage So here's what I noticed recently in my system logs after receiving UPS communication lost and established emails:

          Feb 19 04:33:53 	php-cgi 		nut_email.php: Message sent to kevindd992002@yahoo.com OK
          Feb 19 04:33:49 	php-cgi 		nut_email.php: Message sent to kevindd992002@yahoo.com OK
          Feb 19 04:33:46 	upsmon 	43175 	Communications with UPS ups established
          Feb 19 04:33:44 	upsd 	86349 	UPS [ups] data is no longer stale
          Feb 19 04:33:41 	upsmon 	43175 	Communications with UPS ups lost
          Feb 19 04:33:41 	upsmon 	43175 	Poll UPS [ups] failed - Data stale
          Feb 19 04:33:41 	kernel 		ugen0.2: <EATON 5E> at usbus0
          Feb 19 04:33:38 	kernel 		ugen0.2: <EATON 5E> at usbus0 (disconnected)
          Feb 19 04:33:37 	upsd 	86349 	Data for UPS [ups] is stale - check driver
          

          What does "data is stale" even mean? And why does this happen intermittently?

          GertjanG 1 Reply Last reply Reply Quote 0
          • GertjanG
            Gertjan @kevindd992002
            last edited by

            @kevindd992002 said in NUT package:

            What does "data is stale" even mean? And why does this happen intermittently?

            Probably because :
            Feb 19 04:33:38 kernel ugen0.2: <EATON 5E> at usbus0 (disconnected)
            Feb 19 04:33:37 upsd 86349 Data for UPS [ups] is stale - check driver

            which says to me that the link between the driver (NUT ?) and the UPS device (cable, whatever) isn't "stable".

            No "help me" PM's please. Use the forum, the community will thank you.
            Edit : and where are the logs ??

            K 1 Reply Last reply Reply Quote 0
            • K
              kevindd992002 @Gertjan
              last edited by

              @Gertjan said in NUT package:

              @kevindd992002 said in NUT package:

              What does "data is stale" even mean? And why does this happen intermittently?

              Probably because :
              Feb 19 04:33:38 kernel ugen0.2: <EATON 5E> at usbus0 (disconnected)
              Feb 19 04:33:37 upsd 86349 Data for UPS [ups] is stale - check driver

              which says to me that the link between the driver (NUT ?) and the UPS device (cable, whatever) isn't "stable".

              Right but it's just weird that it happens randomly. It's not the UPS and cable because those were replaced already. I also tried using another usb port on the apu2c4 to no avail. There are only 2 usb ports available. Maybe the hub itself? How can you tell for sure though?

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage @kevindd992002
                last edited by

                @kevindd992002 It's either the host end or the UPS end. On the host end, it can be hardware (bridge controller) or software (kernel driver). On the UPS end it would just be a flakey USB implementation.

                What I generally recommend to people having these types of issues:

                • Try a different port on the host that uses a different bridge chip. Favor ports that are USB 2 as USB 3 ports usually have more problems.
                • If you have a USB hub between the host and the UPS, try removing it.
                • If you don't have a USB hub between the host and the UPS, try adding one.
                • Try a different USB hub that uses a different bridge chip.
                • Try a different UPS model.
                • Try a different host model.

                Regarding the apu2c4, you might find this an interesting read.

                Bonne chance

                1 Reply Last reply Reply Quote 0
                • Q
                  q54e3w
                  last edited by

                  @dennypage I'm seeing the following log entries under 2.4.5, anything to be concerned about?

                  Apr 16 07:09:28	upsmon	92379	Communications with UPS UPS established
                  Apr 16 07:09:28	upsd	33793	User local-monitor@127.0.0.1 logged into UPS [UPS]
                  Apr 16 07:09:23	upsmon	92379	Communications with UPS UPS lost
                  Apr 16 07:09:23	upsmon	92379	Poll UPS [UPS] failed - Write error: Permission denied
                  Apr 16 07:09:21	nginx		2020/04/16 07:09:21 [crit] 11971#100993: *62736 SSL_write() failed (13: Permission denied) while processing HTTP/2 connection, client: 192.168.20.115, server: 0.0.0.0:4433
                  Apr 16 07:08:43	upsmon	92379	Communications with UPS UPS established
                  Apr 16 07:08:43	upsd	33793	User local-monitor@127.0.0.1 logged into UPS [UPS]
                  Apr 16 07:08:38	upsmon	92379	Communications with UPS UPS lost
                  Apr 16 07:08:38	upsmon	92379	Poll UPS [UPS] failed - Write error: Permission denied
                  
                  dennypageD 2 Replies Last reply Reply Quote 0
                  • dennypageD
                    dennypage @q54e3w
                    last edited by

                    @q54e3w Can you provide information on your NUT configuration please?

                    1 Reply Last reply Reply Quote 0
                    • Q
                      q54e3w
                      last edited by

                      UPS is a network connected Eaton 9PX with Network Card 2.

                      UPS Type: Remote SNMP
                      UPS Name: UPS
                      Notifications: Enabled

                      Driver Settings
                      Remote IP: 192.168.10.42
                      Extra args:
                      mibs = pw
                      pollfreq = 15
                      ignorelb

                      Advanced Settings
                      FINALDELAY 180
                      Addition configuration lines for ups.conf = LISTEN 192.168.10.1
                      Additional ups.users
                      [remoteuser]
                      password = mysupersecretpassword
                      upsmon slave

                      This provides the following status

                      UPS Status
                      Name: UPS@localhost
                      Summary status: On line
                      Runtime (H:M:S): 5:17:00
                      UPS Load:
                      36.00%
                      Battery charge:
                      100.00%
                      Battery voltage: 52.00
                      Input frequency: 60.00

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @q54e3w
                        last edited by

                        @q54e3w said in NUT package:

                        Poll UPS [UPS] failed - Write error: Permission denied

                        Is there anything that precedes this entry in the log? Perhaps something similar to this?

                        Q 1 Reply Last reply Reply Quote 0
                        • Q
                          q54e3w @dennypage
                          last edited by

                          @dennypage said in NUT package:

                          Is there anything that precedes this entry in the log? Perhaps something similar to this?

                          No, no other errors or messages from upsd/upsmon above or below that one. First sign of trouble is the Poll UPS failed.

                          dennypageD 1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @q54e3w
                            last edited by

                            @q54e3w said in NUT package:

                            @dennypage said in NUT package:

                            Is there anything that precedes this entry in the log? Perhaps something similar to this?

                            No, no other errors or messages from upsd/upsmon above or below that one. First sign of trouble is the Poll UPS failed.

                            I wasn’t asking about other upsd/upsmon messages, rather I was asking about messages associated with links flapping, DHCP activities, etc. Similar to the logs in the link above.

                            1 Reply Last reply Reply Quote 0
                            • Q
                              q54e3w
                              last edited by

                              ahhhh, gotcha. There was another issue with UPnP that I resolved and thats when I noticed these entries. I'll keep an eye on it but as I haven't seen a repeat maybe it was related. Thank you.

                              1 Reply Last reply Reply Quote 0
                              • K
                                kevindd992002
                                last edited by

                                @dennypage Why is it that in the NUT GUI I see different set of parameters shown between my two pfsense boxes (same version of pfsense, same hardware, same NUT version, different UPS but both USB):

                                9aa33efe-6eac-4042-9246-31ff6fe2b983-image.png

                                69a471ce-7e56-4929-ac85-6ba247eb3f51-image.png

                                I'm missing battery voltage and last test result on the second one. Is this normal?

                                dennypageD 1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage @kevindd992002
                                  last edited by

                                  @kevindd992002 said in NUT package:

                                  @dennypage Why is it that in the NUT GUI I see different set of parameters shown between my two pfsense boxes (same version of pfsense, same hardware, same NUT version, different UPS but both USB):

                                  I'm missing battery voltage and last test result on the second one. Is this normal?

                                  Not unusual. NUT only reports what what the UPS reports.

                                  1 Reply Last reply Reply Quote 0
                                  • GertjanG
                                    Gertjan
                                    last edited by Gertjan

                                    True.
                                    This wouldn't be very assuring :

                                    ff53a6fb-d976-4b1d-8368-10e3450bf821-image.png

                                    ( image is fake of course )

                                    No "help me" PM's please. Use the forum, the community will thank you.
                                    Edit : and where are the logs ??

                                    1 Reply Last reply Reply Quote 0
                                    • K
                                      kevindd992002
                                      last edited by

                                      Ok, that makes sense.

                                      Any idea what can causes a UPS battery low notification even though I don't see a UPS on battery message first? Here's what I get in the system logs:

                                      f78d92a0-dde1-4a24-80d0-87ec47b25e2e-image.png

                                      I've noticed this come and go since a few days ago and I don't know why. I was receiving email notifications about a batt low condition even without an on batt notification first. These are the settings I have:

                                      f554aa69-3e23-4f79-b960-6c0833783769-image.png

                                      eb698fb0-faff-4b96-b94a-21d0e380bdc2-image.png

                                      I don't see the charge.warning and charge.low that high. But what do you think?

                                      Also, how can I set the UPS (after a shutdown condition) to wait for a few minutes before it turns everything back on? Sort of a delay?

                                      GertjanG 1 Reply Last reply Reply Quote 0
                                      • GertjanG
                                        Gertjan @kevindd992002
                                        last edited by

                                        @kevindd992002 said in NUT package:

                                        causes a UPS battery low notification even though I don't see a UPS on battery message first?

                                        If a battery was a perfect device, it couldn't be low. But they are not. They always die .... which start with the tension that starts dropping. It isn't needed to be on battery to see that happen.
                                        It could also be the charging electronics that adapts it's loading tension, because the load current start to rise for some reason.

                                        Also, the "UPS battery low notification" could also be a generic message from the UPS that is shown "as is" by NUT.

                                        @kevindd992002 said in NUT package:

                                        Also, how can I set the UPS (after a shutdown condition) to wait for a few minutes before it turns everything back on? Sort of a delay?

                                        You should add a question to your question :
                                        Does my UPS supports this ?
                                        And if the answer is yes, ask another yourself another question : Is it possible with NUT and the UPS driver to communicate such a setting ?
                                        If yes, then yes, it can be done.
                                        How ? Dono. Up to you to search for it.

                                        Btw : the pfSense widget is nice to see the situation.
                                        But UPS's (batteries) should be observed over (very long) time spans. Use tools like this to see more info.

                                        No "help me" PM's please. Use the forum, the community will thank you.
                                        Edit : and where are the logs ??

                                        K 1 Reply Last reply Reply Quote 0
                                        • K
                                          kevindd992002 @Gertjan
                                          last edited by

                                          @Gertjan said in NUT package:

                                          @kevindd992002 said in NUT package:

                                          causes a UPS battery low notification even though I don't see a UPS on battery message first?

                                          If a battery was a perfect device, it couldn't be low. But they are not. They always die .... which start with the tension that starts dropping. It isn't needed to be on battery to see that happen.
                                          It could also be the charging electronics that adapts it's loading tension, because the load current start to rise for some reason.

                                          Also, the "UPS battery low notification" could also be a generic message from the UPS that is shown "as is" by NUT.

                                          That's the answer I'm expecting. I completely know that batteries tend to die, especially in hot climates. I just thought there's an issue with NUT or something because it was fine a few days ago. There was just a blackout a few weeks ago where the battery was fully depleted in about 10 minutes so I knew it was working fine.

                                          @kevindd992002 said in NUT package:

                                          Also, how can I set the UPS (after a shutdown condition) to wait for a few minutes before it turns everything back on? Sort of a delay?

                                          You should add a question to your question :
                                          Does my UPS supports this ?
                                          And if the answer is yes, ask another yourself another question : Is it possible with NUT and the UPS driver to communicate such a setting ?
                                          If yes, then yes, it can be done.
                                          How ? Dono. Up to you to search for it.

                                          Btw : the pfSense widget is nice to see the situation.
                                          But UPS's (batteries) should be observed over (very long) time spans. Use tools like this to see more info.

                                          Yes, I have to search if my UPS supports it. And yes, I'm sure NUT and the USB ups driver can communicate this setting. I read about it somewhere but cannot find that specific post anymore. This is why I posted here. I guess I have to search harder.

                                          What is that pfsense widget you've linked? Is it a package or something? I'm not seeing such a widget in the available widgets section.

                                          GertjanG 1 Reply Last reply Reply Quote 0
                                          • GertjanG
                                            Gertjan @kevindd992002
                                            last edited by Gertjan

                                            @kevindd992002 said in NUT package:

                                            I guess I have to search harder.

                                            Or being lucky : someone knows what you're asking, and has the same UPS as you (APC SUA750).
                                            I advise you to put chances on your side ;)

                                            @kevindd992002 said in NUT package:

                                            package or something?

                                            Munin.
                                            It exists as a native FreeBSD package. To install it, the traditional FreeBSD CLI commands are needed.
                                            You also need a web server 'some where' that will be hosting the Munin RRD-to-Images.
                                            This means a Munin-client on pfSense, and a Munin server somewhere else.
                                            I have multiple servers, so it somewhat pays of for me to use such a graph service. It reveals a lot of info over time.

                                            No "help me" PM's please. Use the forum, the community will thank you.
                                            Edit : and where are the logs ??

                                            K 1 Reply Last reply Reply Quote 0