    Notification: UPS ups battery is low

    Scheduled Pinned Locked Moved UPS Tools
    19 Posts 2 Posters 3.0k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • F Offline
      fjmp24 @dennypage
      last edited by

      @dennypage I changed the battery this year. I don't understand : "Have you done a calibration test" ?

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD Offline
        dennypage @fjmp24
        last edited by

        @fjmp24 said in Notification: UPS ups battery is low:

        I don't understand : "Have you done a calibration test" ?

        Most UPSs have a "battery calibration test", "runtime calibration test", etc. You are looking for a test that runs the load off of the battery (without cutting mains) to see how the battery behaves under actual load.

        Btw, you should remove the ignorelb directive from the Extra Arguments to driver section. Unless you have a very old UPS that signals low battery whenever the UPS is on battery. You almost certainly do not have such a UPS.

        F 1 Reply Last reply Reply Quote 0
        • F Offline
          fjmp24 @dennypage
          last edited by

          @dennypage My UPD indicate runtime: 18:21

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD Offline
            dennypage @fjmp24
            last edited by

            @fjmp24 said in Notification: UPS ups battery is low:

            @dennypage My UPD indicate runtime: 18:21

            Yes, but that may be completely inaccurate, especially with bad batteries. That's why you run a calibration test.

            F 1 Reply Last reply Reply Quote 0
            • F Offline
              fjmp24 @dennypage
              last edited by

              @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

              I don't understand anything :-((

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD Offline
                dennypage @fjmp24
                last edited by

                @fjmp24 said in Notification: UPS ups battery is low:

                @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                Also, you do not have anything in the Advanced settings section, correct?

                As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                F 1 Reply Last reply Reply Quote 0
                • F Offline
                  fjmp24 @dennypage
                  last edited by

                  I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                  Ok, I will test without ignorelb directive.

                  Also, you do not have anything in the Advanced settings section, correct?

                  Yes

                  As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                  I find anything I will search tomorow

                  F 1 Reply Last reply Reply Quote 0
                  • F Offline
                    fjmp24 @fjmp24
                    last edited by

                    If I remove ignorelb directive, my UPS shuts down after 16 seconds

                    F dennypageD 2 Replies Last reply Reply Quote 0
                    • F Offline
                      fjmp24 @fjmp24
                      last edited by

                      My UPD do an automatic battery test regularly to warn when a replacement of the current battery needs to be carried out.

                      1 Reply Last reply Reply Quote 0
                      • dennypageD Offline
                        dennypage @fjmp24
                        last edited by

                        @fjmp24 said in Notification: UPS ups battery is low:

                        If I remove ignorelb directive, my UPS shuts down after 16 seconds

                        This means your UPS is signaling a low battery. Either your battery is bad, or your UPS is bad. Most likely battery, but you never know. I suggest reaching out to Eaton support.

                        1 Reply Last reply Reply Quote 1