    NUT dashboard widget

    Scheduled Pinned Locked Moved UPS Tools
    43 Posts 5 Posters 5.9k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic was forked from QNAP recognizing NUT dennypage
    This topic has been deleted. Only users with topic management privileges can see it.
    • demD
      dem
      last edited by

      Some older CyberPower units report bogus data for items such as output voltage. One of mine says this:

      input.voltage: 121.0
      input.voltage.nominal: 120
      output.voltage: 137.0
      

      On an even older one I recall the battery voltage being nonsensical as well.

      It would be nice to be able to keep such incorrect values from being shown as they can be annoying.

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @dem
        last edited by

        @dem said in NUT dashboard widget:

        On an even older one I recall the battery voltage being nonsensical as well.

        The widget (and status page) can only report what it sees reported by upsc. A nonsensical value indicates either a bad value coming out of the UPS, or broken interpretation by the driver. I'm afraid I cannot fix that.

        demD 1 Reply Last reply Reply Quote 0
        • demD
          dem @dennypage
          last edited by

          Then perhaps an option not to show the new "extended" information. Fortunately the UPS I'm currently using with pfSense shows the output voltage correctly, but I don't need to be reminded that I never bother with self-tests. 🙂

          Lately the power utility has been regularly testing the UPS for me anyway. 😠

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @dem
            last edited by

            @dem said in NUT dashboard widget:

            I don't need to be reminded that I never bother with self-tests.

            I think it is good to be reminded, however I would expect that if you can ignore self tests for the UPS you can also ignore the last test info. 🙂

            A UPS is critical infrastructure. You want to know if there are issues with it. The last test date and test result are important. This and the battery date are the big reasons that I am updating the widget. The colorization is a nice to have.

            1 Reply Last reply Reply Quote 0
            • F
              FrankZappa @dennypage
              last edited by

              @dennypage Wow! Didn't expect it that fast. Love it! Is there any way to display when and why UPS went to battery last time?

              Thanks for making this.

              F dennypageD 2 Replies Last reply Reply Quote 0
              • F
                FrankZappa @FrankZappa
                last edited by

                @FrankZappa Also, I really like the colors to make it pop in the dashboard. If the battery is not charged to 100% does the bar graph change to yellow, and maybe once it gets down to 50% can it turn red? Just thought it would look cool (not that I want my battery to ever get down to 50%). Thanks

                F 1 Reply Last reply Reply Quote 0
                • F
                  FrankZappa @FrankZappa
                  last edited by

                  @FrankZappa Mine is showing the wrong battery date and I don't have the last test. Other than that, it looks great.
                  3f5f1d26-ee48-4a60-ba8a-dfc70be37953-image.png

                  1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage @FrankZappa
                    last edited by

                    @FrankZappa said in NUT dashboard widget:

                    Wow! Didn't expect it that fast. Love it!

                    Glad you like it. I had some time...

                    @FrankZappa said in NUT dashboard widget:

                    Is there any way to display when and why UPS went to battery last time?

                    I don't believe this is reported. I have a fairly high end APC, and I don't have it. Best alternative is enabling notifications and then you'll get a real-time notification of transfers.

                    @FrankZappa said in NUT dashboard widget:

                    I really like the colors to make it pop in the dashboard. If the battery is not charged to 100% does the bar graph change to yellow, and maybe once it gets down to 50% can it turn red?

                    The battery bar is red below 50%, yellow below 75%, otherwise green. Same for the summary icon, which shows plug, battery (with levels), and unknown. Even if the UPS is on line, if the UPS reports that the battery needs replacing, or if the UPS is overloaded, the plug icon will remain red.

                    The load bar is green below 95%, yellow below 99%, and red above.

                    @FrankZappa said in NUT dashboard widget:

                    Mine is showing the wrong battery date and I don't have the last test.

                    The 2001/09/25 date kinda looks like a "never been set" value. Look for "battery.date" in Services / UPS / UPS Status. This is what is reported to/by NUT. What do you see there?

                    For test info, look for "ups.test.date" and/or "ups.test.result" in Services / UPS /UPS Status. Are these being reported by the UPS to NUT?

                    F T 2 Replies Last reply Reply Quote 0
                    • F
                      FrankZappa @dennypage
                      last edited by

                      @dennypage Thanks dennypage. Here's a screenshot of everything I have.
                      7074717a-e238-4700-b97b-7799530905d3-image.png

                      dennypageD 2 Replies Last reply Reply Quote 0
                      • T
                        tgl
                        last edited by

                        I'm not sure what "battery.date" is really meant to be, but it reads as 2001/09/25 on my APC UPSes too. Maybe it identifies the age of the design? Anyway, these fields seem considerably more plausible as the real age of the one I'm looking at:

                        battery.mfr.date: 2022/04/13
                        ups.mfr.date: 2022/04/13

                        dennypageD 1 Reply Last reply Reply Quote 0
                        • T
                          tgl @dennypage
                          last edited by

                          @dennypage said in NUT dashboard widget:

                          For test info, look for "ups.test.date" and/or "ups.test.result" in Services / UPS /UPS Status. Are these being reported by the UPS to NUT?

                          A field like "ups.test.date" could only get populated accurately if the UPS contains an RTC. I've owned a lot of UPSes over the years, and never seen any indication that they have settable clocks. The date fields they do output all look like burned-in-at-the-factory values.

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage @FrankZappa
                            last edited by

                            @FrankZappa So, your battery date really does show as 2001/09/25. I believe this means that it was not set at the factory. Looks like the apcupsd widget was reporting the UPS manufacture date rather than the battery install date.

                            To set the battery date, you can (hopefully) use upsrw.

                            Use

                            upsrw -l UPSNAME
                            

                            to see what variables you can write in the UPS. The variable you are looking for is "battery.date".

                            Your "ups.test.result" shows that no self test has been run on the UPS. For higher end APC UPSs, this is done by automatic timer. For lower end UPSs, you have to trigger it manually. If you do that, you will have to write the test date yourself--look for variable "ups.test.date" in the upsrw output.

                            F 1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage @tgl
                              last edited by

                              @tgl said in NUT dashboard widget:

                              I'm not sure what "battery.date" is really meant to be, but it reads as 2001/09/25 on my APC UPSes too.

                              See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

                              If the UPS doesn't have time capability, then you are responsible for maintaining this field by hand when you initially install and/or change batteries.

                              If your UPS has a network management card, this would be handled automatically. My current APC is like this.

                              T 1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage @FrankZappa
                                last edited by

                                @FrankZappa Forgot to mention. To run a self-test, would use upscmd. To see a list of commands the UPS will accept, use:

                                upscmd -l UPSNAME
                                

                                Most likely, the command will be:

                                upscmd UPSNAME test.battery.start
                                
                                1 Reply Last reply Reply Quote 0
                                • T
                                  tgl @dennypage
                                  last edited by

                                  @dennypage said in NUT dashboard widget:

                                  See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

                                  On mine, it's not settable period. "upsrw -l" claims to be able to set "battery.mfr.date", but not any other kind of date.

                                  dennypageD 1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage @tgl
                                    last edited by dennypage

                                    @tgl What brand/model?

                                    FWIW, "ups.mfr.date" is a standard field, but I don't recall ever seeing "battery.mfr.date"

                                    T 1 Reply Last reply Reply Quote 0
                                    • T
                                      tgl @dennypage
                                      last edited by

                                      @dennypage
                                      APC Back-UPS Pro BR1500MS2

                                      dennypageD 1 Reply Last reply Reply Quote 0
                                      • dennypageD
                                        dennypage @tgl
                                        last edited by

                                        @tgl Please post Services / UPS / Status.

                                        T 1 Reply Last reply Reply Quote 0
                                        • T
                                          tgl @dennypage
                                          last edited by

                                          @dennypage said in NUT dashboard widget:

                                          @tgl Please post Services / UPS / Status.

                                          I don't actually have NUT installed on my router (yet); this UPS is connected to a Linux server. "upsc" reports what I suppose you want:

                                          battery.charge: 100
                                          battery.charge.low: 10
                                          battery.charge.warning: 50
                                          battery.date: 2001/09/25
                                          battery.mfr.date: 2022/04/13
                                          battery.runtime: 4152
                                          battery.runtime.low: 120
                                          battery.type: PbAc
                                          battery.voltage: 27.3
                                          battery.voltage.nominal: 24.0
                                          device.mfr: American Power Conversion
                                          device.model: Back-UPS RS 1500MS2
                                          device.serial: 0B2216N04901  
                                          device.type: ups
                                          driver.name: usbhid-ups
                                          driver.parameter.offdelay: 50
                                          driver.parameter.ondelay: 60
                                          driver.parameter.pollfreq: 100
                                          driver.parameter.pollinterval: 10
                                          driver.parameter.port: auto
                                          driver.parameter.synchronous: auto
                                          driver.version: 2.8.0
                                          driver.version.data: APC HID 0.98
                                          driver.version.internal: 0.47
                                          driver.version.usb: libusb-1.0.23 (API: 0x1000107)
                                          input.sensitivity: medium
                                          input.transfer.high: 147
                                          input.transfer.low: 88
                                          input.voltage: 124.0
                                          input.voltage.nominal: 120
                                          ups.beeper.status: disabled
                                          ups.delay.shutdown: 50
                                          ups.firmware: 969.e2 .D
                                          ups.firmware.aux: e2     
                                          ups.load: 10
                                          ups.mfr: American Power Conversion
                                          ups.mfr.date: 2022/04/13
                                          ups.model: Back-UPS RS 1500MS2
                                          ups.productid: 0002
                                          ups.realpower.nominal: 900
                                          ups.serial: 0B2216N04901  
                                          ups.status: OL
                                          ups.test.result: No test initiated
                                          ups.timer.reboot: 0
                                          ups.timer.shutdown: -1
                                          ups.vendorid: 051d
                                          
                                          dennypageD 1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage @tgl
                                            last edited by

                                            @tgl two quick questions:

                                            • Output of upsrw -l
                                            • Version of NUT
                                            T 1 Reply Last reply Reply Quote 0