    NUT dashboard widget

    Scheduled Pinned Locked Moved UPS Tools
    43 Posts 5 Posters 5.2k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic was forked from QNAP recognizing NUT dennypage
    This topic has been deleted. Only users with topic management privileges can see it.
    • T
      tgl @dennypage
      last edited by

      @dennypage said in NUT dashboard widget:

      For test info, look for "ups.test.date" and/or "ups.test.result" in Services / UPS /UPS Status. Are these being reported by the UPS to NUT?

      A field like "ups.test.date" could only get populated accurately if the UPS contains an RTC. I've owned a lot of UPSes over the years, and never seen any indication that they have settable clocks. The date fields they do output all look like burned-in-at-the-factory values.

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @FrankZappa
        last edited by

        @FrankZappa So, your battery date really does show as 2001/09/25. I believe this means that it was not set at the factory. Looks like the apcupsd widget was reporting the UPS manufacture date rather than the battery install date.

        To set the battery date, you can (hopefully) use upsrw.

        Use

        upsrw -l UPSNAME
        

        to see what variables you can write in the UPS. The variable you are looking for is "battery.date".

        Your "ups.test.result" shows that no self test has been run on the UPS. For higher end APC UPSs, this is done by automatic timer. For lower end UPSs, you have to trigger it manually. If you do that, you will have to write the test date yourself--look for variable "ups.test.date" in the upsrw output.

        F 1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @tgl
          last edited by

          @tgl said in NUT dashboard widget:

          I'm not sure what "battery.date" is really meant to be, but it reads as 2001/09/25 on my APC UPSes too.

          See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

          If the UPS doesn't have time capability, then you are responsible for maintaining this field by hand when you initially install and/or change batteries.

          If your UPS has a network management card, this would be handled automatically. My current APC is like this.

          T 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @FrankZappa
            last edited by

            @FrankZappa Forgot to mention. To run a self-test, would use upscmd. To see a list of commands the UPS will accept, use:

            upscmd -l UPSNAME
            

            Most likely, the command will be:

            upscmd UPSNAME test.battery.start
            
            1 Reply Last reply Reply Quote 0
            • T
              tgl @dennypage
              last edited by

              @dennypage said in NUT dashboard widget:

              See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

              On mine, it's not settable period. "upsrw -l" claims to be able to set "battery.mfr.date", but not any other kind of date.

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage @tgl
                last edited by dennypage

                @tgl What brand/model?

                FWIW, "ups.mfr.date" is a standard field, but I don't recall ever seeing "battery.mfr.date"

                T 1 Reply Last reply Reply Quote 0
                • T
                  tgl @dennypage
                  last edited by

                  @dennypage
                  APC Back-UPS Pro BR1500MS2

                  dennypageD 1 Reply Last reply Reply Quote 0
                  • dennypageD
                    dennypage @tgl
                    last edited by

                    @tgl Please post Services / UPS / Status.

                    T 1 Reply Last reply Reply Quote 0
                    • T
                      tgl @dennypage
                      last edited by

                      @dennypage said in NUT dashboard widget:

                      @tgl Please post Services / UPS / Status.

                      I don't actually have NUT installed on my router (yet); this UPS is connected to a Linux server. "upsc" reports what I suppose you want:

                      battery.charge: 100
                      battery.charge.low: 10
                      battery.charge.warning: 50
                      battery.date: 2001/09/25
                      battery.mfr.date: 2022/04/13
                      battery.runtime: 4152
                      battery.runtime.low: 120
                      battery.type: PbAc
                      battery.voltage: 27.3
                      battery.voltage.nominal: 24.0
                      device.mfr: American Power Conversion
                      device.model: Back-UPS RS 1500MS2
                      device.serial: 0B2216N04901  
                      device.type: ups
                      driver.name: usbhid-ups
                      driver.parameter.offdelay: 50
                      driver.parameter.ondelay: 60
                      driver.parameter.pollfreq: 100
                      driver.parameter.pollinterval: 10
                      driver.parameter.port: auto
                      driver.parameter.synchronous: auto
                      driver.version: 2.8.0
                      driver.version.data: APC HID 0.98
                      driver.version.internal: 0.47
                      driver.version.usb: libusb-1.0.23 (API: 0x1000107)
                      input.sensitivity: medium
                      input.transfer.high: 147
                      input.transfer.low: 88
                      input.voltage: 124.0
                      input.voltage.nominal: 120
                      ups.beeper.status: disabled
                      ups.delay.shutdown: 50
                      ups.firmware: 969.e2 .D
                      ups.firmware.aux: e2     
                      ups.load: 10
                      ups.mfr: American Power Conversion
                      ups.mfr.date: 2022/04/13
                      ups.model: Back-UPS RS 1500MS2
                      ups.productid: 0002
                      ups.realpower.nominal: 900
                      ups.serial: 0B2216N04901  
                      ups.status: OL
                      ups.test.result: No test initiated
                      ups.timer.reboot: 0
                      ups.timer.shutdown: -1
                      ups.vendorid: 051d
                      
                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @tgl
                        last edited by

                        @tgl two quick questions:

                        • Output of upsrw -l
                        • Version of NUT
                        T 1 Reply Last reply Reply Quote 0
                        • T
                          tgl @dennypage
                          last edited by

                          @dennypage

                          Sure:

                          $ upsrw -l xxx_ups
                          [battery.charge.low]
                          Remaining battery level when UPS switches to LB (percent)
                          Type: STRING
                          Maximum length: 10
                          Value: 10
                          
                          [battery.mfr.date]
                          Battery manufacturing date
                          Type: STRING
                          Maximum length: 10
                          Value: 2022/04/13
                          
                          [battery.runtime.low]
                          Remaining battery runtime when UPS switches to LB (seconds)
                          Type: STRING
                          Maximum length: 10
                          Value: 120
                          
                          [input.sensitivity]
                          Input power sensitivity
                          Type: STRING
                          Maximum length: 10
                          Value: medium
                          
                          [input.transfer.high]
                          High voltage transfer point (V)
                          Type: STRING
                          Maximum length: 10
                          Value: 147
                          
                          [input.transfer.low]
                          Low voltage transfer point (V)
                          Type: STRING
                          Maximum length: 10
                          Value: 88
                          
                          [ups.delay.shutdown]
                          Interval to wait after shutdown with delay command (seconds)
                          Type: STRING
                          Maximum length: 10
                          Value: 50
                          
                          

                          The Linux machine is running RHEL8, and its relevant packages are

                          $ rpm -qa | grep ^nut
                          nut-2.8.0-3.el8.x86_64
                          nut-client-2.8.0-3.el8.x86_64
                          $ rpm -qa | grep ^libusb
                          libusb-0.1.5-12.el8.x86_64
                          libusbx-devel-1.0.23-4.el8.x86_64
                          libusbx-1.0.23-4.el8.x86_64
                          libusb-devel-0.1.5-12.el8.x86_64
                          libusbmuxd-1.0.10-9.el8.x86_64
                          
                          dennypageD 1 Reply Last reply Reply Quote 0
                          • F
                            FrankZappa @dennypage
                            last edited by

                            @dennypage Hmmmm, tried to change the battery date but was asked for a password. Huh?

                            e3cb8abd-d85c-4a7b-8c65-3f741fd71856-image.png

                            GertjanG dennypageD 2 Replies Last reply Reply Quote 0
                            • GertjanG
                              Gertjan @FrankZappa
                              last edited by

                              @FrankZappa

                              Use the real command line, console or SSH for this - option 8.

                              Start with :

                              cat /usr/local/etc/nut/upsd.users
                              

                              and if all goes well, you see the 'user 'admin, and the password to use.

                              No "help me" PM's please. Use the forum, the community will thank you.
                              Edit : and where are the logs ??

                              1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage @FrankZappa
                                last edited by

                                @FrankZappa said in NUT dashboard widget:

                                Hmmmm, tried to change the battery date but was asked for a password. Huh?

                                Yes, writing requires an authorized NUT user. The actual command you will want is:

                                upsrw -s battery.date=2024/05/20 -u admin -p PASSWORD QNAPUPS
                                

                                The admin password is automatically generated when you save the NUT configuration. As @Gertjan notes, you can find the current password in /usr/local/etc/nut/upsd.users.

                                Btw, be sure the date is in the same locale format as upsc outputs.

                                It's easiest to do this all in an ssh session.

                                F 1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage @tgl
                                  last edited by dennypage

                                  @tgl said in NUT dashboard widget:

                                  [battery.mfr.date]
                                  Battery manufacturing date
                                  Type: STRING
                                  Maximum length: 10
                                  Value: 2022/04/13

                                  This looks like a bug in the usbhid-ups driver. The UPS variable being mapped to battery.mfr.date should have been mapped to battery.date. There appear to be other bugs: on my main (new generation) APC, most of the dates and voltages disappear when switching to the USB interface (vs the SNMP interface). I'll dig into this when I have time.

                                  Btw, if interested you can find a list of all possible variables here. Variable "battery.date" is defined as "Battery installation or last change date." Variable "battery.mfr.date" is defined as "Battery manufacturing date", and was read-only prior to NUT 8.0.

                                  1 Reply Last reply Reply Quote 0
                                  • F
                                    FrankZappa @dennypage
                                    last edited by

                                    @dennypage said in NUT dashboard widget:

                                    upsrw -s battery.date=2024/05/20 -u admin -p PASSWORD QNAPUPS

                                    I tried it with the password and i get the following error "Unexpected response from upsd: ERR READONLY"

                                    F 1 Reply Last reply Reply Quote 0
                                    • F
                                      FrankZappa @FrankZappa
                                      last edited by

                                      @FrankZappa Also noticed there are two entries in the NUT Services/UPS/Status
                                      battery.date 2001/09/25
                                      battery.mfr.date 2021/04/10

                                      The battery.mfr.date is correct. Thats when I bought the APC.
                                      However, the battery.date (and install date on widget) is waaaaaaay off. Can the widget reflect the battery.mfr.date?

                                      dennypageD 1 Reply Last reply Reply Quote 0
                                      • dennypageD
                                        dennypage @FrankZappa
                                        last edited by

                                        @FrankZappa said in NUT dashboard widget:

                                        battery.date 2001/09/25
                                        battery.mfr.date 2021/04/10

                                        The battery.mfr.date is correct. Thats when I bought the APC.
                                        However, the battery.date (and install date on widget) is waaaaaaay off. Can the widget reflect the battery.mfr.date?

                                        I've researched a bit, and it appears that the battery date situation with USB UPSs is a bit messed up. In addition to issues like battery.date vs battery.mfr.date you and @tgl encountered with APC, the CyberPower issues appear even worse.

                                        Truth be told, it probably isn't all NUT's fault as it looks like the manufacturers don't seem to completely agree how the dates should map with USB ids.

                                        I think for the time being I'm going to pull the battery install date out of the status widget, at least for USB UPSs. I think as things currently are it would end up causing too much confusion with folks. I'll revisit it in the future.

                                        T 1 Reply Last reply Reply Quote 0
                                        • T
                                          tgl @dennypage
                                          last edited by

                                          @dennypage said in NUT dashboard widget:

                                          I think for the time being I'm going to pull the battery install date out of the status widget, at least for USB UPSs. I think as things currently are it would end up causing too much confusion with folks. I'll revisit it in the future.

                                          Maybe, if the UPS reports both battery.date and battery.mfr.date, you could show the later one?

                                          F dennypageD 2 Replies Last reply Reply Quote 0
                                          • F
                                            FrankZappa @tgl
                                            last edited by

                                            @tgl I was thinking the same thing, but didn't want to bug Dennypage anymore. Of course, if Dennypage is bored........well?

                                            1 Reply Last reply Reply Quote 0