    • dennypageD
      dennypage
      last edited by

      @alanper:

      I have attached screenshots of my UPS status and settings page.  Yep, seeing the values on the UPS Status page.

      The warning that the UPS requires attention appears to be correct. Note that the status is "On line, Bypass"? Bypass is bad. Bypass means that the UPS inverter has been bypassed and will not take over if the mains fail. If you scroll down to the bottom of the UPS Detail section, you should see a field titled "ups.alarm" which will hopefully give you a better indication of why bypass is active.

      I'm surprised that there wouldn't be an alarm going off on the thing.

      1 Reply Last reply Reply Quote 0
      • A
        alanper
        last edited by

        @dennypage:

        @alanper:

        I have attached screenshots of my UPS status and settings page.  Yep, seeing the values on the UPS Status page.

        The warning that the UPS requires attention appears to be correct. Note that the status is "On line, Bypass"? Bypass is bad. Bypass means that the UPS inverter has been bypassed and will not take over if the mains fail. If you scroll down to the bottom of the UPS Detail section, you should see a field titled "ups.alarm" which will hopefully give you a better indication of why bypass is active.

        I'm surprised that there wouldn't be an alarm going off on the thing.

        For all intents and purposes, the UPS is functioning correctly (aside from the bypass status reading).  I am using a generic UPS driver for NUT (it was a trial and error process at the time to find a driver that worked as there was none from the UPS manufacturer), perhaps that is the cause for the "incorrect" bypass reading (I say incorrect because if I disconnect the mains the UPS functions correctly).  Anyway, it's not a major problem for me as it is just aesthetics for now.

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          Okay, glad it's working.

          Was nutdrv_qx one of the drivers you tried?

          1 Reply Last reply Reply Quote 0
          • A
            alanper
            last edited by

            @dennypage:

            Okay, glad it's working.

            Was nutdrv_qx one of the drivers you tried?

            I don't recall specifically at the time if I tried the driver.  However, I tried it today and it does not work.  Currently the blazer_ser driver is working (the best) for my setup.

            1 Reply Last reply Reply Quote 0
            • dennypageD
              dennypage
              last edited by

              Thanks alanper, appreciate you letting me know.

              1 Reply Last reply Reply Quote 0
              • S
                stevel
                last edited by

                Hi

                I have recently upgraded to 2.3 - specifically 2.3.2-RELEASE-p1 (i386) - on my Alix device. In the process NUT was upgraded to 2.7.4_3. On visiting the NUT service page I was asked to confirm the upgrade settings. The UPS Type (local serial) and Driver (apcsmart) had been preserved so I didn't think further and hit 'save'. NUT didn't work despite restart. I believe I know why as I have successfully worked around…

                By hitting 'save' I overwrote the correct serial port setting with one of the ones presented by the drop-down on the serial port field. The issue seems to be this... the serial port only allowed me to choose from the two built in UARTS on the board /dev/cuau[0-1]. I have a USB-to-serial adapter and this assigns a character device called /dev/cuaU0 (note U/C 'U'). Once I had SSH'd into the box and spotted the issue, editing the conf file and restarting NUT cause everything to spring back into life.

                I should also say that I am new to this sort of meddling with conf files. I think these are not really the masters as far as configuration is concerned, i.e. they are auto-generated from elsewhere. i can see, for example that my entries in the other ups*.conf files are not reflected in the NUT UI. Should I be doing this a different way?

                BTW, thanks for all the efforts porting this service, I hope this feedback proves useful.

                Regards

                • Steve
                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  Sorry about the problem Steve. Best that I can tell, in FreeBSD 10.3 and above call-out serial ports are all supposed to match the pattern "/dev/cuau?" which the device you have doesn't. Is the driver for this adapter included in the FreeBSD distribution or is it something that you had to install separately from the vendor? Can you tell me the name of the driver?

                  I don't have an issue adding support for uppercase 'U', but I would like to make I understand what's going on first. Thanks.

                  @stevel:

                  The issue seems to be this… the serial port only allowed me to choose from the two built in UARTS on the board /dev/cuau[0-1]. I have a USB-to-serial adapter and this assigns a character device called /dev/cuaU0 (note U/C 'U').

                  1 Reply Last reply Reply Quote 0
                  • S
                    stevel
                    last edited by

                    Hi,

                    The driver is called "uchcom.ko".

                    Cheers

                    • Steve
                    1 Reply Last reply Reply Quote 0
                    • B
                      bulldog5
                      last edited by

                      Dennypage,

                      I've seen an issue going on where the NUT service gets reset if the WAN connection is lost causing UPS communication loss.  My current setup has my ATT modem in a different area not on UPS backup, so when the power flickers the modem resets.  This is not a permanent setup, eventually the modem will be relocated inside the main rack which it will then be powered by the same UPS as the pfsense box.

                      However, if my WAN link goes down, why should the NUT service be affected?  If an extended power outage was to happen currently keeping my WAN link down, the pfsense box would never shutdown because its now lost communication with the UPS.

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage
                        last edited by

                        Hey Bulldog. pfSense restarts services when the WAN interface disconnects/reconnects. Yes, this is unnecessary for some services such as NUT, but there is no way for pfSense to know which services actually need to be restarted.

                        What you would expect to see is NUT restart once when the interface goes down, and once again when the interface comes back up. Is this what you are seeing? Or are you seeing the NUT service stopped the entire time the interface is down?

                        1 Reply Last reply Reply Quote 0
                        • B
                          bulldog5
                          last edited by

                          @dennypage:

                          Hey Bulldog. pfSense restarts services when the WAN interface disconnects/reconnects. Yes, this is unnecessary for some services such as NUT, but there is no way for pfSense to know which services actually need to be restarted.

                          What you would expect to see is NUT restart once when the interface goes down, and once again when the interface comes back up. Is this what you are seeing? Or are you seeing the NUT service stopped the entire time the interface is down?

                          I will need to verify if it stays dead the entire time.

                          1 Reply Last reply Reply Quote 0
                          • dennypageD
                            dennypage
                            last edited by

                            Steve, I've pushed a fix for this. The release number will be 2.7.4_4. It may take a few days to work it's way through the system.

                            Thank you for your help in sorting this out. Much appreciated.

                            @stevel:

                            The issue seems to be this… the serial port only allowed me to choose from the two built in UARTS on the board /dev/cuau[0-1]. I have a USB-to-serial adapter and this assigns a character device called /dev/cuaU0 (note U/C 'U').

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              Or, it could come out the same day it's pushed. :)

                              Steve, when you have a minute, can you confirm that this fixed the issue for you please?

                              Thanks.

                              @dennypage:

                              Steve, I've pushed a fix for this. The release number will be 2.7.4_4. It may take a few days to work it's way through the system.

                              1 Reply Last reply Reply Quote 0
                              • N
                                n3by
                                last edited by

                                hello,

                                I have an "NoName Polish brand" ups connected on Local USB that work with blazer driver in 2.3.2-RELEASE-p1 (amd64).

                                I get few emails every day with "UPS is unavailable" and "Communication with UPS lost" even I set cron to restart NUT every 9 minute.

                                Is it possible to edit and add NUT restart command to UPS monitoring module instead of sending this emails ?
                                Any idea where to look ?

                                Usually a manual restart of UPS monitoring daemon it fix the problem before cron but it is getting annoying to receive so many emails and entries in syslog from NUT… :o

                                thank you

                                edit:

                                I try now to automate restart ups service with:

                                upssched.conf

                                CMDSCRIPT /usr/local/bin/custom-upssched-cmd
                                
                                PIPEFN /var/db/nut/upssched.pipe
                                LOCKFN /var/db/nut/upssched.lock
                                
                                AT NOCOMM * START-TIMER ups-no-comm 20
                                AT COMMBAD * START-TIMER ups-comm-bad 20
                                AT COMMOK  * CANCEL-TIMER ups-comm-bad COMMOK
                                

                                custom-upssched-cmd

                                #!/bin/sh
                                NAME=`basename $0`
                                LOGGER="/usr/bin/logger -t $NAME"
                                
                                case $1 in
                                    ups-no-comm|ups-comm-bad)
                                        $LOGGER "Timer event '$1' fired, restarting NUT..."
                                        /usr/local/etc/rc.d/nut.sh restart
                                        ;;
                                    *)
                                        $LOGGER "Unrecognized command: '$1'"
                                        ;;
                                esac
                                
                                1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage
                                  last edited by

                                  Continual disconnects generally indicate an issue with the driver, USB hardware, or with the UPS itself. Before trying to implement scripting work-arounds, I would recommend confirming the source of the problem. Lots of suggestions for this…

                                  First thing I would check would be the physicals: good USB cable, direct connection with no hub, etc. Also, try a different USB port and see if this affects the behavior. Run "usbconfig dump_device_desc" during normal operation. What is the vendor id? Does it match what you expect? Run usbconfig again after the disconnect happens. Does the device still appear?

                                  I would also validate the NUT driver. Did the vendor recommend using the blazer driver? Have you tried any of the other usb based drivers? On the Services / UPS /Status page, do all the items in the UPS Detail section make sense? Are they reasonable values? If not, then there is a driver/configuration problem.

                                  1 Reply Last reply Reply Quote 0
                                  • N
                                    n3by
                                    last edited by

                                    After ~12h since my last post when I deleted the cron restart job every 9 minute and I added upssched.conf and custom-upssched-cmd until now I have 0 lost/bad communication event.

                                    here are some data from USB and UPS with my settings

                                    ugen0.2: <usb to="" serial="" inno="" tech=""> at usbus0, cfg=0 md=HOST spd=LOW (1.5Mbps) pwr=ON (100mA)
                                    
                                      bLength = 0x0012
                                      bDescriptorType = 0x0001
                                      bcdUSB = 0x0110
                                      bDeviceClass = 0x0000  <probed by="" interface="" class="">
                                      bDeviceSubClass = 0x0000
                                      bDeviceProtocol = 0x0000
                                      bMaxPacketSize0 = 0x0008
                                      idVendor = 0x0665
                                      idProduct = 0x5161
                                      bcdDevice = 0x0002
                                      iManufacturer = 0x0001  <inno tech="">
                                      iProduct = 0x0002  <usb to="" serial="">
                                      iSerialNumber = 0x0000  <no string="">
                                      bNumConfigurations = 0x0001</no></usb></inno></probed></usb>
                                    

                                    upsmon.conf

                                    DEADTIME 21
                                    POLLFREQ 7
                                    POLLFREQALERT 7
                                    SHUTDOWNCMD "/sbin/halt -p"
                                    

                                    ups.conf

                                    pollinterval = 7
                                    default.battery.voltage.high = 13.7
                                    default.battery.voltage.low = 11.5
                                    runtimecal = 180,100,360,50
                                    ignorelb
                                    override.battery.charge.low = 50
                                    override.battery.runtime.low = 600
                                    
                                    UPS Detail
                                    
                                    Variable 	Value
                                    battery.charge	100
                                    battery.voltage	13.70
                                    battery.voltage.high	13.00
                                    battery.voltage.low	10.40
                                    battery.voltage.nominal	12.0
                                    device.type	ups
                                    driver.name	blazer_usb
                                    driver.parameter.pollinterval	7
                                    driver.parameter.port	auto
                                    driver.parameter.synchronous	no
                                    driver.version	2.7.4
                                    driver.version.internal	0.12
                                    input.current.nominal	2.0
                                    input.frequency	50.0
                                    input.frequency.nominal	50
                                    input.voltage	241.2
                                    input.voltage.fault	241.2
                                    input.voltage.nominal	230
                                    output.voltage	241.2
                                    ups.beeper.status	enabled
                                    ups.delay.shutdown	30
                                    ups.delay.start	180
                                    ups.load	19
                                    ups.productid	5161
                                    ups.status	OL
                                    ups.type	offline / line interactive
                                    ups.vendorid	0665
                                    

                                    Blazer is the only driver that work with this UPS, about the vendor of this ActiveJet UPS they have 0 support and documentation and don't replay at emails, I bought this one because it has UTP port IN/OUT isolation which I am using for WAN but I found that is not documented or marked which one is IN and which is OUT…

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      USB to serial adapters are often the source of problems.

                                      You might try adding this global directive:

                                      pollinterval=10

                                      to the section entitled "Additional configuration lines for ups.conf" in Services / UPS / Settings / Advanced Settings.

                                      1 Reply Last reply Reply Quote 0
                                      • N
                                        n3by
                                        last edited by

                                        Now after I deleted cron UPS schedule restart I don't have any more problems with lost communication, zero problems in 2 days !

                                        Using upssched.conf & custom-upssched-cmd is the proper way to deal with lost communication if you ask me, no need to schedule a restart for UPS driver if communications is good.

                                        edit:

                                        I was to happy… worked only 2-3 days...

                                        1 Reply Last reply Reply Quote 0
                                        • N
                                          n3by
                                          last edited by

                                          Something is NOT OK !

                                          After 2-3 days without any problem today without any reason UPS communication went offline and no chance to be restored with the changes I made to
                                          custom-upssched-cmd & upssched.conf

                                          I think commands I defined there are not executed, syslog show no trace of NUT service restart.

                                          I restarted manually the service but this problem continued… randomly.
                                          even I changed:

                                          DEADTIME 30
                                          POLLFREQ 10
                                          POLLFREQALERT 10
                                          and
                                          pollinterval = 10

                                          No chance to fix for long term... communication go offline randomly.

                                          Only pfsense reboot solved the UPS communication problem.

                                          Definitely a NUT problem as I did not touched anything on UPS.

                                          Any ideas ?
                                          Do I need something else to set for upssched to work ??

                                          I hope I don't have to return to cron schedule NUT restart… because to schedule a pfsense reboot every night for NUT to work properly it is not a good option.

                                          1 Reply Last reply Reply Quote 0
                                          • D
                                            doktornotor Banned
                                            last edited by

                                            Dude, how about changing your "NoName Polish brand" UPS for something that works, instead of wasting time and blaming NUT?

                                            1 Reply Last reply Reply Quote 0