• Categories
  • Recent
  • Tags
  • Popular
  • Users
  • Search
  • Register
  • Login
Netgate Discussion Forum
  • Categories
  • Recent
  • Tags
  • Popular
  • Users
  • Search
  • Register
  • Login

NUT package (2.8.0 and below)

UPS Tools
128
1.2k
4.0m
Loading More Posts
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • D
    dennypage
    last edited by Aug 18, 2017, 5:16 AM

    @bulldog5:

    Hi, it seems that adjusting the following has kept it quiet. Thanks again.
    battery.charge.low: 20
    battery.charge.warning: 25

    Cool. You are quite welcome. Thanks for letting me know.

    1 Reply Last reply Reply Quote 0
    • D
      dennypage
      last edited by Aug 24, 2017, 4:04 PM

      Just FYI, the PR for the dummy driver has gone in. The shutdown issue will have to be addressed in a follow-on release. This issue will need an enhancement in the core so it may have to wait until 2.4 is release.

      1 Reply Last reply Reply Quote 0
      • W
        wishyou
        last edited by Sep 2, 2017, 1:27 PM

        @dennypage:

        I have. The power kill logic is gone from the base os level. Still searching to find out when and why.

        Being a long time NUT user with pfSense this made me curious. Is this a new problem recently?
        I've been adding stuff to rc.shutdown for "ages" to get proper shutdown-killpower-restart loops with a couple of APC serial ups-es:

        
        #Final shutdown stuff, UPS
        if /usr/local/sbin/upsmon -K; then
        
            # Warning message
        	echo "POWERDOWNFLAG detected - Power cycling the UPS loads..."
        
            # Do shutdown
            /usr/local/sbin/upsdrvctl shutdown
        
            #Might be needed for power races
            # /bin/sleep 180
            # /sbin/reboot
        fi
        
        
        1 Reply Last reply Reply Quote 0
        • D
          dennypage
          last edited by Sep 3, 2017, 5:12 PM

          The problem pre dates the current generation of the NUT package, but I'm not sure how far back it goes.

          What needs to be done is pretty much the same thing you are doing with your patch to rc.shutdown, except that I need to genericize it so that it can be used with other packages such as apcupsd.

          1 Reply Last reply Reply Quote 0
          • W
            wishyou
            last edited by Sep 4, 2017, 7:24 PM

            OK, thanks for the update
            And nice to know that I didn't misunderstand anything with my fix, although it would be nice not having to remember the manual rc.shutdown patch every time pfSense is updated.

            Thanks, keep up the good work!

            1 Reply Last reply Reply Quote 0
            • B
              bdf0506
              last edited by Sep 4, 2017, 11:55 PM

              I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

              I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

              One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

              Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              
              
              1 Reply Last reply Reply Quote 0
              • B
                bdf0506
                last edited by Sep 5, 2017, 12:27 AM

                @bdf0506:

                I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

                I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

                One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

                Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                
                

                Okay, this isn't a NUT issue.

                I dove deeper into the logging before these errors hit, and I see each time a log line like this:

                Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%
                

                After that line, bad things were happening. I'm surprised I wasn't having other network issues - I probably was, just unknown to me.

                Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
                Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
                Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
                Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
                Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
                Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
                Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
                Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
                Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
                Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
                Sep  4 19:32:37 check_reload_status: Reloading filter
                Sep  4 19:32:37 check_reload_status: Reloading filter
                Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
                Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
                Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
                Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
                Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
                Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
                Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%</redacted></redacted></redacted></redacted>
                

                The fix was to go into the gateways, and disable the gateway checking on 192.168.35.21. I still don't know what was causing that in the first place, but that's not something that needs to be addressed in the NUT forum.

                1 Reply Last reply Reply Quote 0
                • P
                  pigbrother
                  last edited by Sep 6, 2017, 11:27 AM

                  dennypage, thanks for your great job!

                  My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
                  Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
                  Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

                  Time is always random, but event duration is always 5 seconds exactly.

                  My settings:
                  ups.conf

                  [Back-UPS_RS_1000]
                  driver=usbhid-ups
                  port=auto
                  ignorelb
                  override.battery.charge.low = 30
                  override.battery.runtime.low = 300
                  

                  upsmon.conf

                  MONITOR Back-UPS_RS_1000 1 monuser 7504xxxxxxxxxxxx master
                  SHUTDOWNCMD "/sbin/shutdown -p +0"
                  POWERDOWNFLAG /etc/killpower
                  NOTIFYCMD /usr/local/pkg/nut/nut_email.php
                  NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
                  NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
                  NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
                  NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
                  NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
                  NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                  NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
                  NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
                  NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
                  NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
                  RUN_AS_USER root
                  
                  

                  I realize that is UPS problem but apart from that it works fine.
                  Are there any NUT tweaks to avoid such behavior?

                  1 Reply Last reply Reply Quote 0
                  • D
                    dennypage
                    last edited by Sep 6, 2017, 8:01 PM

                    @pigbrother:

                    dennypage, thanks for your great job!

                    My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
                    Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
                    Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

                    Time is always random, but event duration is always 5 seconds exactly.

                    …

                    I realize that is UPS problem but apart from that it works fine.
                    Are there any NUT tweaks to avoid such behavior?

                    You're welcome!

                    The event itself may be very brief in duration, but is logged as 5 seconds due to the polling interval. There are several reasons that a momentary transfer to battery can happen depending upon the UPS.

                    Some UPSs allow the variables which control transfer to be changed. The complete list of variables supported by NUT can be found here. To see what your UPS actually supports, use the upsc command. For transfer items, look for variables "input sensitivity" or "input.transfer…"

                    Be careful with these. :)

                    1 Reply Last reply Reply Quote 0
                    • P
                      pigbrother
                      last edited by Sep 7, 2017, 9:31 AM

                      My UPS variables:

                      battery.charge: 100
                      battery.charge.low: 30
                      battery.charge.warning: 50
                      battery.date: 2001/09/25
                      battery.mfr.date: 2016/10/10
                      battery.runtime: 5798
                      battery.runtime.low: 300
                      battery.type: PbAc
                      battery.voltage: 26.9
                      battery.voltage.nominal: 24.0
                      device.mfr: American Power Conversion
                      device.model: Back-UPS RS 1000
                      device.serial:xxxxxxxxxx
                      device.type: ups
                      driver.flag.ignorelb: enabled
                      driver.name: usbhid-ups
                      driver.parameter.pollfreq: 30
                      driver.parameter.pollinterval: 2
                      driver.parameter.port: auto
                      driver.parameter.synchronous: no
                      driver.version: 2.7.4
                      driver.version.data: APC HID 0.96
                      driver.version.internal: 0.41
                      input.sensitivity: medium
                      input.transfer.high: 264
                      input.transfer.low: 194
                      input.transfer.reason: input voltage out of range
                      input.voltage: 228.0
                      input.voltage.nominal: 230
                      ups.beeper.status: enabled
                      ups.delay.shutdown: 20
                      ups.firmware: 7.g8 .I
                      ups.firmware.aux: g8
                      ups.load: 5
                      ups.mfr: American Power Conversion
                      ups.mfr.date: 2004/07/28
                      ups.model: Back-UPS RS 1000
                      ups.productid: 0002
                      ups.realpower.nominal: 600
                      ups.serial: xxxxxxxxxxxx
                      ups.status: OL
                      ups.test.result: No test initiated
                      ups.timer.reboot: 0
                      ups.timer.shutdown: -1
                      ups.vendorid: 051d
                      

                      input.transfer.reason: input voltage out of range - probably is the event reason?

                      I believe that
                      input.transfer.high:264 and  input.transfer.low:194
                      are just voltage threshold? Am I right?

                      Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

                      1 Reply Last reply Reply Quote 0
                      • D
                        doktornotor Banned
                        last edited by Sep 7, 2017, 11:27 AM

                        Why would you be doing any such thing? The UPS is doing its job, just leave it alone.

                        1 Reply Last reply Reply Quote 0
                        • D
                          dennypage
                          last edited by Sep 7, 2017, 3:21 PM

                          @pigbrother:

                          nput.transfer.reason: input voltage out of range - probably is the event reason?

                          I believe that
                          input.transfer.high:264 and  input.transfer.low:194
                          are just voltage threshold? Am I right?

                          Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

                          Yes, those are the voltage levels that will trigger transfer.

                          Setting UPS variables is not something that you do in your NUT config. You set them in the UPS using the upsrw command.

                          As Dok notes, the UPS is doing it's job, protecting the attached systems from excessive power fluctuations. You might want to investigate the source of the voltage problem before turning down the sensitivity. Consulting with the UPS manufacturer might be a good idea as well.

                          1 Reply Last reply Reply Quote 0
                          • P
                            pigbrother
                            last edited by Sep 8, 2017, 7:41 AM

                            dennypaged, oktornotor, thanks for answers.
                            Agreed,  the UPS is doing it's job. I'm just trying to avoid annoying mail reports (at the night time especially).
                            Another SMART UPSes connected  to same power input do not have any complains about power conditions.

                            1 Reply Last reply Reply Quote 0
                            • S
                              SilverJS
                              last edited by Oct 26, 2017, 4:03 AM

                              Denny (or whoever else wants to lend a hand!),

                              Running pfSense 2.4.1 as a firewall and router, with NUT 2.7.4_5.  I have the pfSense box, a FreeNAS server, and another FreeNAS server (Replication target) all on a CyberPower CP1000AVRLCD UPS.  (My switch is also on that, a 16-port Netgear item.)  I currently have my FreeNAS server as the master, and both the backups box and pfSense are "seeing" the master no problem.  When I pull the cord on the UPS, I get three nice e-mail notifications (one from each of the boxes), and all boxes shutdown in an orderly fashion when ordered to by the master (tested both Battery Low and On Battery, the latter with a 10 second timer in my tests).

                              The problem is : none of the boxes start back up when I plug the UPS back in!  I'm sure this is something dumb, because I'm not that knowledgeable at all - but what I CAN say is, the blue LED is lit on the UPS (but the display itself is blank).  As in, it's not shut down.  If I press it, it goes completely dark, and if I press it again, it lights up again, along with the LCD display and all - and, voila, most of the boxes start up.  That is, both FreeNAS boxes start up - the pfSense one needs to be started manually.  All three boxes have Always On setting in the BIOS for waking up after power loss.

                              Any ideas…?  I think it would make more sense to have the box doing the routing (pfSense) also being the master, but I'm not 100% sure how to configure that.  But the better question is - do I need to?  Would that fix anything?

                              Thanks in advance, and thanks also both for all your work on this package, and for the continued support you offer to us plebes on this forum! =)

                              Cheers!

                              pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                              1 Reply Last reply Reply Quote 0
                              • D
                                dennypage
                                last edited by Oct 26, 2017, 5:17 AM

                                Can you clarify what you mean by “the pfSense one needs to be started manually”?

                                Traveling, so expect delayed responses…

                                Thanks.

                                1 Reply Last reply Reply Quote 0
                                • S
                                  SilverJS
                                  last edited by Oct 26, 2017, 11:17 AM

                                  Thanks for the quick reply - far from "delayed"!

                                  I mean I have to physically push the power button on the pfSense box.

                                  Enjoy your travels!

                                  pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                  1 Reply Last reply Reply Quote 0
                                  • B
                                    bdf0506
                                    last edited by Oct 26, 2017, 1:35 PM

                                    @SilverJS:

                                    Thanks for the quick reply - far from "delayed"!

                                    I mean I have to physically push the power button on the pfSense box.

                                    Enjoy your travels!

                                    This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                    I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                                    1 Reply Last reply Reply Quote 0
                                    • S
                                      SilverJS
                                      last edited by Oct 26, 2017, 1:55 PM

                                      @bdf0506:

                                      This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                      I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                                      Oh!  So the UPS NEEDS to be shut down too? Too easy - FreeNAS has a setting for that in the UPS settings.  I'll tick that box, try again and report.

                                      pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                      1 Reply Last reply Reply Quote 0
                                      • S
                                        SilverJS
                                        last edited by Oct 26, 2017, 2:25 PM

                                        And THERE it is!!  As soon as I instructed the UPS to shut down in my settings, everything worked perfectly.  All boxes shutdown properly, UPS shut down, and when I plugged the UPS back in, all three computers spun right back up.  The very first time I went through the whole cycle, comms with the UPS couldn't be re-established for some reason (got a flurry of e-mails from all three boxes), but I've tested it a few times since and it's always worked.  The one I'm most worried about is the pfSense box - as long as IT comes back online while I'm away, I can VPN in and restart or whatnot, and do what I need to do, and it always has, regardless of UPS comms status.  So, all seems well.

                                        The one scenario I haven't tested yet is a power race, but that'll have to wait - the little one is up…=)

                                        Thanks for your help!!

                                        pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                        1 Reply Last reply Reply Quote 0
                                        • F
                                          fr3ddie
                                          last edited by Oct 29, 2017, 7:13 PM

                                          @bdf0506:

                                          This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                          I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side.

                                          Hello,
                                          I'd like to report I have the same issue: UPS brand is Eaton, fully supported by usbhid driver and "upsdrvctl shutdown" works perfectly on a Debian Jessie but not with pfSense NUT package.

                                          I've tried to dig the init script in /usr/local/etc/rc.d/nut modifying it with no luck.

                                          Can I solve it or is it a bug in the pfSense package? If it is a bug, do the maintainer of the package has any forecast about its resolution?

                                          Thank you

                                          1 Reply Last reply Reply Quote 0
                                          • First post
                                            Last post
                                          Copyright 2025 Rubicon Communications LLC (Netgate). All rights reserved.