Netgate Discussion Forum
    • Categories
    • Recent
    • Tags
    • Popular
    • Users
    • Search
    • Register
    • Login

    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.8m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • B
      bdf0506
      last edited by

      I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

      I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

      One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

      Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      
      
      1 Reply Last reply Reply Quote 0
      • B
        bdf0506
        last edited by

        @bdf0506:

        I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

        I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

        One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

        Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        
        

        Okay, this isn't a NUT issue.

        I dove deeper into the logging before these errors hit, and I see each time a log line like this:

        Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%
        

        After that line, bad things were happening. I'm surprised I wasn't having other network issues - I probably was, just unknown to me.

        Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
        Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
        Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
        Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
        Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
        Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
        Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
        Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
        Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
        Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
        Sep  4 19:32:37 check_reload_status: Reloading filter
        Sep  4 19:32:37 check_reload_status: Reloading filter
        Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
        Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
        Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
        Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
        Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
        Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
        Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%</redacted></redacted></redacted></redacted>
        

        The fix was to go into the gateways, and disable the gateway checking on 192.168.35.21. I still don't know what was causing that in the first place, but that's not something that needs to be addressed in the NUT forum.

        1 Reply Last reply Reply Quote 0
        • P
          pigbrother
          last edited by

          dennypage, thanks for your great job!

          My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
          Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
          Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

          Time is always random, but event duration is always 5 seconds exactly.

          My settings:
          ups.conf

          [Back-UPS_RS_1000]
          driver=usbhid-ups
          port=auto
          ignorelb
          override.battery.charge.low = 30
          override.battery.runtime.low = 300
          

          upsmon.conf

          MONITOR Back-UPS_RS_1000 1 monuser 7504xxxxxxxxxxxx master
          SHUTDOWNCMD "/sbin/shutdown -p +0"
          POWERDOWNFLAG /etc/killpower
          NOTIFYCMD /usr/local/pkg/nut/nut_email.php
          NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
          NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
          NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
          NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
          NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
          NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
          NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
          NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
          NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
          NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
          RUN_AS_USER root
          
          

          I realize that is UPS problem but apart from that it works fine.
          Are there any NUT tweaks to avoid such behavior?

          1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage
            last edited by

            @pigbrother:

            dennypage, thanks for your great job!

            My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
            Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
            Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

            Time is always random, but event duration is always 5 seconds exactly.

            …

            I realize that is UPS problem but apart from that it works fine.
            Are there any NUT tweaks to avoid such behavior?

            You're welcome!

            The event itself may be very brief in duration, but is logged as 5 seconds due to the polling interval. There are several reasons that a momentary transfer to battery can happen depending upon the UPS.

            Some UPSs allow the variables which control transfer to be changed. The complete list of variables supported by NUT can be found here. To see what your UPS actually supports, use the upsc command. For transfer items, look for variables "input sensitivity" or "input.transfer…"

            Be careful with these. :)

            1 Reply Last reply Reply Quote 0
            • P
              pigbrother
              last edited by

              My UPS variables:

              battery.charge: 100
              battery.charge.low: 30
              battery.charge.warning: 50
              battery.date: 2001/09/25
              battery.mfr.date: 2016/10/10
              battery.runtime: 5798
              battery.runtime.low: 300
              battery.type: PbAc
              battery.voltage: 26.9
              battery.voltage.nominal: 24.0
              device.mfr: American Power Conversion
              device.model: Back-UPS RS 1000
              device.serial:xxxxxxxxxx
              device.type: ups
              driver.flag.ignorelb: enabled
              driver.name: usbhid-ups
              driver.parameter.pollfreq: 30
              driver.parameter.pollinterval: 2
              driver.parameter.port: auto
              driver.parameter.synchronous: no
              driver.version: 2.7.4
              driver.version.data: APC HID 0.96
              driver.version.internal: 0.41
              input.sensitivity: medium
              input.transfer.high: 264
              input.transfer.low: 194
              input.transfer.reason: input voltage out of range
              input.voltage: 228.0
              input.voltage.nominal: 230
              ups.beeper.status: enabled
              ups.delay.shutdown: 20
              ups.firmware: 7.g8 .I
              ups.firmware.aux: g8
              ups.load: 5
              ups.mfr: American Power Conversion
              ups.mfr.date: 2004/07/28
              ups.model: Back-UPS RS 1000
              ups.productid: 0002
              ups.realpower.nominal: 600
              ups.serial: xxxxxxxxxxxx
              ups.status: OL
              ups.test.result: No test initiated
              ups.timer.reboot: 0
              ups.timer.shutdown: -1
              ups.vendorid: 051d
              

              input.transfer.reason: input voltage out of range - probably is the event reason?

              I believe that
              input.transfer.high:264 and  input.transfer.low:194
              are just voltage threshold? Am I right?

              Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

              1 Reply Last reply Reply Quote 0
              • D
                doktornotor Banned
                last edited by

                Why would you be doing any such thing? The UPS is doing its job, just leave it alone.

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  @pigbrother:

                  nput.transfer.reason: input voltage out of range - probably is the event reason?

                  I believe that
                  input.transfer.high:264 and  input.transfer.low:194
                  are just voltage threshold? Am I right?

                  Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

                  Yes, those are the voltage levels that will trigger transfer.

                  Setting UPS variables is not something that you do in your NUT config. You set them in the UPS using the upsrw command.

                  As Dok notes, the UPS is doing it's job, protecting the attached systems from excessive power fluctuations. You might want to investigate the source of the voltage problem before turning down the sensitivity. Consulting with the UPS manufacturer might be a good idea as well.

                  1 Reply Last reply Reply Quote 0
                  • P
                    pigbrother
                    last edited by

                    dennypaged, oktornotor, thanks for answers.
                    Agreed,  the UPS is doing it's job. I'm just trying to avoid annoying mail reports (at the night time especially).
                    Another SMART UPSes connected  to same power input do not have any complains about power conditions.

                    1 Reply Last reply Reply Quote 0
                    • S
                      SilverJS
                      last edited by

                      Denny (or whoever else wants to lend a hand!),

                      Running pfSense 2.4.1 as a firewall and router, with NUT 2.7.4_5.  I have the pfSense box, a FreeNAS server, and another FreeNAS server (Replication target) all on a CyberPower CP1000AVRLCD UPS.  (My switch is also on that, a 16-port Netgear item.)  I currently have my FreeNAS server as the master, and both the backups box and pfSense are "seeing" the master no problem.  When I pull the cord on the UPS, I get three nice e-mail notifications (one from each of the boxes), and all boxes shutdown in an orderly fashion when ordered to by the master (tested both Battery Low and On Battery, the latter with a 10 second timer in my tests).

                      The problem is : none of the boxes start back up when I plug the UPS back in!  I'm sure this is something dumb, because I'm not that knowledgeable at all - but what I CAN say is, the blue LED is lit on the UPS (but the display itself is blank).  As in, it's not shut down.  If I press it, it goes completely dark, and if I press it again, it lights up again, along with the LCD display and all - and, voila, most of the boxes start up.  That is, both FreeNAS boxes start up - the pfSense one needs to be started manually.  All three boxes have Always On setting in the BIOS for waking up after power loss.

                      Any ideas…?  I think it would make more sense to have the box doing the routing (pfSense) also being the master, but I'm not 100% sure how to configure that.  But the better question is - do I need to?  Would that fix anything?

                      Thanks in advance, and thanks also both for all your work on this package, and for the continued support you offer to us plebes on this forum! =)

                      Cheers!

                      pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage
                        last edited by

                        Can you clarify what you mean by “the pfSense one needs to be started manually”?

                        Traveling, so expect delayed responses…

                        Thanks.

                        1 Reply Last reply Reply Quote 0
                        • S
                          SilverJS
                          last edited by

                          Thanks for the quick reply - far from "delayed"!

                          I mean I have to physically push the power button on the pfSense box.

                          Enjoy your travels!

                          pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                          1 Reply Last reply Reply Quote 0
                          • B
                            bdf0506
                            last edited by

                            @SilverJS:

                            Thanks for the quick reply - far from "delayed"!

                            I mean I have to physically push the power button on the pfSense box.

                            Enjoy your travels!

                            This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                            I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                            1 Reply Last reply Reply Quote 0
                            • S
                              SilverJS
                              last edited by

                              @bdf0506:

                              This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                              I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                              Oh!  So the UPS NEEDS to be shut down too? Too easy - FreeNAS has a setting for that in the UPS settings.  I'll tick that box, try again and report.

                              pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                              1 Reply Last reply Reply Quote 0
                              • S
                                SilverJS
                                last edited by

                                And THERE it is!!  As soon as I instructed the UPS to shut down in my settings, everything worked perfectly.  All boxes shutdown properly, UPS shut down, and when I plugged the UPS back in, all three computers spun right back up.  The very first time I went through the whole cycle, comms with the UPS couldn't be re-established for some reason (got a flurry of e-mails from all three boxes), but I've tested it a few times since and it's always worked.  The one I'm most worried about is the pfSense box - as long as IT comes back online while I'm away, I can VPN in and restart or whatnot, and do what I need to do, and it always has, regardless of UPS comms status.  So, all seems well.

                                The one scenario I haven't tested yet is a power race, but that'll have to wait - the little one is up…=)

                                Thanks for your help!!

                                pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                1 Reply Last reply Reply Quote 0
                                • F
                                  fr3ddie
                                  last edited by

                                  @bdf0506:

                                  This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                  I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side.

                                  Hello,
                                  I'd like to report I have the same issue: UPS brand is Eaton, fully supported by usbhid driver and "upsdrvctl shutdown" works perfectly on a Debian Jessie but not with pfSense NUT package.

                                  I've tried to dig the init script in /usr/local/etc/rc.d/nut modifying it with no luck.

                                  Can I solve it or is it a bug in the pfSense package? If it is a bug, do the maintainer of the package has any forecast about its resolution?

                                  Thank you

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    Sorry again for the delay. Had a few real-life things come up.

                                    For a temporary work-around, please see reply #250.

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage
                                      last edited by

                                      PRs are in, one for mainline pfSense and one for the NUT package, both of which are required to address the power kill issue. The mainline PR needs to go into a pfSense release cycle, so 2.4.2 is the earliest possible, but I expect 2.4.3 is more likely at this point.

                                      1 Reply Last reply Reply Quote 0
                                      • w0wW
                                        w0w
                                        last edited by

                                        So does the latest beta 2.4.3 have these PR's?

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          Hey w0w,

                                          I’m traveling…  I don’t recall seeing merge notifications, but I get a lot of email. You should be able to check the PRs in the main pfSense and FreeBSD repos to see if they’re still outstanding. If not I’ll check it when I get home.

                                          Thanks,
                                          Denny

                                          1 Reply Last reply Reply Quote 0
                                          • F
                                            fox983
                                            last edited by

                                            @dennypage:

                                            @endy66:

                                            But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

                                            
                                            ignorelb
                                            override.battery.charge.low = 50
                                            override.battery.runtime.low = 1200
                                            
                                            

                                            BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

                                            The section entitled "Additional configuration lines for ups.conf" in Advanced settings is for global directives. The values you are trying to set are UPS specific arguments. UPS specific arguments should be entered in the section above that says "Extra Arguments to driver"

                                            Sorry this isn't clear. I'll have a look at clarifying.

                                            Hello and thanks for the great work.
                                            I'm working with pfSense and NUT  2.7.4_5 package. The "bug" still remains, if I edit (via webpage) the "Extra Arguments to driver (optional)" with

                                            ignorelb
                                            override.battery.charge.low = 30

                                            all works correctly, it adds the 2 lines AFTER

                                            [myups]
                                            driver=usbhid-ups
                                            port=auto

                                            in "/usr/local/etc/nut/ups.conf" file.
                                            But if I edit the "Additional configuration lines for ups.conf", which it seems to be more correct (http://networkupstools.org/docs/man/ups.conf.html), it adds the lines at beginning of the file, and it doesn't work.
                                            All other configuration settings (upsmon.conf, upsd.conf, upsd.users) add lines at the end of the files (checked via ssh), as it should be I think…

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post
                                            Copyright 2025 Rubicon Communications LLC (Netgate). All rights reserved.