    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.4m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • W
      wishyou
      last edited by

      @dennypage:

      I have. The power kill logic is gone from the base os level. Still searching to find out when and why.

      Being a long time NUT user with pfSense this made me curious. Is this a new problem recently?
      I've been adding stuff to rc.shutdown for "ages" to get proper shutdown-killpower-restart loops with a couple of APC serial ups-es:

      
      #Final shutdown stuff, UPS
      if /usr/local/sbin/upsmon -K; then
      
          # Warning message
      	echo "POWERDOWNFLAG detected - Power cycling the UPS loads..."
      
          # Do shutdown
          /usr/local/sbin/upsdrvctl shutdown
      
          #Might be needed for power races
          # /bin/sleep 180
          # /sbin/reboot
      fi
      
      
      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage
        last edited by

        The problem pre dates the current generation of the NUT package, but I'm not sure how far back it goes.

        What needs to be done is pretty much the same thing you are doing with your patch to rc.shutdown, except that I need to genericize it so that it can be used with other packages such as apcupsd.

        1 Reply Last reply Reply Quote 0
        • W
          wishyou
          last edited by

          OK, thanks for the update
          And nice to know that I didn't misunderstand anything with my fix, although it would be nice not having to remember the manual rc.shutdown patch every time pfSense is updated.

          Thanks, keep up the good work!

          1 Reply Last reply Reply Quote 0
          • B
            bdf0506
            last edited by

            I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

            I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

            One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

            Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
            Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
            Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
            Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
            Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
            Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
            Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
            Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
            Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
            Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
            Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
            Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
            Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
            Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
            Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
            Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
            Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
            Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
            Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
            Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
            Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
            Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
            Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
            Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
            
            
            1 Reply Last reply Reply Quote 0
            • B
              bdf0506
              last edited by

              @bdf0506:

              I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

              I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

              One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

              Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              
              

              Okay, this isn't a NUT issue.

              I dove deeper into the logging before these errors hit, and I see each time a log line like this:

              Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%
              

              After that line, bad things were happening. I'm surprised I wasn't having other network issues - I probably was, just unknown to me.

              Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
              Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
              Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
              Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
              Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
              Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
              Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
              Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
              Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
              Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
              Sep  4 19:32:37 check_reload_status: Reloading filter
              Sep  4 19:32:37 check_reload_status: Reloading filter
              Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
              Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
              Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
              Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
              Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
              Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
              Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%</redacted></redacted></redacted></redacted>
              

              The fix was to go into the gateways, and disable the gateway checking on 192.168.35.21. I still don't know what was causing that in the first place, but that's not something that needs to be addressed in the NUT forum.

              1 Reply Last reply Reply Quote 0
              • P
                pigbrother
                last edited by

                dennypage, thanks for your great job!

                My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
                Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
                Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

                Time is always random, but event duration is always 5 seconds exactly.

                My settings:
                ups.conf

                [Back-UPS_RS_1000]
                driver=usbhid-ups
                port=auto
                ignorelb
                override.battery.charge.low = 30
                override.battery.runtime.low = 300
                

                upsmon.conf

                MONITOR Back-UPS_RS_1000 1 monuser 7504xxxxxxxxxxxx master
                SHUTDOWNCMD "/sbin/shutdown -p +0"
                POWERDOWNFLAG /etc/killpower
                NOTIFYCMD /usr/local/pkg/nut/nut_email.php
                NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
                NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
                NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
                NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
                NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
                NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
                NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
                NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
                NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
                RUN_AS_USER root
                
                

                I realize that is UPS problem but apart from that it works fine.
                Are there any NUT tweaks to avoid such behavior?

                1 Reply Last reply Reply Quote 0
                • dennypageD
                  dennypage
                  last edited by

                  @pigbrother:

                  dennypage, thanks for your great job!

                  My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
                  Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
                  Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

                  Time is always random, but event duration is always 5 seconds exactly.

                  …

                  I realize that is UPS problem but apart from that it works fine.
                  Are there any NUT tweaks to avoid such behavior?

                  You're welcome!

                  The event itself may be very brief in duration, but is logged as 5 seconds due to the polling interval. There are several reasons that a momentary transfer to battery can happen depending upon the UPS.

                  Some UPSs allow the variables which control transfer to be changed. The complete list of variables supported by NUT can be found here. To see what your UPS actually supports, use the upsc command. For transfer items, look for variables "input sensitivity" or "input.transfer…"

                  Be careful with these. :)

                  1 Reply Last reply Reply Quote 0
                  • P
                    pigbrother
                    last edited by

                    My UPS variables:

                    battery.charge: 100
                    battery.charge.low: 30
                    battery.charge.warning: 50
                    battery.date: 2001/09/25
                    battery.mfr.date: 2016/10/10
                    battery.runtime: 5798
                    battery.runtime.low: 300
                    battery.type: PbAc
                    battery.voltage: 26.9
                    battery.voltage.nominal: 24.0
                    device.mfr: American Power Conversion
                    device.model: Back-UPS RS 1000
                    device.serial:xxxxxxxxxx
                    device.type: ups
                    driver.flag.ignorelb: enabled
                    driver.name: usbhid-ups
                    driver.parameter.pollfreq: 30
                    driver.parameter.pollinterval: 2
                    driver.parameter.port: auto
                    driver.parameter.synchronous: no
                    driver.version: 2.7.4
                    driver.version.data: APC HID 0.96
                    driver.version.internal: 0.41
                    input.sensitivity: medium
                    input.transfer.high: 264
                    input.transfer.low: 194
                    input.transfer.reason: input voltage out of range
                    input.voltage: 228.0
                    input.voltage.nominal: 230
                    ups.beeper.status: enabled
                    ups.delay.shutdown: 20
                    ups.firmware: 7.g8 .I
                    ups.firmware.aux: g8
                    ups.load: 5
                    ups.mfr: American Power Conversion
                    ups.mfr.date: 2004/07/28
                    ups.model: Back-UPS RS 1000
                    ups.productid: 0002
                    ups.realpower.nominal: 600
                    ups.serial: xxxxxxxxxxxx
                    ups.status: OL
                    ups.test.result: No test initiated
                    ups.timer.reboot: 0
                    ups.timer.shutdown: -1
                    ups.vendorid: 051d
                    

                    input.transfer.reason: input voltage out of range - probably is the event reason?

                    I believe that
                    input.transfer.high:264 and  input.transfer.low:194
                    are just voltage threshold? Am I right?

                    Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

                    1 Reply Last reply Reply Quote 0
                    • D
                      doktornotor Banned
                      last edited by

                      Why would you be doing any such thing? The UPS is doing its job, just leave it alone.

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage
                        last edited by

                        @pigbrother:

                        nput.transfer.reason: input voltage out of range - probably is the event reason?

                        I believe that
                        input.transfer.high:264 and  input.transfer.low:194
                        are just voltage threshold? Am I right?

                        Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

                        Yes, those are the voltage levels that will trigger transfer.

                        Setting UPS variables is not something that you do in your NUT config. You set them in the UPS using the upsrw command.

                        As Dok notes, the UPS is doing it's job, protecting the attached systems from excessive power fluctuations. You might want to investigate the source of the voltage problem before turning down the sensitivity. Consulting with the UPS manufacturer might be a good idea as well.

                        1 Reply Last reply Reply Quote 0
                        • P
                          pigbrother
                          last edited by

                          dennypaged, oktornotor, thanks for answers.
                          Agreed,  the UPS is doing it's job. I'm just trying to avoid annoying mail reports (at the night time especially).
                          Another SMART UPSes connected  to same power input do not have any complains about power conditions.

                          1 Reply Last reply Reply Quote 0
                          • S
                            SilverJS
                            last edited by

                            Denny (or whoever else wants to lend a hand!),

                            Running pfSense 2.4.1 as a firewall and router, with NUT 2.7.4_5.  I have the pfSense box, a FreeNAS server, and another FreeNAS server (Replication target) all on a CyberPower CP1000AVRLCD UPS.  (My switch is also on that, a 16-port Netgear item.)  I currently have my FreeNAS server as the master, and both the backups box and pfSense are "seeing" the master no problem.  When I pull the cord on the UPS, I get three nice e-mail notifications (one from each of the boxes), and all boxes shutdown in an orderly fashion when ordered to by the master (tested both Battery Low and On Battery, the latter with a 10 second timer in my tests).

                            The problem is : none of the boxes start back up when I plug the UPS back in!  I'm sure this is something dumb, because I'm not that knowledgeable at all - but what I CAN say is, the blue LED is lit on the UPS (but the display itself is blank).  As in, it's not shut down.  If I press it, it goes completely dark, and if I press it again, it lights up again, along with the LCD display and all - and, voila, most of the boxes start up.  That is, both FreeNAS boxes start up - the pfSense one needs to be started manually.  All three boxes have Always On setting in the BIOS for waking up after power loss.

                            Any ideas…?  I think it would make more sense to have the box doing the routing (pfSense) also being the master, but I'm not 100% sure how to configure that.  But the better question is - do I need to?  Would that fix anything?

                            Thanks in advance, and thanks also both for all your work on this package, and for the continued support you offer to us plebes on this forum! =)

                            Cheers!

                            pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                            1 Reply Last reply Reply Quote 0
                            • dennypageD
                              dennypage
                              last edited by

                              Can you clarify what you mean by “the pfSense one needs to be started manually”?

                              Traveling, so expect delayed responses…

                              Thanks.

                              1 Reply Last reply Reply Quote 0
                              • S
                                SilverJS
                                last edited by

                                Thanks for the quick reply - far from "delayed"!

                                I mean I have to physically push the power button on the pfSense box.

                                Enjoy your travels!

                                pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                1 Reply Last reply Reply Quote 0
                                • B
                                  bdf0506
                                  last edited by

                                  @SilverJS:

                                  Thanks for the quick reply - far from "delayed"!

                                  I mean I have to physically push the power button on the pfSense box.

                                  Enjoy your travels!

                                  This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                  I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                                  1 Reply Last reply Reply Quote 0
                                  • S
                                    SilverJS
                                    last edited by

                                    @bdf0506:

                                    This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                    I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                                    Oh!  So the UPS NEEDS to be shut down too? Too easy - FreeNAS has a setting for that in the UPS settings.  I'll tick that box, try again and report.

                                    pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                    1 Reply Last reply Reply Quote 0
                                    • S
                                      SilverJS
                                      last edited by

                                      And THERE it is!!  As soon as I instructed the UPS to shut down in my settings, everything worked perfectly.  All boxes shutdown properly, UPS shut down, and when I plugged the UPS back in, all three computers spun right back up.  The very first time I went through the whole cycle, comms with the UPS couldn't be re-established for some reason (got a flurry of e-mails from all three boxes), but I've tested it a few times since and it's always worked.  The one I'm most worried about is the pfSense box - as long as IT comes back online while I'm away, I can VPN in and restart or whatnot, and do what I need to do, and it always has, regardless of UPS comms status.  So, all seems well.

                                      The one scenario I haven't tested yet is a power race, but that'll have to wait - the little one is up…=)

                                      Thanks for your help!!

                                      pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                                      1 Reply Last reply Reply Quote 0
                                      • F
                                        fr3ddie
                                        last edited by

                                        @bdf0506:

                                        This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                        I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side.

                                        Hello,
                                        I'd like to report I have the same issue: UPS brand is Eaton, fully supported by usbhid driver and "upsdrvctl shutdown" works perfectly on a Debian Jessie but not with pfSense NUT package.

                                        I've tried to dig the init script in /usr/local/etc/rc.d/nut modifying it with no luck.

                                        Can I solve it or is it a bug in the pfSense package? If it is a bug, do the maintainer of the package has any forecast about its resolution?

                                        Thank you

                                        1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          Sorry again for the delay. Had a few real-life things come up.

                                          For a temporary work-around, please see reply #250.

                                          1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            PRs are in, one for mainline pfSense and one for the NUT package, both of which are required to address the power kill issue. The mainline PR needs to go into a pfSense release cycle, so 2.4.2 is the earliest possible, but I expect 2.4.3 is more likely at this point.

                                            1 Reply Last reply Reply Quote 0