    NUT package (2.8.0 and below)

    Scheduled Pinned Locked Moved UPS Tools
    1.2k Posts 128 Posters 4.1m Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • B
      bdf0506
      last edited by

      @bdf0506:

      I upgraded NUT on pfSense to latest 2.7.4_5, and ever since I did that, it seems there is a high uptick in UPS communication errors. It's possible that it's another environmental condition that is going on here, but wanted to see if anyone else has had issues. PfSense is running on a small physical box, and it is directly connected via USB to a CyberPower EC650.

      I've been getting flooded with emails as a result of this (yes, I know that I can turn them off). But it points to something else that is going on. Here is a dump of the ups related events for a small window on 9/4. In the last 24 hours, I have 232 events that are the Permission denied error.

      One thing I did notice, if you look in /usr/local/etc/nut, all the *.conf files have perms of 640, but all the *.conf.sample files have perms of 644. Not sure if that matters or not, and also not sure if that's "new" or not.

      Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:36:09 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:36:09 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:36:04 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:36:04 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:30:12 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:30:12 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:30:07 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:30:07 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      
      

      Okay, this isn't a NUT issue.

      I dove deeper into the logging before these errors hit, and I see each time a log line like this:

      Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%
      

      After that line, bad things were happening. I'm surprised I wasn't having other network issues - I probably was, just unknown to me.

      Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
      Sep  4 19:32:48 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
      Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:32:48 upsmon[32699]: Communications with UPS ups established
      Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:32:48 upsd[73255]: User monuser@::1 logged into UPS [ups]
      Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
      Sep  4 19:32:43 php-cgi: nut_email.php: Message sent to <redacted>@gmail.com OK
      Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:32:43 upsmon[32699]: Communications with UPS ups lost
      Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:32:43 upsmon[32699]: Poll UPS [ups] failed - Write error: Permission denied
      Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
      Sep  4 19:32:38 php-fpm[30305]: /rc.openvpn: OpenVPN: One or more OpenVPN tunnel endpoints may have changed its IP. Reloading endpoints that may use Mobility_Server.
      Sep  4 19:32:37 check_reload_status: Reloading filter
      Sep  4 19:32:37 check_reload_status: Reloading filter
      Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
      Sep  4 19:32:37 check_reload_status: Restarting OpenVPN tunnels/interfaces
      Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
      Sep  4 19:32:37 check_reload_status: Restarting ipsec tunnels
      Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
      Sep  4 19:32:37 check_reload_status: updating dyndns Mobility_Server
      Sep  4 19:32:37 dpinger: Mobility_Server 192.168.35.21: Alarm latency 266us stddev 32us loss 21%</redacted></redacted></redacted></redacted>
      

      The fix was to go into the gateways, and disable the gateway checking on 192.168.35.21. I still don't know what was causing that in the first place, but that's not something that needs to be addressed in the NUT forum.

      1 Reply Last reply Reply Quote 0
      • P
        pigbrother
        last edited by

        dennypage, thanks for your great job!

        My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
        Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
        Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

        Time is always random, but event duration is always 5 seconds exactly.

        My settings:
        ups.conf

        [Back-UPS_RS_1000]
        driver=usbhid-ups
        port=auto
        ignorelb
        override.battery.charge.low = 30
        override.battery.runtime.low = 300
        

        upsmon.conf

        MONITOR Back-UPS_RS_1000 1 monuser 7504xxxxxxxxxxxx master
        SHUTDOWNCMD "/sbin/shutdown -p +0"
        POWERDOWNFLAG /etc/killpower
        NOTIFYCMD /usr/local/pkg/nut/nut_email.php
        NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
        NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
        NOTIFYFLAG LOWBATT  SYSLOG+WALL+EXEC
        NOTIFYFLAG FSD	  SYSLOG+WALL+EXEC
        NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
        NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
        NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
        NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC
        NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
        NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC
        RUN_AS_USER root
        
        

        I realize that is UPS problem but apart from that it works fine.
        Are there any NUT tweaks to avoid such behavior?

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage
          last edited by

          @pigbrother:

          dennypage, thanks for your great job!

          My old Back-UPS RS 1000 connected to pfsense working great, but once or few times a day shows the following in the log\email:
          Sep 6 10:47:16 upsmon 42126 UPS Back-UPS_RS_1000 on battery
          Sep 6 10:47:21 upsmon 42126 UPS Back-UPS_RS_1000 on line power.

          Time is always random, but event duration is always 5 seconds exactly.

          …

          I realize that is UPS problem but apart from that it works fine.
          Are there any NUT tweaks to avoid such behavior?

          You're welcome!

          The event itself may be very brief in duration, but is logged as 5 seconds due to the polling interval. There are several reasons that a momentary transfer to battery can happen depending upon the UPS.

          Some UPSs allow the variables which control transfer to be changed. The complete list of variables supported by NUT can be found here. To see what your UPS actually supports, use the upsc command. For transfer items, look for variables "input sensitivity" or "input.transfer…"

          Be careful with these. :)

          1 Reply Last reply Reply Quote 0
          • P
            pigbrother
            last edited by

            My UPS variables:

            battery.charge: 100
            battery.charge.low: 30
            battery.charge.warning: 50
            battery.date: 2001/09/25
            battery.mfr.date: 2016/10/10
            battery.runtime: 5798
            battery.runtime.low: 300
            battery.type: PbAc
            battery.voltage: 26.9
            battery.voltage.nominal: 24.0
            device.mfr: American Power Conversion
            device.model: Back-UPS RS 1000
            device.serial:xxxxxxxxxx
            device.type: ups
            driver.flag.ignorelb: enabled
            driver.name: usbhid-ups
            driver.parameter.pollfreq: 30
            driver.parameter.pollinterval: 2
            driver.parameter.port: auto
            driver.parameter.synchronous: no
            driver.version: 2.7.4
            driver.version.data: APC HID 0.96
            driver.version.internal: 0.41
            input.sensitivity: medium
            input.transfer.high: 264
            input.transfer.low: 194
            input.transfer.reason: input voltage out of range
            input.voltage: 228.0
            input.voltage.nominal: 230
            ups.beeper.status: enabled
            ups.delay.shutdown: 20
            ups.firmware: 7.g8 .I
            ups.firmware.aux: g8
            ups.load: 5
            ups.mfr: American Power Conversion
            ups.mfr.date: 2004/07/28
            ups.model: Back-UPS RS 1000
            ups.productid: 0002
            ups.realpower.nominal: 600
            ups.serial: xxxxxxxxxxxx
            ups.status: OL
            ups.test.result: No test initiated
            ups.timer.reboot: 0
            ups.timer.shutdown: -1
            ups.vendorid: 051d
            

            input.transfer.reason: input voltage out of range - probably is the event reason?

            I believe that
            input.transfer.high:264 and  input.transfer.low:194
            are just voltage threshold? Am I right?

            Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

            1 Reply Last reply Reply Quote 0
            • D
              doktornotor Banned
              last edited by

              Why would you be doing any such thing? The UPS is doing its job, just leave it alone.

              1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage
                last edited by

                @pigbrother:

                nput.transfer.reason: input voltage out of range - probably is the event reason?

                I believe that
                input.transfer.high:264 and  input.transfer.low:194
                are just voltage threshold? Am I right?

                Should  I try change input.sensitivity to low? If so - where to put it in NUT settings page?

                Yes, those are the voltage levels that will trigger transfer.

                Setting UPS variables is not something that you do in your NUT config. You set them in the UPS using the upsrw command.

                As Dok notes, the UPS is doing it's job, protecting the attached systems from excessive power fluctuations. You might want to investigate the source of the voltage problem before turning down the sensitivity. Consulting with the UPS manufacturer might be a good idea as well.

                1 Reply Last reply Reply Quote 0
                • P
                  pigbrother
                  last edited by

                  dennypaged, oktornotor, thanks for answers.
                  Agreed,  the UPS is doing it's job. I'm just trying to avoid annoying mail reports (at the night time especially).
                  Another SMART UPSes connected  to same power input do not have any complains about power conditions.

                  1 Reply Last reply Reply Quote 0
                  • S
                    SilverJS
                    last edited by

                    Denny (or whoever else wants to lend a hand!),

                    Running pfSense 2.4.1 as a firewall and router, with NUT 2.7.4_5.  I have the pfSense box, a FreeNAS server, and another FreeNAS server (Replication target) all on a CyberPower CP1000AVRLCD UPS.  (My switch is also on that, a 16-port Netgear item.)  I currently have my FreeNAS server as the master, and both the backups box and pfSense are "seeing" the master no problem.  When I pull the cord on the UPS, I get three nice e-mail notifications (one from each of the boxes), and all boxes shutdown in an orderly fashion when ordered to by the master (tested both Battery Low and On Battery, the latter with a 10 second timer in my tests).

                    The problem is : none of the boxes start back up when I plug the UPS back in!  I'm sure this is something dumb, because I'm not that knowledgeable at all - but what I CAN say is, the blue LED is lit on the UPS (but the display itself is blank).  As in, it's not shut down.  If I press it, it goes completely dark, and if I press it again, it lights up again, along with the LCD display and all - and, voila, most of the boxes start up.  That is, both FreeNAS boxes start up - the pfSense one needs to be started manually.  All three boxes have Always On setting in the BIOS for waking up after power loss.

                    Any ideas…?  I think it would make more sense to have the box doing the routing (pfSense) also being the master, but I'm not 100% sure how to configure that.  But the better question is - do I need to?  Would that fix anything?

                    Thanks in advance, and thanks also both for all your work on this package, and for the continued support you offer to us plebes on this forum! =)

                    Cheers!

                    pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                    1 Reply Last reply Reply Quote 0
                    • dennypageD
                      dennypage
                      last edited by

                      Can you clarify what you mean by “the pfSense one needs to be started manually”?

                      Traveling, so expect delayed responses…

                      Thanks.

                      1 Reply Last reply Reply Quote 0
                      • S
                        SilverJS
                        last edited by

                        Thanks for the quick reply - far from "delayed"!

                        I mean I have to physically push the power button on the pfSense box.

                        Enjoy your travels!

                        pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                        1 Reply Last reply Reply Quote 0
                        • B
                          bdf0506
                          last edited by

                          @SilverJS:

                          Thanks for the quick reply - far from "delayed"!

                          I mean I have to physically push the power button on the pfSense box.

                          Enjoy your travels!

                          This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                          I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                          1 Reply Last reply Reply Quote 0
                          • S
                            SilverJS
                            last edited by

                            @bdf0506:

                            This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                            I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side. But I don’t think this will help you out, as it sounds like the freeNAS isn’t shutting down the UPS prior to fully draining it.

                            Oh!  So the UPS NEEDS to be shut down too? Too easy - FreeNAS has a setting for that in the UPS settings.  I'll tick that box, try again and report.

                            pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                            1 Reply Last reply Reply Quote 0
                            • S
                              SilverJS
                              last edited by

                              And THERE it is!!  As soon as I instructed the UPS to shut down in my settings, everything worked perfectly.  All boxes shutdown properly, UPS shut down, and when I plugged the UPS back in, all three computers spun right back up.  The very first time I went through the whole cycle, comms with the UPS couldn't be re-established for some reason (got a flurry of e-mails from all three boxes), but I've tested it a few times since and it's always worked.  The one I'm most worried about is the pfSense box - as long as IT comes back online while I'm away, I can VPN in and restart or whatnot, and do what I need to do, and it always has, regardless of UPS comms status.  So, all seems well.

                              The one scenario I haven't tested yet is a power race, but that'll have to wait - the little one is up…=)

                              Thanks for your help!!

                              pfSense Rig : SuperMicro X8SIL-F with X3430 Xeon CPU, Shuriken cooler | 12 Gb ECC RAM | Kingston 64GB SSD | Antec VP450 P/S | Silverstone ML03B Case

                              1 Reply Last reply Reply Quote 0
                              • F
                                fr3ddie
                                last edited by

                                @bdf0506:

                                This is kind of a known issue…what should happen is that the master should shut down the UPS before the UPS fully drains. In your case, the master is your free NAS so you likely need to look there.

                                I reported this issue back in June or so. Now that 2.4 is out I believe a bug fix for the nut package for pfSense can be released to fix this on the pfSense side.

                                Hello,
                                I'd like to report I have the same issue: UPS brand is Eaton, fully supported by usbhid driver and "upsdrvctl shutdown" works perfectly on a Debian Jessie but not with pfSense NUT package.

                                I've tried to dig the init script in /usr/local/etc/rc.d/nut modifying it with no luck.

                                Can I solve it or is it a bug in the pfSense package? If it is a bug, do the maintainer of the package has any forecast about its resolution?

                                Thank you

                                1 Reply Last reply Reply Quote 0
                                • dennypageD
                                  dennypage
                                  last edited by

                                  Sorry again for the delay. Had a few real-life things come up.

                                  For a temporary work-around, please see reply #250.

                                  1 Reply Last reply Reply Quote 0
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    PRs are in, one for mainline pfSense and one for the NUT package, both of which are required to address the power kill issue. The mainline PR needs to go into a pfSense release cycle, so 2.4.2 is the earliest possible, but I expect 2.4.3 is more likely at this point.

                                    1 Reply Last reply Reply Quote 0
                                    • w0wW
                                      w0w
                                      last edited by

                                      So does the latest beta 2.4.3 have these PR's?

                                      1 Reply Last reply Reply Quote 0
                                      • dennypageD
                                        dennypage
                                        last edited by

                                        Hey w0w,

                                        I’m traveling…  I don’t recall seeing merge notifications, but I get a lot of email. You should be able to check the PRs in the main pfSense and FreeBSD repos to see if they’re still outstanding. If not I’ll check it when I get home.

                                        Thanks,
                                        Denny

                                        1 Reply Last reply Reply Quote 0
                                        • F
                                          fox983
                                          last edited by

                                          @dennypage:

                                          @endy66:

                                          But i found a Problem with the override values. As i said above, i have set the following to the additional ups.conf field in pfSense:

                                          
                                          ignorelb
                                          override.battery.charge.low = 50
                                          override.battery.runtime.low = 1200
                                          
                                          

                                          BUT These values are added on top of the ups.conf file, which means in my case, they are ignored. When i edit the ups.conf manually from ssh / Shell, and set thes override values at the bottom of the file and restart the daemon, the everything works and also the Monitoring in pfsense Show the new values. Is this a bug? Problem is, after reboot or restart the daemon, These values are not the anymore…

                                          The section entitled "Additional configuration lines for ups.conf" in Advanced settings is for global directives. The values you are trying to set are UPS specific arguments. UPS specific arguments should be entered in the section above that says "Extra Arguments to driver"

                                          Sorry this isn't clear. I'll have a look at clarifying.

                                          Hello and thanks for the great work.
                                          I'm working with pfSense and NUT  2.7.4_5 package. The "bug" still remains, if I edit (via webpage) the "Extra Arguments to driver (optional)" with

                                          ignorelb
                                          override.battery.charge.low = 30

                                          all works correctly, it adds the 2 lines AFTER

                                          [myups]
                                          driver=usbhid-ups
                                          port=auto

                                          in "/usr/local/etc/nut/ups.conf" file.
                                          But if I edit the "Additional configuration lines for ups.conf", which it seems to be more correct (http://networkupstools.org/docs/man/ups.conf.html), it adds the lines at beginning of the file, and it doesn't work.
                                          All other configuration settings (upsmon.conf, upsd.conf, upsd.users) add lines at the end of the files (checked via ssh), as it should be I think…

                                          1 Reply Last reply Reply Quote 0
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            @fox983:

                                            The "bug" still remains, if I edit (via webpage) the "Extra Arguments to driver (optional)" with

                                            ignorelb
                                            override.battery.charge.low = 30

                                            all works correctly, it adds the 2 lines AFTER

                                            [myups]
                                            driver=usbhid-ups
                                            port=auto

                                            in "/usr/local/etc/nut/ups.conf" file.
                                            But if I edit the "Additional configuration lines for ups.conf", which it seems to be more correct (http://networkupstools.org/docs/man/ups.conf.html), it adds the lines at beginning of the file, and it doesn't work.

                                            Not sure what "bug" you are referring to…

                                            The directives you are trying to use are not global directives, but are UPS specific directives.
                                            It's easy to overlook this at the beginning of the ups.conf manual page:

                                            "The file begins with global directives, and then each UPS has a section which contains a number of directives that set parameters for that UPS."

                                            In other words, the general format of ups.conf looks like this:

                                            global_directive1
                                            global_directive2
                                            global_directive3
                                            
                                            [ups1]
                                            ups_directive1
                                            ups_directive2
                                            ups_directive3
                                            
                                            [ups2]
                                            ups_directive1
                                            ups_directive2
                                            ups_directive3
                                            
                                            

                                            All global directives must appear before the first UPS section. So the "Additional configuration lines for ups.conf" in the Advanced section is only for global directives only, and anything put there will appear before the UPS section. The "Extra Arguments to driver" section is for things that apply to your UPS driver, and will be placed in the UPS section.

                                            Adding extra driver arguments is somewhat common, but the vast majority of users do not need anything under Advanced settings which is why they are hidden by default.

                                            1 Reply Last reply Reply Quote 0