    Notification: UPS ups battery is low

    Scheduled Pinned Locked Moved UPS Tools
    7 Posts 2 Posters 1.3k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • F
      fjmp24
      last edited by

      Hi,

      I receive the notification "UPS ups battery is low" and I don't understand why.
      I changed the battery without success.
      I changed UPS (EATON ELLIPSE PRO 850) to a more powerful one without success.

      Do you have an idea ? Sorry I'm newbie Thanks.

      My UPS status:

      Summary status = On line
      Runtime (H:M:S) = 0:36:47
      UPS Load = 13%
      Battery charge = 100%
      Input voltage = 225.0
      Input frequency =50.0
      

      My UPS details:

      battery.charge = 100
      battery.charge.low = 20
      battery.runtime = 2207
      battery.runtime.low = 1200
      battery.runtime.warn = 1800
      battery.type = PbAc
      device.mfr = EATON
      device.mode = Ellipse PRO 850
      device.serial = G357P05206
      device.type = ups
      driver.debug = 0
      driver.flag.allow_killpower = 0
      driver.flag.ignorelb = enabled
      driver.name = usbhid-ups
      driver.parameter.override.battery.runtime.low = 1200
      driver.parameter.override.battery.runtime.warn = 1800
      driver.parameter.override.ups.delay.shutdown = 600
      driver.parameter.pollfreq = 30
      driver.parameter.pollinterval = 2
      driver.parameter.port = auto
      driver.parameter.synchronous = auto
      driver.state = updateinfo
      driver.version = 2.8.0.1
      driver.version.data = MGE HID 1.46
      driver.version.internal = 0.52
      driver.version.usb = libusb-1.0.0 (API: 0x1000102)
      input.frequency = 50.0
      input.transfer.high = 285
      input.transfer.low = 165
      input.voltage = 225.0
      input.voltage.extended = no
      outlet.1.desc = PowerShare Outlet 1
      outlet.1.id = 2
      outlet.1.status = on
      outlet.1.switchable = no
      outlet.2.desc = PowerShare Outlet 2
      outlet.2.id = 3
      outlet.2.status = on
      outlet.2.switchable = no
      outlet.desc = Main Outlet
      outlet.id = 1
      outlet.switchable = no
      output.frequency = 50.0
      output.frequency.nominal = 50
      output.voltage = 227.0
      output.voltage.nominal = 230
      ups.beeper.status = enabled
      ups.delay.shutdown = 600
      ups.delay.start = 30
      ups.firmware = 01.18.0022
      ups.load = 13
      ups.mfr = EATON
      ups.model = Ellipse PRO 850
      ups.power = 98
      ups.power.nominal = 850
      ups.productid = ffff
      ups.realpower = 73
      ups.serial = G357P05206
      ups.status = OL
      ups.timer.shutdown = -1
      ups.timer.start = -1
      ups.vendorid = 0463
      

      My UPS Extra Arguments to driver

      ignorelb
      override.battery.runtime.warn = 1800
      override.battery.runtime.low = 1200
      override.ups.delay.shutdown = 600
      

      With the EATON ELLIPSE PRO 850, I have less notification.
      The UPS powers a Synoloy NAS and a PC (I7)

      My UPS load graphic:
      Capture d’écran du 2024-02-10 16-56-10.png

      My UPS time left graphic:
      Capture d’écran du 2024-02-10 16-56-28.png

      F dennypageD 2 Replies Last reply Reply Quote 0
      • F
        fjmp24 @fjmp24
        last edited by

        Nobody have an idea ?

        1 Reply Last reply Reply Quote 0
        • dennypageD
          dennypage @fjmp24
          last edited by

          @fjmp24 said in Notification: UPS ups battery is low:

          I receive the notification "UPS ups battery is low" and I don't understand why.
          I changed the battery without success.
          I changed UPS (EATON ELLIPSE PRO 850) to a more powerful one without success.

          You indicated that you have 3 systems powered by the UPS, however your post does not include the notification that you are referring to, nor any information about the circumstance when the notification occurs or which system it originates from.

          Btw, unless you are trying to address a very specific problem, you should not have the items in the "Extra Arguments to driver" section. Specifically, setting "ignorelb" and specifying runtimes is almost always a mistake, although a commonly made one. Likely the only one that should be there is the shutdown delay, but that only if you need more than 20 seconds to completely a shutdown on one of the systems. My expectation is that would probably only apply if you are running the Synology as a remote client to pfSense.

          F 2 Replies Last reply Reply Quote 0
          • F
            fjmp24 @dennypage
            last edited by

            This post is deleted!
            1 Reply Last reply Reply Quote 0
            • F
              fjmp24 @dennypage
              last edited by

              @dennypage Thanks I deleted override.battery.runtime.low and override.battery.runtime.warn and I don't receive notifications anymore. But I have another questions.

              1. When I cut power to my NUT, pfsense sends a shutdown when my NUT have :
              • runtime is equal to 0:01:41
              • battery charge is equal to 19%
                Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300
              1. Once my devices have been shutdown, the NUT runs for about 1 minute and displays the runtime. Then it doesn't display runtime and works about 0:02:49. I don't understand how it works.An idea ?

              Below my configuration:

              battery.charge	9
              battery.charge.low	20
              battery.runtime	355
              battery.type	PbAc
              device.mfr	EATON
              device.model	Ellipse PRO 650
              device.serial	P354L18GBN
              device.type	ups
              driver.debug	0
              driver.flag.allow_killpower	0
              driver.flag.ignorelb	enabled
              driver.name	usbhid-ups
              driver.parameter.override.ups.delay.shutdown	300
              driver.parameter.pollfreq	30
              driver.parameter.pollinterval	2
              driver.parameter.port	auto
              driver.parameter.synchronous	auto
              driver.state	quiet
              driver.version	2.8.0.1
              driver.version.data	MGE HID 1.46
              driver.version.internal	0.52
              driver.version.usb	libusb-1.0.0 (API: 0x1000102)
              input.frequency	50.0
              input.transfer.high	285
              input.transfer.low	165
              input.voltage	225.0
              input.voltage.extended	no
              outlet.1.desc	PowerShare Outlet 1
              outlet.1.id	2
              outlet.1.status	on
              outlet.1.switchable	no
              outlet.2.desc	PowerShare Outlet 2
              outlet.2.id	3
              outlet.2.status	on
              outlet.2.switchable	no
              outlet.desc	Main Outlet
              outlet.id	1
              outlet.switchable	no
              output.frequency	50.0
              output.frequency.nominal	50
              output.voltage	227.0
              output.voltage.nominal	230
              ups.beeper.status	enabled
              ups.delay.shutdown	300
              ups.delay.start	30
              ups.firmware	01.16.0020
              ups.load	7
              ups.mfr	EATON
              ups.model	Ellipse PRO 650
              ups.power	49
              ups.power.nominal	650
              ups.productid	ffff
              ups.realpower	18
              ups.serial	P354L18GBN
              ups.status	OL LB
              ups.timer.shutdown	-1
              ups.timer.start	-1
              ups.vendorid	0463
              

              Thank you for your help and sorry for my newbie's questions.

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage @fjmp24
                last edited by

                @fjmp24 said in Notification: UPS ups battery is low:

                • runtime is equal to 0:01:41
                • battery charge is equal to 19%
                  Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300

                NUT initiates a shutdown when the UPS declares that the battery is low (LB). The decision regarding a low battery is made by the UPS itself. Some UPSs have configurable LB levels, and some have fixed LB levels. If your UPS has a configurable LB level, this is configured by the battery.charge.low variable. 20% is a common default.

                When performing a shutdown, one of the last steps is for the OS (pfSense) to instruction the UPS to cut the power. After receiving that command, the UPS waits a short period of time before it actually turns off the power. The purpose of this delay is to allow the OS to complete its shutdown before power is cut. Some UPSs have configurable delays, and some have fixed delays. If your UPS has a configurable delay, this is configured by the ups.delay.shutdown variable. 20 seconds is a common default.

                F 1 Reply Last reply Reply Quote 0
                • stephenw10S stephenw10 moved this topic from pfSense Packages on
                • F
                  fjmp24 @dennypage
                  last edited by

                  @dennypage Thank you for your help

                  1 Reply Last reply Reply Quote 0