    Notification: UPS ups battery is low

    Scheduled Pinned Locked Moved UPS Tools
    16 Posts 2 Posters 3.0k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • F Offline
      fjmp24 @fjmp24
      last edited by

      Nobody have an idea ?

      1 Reply Last reply Reply Quote 0
      • dennypageD Offline
        dennypage @fjmp24
        last edited by

        @fjmp24 said in Notification: UPS ups battery is low:

        I receive the notification "UPS ups battery is low" and I don't understand why.
        I changed the battery without success.
        I changed UPS (EATON ELLIPSE PRO 850) to a more powerful one without success.

        You indicated that you have 3 systems powered by the UPS, however your post does not include the notification that you are referring to, nor any information about the circumstance when the notification occurs or which system it originates from.

        Btw, unless you are trying to address a very specific problem, you should not have the items in the "Extra Arguments to driver" section. Specifically, setting "ignorelb" and specifying runtimes is almost always a mistake, although a commonly made one. Likely the only one that should be there is the shutdown delay, but that only if you need more than 20 seconds to completely a shutdown on one of the systems. My expectation is that would probably only apply if you are running the Synology as a remote client to pfSense.

        F 2 Replies Last reply Reply Quote 0
        • F Offline
          fjmp24 @dennypage
          last edited by

          This post is deleted!
          1 Reply Last reply Reply Quote 0
          • F Offline
            fjmp24 @dennypage
            last edited by

            @dennypage Thanks I deleted override.battery.runtime.low and override.battery.runtime.warn and I don't receive notifications anymore. But I have another questions.

            1. When I cut power to my NUT, pfsense sends a shutdown when my NUT have :
            • runtime is equal to 0:01:41
            • battery charge is equal to 19%
              Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300
            1. Once my devices have been shutdown, the NUT runs for about 1 minute and displays the runtime. Then it doesn't display runtime and works about 0:02:49. I don't understand how it works.An idea ?

            Below my configuration:

            battery.charge	9
            battery.charge.low	20
            battery.runtime	355
            battery.type	PbAc
            device.mfr	EATON
            device.model	Ellipse PRO 650
            device.serial	P354L18GBN
            device.type	ups
            driver.debug	0
            driver.flag.allow_killpower	0
            driver.flag.ignorelb	enabled
            driver.name	usbhid-ups
            driver.parameter.override.ups.delay.shutdown	300
            driver.parameter.pollfreq	30
            driver.parameter.pollinterval	2
            driver.parameter.port	auto
            driver.parameter.synchronous	auto
            driver.state	quiet
            driver.version	2.8.0.1
            driver.version.data	MGE HID 1.46
            driver.version.internal	0.52
            driver.version.usb	libusb-1.0.0 (API: 0x1000102)
            input.frequency	50.0
            input.transfer.high	285
            input.transfer.low	165
            input.voltage	225.0
            input.voltage.extended	no
            outlet.1.desc	PowerShare Outlet 1
            outlet.1.id	2
            outlet.1.status	on
            outlet.1.switchable	no
            outlet.2.desc	PowerShare Outlet 2
            outlet.2.id	3
            outlet.2.status	on
            outlet.2.switchable	no
            outlet.desc	Main Outlet
            outlet.id	1
            outlet.switchable	no
            output.frequency	50.0
            output.frequency.nominal	50
            output.voltage	227.0
            output.voltage.nominal	230
            ups.beeper.status	enabled
            ups.delay.shutdown	300
            ups.delay.start	30
            ups.firmware	01.16.0020
            ups.load	7
            ups.mfr	EATON
            ups.model	Ellipse PRO 650
            ups.power	49
            ups.power.nominal	650
            ups.productid	ffff
            ups.realpower	18
            ups.serial	P354L18GBN
            ups.status	OL LB
            ups.timer.shutdown	-1
            ups.timer.start	-1
            ups.vendorid	0463
            

            Thank you for your help and sorry for my newbie's questions.

            dennypageD 1 Reply Last reply Reply Quote 0
            • dennypageD Offline
              dennypage @fjmp24
              last edited by

              @fjmp24 said in Notification: UPS ups battery is low:

              • runtime is equal to 0:01:41
              • battery charge is equal to 19%
                Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300

              NUT initiates a shutdown when the UPS declares that the battery is low (LB). The decision regarding a low battery is made by the UPS itself. Some UPSs have configurable LB levels, and some have fixed LB levels. If your UPS has a configurable LB level, this is configured by the battery.charge.low variable. 20% is a common default.

              When performing a shutdown, one of the last steps is for the OS (pfSense) to instruction the UPS to cut the power. After receiving that command, the UPS waits a short period of time before it actually turns off the power. The purpose of this delay is to allow the OS to complete its shutdown before power is cut. Some UPSs have configurable delays, and some have fixed delays. If your UPS has a configurable delay, this is configured by the ups.delay.shutdown variable. 20 seconds is a common default.

              F 1 Reply Last reply Reply Quote 0
              • stephenw10S stephenw10 moved this topic from pfSense Packages on
              • F Offline
                fjmp24 @dennypage
                last edited by

                @dennypage Thank you for your help

                F 1 Reply Last reply Reply Quote 0
                • F Offline
                  fjmp24 @fjmp24
                  last edited by

                  Hi,

                  I did a test to see if my UPS is working properly. I could see that it wasn't :-(
                  The UPS cuts the power very quickly (about 1 minute), which means, for example, my NAS doesn't have time to shut down properly.
                  My setup was working before. I updated pfSense. The problem might be coming from there.

                  UPS Detail

                  Variable 	Value
                  battery.charge	100
                  battery.charge.low	20
                  battery.runtime	1417
                  battery.type	PbAc
                  device.mfr	EATON
                  device.model	Ellipse PRO 650
                  device.serial	P354L18GBN
                  device.type	ups
                  driver.debug	0
                  driver.flag.allow_killpower	0
                  driver.flag.ignorelb	enabled
                  driver.name	usbhid-ups
                  driver.parameter.override.ups.delay.shutdown	90
                  driver.parameter.pollfreq	30
                  driver.parameter.pollinterval	2
                  driver.parameter.port	auto
                  driver.parameter.synchronous	auto
                  driver.state	updateinfo
                  driver.version	2.8.2
                  driver.version.data	MGE HID 1.46
                  driver.version.internal	0.53
                  driver.version.usb	libusb-1.0.0 (API: 0x1000102)
                  input.frequency	50.0
                  input.transfer.high	285
                  input.transfer.low	165
                  input.voltage	229.0
                  input.voltage.extended	no
                  outlet.1.desc	PowerShare Outlet 1
                  outlet.1.id	2
                  outlet.1.status	on
                  outlet.1.switchable	no
                  outlet.2.desc	PowerShare Outlet 2
                  outlet.2.id	3
                  outlet.2.status	on
                  outlet.2.switchable	no
                  outlet.desc	Main Outlet
                  outlet.id	1
                  outlet.switchable	no
                  output.frequency	50.0
                  output.frequency.nominal	50
                  output.voltage	230.0
                  output.voltage.nominal	230
                  ups.beeper.status	enabled
                  ups.delay.shutdown	90
                  ups.delay.start	30
                  ups.firmware	01.16.0020
                  ups.load	19
                  ups.mfr	EATON
                  ups.model	Ellipse PRO 650
                  ups.power	114
                  ups.power.nominal	650
                  ups.productid	ffff
                  ups.realpower	76
                  ups.serial	P354L18GBN
                  ups.status	OL
                  ups.timer.shutdown	-1
                  ups.timer.start	-1
                  ups.vendorid	0463
                  

                  Extra Arguments to driver

                  ignorelb
                  override.ups.delay.shutdown = 90
                  

                  Do you have an idea ? Sorry I'm newbie Thanks.

                  dennypageD 1 Reply Last reply Reply Quote 0
                  • dennypageD Offline
                    dennypage @fjmp24
                    last edited by

                    @fjmp24 How old is the battery? Have you done a calibration test?

                    F 1 Reply Last reply Reply Quote 0
                    • F Offline
                      fjmp24 @dennypage
                      last edited by

                      @dennypage I changed the battery this year. I don't understand : "Have you done a calibration test" ?

                      dennypageD 1 Reply Last reply Reply Quote 0
                      • dennypageD Offline
                        dennypage @fjmp24
                        last edited by

                        @fjmp24 said in Notification: UPS ups battery is low:

                        I don't understand : "Have you done a calibration test" ?

                        Most UPSs have a "battery calibration test", "runtime calibration test", etc. You are looking for a test that runs the load off of the battery (without cutting mains) to see how the battery behaves under actual load.

                        Btw, you should remove the ignorelb directive from the Extra Arguments to driver section. Unless you have a very old UPS that signals low battery whenever the UPS is on battery. You almost certainly do not have such a UPS.

                        F 1 Reply Last reply Reply Quote 0
                        • F Offline
                          fjmp24 @dennypage
                          last edited by

                          @dennypage My UPD indicate runtime: 18:21

                          dennypageD 1 Reply Last reply Reply Quote 0
                          • dennypageD Offline
                            dennypage @fjmp24
                            last edited by

                            @fjmp24 said in Notification: UPS ups battery is low:

                            @dennypage My UPD indicate runtime: 18:21

                            Yes, but that may be completely inaccurate, especially with bad batteries. That's why you run a calibration test.

                            F 1 Reply Last reply Reply Quote 0
                            • F Offline
                              fjmp24 @dennypage
                              last edited by

                              @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                              I don't understand anything :-((

                              dennypageD 1 Reply Last reply Reply Quote 0
                              • dennypageD Offline
                                dennypage @fjmp24
                                last edited by

                                @fjmp24 said in Notification: UPS ups battery is low:

                                @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                                I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                                Also, you do not have anything in the Advanced settings section, correct?

                                As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                                F 1 Reply Last reply Reply Quote 0
                                • F Offline
                                  fjmp24 @dennypage
                                  last edited by

                                  I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                                  Ok, I will test without ignorelb directive.

                                  Also, you do not have anything in the Advanced settings section, correct?

                                  Yes

                                  As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                                  I find anything I will search tomorow

                                  1 Reply Last reply Reply Quote 0