    Notification: UPS ups battery is low

    Scheduled Pinned Locked Moved UPS Tools
    16 Posts 2 Posters 3.0k Views 3 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • F Offline
      fjmp24 @dennypage
      last edited by

      @dennypage Thanks I deleted override.battery.runtime.low and override.battery.runtime.warn and I don't receive notifications anymore. But I have another questions.

      1. When I cut power to my NUT, pfsense sends a shutdown when my NUT have :
      • runtime is equal to 0:01:41
      • battery charge is equal to 19%
        Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300
      1. Once my devices have been shutdown, the NUT runs for about 1 minute and displays the runtime. Then it doesn't display runtime and works about 0:02:49. I don't understand how it works.An idea ?

      Below my configuration:

      battery.charge	9
      battery.charge.low	20
      battery.runtime	355
      battery.type	PbAc
      device.mfr	EATON
      device.model	Ellipse PRO 650
      device.serial	P354L18GBN
      device.type	ups
      driver.debug	0
      driver.flag.allow_killpower	0
      driver.flag.ignorelb	enabled
      driver.name	usbhid-ups
      driver.parameter.override.ups.delay.shutdown	300
      driver.parameter.pollfreq	30
      driver.parameter.pollinterval	2
      driver.parameter.port	auto
      driver.parameter.synchronous	auto
      driver.state	quiet
      driver.version	2.8.0.1
      driver.version.data	MGE HID 1.46
      driver.version.internal	0.52
      driver.version.usb	libusb-1.0.0 (API: 0x1000102)
      input.frequency	50.0
      input.transfer.high	285
      input.transfer.low	165
      input.voltage	225.0
      input.voltage.extended	no
      outlet.1.desc	PowerShare Outlet 1
      outlet.1.id	2
      outlet.1.status	on
      outlet.1.switchable	no
      outlet.2.desc	PowerShare Outlet 2
      outlet.2.id	3
      outlet.2.status	on
      outlet.2.switchable	no
      outlet.desc	Main Outlet
      outlet.id	1
      outlet.switchable	no
      output.frequency	50.0
      output.frequency.nominal	50
      output.voltage	227.0
      output.voltage.nominal	230
      ups.beeper.status	enabled
      ups.delay.shutdown	300
      ups.delay.start	30
      ups.firmware	01.16.0020
      ups.load	7
      ups.mfr	EATON
      ups.model	Ellipse PRO 650
      ups.power	49
      ups.power.nominal	650
      ups.productid	ffff
      ups.realpower	18
      ups.serial	P354L18GBN
      ups.status	OL LB
      ups.timer.shutdown	-1
      ups.timer.start	-1
      ups.vendorid	0463
      

      Thank you for your help and sorry for my newbie's questions.

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD Offline
        dennypage @fjmp24
        last edited by

        @fjmp24 said in Notification: UPS ups battery is low:

        • runtime is equal to 0:01:41
        • battery charge is equal to 19%
          Why doesn't it send the message when runtime is equal to 0:05:00 ? I set override.ups.delay.shutdown = 300

        NUT initiates a shutdown when the UPS declares that the battery is low (LB). The decision regarding a low battery is made by the UPS itself. Some UPSs have configurable LB levels, and some have fixed LB levels. If your UPS has a configurable LB level, this is configured by the battery.charge.low variable. 20% is a common default.

        When performing a shutdown, one of the last steps is for the OS (pfSense) to instruction the UPS to cut the power. After receiving that command, the UPS waits a short period of time before it actually turns off the power. The purpose of this delay is to allow the OS to complete its shutdown before power is cut. Some UPSs have configurable delays, and some have fixed delays. If your UPS has a configurable delay, this is configured by the ups.delay.shutdown variable. 20 seconds is a common default.

        F 1 Reply Last reply Reply Quote 0
        • stephenw10S stephenw10 moved this topic from pfSense Packages on
        • F Offline
          fjmp24 @dennypage
          last edited by

          @dennypage Thank you for your help

          F 1 Reply Last reply Reply Quote 0
          • F Offline
            fjmp24 @fjmp24
            last edited by

            Hi,

            I did a test to see if my UPS is working properly. I could see that it wasn't :-(
            The UPS cuts the power very quickly (about 1 minute), which means, for example, my NAS doesn't have time to shut down properly.
            My setup was working before. I updated pfSense. The problem might be coming from there.

            UPS Detail

            Variable 	Value
            battery.charge	100
            battery.charge.low	20
            battery.runtime	1417
            battery.type	PbAc
            device.mfr	EATON
            device.model	Ellipse PRO 650
            device.serial	P354L18GBN
            device.type	ups
            driver.debug	0
            driver.flag.allow_killpower	0
            driver.flag.ignorelb	enabled
            driver.name	usbhid-ups
            driver.parameter.override.ups.delay.shutdown	90
            driver.parameter.pollfreq	30
            driver.parameter.pollinterval	2
            driver.parameter.port	auto
            driver.parameter.synchronous	auto
            driver.state	updateinfo
            driver.version	2.8.2
            driver.version.data	MGE HID 1.46
            driver.version.internal	0.53
            driver.version.usb	libusb-1.0.0 (API: 0x1000102)
            input.frequency	50.0
            input.transfer.high	285
            input.transfer.low	165
            input.voltage	229.0
            input.voltage.extended	no
            outlet.1.desc	PowerShare Outlet 1
            outlet.1.id	2
            outlet.1.status	on
            outlet.1.switchable	no
            outlet.2.desc	PowerShare Outlet 2
            outlet.2.id	3
            outlet.2.status	on
            outlet.2.switchable	no
            outlet.desc	Main Outlet
            outlet.id	1
            outlet.switchable	no
            output.frequency	50.0
            output.frequency.nominal	50
            output.voltage	230.0
            output.voltage.nominal	230
            ups.beeper.status	enabled
            ups.delay.shutdown	90
            ups.delay.start	30
            ups.firmware	01.16.0020
            ups.load	19
            ups.mfr	EATON
            ups.model	Ellipse PRO 650
            ups.power	114
            ups.power.nominal	650
            ups.productid	ffff
            ups.realpower	76
            ups.serial	P354L18GBN
            ups.status	OL
            ups.timer.shutdown	-1
            ups.timer.start	-1
            ups.vendorid	0463
            

            Extra Arguments to driver

            ignorelb
            override.ups.delay.shutdown = 90
            

            Do you have an idea ? Sorry I'm newbie Thanks.

            dennypageD 1 Reply Last reply Reply Quote 0
            • dennypageD Offline
              dennypage @fjmp24
              last edited by

              @fjmp24 How old is the battery? Have you done a calibration test?

              F 1 Reply Last reply Reply Quote 0
              • F Offline
                fjmp24 @dennypage
                last edited by

                @dennypage I changed the battery this year. I don't understand : "Have you done a calibration test" ?

                dennypageD 1 Reply Last reply Reply Quote 0
                • dennypageD Offline
                  dennypage @fjmp24
                  last edited by

                  @fjmp24 said in Notification: UPS ups battery is low:

                  I don't understand : "Have you done a calibration test" ?

                  Most UPSs have a "battery calibration test", "runtime calibration test", etc. You are looking for a test that runs the load off of the battery (without cutting mains) to see how the battery behaves under actual load.

                  Btw, you should remove the ignorelb directive from the Extra Arguments to driver section. Unless you have a very old UPS that signals low battery whenever the UPS is on battery. You almost certainly do not have such a UPS.

                  F 1 Reply Last reply Reply Quote 0
                  • F Offline
                    fjmp24 @dennypage
                    last edited by

                    @dennypage My UPD indicate runtime: 18:21

                    dennypageD 1 Reply Last reply Reply Quote 0
                    • dennypageD Offline
                      dennypage @fjmp24
                      last edited by

                      @fjmp24 said in Notification: UPS ups battery is low:

                      @dennypage My UPD indicate runtime: 18:21

                      Yes, but that may be completely inaccurate, especially with bad batteries. That's why you run a calibration test.

                      F 1 Reply Last reply Reply Quote 0
                      • F Offline
                        fjmp24 @dennypage
                        last edited by

                        @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                        I don't understand anything :-((

                        dennypageD 1 Reply Last reply Reply Quote 0
                        • dennypageD Offline
                          dennypage @fjmp24
                          last edited by

                          @fjmp24 said in Notification: UPS ups battery is low:

                          @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                          I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                          Also, you do not have anything in the Advanced settings section, correct?

                          As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                          F 1 Reply Last reply Reply Quote 0
                          • F Offline
                            fjmp24 @dennypage
                            last edited by

                            I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                            Ok, I will test without ignorelb directive.

                            Also, you do not have anything in the Advanced settings section, correct?

                            Yes

                            As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                            I find anything I will search tomorow

                            1 Reply Last reply Reply Quote 0