      fjmp24 @fjmp24
      last edited by

      Hi,

      I did a test to see if my UPS is working properly. I could see that it wasn't :-(
      The UPS cuts the power very quickly (about 1 minute), which means, for example, my NAS doesn't have time to shut down properly.
      My setup was working before. I updated pfSense. The problem might be coming from there.

      UPS Detail

      Variable 	Value
      battery.charge	100
      battery.charge.low	20
      battery.runtime	1417
      battery.type	PbAc
      device.mfr	EATON
      device.model	Ellipse PRO 650
      device.serial	P354L18GBN
      device.type	ups
      driver.debug	0
      driver.flag.allow_killpower	0
      driver.flag.ignorelb	enabled
      driver.name	usbhid-ups
      driver.parameter.override.ups.delay.shutdown	90
      driver.parameter.pollfreq	30
      driver.parameter.pollinterval	2
      driver.parameter.port	auto
      driver.parameter.synchronous	auto
      driver.state	updateinfo
      driver.version	2.8.2
      driver.version.data	MGE HID 1.46
      driver.version.internal	0.53
      driver.version.usb	libusb-1.0.0 (API: 0x1000102)
      input.frequency	50.0
      input.transfer.high	285
      input.transfer.low	165
      input.voltage	229.0
      input.voltage.extended	no
      outlet.1.desc	PowerShare Outlet 1
      outlet.1.id	2
      outlet.1.status	on
      outlet.1.switchable	no
      outlet.2.desc	PowerShare Outlet 2
      outlet.2.id	3
      outlet.2.status	on
      outlet.2.switchable	no
      outlet.desc	Main Outlet
      outlet.id	1
      outlet.switchable	no
      output.frequency	50.0
      output.frequency.nominal	50
      output.voltage	230.0
      output.voltage.nominal	230
      ups.beeper.status	enabled
      ups.delay.shutdown	90
      ups.delay.start	30
      ups.firmware	01.16.0020
      ups.load	19
      ups.mfr	EATON
      ups.model	Ellipse PRO 650
      ups.power	114
      ups.power.nominal	650
      ups.productid	ffff
      ups.realpower	76
      ups.serial	P354L18GBN
      ups.status	OL
      ups.timer.shutdown	-1
      ups.timer.start	-1
      ups.vendorid	0463
      

      Extra Arguments to driver

      ignorelb
      override.ups.delay.shutdown = 90
      

      Do you have an idea ? Sorry I'm newbie Thanks.

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD Offline
        dennypage @fjmp24
        last edited by

        @fjmp24 How old is the battery? Have you done a calibration test?

        F 1 Reply Last reply Reply Quote 0
        • F Offline
          fjmp24 @dennypage
          last edited by

          @dennypage I changed the battery this year. I don't understand : "Have you done a calibration test" ?

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD Offline
            dennypage @fjmp24
            last edited by

            @fjmp24 said in Notification: UPS ups battery is low:

            I don't understand : "Have you done a calibration test" ?

            Most UPSs have a "battery calibration test", "runtime calibration test", etc. You are looking for a test that runs the load off of the battery (without cutting mains) to see how the battery behaves under actual load.

            Btw, you should remove the ignorelb directive from the Extra Arguments to driver section. Unless you have a very old UPS that signals low battery whenever the UPS is on battery. You almost certainly do not have such a UPS.

            F 1 Reply Last reply Reply Quote 0
            • F Offline
              fjmp24 @dennypage
              last edited by

              @dennypage My UPD indicate runtime: 18:21

              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD Offline
                dennypage @fjmp24
                last edited by

                @fjmp24 said in Notification: UPS ups battery is low:

                @dennypage My UPD indicate runtime: 18:21

                Yes, but that may be completely inaccurate, especially with bad batteries. That's why you run a calibration test.

                F 1 Reply Last reply Reply Quote 0
                • F Offline
                  fjmp24 @dennypage
                  last edited by

                  @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                  I don't understand anything :-((

                  dennypageD 1 Reply Last reply Reply Quote 0
                  • dennypageD Offline
                    dennypage @fjmp24
                    last edited by

                    @fjmp24 said in Notification: UPS ups battery is low:

                    @dennypage I can't run the test. But there's an automated system that does it every week. I tested it without override.ups.delay.shutdown. My UPS shuts down after 30 seconds, compared to 1 minute with the override.ups.delay.shutdown.

                    I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                    Also, you do not have anything in the Advanced settings section, correct?

                    As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                    F 1 Reply Last reply Reply Quote 0
                    • F Offline
                      fjmp24 @dennypage
                      last edited by

                      I didn't say you should remove the override.ups.delay.shutdown directive, I said you should remove the ignorelb directive.

                      Ok, I will test without ignorelb directive.

                      Also, you do not have anything in the Advanced settings section, correct?

                      Yes

                      As to running a calibration test, consult your UPS manual or support from the manufacturer of your UPS.

                      I find anything I will search tomorow

                      F 1 Reply Last reply Reply Quote 0
                      • F Offline
                        fjmp24 @fjmp24
                        last edited by

                        If I remove ignorelb directive, my UPS shuts down after 16 seconds

                        F dennypageD 2 Replies Last reply Reply Quote 0
                        • F Offline
                          fjmp24 @fjmp24
                          last edited by

                          My UPD do an automatic battery test regularly to warn when a replacement of the current battery needs to be carried out.

                          1 Reply Last reply Reply Quote 0
                          • dennypageD Offline
                            dennypage @fjmp24
                            last edited by

                            @fjmp24 said in Notification: UPS ups battery is low:

                            If I remove ignorelb directive, my UPS shuts down after 16 seconds

                            This means your UPS is signaling a low battery. Either your battery is bad, or your UPS is bad. Most likely battery, but you never know. I suggest reaching out to Eaton support.

                            1 Reply Last reply Reply Quote 1