ONLINE LOW BATTERY message
-
@dennypage said in ONLINE LOW BATTERY message:
self-test
Ok did a manual reeset (I belive press and hold start button and it blinkcs for 20 seconds or so).
Now the status says low battery and charging -
@netboy Back to status OL LB - How to reset BE850G - any idea ? The manual does not detail how to reset
-
@netboy Leave it on to charge for 16 hours or so before passing judgment. I just installed a new APC UPS and instructions say so.
Ted
-
@tedquade said in ONLINE LOW BATTERY message:
@netboy Leave it on to charge for 16 hours or so before passing judgment. I just installed a new APC UPS and instructions say so.
Ted
Ok patience is warranted on my part
-
Just throwing this out here. If you cannot change the battery replacement date from the console (like me!), you can download a copy of APC's PowerChute Personal Edition and use it to set the date from a Windows PC.
-
@provels said in ONLINE LOW BATTERY message:
Just throwing this out here. If you cannot change the battery replacement date from the console (like me!), you can download a copy of APC's PowerChute Personal Edition and use it to set the date from a Windows PC.
I have UPS attached to pfsense netgatge 2100 - I am aware of powerchute software - the only problem is I have to take a WINDOWS PC / LAPTOP and then install the software and connect to the battery. I might do this if 16 hours have passed. Any way thanks for the suggestion
-
@netboy said in ONLINE LOW BATTERY message:
How to reset BE850G - any idea ? The manual does not detail how to reset
From link I've posted above. In case you didn't read that or missed:
instructions from APC's e-mail support:
- Disconnect any attached load.
- Turn off the UPS
- Unplug the UPS from the wall socket.
- Disconnect the UPS internal battery.
- Push and hold the "On" button on the UPS for 5 seconds.
- Reconnect internal battery.
- Plug UPS in to known good power source.
- Turn the UPS ON.
-
@w0w said in ONLINE LOW BATTERY message:
@netboy said in ONLINE LOW BATTERY message:
How to reset BE850G - any idea ? The manual does not detail how to reset
From link I've posted above. In case you didn't read that or missed:
instructions from APC's e-mail support:
- Disconnect any attached load.
- Turn off the UPS
- Unplug the UPS from the wall socket.
- Disconnect the UPS internal battery.
- Push and hold the "On" button on the UPS for 5 seconds.
- Reconnect internal battery.
- Plug UPS in to known good power source.
- Turn the UPS ON.
I am aware of the above instructions for Easy-UPS - unfortunately I guess this does not apply to BE750G unless somebody says I am wrong!
-
@netboy
It's the same for the back series UPS. -
@w0w Ok shall try it
-
@netboy The procedure did not work
-
-
@w0w No... that is my next milestone
-
@dennypage This is what worked for APC battery ES 750G FYI
-
Installed powerchute software in windows machine. Connected the APC
-
Ran self test
-
Changed battery date (battery date not possible to change using NUT command line upsrw)
-
-
@netboy Your UPS battery fun caused me to take a look at the array of UPS devices I have and found the unit on my wife computer had a dodgy battery (aborted self test). Installed new battery and it now passes.
I have two others that I still need to dig into.
Thanks for prompting me to look at my own stuff!
Ted
-
@tedquade said in ONLINE LOW BATTERY message:
@netboy Your UPS battery fun caused me to take a look at the array of UPS devices I have and found the unit on my wife computer had a dodgy battery (aborted self test). Installed new battery and it now passes.
I have two others that I still need to dig into.
Thanks for prompting me to look at my own stuff!
Ted
I wanted to document my experience so that it will help others if they encounter similar problems. Many folks in this forum helped me a lot and I am very thankful.
-
@netboy Glad you got it sorted.