    • JonathanLeeJ
      JonathanLee @dennypage
      last edited by

      @dennypage I show nothing for logs they already rotated for me. :(

      Make sure to upvote

      1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @shaffergr
        last edited by

        @shaffergr I don't think it will be necessary, but if it doesn't generate a core file, add this:

        sysctl kern.sugid_coredump=1
        
        S 1 Reply Last reply Reply Quote 1
        • L
          lcbbcl @dennypage
          last edited by lcbbcl

          @dennypage
          Well i just delete, reboot and reinstall nut not the operating system. Weird that i don't know why after remove nut i still had the settings when i did reinstall.
          Feb 19 20:34:08 zid upsd[20330]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 19 20:34:17 zid upsd[42475]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 19 20:34:54 zid upsd[15895]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 19 20:35:00 zid upsd[30880]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 19 20:38:11 zid upsd[36439]: Can't connect to UPS [ups] (usbhid-ups-ups): No such file or directory
          Feb 19 20:38:30 zid upsd[79042]: Can't connect to UPS [ups] (usbhid-ups-ups): No such file or directory
          Feb 19 20:39:12 zid upsd[51078]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:23:30 zid upsd[46012]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:28:30 zid upsd[46012]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:45:54 zid upsd[12751]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:49:57 zid upsd[82271]: Can't connect to UPS [ups] (usbhid-ups-ups): No such file or directory
          Feb 20 20:50:51 zid upsd[64233]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:52:27 zid upsd[415]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:52:36 zid upsd[85556]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 20:52:39 zid upsd[59802]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:08:57 zid upsd[92079]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:16:05 zid upsd[94197]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:19:28 zid upsd[60128]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:20:08 zid upsd[45874]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:20:11 zid upsd[73849]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:22:57 zid upsd[87326]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:23:07 zid upsd[93669]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:23:10 zid upsd[66247]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          Feb 20 22:24:27 zid upsd[70162]: Can't connect to UPS [APC] (usbhid-ups-APC): No such file or directory
          [23.01-RELEASE][admin@]/var/log: usbconfig
          ugen0.1: <Intel XHCI root HUB> at usbus0, cfg=0 md=HOST spd=SUPER (5.0Gbps) pwr=SAVE (0mA)
          ugen0.2: <American Power Conversion Smart-UPS C 1000 FW:UPS 12.0 / ID1005> at usbus0, cfg=0 md=HOST spd=FULL (12Mbps) pwr=ON (2mA)

          dennypageD 1 Reply Last reply Reply Quote 1
          • dennypageD
            dennypage @lcbbcl
            last edited by

            @lcbbcl I need the messages from the usbhid-ups process. The messages from upsd are expected when usbhid-ups isn't running.

            If you don't have any log entries from usbhid-ups, then please post your ups settings (Services / UPS / Settings)

            I'll be away for a bit... but will look at it when I'm back.

            L 1 Reply Last reply Reply Quote 1
            • L
              lcbbcl @dennypage
              last edited by

              @dennypage
              I have no msg/error from usbhid-ups
              Screenshot_20230220_223805.png

              dennypageD 2 Replies Last reply Reply Quote 1
              • dennypageD
                dennypage @lcbbcl
                last edited by

                @lcbbcl If you re-save your ups settings, it will restart the processes and you should be able to find usbhid entries.

                1 Reply Last reply Reply Quote 1
                • S
                  shaffergr @dennypage
                  last edited by

                  @dennypage

                  16:07 removed interruptonly and saved settings

                  On console:

                  [23.01-RELEASE][X@Y]/root: sysctl kern.corefile=/var/tmp/%N.core
                  kern.corefile: /root/%N.core -> /var/tmp/%N.core

                  Broadcast Message from root@gw.fubr.org
                  (no tty) at 16:07 EST...

                  Communications with UPS CyberPower lost

                  Broadcast Message from root@gw.fubr.org
                  (no tty) at 16:07 EST...

                  Communications with UPS CyberPower established

                  Feb 20 16:07:40 Y php-fpm[83664]: /nut_settings.php: Stopping service nut
                  Feb 20 16:07:40 Y upsmon[66045]: Signal 15: exiting
                  Feb 20 16:07:40 Y upsd[97704]: User local-monitor@::1 logged out from UPS [CyberPower]
                  Feb 20 16:07:40 Y upsd[97704]: mainloop: Interrupted system call
                  Feb 20 16:07:40 Y upsd[97704]: Signal 15: exiting
                  Feb 20 16:07:40 Y usbhid-ups[82519]: Signal 15: exiting
                  Feb 20 16:07:40 Y php-fpm[83664]: /nut_settings.php: Starting service nut
                  Feb 20 16:07:40 Y upsmon[7684]: Startup successful
                  Feb 20 16:07:40 Y upsmon[7684]: UPS [CyberPower]: connect failed: Connection failure: Connection refused
                  Feb 20 16:07:40 Y upsmon[7684]: Communications with UPS CyberPower lost
                  Feb 20 16:07:40 Y usbhid-ups[8439]: Startup successful
                  Feb 20 16:07:41 Y upsd[8857]: listening on 192.168.11.1 port 3493
                  Feb 20 16:07:41 Y upsd[8857]: listening on ::1 port 3493
                  Feb 20 16:07:41 Y upsd[8857]: listening on 127.0.0.1 port 3493
                  Feb 20 16:07:41 Y upsd[8857]: Connected to UPS [CyberPower]: usbhid-ups-CyberPower
                  Feb 20 16:07:41 Y upsd[8857]: Startup successful
                  Feb 20 16:07:45 Y upsd[8857]: User local-monitor@::1 logged into UPS [CyberPower]
                  Feb 20 16:07:45 Y upsmon[7684]: Communications with UPS CyberPower established

                  Feb 20 17:57:45 Y upsd[8857]: Can't connect to UPS [CyberPower] (usbhid-ups-CyberPower): Connection refused
                  Feb 20 17:57:45 Y kernel: pid 8439 (usbhid-ups), jid 0, uid 66: exited on signal 10 (core dumped)
                  Feb 20 17:57:48 Y upsmon[7684]: Poll UPS [CyberPower] failed - Driver not connected
                  Feb 20 17:57:48 Y upsmon[7684]: Communications with UPS CyberPower lost
                  Feb 20 17:57:53 Y upsmon[7684]: Poll UPS [CyberPower] failed - Driver not connected
                  Feb 20 17:57:58 Y upsmon[7684]: Poll UPS [CyberPower] failed - Driver not connected

                  Also set about 10 minutes later: sysctl kern.sugid_coredump=1

                  I have a core dump in /var/tmp/usbhid-ups.core

                  What do you want me to do with it?

                  dennypageD 1 Reply Last reply Reply Quote 1
                  • dennypageD
                    dennypage @shaffergr
                    last edited by

                    @shaffergr said in NUT package:

                    I have a core dump in /var/tmp/usbhid-ups.core
                    What do you want me to do with it?

                    Perfect! Compress and email it to me. Thanks!

                    S 1 Reply Last reply Reply Quote 1
                    • S
                      shaffergr @dennypage
                      last edited by

                      @dennypage

                      email address?

                      dennypageD 1 Reply Last reply Reply Quote 1
                      • dennypageD
                        dennypage @shaffergr
                        last edited by

                        @shaffergr Sent in chat. Look for a quote bubble next to the pic of your icon at the top. Should have an alert there.

                        S 1 Reply Last reply Reply Quote 1
                        • S
                          shaffergr @dennypage
                          last edited by

                          @dennypage

                          sent via email. Let me know if you don't get it.

                          1 Reply Last reply Reply Quote 1
                          • dennypageD
                            dennypage @lcbbcl
                            last edited by dennypage

                            @lcbbcl I believe I have found what is causing the issue you are experiencing. To correct the issue will require an update to the pfSense nut package as well as updating the underlying FreeBSD nut package used by pfSense. It will take some time.

                            In the interim, you can address the issue by adding the line "user=root" to "Additional configuration lines for ups.conf" under Advanced settings.

                            L keyserK X 3 Replies Last reply Reply Quote 4
                            • L
                              lcbbcl @dennypage
                              last edited by

                              @dennypage
                              Thank you, now is working

                              1 Reply Last reply Reply Quote 1
                              • keyserK
                                keyser Rebel Alliance @dennypage
                                last edited by

                                @dennypage said in NUT package:

                                @lcbbcl I believe I have found what is causing the issue you are experiencing. To correct the issue will require an update to the pfSense nut package as well as updating the underlying FreeBSD nut package used by pfSense. It will take some time.

                                In the interim, you can address the issue by adding the line "user=root" to "Additional configuration lines for ups.conf" under Advanced settings.

                                Your hard and dedicated work on this package is an inspiration. Thank you for the effort :-)

                                I assume it was an access permissions issue since running it as root solves the issue? Can you comment on why it only happens for some UPS models?

                                Love the no fuss of using the official appliances :-)

                                dennypageD 1 Reply Last reply Reply Quote 1
                                • dennypageD
                                  dennypage @keyser
                                  last edited by

                                  @keyser said in NUT package:

                                  I assume it was an access permissions issue since running it as root solves the issue? Can you comment on why it only happens for some UPS models?

                                  Yes, it's a permissions issue. I am hoping it can be addressed in the FreeBSD nut package (or perhaps in kernel config?), but if not I will have to add the user=root to the config for all usb devices.

                                  What models it happens on are dependent upon the quirks defined for that device. If you want to jump down the rabbit hole, run "usbconfig dump_quirk_names" and "usbconfig dump_device_quirks".

                                  NB: This is not related to the signal 10/11 issue being experienced with CyberPower units.

                                  1 Reply Last reply Reply Quote 3
                                  • 4
                                    4o4rh
                                    last edited by 4o4rh

                                    I see the github packages have been moved to

                                    https://github.com/pfsense/FreeBSD-ports

                                    But i don't see the nut package in there.

                                    Where is the code for nut, or is it closed source now?

                                    In the upsmon configuration, can we please add two config boxes for the below files.

                                    /usr/local/etc/nut/upssched.conf with permission 644
                                    /usr/local/bin/upssched-cmd with permission 755

                                    To use the scheduler to trigger events from upsmon. these files need to be configurable.
                                    Also, there should be a note for using them, the notification box has to be disabled.
                                    here is a sample of working files

                                    upsmon

                                    # upsmon.conf - Configuration for network UPS Tools upsmon
                                    # set the path to the notify command processor !!! the UPS notifications option must be unchecked !!! 
                                    NOTIFYCMD /usr/local/sbin/upssched
                                    
                                    # Poll the UPS every 60 seconds.
                                    POLLFREQ 60
                                    
                                    # Wait this many seconds for "Notify Shutdown" messages from slaves
                                    POLLFREQALERT 30
                                    
                                    # time UPS may go missing before being declared dead
                                    DEADTIME 600
                                    
                                    # Warn every 12 hours if battery needs to be replaced
                                    RBWARNTIME 43200
                                    
                                    # Warn every 5 minutes, if UPS is unreachable
                                    NOCOMMWARNTIME 300
                                    
                                    # Messages for the events %s will be replaced with the UPS system identifier in question
                                    NOTIFYMSG ONLINE   "UPS %s on line power"
                                    NOTIFYMSG ONBATT   "UPS %s on battery"
                                    NOTIFYMSG LOWBATT  "UPS %s battery is low"
                                    NOTIFYMSG FSD      "UPS %s forced shutdown in progress"
                                    NOTIFYMSG COMMOK   "UPS %s communications (re-)established"
                                    NOTIFYMSG COMMBAD  "UPS %s communications lost"
                                    NOTIFYMSG SHUTDOWN "Auto logout and shutdown proceeding"
                                    NOTIFYMSG REPLBATT "UPS %s battery needs to be replaced"
                                    NOTIFYMSG NOCOMM   "UPS %s is not reachable"
                                    NOTIFYMSG NOPARENT "upsmon parent process died, shutdown impossible"
                                    
                                    # Change behavior of upsmon on certain events.
                                    # Possible values for the flags:
                                    # SYSLOG - Write the message in the syslog
                                    # WALL - Write the message to all users on the system
                                    # EXEC - Execute NOTIFYCMD (see above, in our case see upssched.conf) with the message
                                    # IGNORE - Don't do anything
                                    # If you use IGNORE, don't use any other flags on the same line.
                                    # NOTIFYFLAG <notify type> <flag>[+<flag>][+<flag>] ...
                                    NOTIFYFLAG ONLINE   SYSLOG
                                    NOTIFYFLAG ONBATT   SYSLOG
                                    NOTIFYFLAG LOWBATT  SYSLOG
                                    NOTIFYFLAG FSD      SYSLOG+WALL+EXEC
                                    NOTIFYFLAG COMMOK   SYSLOG+EXEC
                                    NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                                    NOTIFYFLAG SHUTDOWN SYSLOG
                                    NOTIFYFLAG REPLBATT SYSLOG
                                    NOTIFYFLAG NOCOMM   SYSLOG
                                    NOTIFYFLAG NOPARENT SYSLOG
                                    

                                    upssched

                                    # Network UPS Tools - upssched.conf file
                                    
                                    #Command script to run
                                    CMDSCRIPT /usr/local/bin/upssched-cmd
                                    
                                    # command for pipe and lock files
                                    PIPEFN /var/db/nut/upssched.pipe
                                    LOCKFN /var/db/nut/upssched.lock
                                    
                                    # ============================================================================
                                    # AT <notifytype> <upsname> <command>
                                    # Define a handler for a specific event <notifytype> on UPS <upsname>.
                                    # <upsname> can be the special value * to apply this handler to every
                                    # possible value of <upsname>.
                                    # Run the command <command> via your CMDSCRIPT when it happens.
                                    # Note that any AT that matches both the <notifytype> and the <upsname>
                                    # for the current event will be used.
                                    # ============================================================================
                                    # Possible AT commands
                                    # - START-TIMER <timername> <interval>
                                    #   Start a timer called <timername> that will trigger after <interval>
                                    #   seconds, calling your CMDSCRIPT with <timername> as the first
                                    #   argument.
                                    #   Example:
                                    #   Start a timer that'll execute when any UPS (*) has been gone 10 seconds
                                    # AT COMMBAD * START-TIMER COMMBAD 1800
                                    #   -----------------------------------------------------------------------
                                    # - CANCEL-TIMER <timername> [cmd]
                                    #   Cancel a running timer called <timername>, if possible. If the timer
                                    #   has passed then pass the optional argument <cmd> to CMDSCRIPT.
                                    #   Example:
                                    #   If a specific UPS (myups@localhost) comes back online, then stop the
                                    #   timer before it triggers
                                    # AT COMMOK * CANCEL-TIMER COMMBAD COMMOK
                                    #   -----------------------------------------------------------------------
                                    # - EXECUTE <command>
                                    #   Immediately pass <command> as an argument to CMDSCRIPT.
                                    #
                                    #   Example:
                                    #   If any UPS (*) reverts to utility power, then execute
                                    #   'ups-back-on-line' via CMDSCRIPT.
                                    
                                    # UPS is online in syslog. we don't need action when no UPS connected
                                    # AT ONLINE * CANCEL-TIMER onbatt 
                                    
                                    # UPS on battery in syslog. badcomms will shutdown for us
                                    # AT ONBATT * START-TIMER onbatt 300
                                    
                                    # UPS low battery is syslog. we should badcomms to shutdown
                                    # AT LOWBATT * START-TIMER lowbatt 300
                                    
                                    # UPS forced shutdown by master or upsmon
                                    AT FSD * EXECUTE powerdown
                                    
                                    # UPS communications restored
                                    AT COMMOK * CANCEL-TIMER badcomms
                                    
                                    # UPS communications failed. 
                                    AT COMMBAD * START-TIMER badcomms 600
                                    
                                    # UPS shutdown recorded in syslog
                                    # AT SHUTDOWN * EXECUTE powerdown
                                    
                                    # UPS needs replacement battery. Info in syslog
                                    # AT REPLBATT * EXECUTE replbatt
                                    
                                    # UPS is not reachable. Relying on deadtime for shutdown
                                    AT NOCOMM * EXECUTE commbad
                                    
                                    # UPSMON parent process has died - shutdown not possible.
                                    # AT NOPARENT * EXECUTE noparent
                                    

                                    upssched-cmd

                                    #! /bin/sh
                                    #
                                    # This script should be called by upssched via the CMDSCRIPT directive.
                                    #
                                    # Here is a quick example to show how to handle a bunch of possible
                                    # timer names with the help of the case structure.
                                    #
                                    # This script may be replaced with another program without harm.
                                    #
                                    # The first argument passed to your CMDSCRIPT is the name of the timer
                                    # from your AT lines.
                                    #
                                    # case $1 in
                                    #	upsgone)
                                    #		logger -t upssched-cmd "The UPS has been gone for awhile"
                                    #		;;
                                    #	*)
                                    #		logger -t upssched-cmd "Unrecognized command: $1"
                                    #		;;
                                    # esac
                                    
                                    case $1 in
                                       onbatt)
                                          # function not needed as we only use syslog
                                          logger -t upssched-cmd "UPS is running on battery."
                                       ;;
                                       
                                       online)
                                          # function not needed as we only use syslog
                                          logger -t upssched-cmd "UPS back online."
                                       ;;
                                    
                                       lowbatt)
                                          # function not needed as we only use syslog
                                          logger -t upssched-cmd "UPS has low battery"
                                          # we rely on badcomms when no UPS connected
                                          # /usr/local/sbin/upsmon -c fsd
                                       ;;
                                    
                                       badcomms)
                                          logger -t upssched-cmd "UPS offline too long, forced shutdown."
                                          /usr/local/sbin/upsmon -c fsd
                                       ;;
                                    
                                       commok)
                                          # function not needed as we only use syslog
                                          logger -t upssched-cmd "UPS communications restored."
                                       ;;
                                       
                                       powerdown)
                                          logger -t upssched-cmd "UPS forced shutdown started"
                                          /usr/local/sbin/upsmon -c fsd
                                       ;;
                                    
                                       replbatt)
                                          # function not needed as we only use syslog
                                          logger -t upssched-cmd "UPS battery needs replacing"
                                       ;;
                                    
                                       noparent)
                                          # function not needed as we only use syslog
                                          logger -t upssched-cmd "upsmon parent process died. Shutdown not possible"
                                       ;;
                                    
                                       *)
                                          logger -t upssched-cmd "No code defined for command: $1"
                                       ;;
                                    esac
                                    
                                    dennypageD 1 Reply Last reply Reply Quote 1
                                    • dennypageD
                                      dennypage @4o4rh
                                      last edited by

                                      @gwaitsi It hasn't moved since I wrote it. sysutils/pfSense-pkg-nut.

                                      1 Reply Last reply Reply Quote 1
                                      • X
                                        xavier1 @dennypage
                                        last edited by

                                        This solved my issue. Everything is working great. Thank you :)

                                        @dennypage said in NUT package:

                                        @lcbbcl I believe I have found what is causing the issue you are experiencing. To correct the issue will require an update to the pfSense nut package as well as updating the underlying FreeBSD nut package used by pfSense. It will take some time.

                                        In the interim, you can address the issue by adding the line "user=root" to "Additional configuration lines for ups.conf" under Advanced settings.

                                        1 Reply Last reply Reply Quote 1
                                        • dennypageD
                                          dennypage
                                          last edited by

                                          @lcbbcl, @xavier1 Would you do me a favor and post the result of

                                          usbconfig -v
                                          

                                          from your systems please? Thanks.

                                          L 1 Reply Last reply Reply Quote 1
                                          • L
                                            lcbbcl @dennypage
                                            last edited by

                                            @dennypage
                                            Here it is

                                            usbconfig -v
                                            ugen0.1: <Intel XHCI root HUB> at usbus0, cfg=0 md=HOST spd=SUPER (5.0Gbps) pwr=SAVE (0mA)
                                            ugen0.1.0: uhub0: <Intel XHCI root HUB, class 9/0, rev 3.00/1.00, addr 1>
                                            
                                             bLength = 0x0012 
                                             bDescriptorType = 0x0001 
                                             bcdUSB = 0x0300 
                                             bDeviceClass = 0x0009  <HUB>
                                             bDeviceSubClass = 0x0000 
                                             bDeviceProtocol = 0x0003 
                                             bMaxPacketSize0 = 0x0009 
                                             idVendor = 0x0000 
                                             idProduct = 0x0000 
                                             bcdDevice = 0x0100 
                                             iManufacturer = 0x0001  <Intel>
                                             iProduct = 0x0002  <XHCI root HUB>
                                             iSerialNumber = 0x0000  <no string>
                                             bNumConfigurations = 0x0001 
                                            
                                            
                                            Configuration index 0
                                            
                                               bLength = 0x0009 
                                               bDescriptorType = 0x0002 
                                               wTotalLength = 0x001f 
                                               bNumInterfaces = 0x0001 
                                               bConfigurationValue = 0x0001 
                                               iConfiguration = 0x0000  <no string>
                                               bmAttributes = 0x0040 
                                               bMaxPower = 0x0000 
                                            
                                               Interface 0
                                                 bLength = 0x0009 
                                                 bDescriptorType = 0x0004 
                                                 bInterfaceNumber = 0x0000 
                                                 bAlternateSetting = 0x0000 
                                                 bNumEndpoints = 0x0001 
                                                 bInterfaceClass = 0x0009  <HUB>
                                                 bInterfaceSubClass = 0x0000 
                                                 bInterfaceProtocol = 0x0000 
                                                 iInterface = 0x0000  <no string>
                                            
                                                Endpoint 0
                                                   bLength = 0x0007 
                                                   bDescriptorType = 0x0005 
                                                   bEndpointAddress = 0x0081  <IN>
                                                   bmAttributes = 0x0003  <INTERRUPT>
                                                   wMaxPacketSize = 0x0002 
                                                   bInterval = 0x00ff 
                                                   bRefresh = 0x0000 
                                                   bSynchAddress = 0x0000 
                                            
                                                 Additional Descriptor
                                            
                                                 bLength = 0x06
                                                 bDescriptorType = 0x30
                                                 bDescriptorSubType = 0x00
                                                  RAW dump: 
                                                  0x00 | 0x06, 0x30, 0x00, 0x00, 0x00, 0x00
                                            
                                            
                                            
                                            
                                            ugen0.2: <American Power Conversion Smart-UPS C 1000 FW:UPS 12.0 / ID1005> at usbus0, cfg=0 md=HOST spd=FULL (12Mbps) pwr=ON (2mA)
                                            
                                             bLength = 0x0012 
                                             bDescriptorType = 0x0001 
                                             bcdUSB = 0x0200 
                                             bDeviceClass = 0x0000  <Probed by interface class>
                                             bDeviceSubClass = 0x0000 
                                             bDeviceProtocol = 0x0000 
                                             bMaxPacketSize0 = 0x0040 
                                             idVendor = 0x051d 
                                             idProduct = 0x0003 
                                             bcdDevice = 0x0106 
                                             iManufacturer = 0x0001  <American Power Conversion >
                                             iProduct = 0x0002  <Smart-UPS C 1000 FW:UPS 12.0 / ID=1005>
                                             iSerialNumber = 0x0003  <AS1506222288  >
                                             bNumConfigurations = 0x0001 
                                            
                                            
                                            Configuration index 0
                                            
                                               bLength = 0x0009 
                                               bDescriptorType = 0x0002 
                                               wTotalLength = 0x0029 
                                               bNumInterfaces = 0x0001 
                                               bConfigurationValue = 0x0001 
                                               iConfiguration = 0x0000  <no string>
                                               bmAttributes = 0x00e0 
                                               bMaxPower = 0x0001 
                                            
                                               Interface 0
                                                 bLength = 0x0009 
                                                 bDescriptorType = 0x0004 
                                                 bInterfaceNumber = 0x0000 
                                                 bAlternateSetting = 0x0000 
                                                 bNumEndpoints = 0x0002 
                                                 bInterfaceClass = 0x0003  <HID device>
                                                 bInterfaceSubClass = 0x0000 
                                                 bInterfaceProtocol = 0x0000 
                                                 iInterface = 0x0000  <no string>
                                            
                                                 Additional Descriptor
                                            
                                                 bLength = 0x09
                                                 bDescriptorType = 0x21
                                                 bDescriptorSubType = 0x00
                                                  RAW dump: 
                                                  0x00 | 0x09, 0x21, 0x00, 0x01, 0x21, 0x01, 0x22, 0x03, 
                                                  0x08 | 0x02
                                            
                                                Endpoint 0
                                                   bLength = 0x0007 
                                                   bDescriptorType = 0x0005 
                                                   bEndpointAddress = 0x0081  <IN>
                                                   bmAttributes = 0x0003  <INTERRUPT>
                                                   wMaxPacketSize = 0x0040 
                                                   bInterval = 0x0014 
                                                   bRefresh = 0x0000 
                                                   bSynchAddress = 0x0000 
                                            
                                                Endpoint 1
                                                   bLength = 0x0007 
                                                   bDescriptorType = 0x0005 
                                                   bEndpointAddress = 0x0001  <OUT>
                                                   bmAttributes = 0x0003  <INTERRUPT>
                                                   wMaxPacketSize = 0x0040 
                                                   bInterval = 0x000a 
                                                   bRefresh = 0x0000 
                                                   bSynchAddress = 0x0000 
                                            
                                            1 Reply Last reply Reply Quote 2